Home  5  Books  5  GBEzine  5  News  5  HelpDesk  5  Register  5  GreenBuilding.co.uk
Not signed in (Sign In)

Categories



Green Building Bible, Fourth Edition
Green Building Bible, fourth edition (both books)
These two books are the perfect starting place to help you get to grips with one of the most vitally important aspects of our society - our homes and living environment.

PLEASE NOTE: A download link for Volume 1 will be sent to you by email and Volume 2 will be sent to you by post as a book.

Buy individually or both books together. Delivery is free!


powered by Surfing Waves




Vanilla 1.0.3 is a product of Lussumo. More Information: Documentation, Community Support.

Welcome to new Forum Visitors
Join the forum now and benefit from discussions with thousands of other green building fans and discounts on Green Building Press publications: Apply now.

The AECB accepts no responsibility or liability for any errors or omissions in the content of this site. Views given in posts are not necessarily the views of the AECB.



    • CommentAuthorRoobarb
    • CommentTimeNov 3rd 2008
     
    The loft in our new home is insulated with glass fibre blanket. Some of this insulation covers the electrical cables running through the loft, but our Reader's Digest DIY Manual claims that you should avoid covering cables with insulation "so that there is no danger of them becoming overheated". Is this correct? It seems a bit odd, because I can't see why keeping the cables warm would be dangerous. Surely electrical cables can withstand temperatures much higher than you'd get in a loft, even in summer?

    Also, on the subject of loft insulation, is it a must to have either foil-backed insulation lying on a plasterboard ceiling or a separate foil layer + insulation? At the moment ours in just unbacked insulation lying directly on the plasterboard, but I've read that this can cause condensation to form in the insulation.

    Thanks
    Simon
    • CommentAuthortony
    • CommentTimeNov 3rd 2008
     
    They are technically correct -- in practice there isnt a problem

    So long as you have at least 300mm of insulation you will be ok
    • CommentAuthorBluemoon
    • CommentTimeNov 3rd 2008
     
    A good reason for not covering cables with insulation is, you can find them afterwards. The contractors who put the glassfibre blanket in my loft told me that they are told to cover all except for the shower and cooker cables.
    • CommentAuthorjamesingram
    • CommentTimeNov 3rd 2008 edited
     
    The current carrying capacity of a cable is related to its cross sectional area (1mm2 , 2.5mm2 etc) at a set range of temperature
    if this temperature is likely to remain around the higher end of the scale ( as its covered in insulation) then this needs to be taken into account
    when designing an electricial installation and choosing cable sizes
    the installation method of the cable changes the rated current carrying capacity of each cable
    If a cable is say clipped along a joist and surround by free area its rated to carry a higher current than say one covered in 100mm insulation
    for example a 2.5mm2 twin and earth copper PVC cable clipped direct would be rated up to 27 amps. Above a plasterboard ceiling covered by not more than 100mm it would be rated at 21 amps
    If then insulation >100mm then it drop to 17amps. which if in a ring circuit ( which is 2, 2.5mm2) protected by a 32 amp fuse is fine
    If on a radial (single 2.5mm2) which should be on a 16 amp fuse, again its fine
    This by the book
    As long as your electrics is up to standard and you've a newer fuse board it shouldn 't be a problem

    cheers Jim
    • CommentAuthorwookey
    • CommentTimeNov 4th 2008
     
    Like the man said. In practice unless you have a bungalow there will normally only be lights wiring, and maybe a bathroom shower cable, in the loft. The light wiring is low current and it will still be in spec even under huge piles of insulation. The shower cable can be very high current and may be specced such that it needs to be kept above the insulation. So Bluemoon's loft-fitters rule of thumb will generally be good enough in practice. If you get the wiring regs it has nice tables in it which make it easy to check (in combination with knowing which circuit is which and what the fusebox/CU fuse/breaker for the circuit is, and which size cable has been fitted).

    The potential high temps come from the power flowing in the cable (especially under fault conditions), not the ambient temps.
    • CommentAuthorRoobarb
    • CommentTimeNov 4th 2008
     
    Thanks, I hadn't considered the effect of temperature on current carrying capacity.

    Any thoughts on my second question, i.e. foil backing for insulation? I'm leaning towards putting foil under the insulation, but I don't know if this is a waste of time. I hate going in the loft ;-)

    Thanks
    Simon
    • CommentAuthorwookey
    • CommentTimeNov 4th 2008
     
    Ah, foils in insulation is an area few dare to tread. Go read the 300post multifoils thread :-)

    For lofts no-one bothers in retro-fit. Just add more fluff/insulation of whatever sort you prefer. There might be marginal benfit, but it's certainly not 'a must'.
    • CommentAuthorDaveK
    • CommentTimeNov 5th 2008
     
    Never ever use 'rule of thumb' when deciding current capacity ratings of cables. Calculations must be carried out to determine if the cable used is of sufficient size to carry the required load (this will vary if the cable is covered in insulation or not, buried in walls, run through wall penetrations, run along side other circuits etc). In practice there may not be a problem, however complying with the 17th edition of the wiring regs is a legal requirement. If you are in a new build you should take some comfort in the fact that the installation should meet current regulations, if not, your developer has broken the law.

