    • CommentAuthorDantenz
    • CommentTimeDec 20th 2008 edited
     
    The application of using a ground source heat pump to heat an indoor swimming pool is the perfect partnership (low temps and all that) but can anyone offer me advice on how to size the heat pump. Certain heat pump manufacturers steer away from this responsibility saying that that it is too detailed and complicated and yet those that do end up specifying a heat pump that is in my opinion, way too big. Any advice would be much appreciated.
    • CommentAuthortony
    • CommentTimeDec 20th 2008
     
    first you should do some solar -- the sun is free and it will cost you only the pump power.

    then for winter consider additional solar instead of the heat pump.

    how big is the pool and is in a heated part of the building?
    • CommentAuthorludite
    • CommentTimeDec 21st 2008
     
    Would it be possible to have a swimming pool - under cover - heated by solar in the summer, then use it as a heat source (taking the heat out of it via a heat pump) during the winter? How big would the pool have to be? Would there ever be a time when the pool was warm enough - but not too hot to swim in? What about legionella, or would the chlorine treatment take care of that?
    • CommentAuthorGBP-Keith
    • CommentTimeDec 21st 2008
     
    General advice to site visitors: Don't install a heat pump unless you have enough on-site renewables capacity to power it.
    Heat pumps are not a renewables technology.
    • CommentAuthorCWatters
    • CommentTimeDec 21st 2008
     
    If you were to heat the pool once using portable equipment of some sort and then allow it to cool down you could measure the heat losses and work out the size pump you needed to maintain the required temperature. You then need to work out how fast you need it to warm up.

    Regarding use as a heat store.. It's quite easy to work out how much energy is stored in 1L of water...

    Energy (Joules) = 4186 x delta T x Volume in Liters

    Lets say the pool was small a 5 meters x 3 meters x 1 meter. That would have a volume of 15 cubic meters or 15,000L

    If you heated it from 20C to 40C and then it would contain..

    4186 x 20 x 15000 = 1256 MJoules

    So how long would that heat your house?...Well 1J = 1 Watt Second so...

    Lets say your house needed 4KW continuously..

    1256 x 10^6 / 4000 = 314000 seconds or 3.5 days.

    Perhaps you can check my sums.
    • CommentAuthorDantenz
    • CommentTimeDec 21st 2008
     
    I am of the understanding that 90% of the heat loss from a pool is through evaporation off the surface and that the deeper the pool relative to surface area = less loss. Assuming the pool has insulated sides base etc and the time taken to heat the pool from cold is of no real significance then the heat loss from a covered surface would be small ish would it not ? Also with indoor pools the ambient air temperature is usually kept 1-2 'C warmer than the pool itself so again wouldn't the pool actually be heated by the air rather than the other way round. I guess what would need to be determined is the steady state heat loss from the surface of the pool when it is in use and not covered. Add to this 10-15% to offset other heat losses. Does this seem reasonable?
    • CommentAuthorTheDoctor
    • CommentTimeDec 22nd 2008
     
    i think even though air temp is kept above pool temp (to prevent condensation) the water is also heated separately.

    I'd go mega on the solar, and big bucks on a super-duper thermal cover.

    Assuming this is a new build, design the poolhouse to the shape required to best harness the sun, rather than designing a retro-fit 'add-on'
    •  
      CommentAuthorPaulT
    • CommentTimeDec 22nd 2008
     
    I am planning on building a pool/thermal store home in next year.

    My plan is to use a very large Solar array and a wood burning stove. These provide Hot water form the home and then switch down to heating the pool. The pool is in a basement under the house (and up against two quarry walls)
    U values around the pool will be around 0.1 /0/15. So the elemental heat loss from the pool area is likely to be around 10-15W/C of pool above ambient temperature (12C ground temp) - around 300W (24/7)


    The following are thoughts I will be developing...


    The biggest "Heat Loss" would be from ventilation/evaporation - except I am going to use a two/three stage HRV system to use this heat loss to provide space heating for the home...

    I can do this because I am designing to Passiv House levels of performance (and have my own HRV equipment).

    The HRV air flow rates will been to be significantly higher than would normally be required for home ventilation, but the two stage heat exchanger will allow for this (each exchanger 90% efficient)

    Another alternative is to provide a simple Underfloor heating system on the ground floor - linked to the pool via a buffer tank...

    I expect to large slabs of EXP over the pool when not in use

    An Economy 7 air source heat pump may also be of interest

    I have very rough figures at the moment and will be running SAP,Passiv Haus,Retscreen and Energyplus simulations over the next few months.

    - the exciting prospect is the use of the pool as a thermal store form renewables maximising Solar through winter - I will be collecting data for a full study.

    Could be interesting to exchange ideas.
    • CommentAuthorIce Energy
    • CommentTimeDec 23rd 2008 edited
     
    Posted By: General advice to site visitors: Don't install a heat pump unless you have enough on-site renewables capacity to power it.
    Heat pumps are not a renewables technology.


    I'm sorry you didn't get the chance to reply to my email about your claims that heat pumps are not renewable technology.

    I believe you are doing your readers a huge dis-service in giving your "general advice" based on one biased report.

    I have just received this letter from the Energy Saving Trust an independent NGO who has tested a range of different heat pumps. They confirm significant savings on running costs and reduction of CO2.

    The reality is not all heat pump are equal, some are better than others and we (Ice Energy) has demonstratable evidence of seasonally adjusted COPs of greater than 4:1 for ground source and 3.2:1 for air source.

    Your uninformed statements as fact and advice does nothing to enlighten your readership about real options in real situations.

    Extract from EST letter:
    Percentages of Energy and Carbon Dioxide Saved by Heat Pumps
    Supplied by Energy Saving Trust

    Air Source Heat Pumps
    The savings below are based on a detached property, and relate to space heating only.
    They assume a typical system, with a seasonal performance factor of 2.5
    Figures have been rounded

    Gas Oil LPG Electricity Coal Air Source Heat Pump
    Running Cost £750 £1,020 £1,100 £1,320 £720 £440
    % financial saving 40% 55% 60% 65% 40%
    Tonnes CO2 3.8 4.3 4.2 8.9 8.1 3
    % CO2 saving 20% 30% 30% 65% 60%

    Sample saving statements:
    Replacing an oil heating system with an air source heat pump for space heating in a detached home can reduce running costs by 55%, and carbon dioxide emissions by 30%.


    Ground Source Heat Pumps
    The savings below are based on a detached property. They assume that the heat pump provides 100% of space heating and 50% of water heating, with the remaining 50% of water heating provided by electric immersion heater.
    They assume a typical system, with a seasonal performance factor of 3.2.
    Figures have been rounded

    Gas Oil LPG Electricity Coal Ground Source Heat Pump
    Running Cost £970 £1,310 £1,420 £1,560 £900 £550
    % financial saving 45% 60% 60% 65% 40%
    Tonnes CO2 5 5.5 5.4 10.6 10.2 3.8
    % CO2 saving 25% 30% 30% 65% 65%

    Sample saving statements:
    Replacing an oil heating system with a ground source heat pump for 100% space heating and 50% water heating in a detached home can reduce running costs by 60%, and carbon dioxide emissions by 30%.

    Fuel prices and carbon factors
    Gas Oil LPG Electricity (heat tariff) Coal
    p/kWh 4.03 6.09 5.93 8.27 2.77
    Kg CO2/kwh 0.206 0.258 .0.225 0.562 0.313
  1.  
    Ice energy
    Heat pumps are not renewable energy. You still use eleectricity to run them. You are missing the point. Some heatpumps may be better than others but they all use electricity in varying levels. A renewable energy source is best described as one that doesnt use any gas, electricity or oil to operate it. For example solar hot water heating for domestic water generation is a renewable. You get is for free without burning fossil fuels.
    The current fashion in installing heat pumps is not ecenomic if you have mains gas available. We advise are clients against this as you are going to see no advantage in running costs for a heatpump compared to a condensing gas boiler.
    If you have an oil boiler that needs replacing then it just might be worth considering a heatpump although the financial outlay to go the heatpump route compared to a new boiler is a big downside.
    The figues above are mis leading as they do not take into account the 35% efficiency of the central electricity generation. ( 40% efficient and further 5% distribution losses)
    • CommentAuthorTheDoctor
    • CommentTimeDec 23rd 2008 edited
     
    that said, the point was a little unfair
    He is right that it is not renewable, as such, but

    "Don't install a heat pump unless you have enough on-site renewables capacity to power it."

    this only applies if you are building an off-grid home, and is off no help to anyone trying to reduce their bills rather than eliminate them.

    we'd all love to eliminate electricity, but the reality is it is going to happen in stages.
    A heat pump, when designed and installed correctly, seems an eminently sensible choice.
    • CommentAuthorDantenz
    • CommentTimeDec 23rd 2008
     
    Heat pumps for the most part extract renewable energy do they not. If not, what would you call the energy that comes from the ground or air then?
  2.  
    Posted By: timevans2000The figues above are mis leading as they do not take into account the 35% efficiency of the central electricity generation.


    Looks like they do in the quoted CO2/kWh figures.

    Posted By: DantenzHeat pumps for the most part extract renewable energy do they not.


    Exactly.

    Paul in Montreal.
    •  
      CommentAuthornigel
    • CommentTimeDec 23rd 2008
     
    EST is some providing out of date information to calculate those numbers.

    The carbon intensity of grid electricity used to be taken as 0.43kgC02/kWh which when you take a COP of 2.5 gives emissions of 0.172kgCO2/kWh.
    This compares with natural gas having a carbon intensity of 0.19kgCo2/kWh with a 93% conversion efficiency gives emission of 0.204kgCO2/kwh.

    Hence the concept that heat pumps are so green is created.

    Recently the carbon intensity of electricity has been adjusted upwards to 0.537kgCO2/kWh.
    The figures for net emissions for a heat pump is now 0.2148kgCO2/kWh which is WORSE than for natural gas which is a fossil fuel.

    The heat pump industry is responsible for promoting unreliable claims about COP's, they don't tell us how they work in real life situations and how they are dependent on other external factors.
    COP's vary enormously with output temperatures, they don't tell you that in their adverts. The headline is 450% efficiency.

    If you have mains gas you are far better off installing a condensing boiler and spending the rest adding extra insulation.
    •  
      CommentAuthorPaulT
    • CommentTimeDec 23rd 2008 edited
     
    Heat pumps are not renewable energy

    "A heat pump is a device which takes heat energy from a low temperature source and upgrades it to a higher
    temperature at which it can be usefully employed for heating" - SAP document (BRE/DEFRA ,2008)

    You will note that the EST calculations are theoretical and base on performance assumptions and so should not be regarded as evidence.

    It is interesting to note that the EST statement does not make any comparison with more widely accepted renewable solutions, such a Solar and biomass.

    It is also interesting that the EST Air Source Heat Pump example does not include hot water - a bit of a selective comparison and indicitive of low standards I have come to expect from the EST

    I have a real problem with heat pump salespeople and find Clients are often mis-sold to, based on unrealistic performance claims which can not be substantiated; This diverts money away from sustainable building and true low carbon heating systems. I have only ever ONCE come across a HP sales guy who was prepared to talk about frost cycles and reduced efficiency! (they got the contract)!

    Regarding building regulations (ie THE LAW):

    In SAP COP's of 2.5 and 3.2 may only be used (for Air source and ground source respectively)

    Unless Underfloor heating is used then the efficiency should be multiplied by 0.7 (The EST statement is not clear on the type of heat delivery - but it would be safe to say no GSHP salesperson is going to suggest ripping up your ground floor so their system works better, unless they get to do the work)

    Also if the underfloor heating is in a screed the responsiveness of the heating should be adjusted to 0.75, also detrimental to the final rating.... and so on
    • CommentAuthorGotanewlife
    • CommentTimeDec 23rd 2008 edited
     
    Perhaps it is lucky that I am no expert in all this. Perhaps, though, as a result of NOT really understanding all this my little bit of KISS might help.

    1 - To me 'renewable' means using something that can be renewed (Animal Farm - in my lifetime).

    2 - Heat pumps 'simply' make electricity more efficient (1 kw in gets 3 out) - the extra '2' is always from renewable energy (Animal Farm - unless the ground has too much heat taken out of it).

    3 - Electricity can be renewable (from PV, wave, wind etc) or not (from Gas, Coal, oil). (Animal Farm - ignoring embodied energy, transportation of kit etc).

    4 - 'Green' - to me means 'greener' - replacing an old oil fired boiler with a GSHP powered by non-renewable energy is 'green(er)', replacing a pellet burner is not 'green(er)'.

    We can (and do!) debate relative greeness (insulate vs GSHP over already installed gas combi anyone) but, to me, the first 3 points above are QED.

    I think we should all strive to be green(er) and i am delighted to say that my friends (who have (yes still!) 'loads of money') have just installed a PV system married to a GSHP - is it really possible that those who know about these things above are really wrong and that this PV powered GSHP is not renewable? Perhaps it is something to do with the timing - my friends use less energy from the grid than they give back, anyway, if its me please somone explain! As for me I have a I little money and have today paid for a 40Kw wood burner (and I have a good business case too).

    By the by - that GSHP, yup you guessed it, nowhere near the COP 'advertised' - could be for any number of reasons of course......

    Sorry Dantenz - nothing to do with your pool:shamed:
    • CommentAuthorludite
    • CommentTimeDec 31st 2008
     
    Another hijack.

    Was watching one of those american 'disaster documentaries' the other day - about a solar storm. Electricity gets cut off. . . . .

    Hubby started to worry. We have a woodburner that heats rads and water, but it can't do it without electric pumps.

    Does the water in our taps get there by gravity alone? I think electricity comes into it somewhere.

    Made me start to revise my dream house plans, so that the rainwater harvested can still come out of the taps - or get flushed away - without the need for electricity. . . . . .. does that ramble make sense?