    If you want to satisfy yourself that everything is ok, there are plenty of books to be found on amazon that give guidance to complying with the regulations and provide examples on how to calculate current carrying capacities of cables. Books providing guidance to complying with the regs are usually cheaper to buy than the regs themselves and much easier to understand.
    • CommentAuthortony
    • CommentTimeNov 5th 2008
     
    How come everyone uses 2.5 for ring mains when even running it down a new wall insulated to building regs and plastering it in doesn't comply?
  1.  
    [edited a few times to try and get this brain-dead forum software to display quotes AND hyperlinks that work. No such luck - the authors deserve a thorough kicking :devil:]

    Posted By: RoobarbThe loft in our new home is insulated with glass fibre blanket. Some of this insulation covers the electrical cables running through the loft, but our Reader's Digest DIY Manual claims that you should avoid covering cables with insulation "so that there is no danger of them becoming overheated". Is this correct? It seems a bit odd, because I can't see why keeping the cables warm would be dangerous. Surely electrical cables can withstand temperatures much higher than you'd get in a loft, even in summer?

    The issue is that current flowing through cables make them warm, and if they can't get rid of the heat they get too warm, then the insulation softens, then where the cables are bent or not properly supported the conductors migrate through the PVC, and then eventually they touch, and Bad Things happen.

    Insulation has a marked effect on current carrying capacity - a cable surrounded by insulation can only carry half the current that it can if clipped to the surface of a wall or covered in a bit of plaster.


    Posted By: BluemoonA good reason for not covering cables with insulation is, you can find them afterwards. The contractors who put the glassfibre blanket in my loft told me that they are told to cover all except for the shower and cooker cables.

    See here: http://www.diynot.com/forums/viewtopic.php?t=154936 for what happens when contractors are told to do that.

    And if they've done it to you, you should get it sorted before Bad Things happen...


    Posted By: jamesingramIf then insulation >100mm then it drop to 17amps. which if in a ring circuit ( which is 2, 2.5mm2) protected by a 32 amp fuse is fine

    No it's not - 433.1.4 requires that the capacity not be less than 20A...
  2.  
    Err - why doesn't clicking on 'quote' produce quotes that work?
    • CommentAuthorwookey
    • CommentTimeNov 5th 2008
     
    DaveK, 'never ever' is too strong. What's wrong with the rule-of-thumb that in a normal size house with normal size cables in a loft that only do lighting it will always be fine. There is no point doing calculations - we know what the answer will be: said calculation has been done done hundreds of times before. The law requires the regs to be complied with, not explicitly that calcs are done (SFAIK). After all, if you are building 10houses, you'll only do the sums once.
    • CommentAuthorJackyR
    • CommentTimeNov 5th 2008 edited
     
    Ban-all-sheds, to make quotes work, check "Format comments as html" before posting. Or click "Edit" on your post (while signed in) and re-save it as html.

    Took me forever to work that one out...

    [edit] But then your links won't work. Annoying, isn't it...
    • CommentAuthorJackyR
    • CommentTimeNov 5th 2008
     
    What are you all doing up at this time, anyway? Surely not the US elections...?
    • CommentAuthorwookey
    • CommentTimeNov 5th 2008
     
    Nope - I've got a presentation to write before I catch a plane at midday. 6.5hrs left...
  3.  
    Quote from Tony "How come everyone uses 2.5 for ring mains when even running it down a new wall insulated to building regs and plastering it in doesn't comply? "

    dont follow you ? You just size the MCB/fuse to suit
    2.5 enclosed in conduit in a insulated wall is rate up to 20amps (2*20=40 so 32 amp MCB)

    the only time you get a problem, is if the cable is in a stud wall filled with insulation and the cable is not touching the inner wall surface
    its rated up to 13.5 amps in this case. for a ring you just use a 20 amp MCB
    I recently did something similiar but ran radials,I then relised I had to put them on a 10 amp MCB . which is not ideal as they can only power equipment up to
    2.3kw . eg. a kettle and toaster will trip it out

    cheers jim
  4.  
    Posted By: JackyRBan-all-sheds, to make quotes work, check "Format comments as html" before posting. Or click "Edit" on your post (while signed in) and re-save it as html.

    Took me forever to work that one out...

    [edit] But then your links won't work. Annoying, isn't it...

    Annoying?

    Perverse, more like, to pick a discussion forum package that doesn't work when there are free ones available that do...
  5.  
    CommentAuthorban-all-sheds" No it's not - 433.1.4 requires that the capacity not be less than 20A..."

    dont follow you sorry , 433.1.4 in the 17th ?, I cant see the bit you mean
  6.  
    Err - did I get the number wrong? I'll check later when I'm back home.

    And to save anyone interested from having to copy/paste the URL above (Bluemoon should be) this should be clickable: http://www.diynot.com/forums/viewtopic.php?t=154936

    Jeez I can't believe how c**p this forum package is... :angry:
    • CommentAuthorjamesingram
    • CommentTimeNov 5th 2008 edited
     
    Following 433.1.4 if the cables buried under the insulation then the protective device should not exceed 0.9 of Iz
    so 34 *0.9=30.6 so a 20amp mcb should be used , is this what you mean?
    or are you saying the capacity of the any cables in a ring should be no lower than 20amps?

    regarding light circuits ,the amount of downlights people seem to go for now, 1mm2 might well not be up to the job in a superinsulated loft
    and how many people do you know running thier 9.5kw electric shower on 16mm2 ?

    cheers Jim
    • CommentAuthorBluemoon
    • CommentTimeNov 6th 2008 edited
     
    <blockquote><cite>Posted By: Bluemoon</cite>A good reason for not covering cables with insulation is, you can find them afterwards. The contractors who put the glassfibre blanket in my loft told me that they are told to cover all except for the shower and cooker cables.</blockquote>

    I have uncovered the mains cables, and others such as aerials, network, phone, and Possum signal cables so that I can find them. Two ringmains, 2.5T&E's, pass through a 750mm stone wall, it's easy to get hotspots.
    • CommentAuthorJackyR
    • CommentTimeNov 6th 2008
     
    How much leeway d'ya get in all this?

    My cables are carefully above loft insulation almost everywhere, but have to dive through it obliquely for up to 50 cm.

    Also, above suggests major difference between surrounded by insulation, and resting on ceiling/clipped to joist and top covered by insulation. True?
    • CommentAuthorRoobarb
    • CommentTimeNov 6th 2008
     
    The cables in our loft are just for the upstairs lighting circuit so the load is low. I'm trying to keep as much of the cabling above the insulation as I can but without completely rewiring it I won't be able to avoid some of the wiring being surrounded/covered by insulation.
    • CommentAuthorjamesingram
    • CommentTimeNov 8th 2008 edited
     
    Jacky R for reference
    From the latest regs book, current carrying capacity of cable completely surrounded in more than 100mm of thermal insulation for more than or equal to 0.5m
    (p282 table 4D5)

    1 mm2 twin& earth 8 amps , a 6 amp MCB/fuse is used in this case for domestic lighting circuits . approx. max load 1380 watts (P=VA , 230*6) so OK
    1.5mm2 T&E 10 A
    2.5mm2 T&E 13.5 A (27A ring)
    4 mm2 T&E 17.5 A
    6 mm2 T&E 23.5 A
    10 mm2 T&E 32 A
    16 mm2 T&E 42.5 A

    if its less than 0.5m the derating factors are . (in the above table, the values have already been derated by 0.5)
    50mm =0.88
    100mm=0.7
    200mm=0.63
    400mm=0.51

    yes, there is a difference between cables surrounded and laying on insulation a one will lose heat quicker so can carry more current

    as mentioned above electric shower cables are a potential problem, most other stuff should be fine

    a 9.5Kw shower may use up 41.3 amps A=P/V (V=230) so in the above situation a 16mm2 cable should be selected
    most showers are run on 10mm2 , and I've seen them wrongly run on 4-6mm2 as well
    I once burn my hand on a dangerously undersized cable running a shower as it was so hot.

    If your in any doubt you should get a qualified electrician to have a look

    cheers Jim
    • CommentAuthorJackyR
    • CommentTimeNov 8th 2008
     
    Thanks Jim. Clearly some kneeling in prayer before the fuse cupboard is required.

    Was going to add that, insulation aside, wiring is now in good nick. But monitoring power consumption of washing machine has yielded some... interesting results :cry:
  7.  
    probably old news to you , but a lot of the energy for washing machines is used in the water heating so , 30 or cold washing is the way to go
    also if its a washer/dryer dont use the dryer bit , unless of course you're in a rush to dry that item of clothing for a night out on the town.

    Average should be one load per person a week.

    cheers Jim
    • CommentAuthorJackyR
    • CommentTimeNov 8th 2008
     
    Yeah, was thinking more of the 5W apparently drawn when the machine is "off". Jumping up another 5W when the socket is also "off".

    Still checking monitoring equipment before I join ludite's Mummy Make the Scary Person Go Away club...:shocked: