  1.  
    I'm planning to insulate under the floor boards on the ground floor of our end-of-terrace house. I've lifted a few floor boards in the living room and I've found that the joists are touching the soil underneath the house! I presume this is bad because moisture will wick into the joists and cause problems. After I lift all the floor boards, should I also remove some of the soil & rubble so there is an air gap between the bottom of the joists and the ground, to prevent moisture travelling from the ground into the joists? My initial inspection suggests that most of the joists are currently not suffering from rot but the joist at the far edge of the room (nearest to the exterior wall) is in a bad way. Here are some photos:

    http://xlk.org.uk/ext_images/house/DSC_0079.jpg
    http://xlk.org.uk/ext_images/house/DSC_0084.jpg
    http://xlk.org.uk/ext_images/house/DSC_0088.jpg

    The house was built sometime between 1895 and 1905 we think. I'd like to achieve the Energy Saving Trust's "best practice" U-value of 0.24 W/m2/K for floors which I believe would require 100mm of rigid polyurethane foam insulation. The joists are only 76mm (3") high so if I want to fit 100mm of insulation then I have to dig down anyway to fit the insulation and to leave an air gap under the insulation.

    Any advice would be really helpful!
  2.  
    to be very honest i think you really need to take the floor up....
    you need to lay a barrier to prevent moisture rising (DPM) and you need to install proper structural joists (a suspended timber floor) and install adequate insulation between these joists. either that or lay the DPm, then insulation and then a solid concrete floor of about 125mm .....
    • CommentAuthorDavipon
    • CommentTimeJan 7th 2009
     
    Dig out the rubble near end of joists to check plates that joists are sat on,it may be the warmth from ground floor living space keeping moisture at bay so sort out any damp issues first!
    • CommentAuthordickster
    • CommentTimeJan 7th 2009
     
    Hi Dan,

    No way am I an expert, but those joists look relatively new and seem to have been laid directly onto the floor. They don't look strong enough to support the floor if you dig the underfloor out. Looks like a bodge to me. Be v careful regarding putting it right.
  3.  
    Posted By: dan_aka_jackThe house was built sometime between 1895 and 1905 we think


    Have those joists been there since the house was built? If so, then there obviously weren't any moisture/rot problems.

    Posted By: dicksterThey don't look strong enough to support the floor if you dig the underfloor out.


    They look like they're 2x8s - I guess the important question to ask is what is the span? You could always put supports in if you do dig out.

    Paul in Montreal.
    • CommentAuthorCWatters
    • CommentTimeJan 7th 2009
     
    Posted By: Paul in Montreal They look like they're 2x8s
    Paul in Montreal.


    Check the last photo. They seem to be <3" deep. Not strong enough.
  4.  
    Many thanks for the replies!

    Hmm, bother... sounds like there's lots of work ahead of me and some expensive trips to the wood merchants!

    At a minimum, how much space should there be between the bottom of the joists and the ground?

    It sounds like the consensus is: take up the floor, remove the existing joists, dig out the ground, lay a damp-proof membrane (and hold it in place with some rubble? or is it necessary to lay concrete over the DPM?), fix new joists in place, insulate and re-fit the old floor boards. Yikes. So much for my hopes that insulating the floor would be a weekend's worth of work!

    Posted By: Paul in Montreal
    Have those joists been there since the house was built? If so, then there obviously weren't any moisture/rot problems.


    I'm afraid I don't know how old those joists are. As Dickster mentioned, the joists look fairly new (I'm no expert on wood ageing though!)

    In terms of room dimensions... the room as it stands at the moment is 6.85m x 3.60m but I'm almost certain that it used to be two rooms.

    We've been in the house since 2006. Over the past few years we have found quite a few bits of evidence that at least one previous owner has done some real bodge-jobs.
  5.  
    Posted By: CWattersCheck the last photo. They seem to be <3" deep. Not strong enough.

    You're right, I was reading the cm as inches!

    Posted By: dan_aka_jackAs Dickster mentioned, the joists look fairly new

    Actually, the wood looks old to me - it looks very similar to the studs I exposed in our 110 year old house - plus you have square cut nails in there. The dimensions seem to be "true" 3x4s - but they would not be strong enough if unsupported.

    Paul in Montreal.
    • CommentAuthorCWatters
    • CommentTimeJan 7th 2009
     
    Posted By: dan_aka_jackMany thanks for the replies!

    Hmm, bother... sounds like there's lots of work ahead of me and some expensive trips to the wood merchants!

    At a minimum, how much space should there be between the bottom of the joists and the ground?


    The recommendation min is 150mm and it should be veltilated.


    It sounds like the consensus is: take up the floor, remove the existing joists, dig out the ground, lay a damp-proof membrane (and hold it in place with some rubble? or is it necessary to lay concrete over the DPM?), fix new joists in place, insulate and re-fit the old floor boards.


    I don't believe a DPM is needed for a ventilated void. It is for a solid concrete floor.


    Yikes. So much for my hopes that insulating the floor would be a weekend's worth of work!


    The government banned weekend DIY insulation jobs... Technically I believe you would need Building Control Approval for this as you are changing an "insulating element".

    Think carefully about the ends of the joists and how they are fixed to/into the wall. Don't want the ends rotting.
  6.  
    Posted By: CWatters
    Technically I believe you would need Building Control Approval for this as you are changing an "insulating element".


    Yup, I believe you are correct. Not only am I changing the insulating properties of the floor but it looks like I'm going to be changing the joists as well and I believe I need to get building control approval before I fit a whole new floor (even if I wasn't changing the thermal performance of the floor)... although I'm not sure if I also need to get a structural engineer involved to provide building control with the necessary calculations (the length the joist can go without requiring support etc). This could get expensive.

    Posted By: CWatters
    Think carefully about the ends of the joists and how they are fixed to/into the wall. Don't want the ends rotting.


    Yup... what would you recommend? Should I glue some DPM onto the vertical face of the wall and then bolt a face-fixing joist hanger onto the wall? (i.e. the DPM would be sandwiched between the vertical face of the wall and the joist hanger).
  7.  
    Here's a picture of the whole room, just in case anyone's interested:

    http://xlk.org.uk/ext_images/house/DSC_0103.jpg
    • CommentAuthorken davis
    • CommentTimeJan 7th 2009
     
    We appear to be looking (with regard to this problem) at just one room so far, surely the sam problem is likely to occur in the other g/f rooms also (I guess they are probably the hall and kitchen?).
    If you put in some honeycomb sleeper walls i.e traditional suspended g/f construction you can avoid the use of deep joists and even cutting in to surrounding walls, but you will need to sit the walls on strip foundations that go down below the frost line (notionally 450) or as otherwise agreed with you BCO. You will need to dig a small trial hole for him to look at. Sleeper wall could be as simple as one course of bricks, then dpm, then 100x50 timber plate, then (probably) 100x50 joists (insulation between, say CELOTEX). Do a little digging and see how helpful your BCO is. Check other rooms!
  8.  
    Good advice, many thanks.

    When you say that I could avoid using deep joists if I construct sleeper walls, does that mean that I could retain the existing 3"x4" joists if I construct sleeper walls? Might it be easier for me to use deep joists and to forget about sleeper walls? What span can deep joists cope with, assuming they're only supported at both ends?

    I will get in touch with our local Building Control Office.

    Thanks again for all the advice!
    • CommentAuthorchuckey
    • CommentTimeJan 7th 2009
     
    I weas going to say the joists look new. Every old floor I have lifted have the joists covered in grey muck, loose dust that has fallen down the cracks in the floor boards.
    The joist needs to sat on something that does not transmit the moisture through it and can take the weight of the floor loading. Sleeper walls are entirely suitable but would require the whole floor to be lifted to gain enough working room, also the walls would need strip foundations, which could undermine the existing foundations of the house.
    What I would do is to support the joists on a 9" square paving stone, every 18" along their length. Mark out with tape the centre of each stone on the floor boards (just a dab of tape would do). Lift two boards next to each other, one with the line of tape bits on. Dig out say 11"" square under one joist centre, giving a gap of about paving stone thickness + 1/2". Put down a batter of mortar, put a paving stone on it (leave a gap of 1/4"+ on top)and make sure its tight on the mortar (use a crow bar against the underside of the joist). Slip in a piece of DPC membrane and push mortar in the slab/DPC gap - make sure its tight. Repeat for the rest of the joists exposed. Avoid walking on that area for 3 days, but you can do various strips say at 4' centres. then when the cement has gone off, do some more. The theory is that you won't be disturbing the floor level or the walls too much.
    Frank
    • CommentAuthortony
    • CommentTimeJan 7th 2009
     
    The whole thing is not right or good nor should it still be there

    None the less my advice would be to leave it all as it is!! How long has it been there like that? --- proves my point
    •  
      CommentAuthorrichy
    • CommentTimeJan 7th 2009
     
    If it aint broke don't fix it. Looks like dry soil, good timber joists and a nice old pine floor to me. Looks like it's been there for a century without problems. We don't do it like that now, but sometimes they did then!
  9.  
    Many thanks for all the very helpful replies.

    Posted By: richyIf it aint broke don't fix it.


    True... except I'd like to insulate the floor between the joists (ideally I'd like to install 100mm of rigid foam insulation under the floor boards to achieve the Energy Saving Trust's target U-value for refurbished floors of 0.26 W/m2/K). As Davipon mentioned above, it may be the warmth from the living space which is currently keeping moisture at bay under the floor. If I add insulation to the floor as it is currently constructed then I risk making the joists rot quickly.

    Having said that, this job is starting to look truly enormous for a DIYer like me.

    Posted By: chuckeyalso the walls would need strip foundations, which could undermine the existing foundations of the house.


    OK, undermining the existing foundations sounds bad! Is there any way to tell whether or not I might undermine the existing foundations before I do the job???
    • CommentAuthortony
    • CommentTimeJan 8th 2009
     
    Try a little bit or dig a hole outside to see how deep they are.
  10.  
    ....it might no be popular... but... .. interms of simplicity and robustness (if not immediate environmental impact...)

    1. Dig and fill with concrete ( PFA... / limecrete...?)
    2. Insulation on DPM
    3. Screed / floating floor...

    just a thought....

    J
  11.  
    Wow, amazing timing... Just a few minutes ago I was just thinking about lifting the existing floor boards, removing the joists, digging out and fitting wet underfloor heating set into a concrete (or alternative?) floor. Excuse my ignorance but is it possible to fit wooden floor boards over a wet underfloor heating system?

    Many thanks,
    Jack
    • CommentAuthortony
    • CommentTimeJan 8th 2009
     
    Yes
  12.  
    Great, thanks for the reply.

    By the way, here's a photo of the end joist (nearest to the external wall) which isn't a happy joist:

    http://xlk.org.uk/ext_images/house/DSC_0003.jpg
    •  
      CommentAuthorrichy
    • CommentTimeJan 8th 2009
     
    The building regulations dictate joist sizes/spans, look here: http://www.haringey.gov.uk/trada_span_tables.pdf
    • CommentAuthortony
    • CommentTimeJan 8th 2009
     
    Re edge joist -- looks like little dampness as woodworm won't eat dry wood. Reduce g/l outside, check gutters etc.

    Is the floor ventilated from outside?
  13.  
    Many thanks for all the help - your advice has all been extremely useful, thank you so much.

    Richy, thanks for the joist span document. That's good news... it sounds like I wont have to fabricate any extra sleeper walls if I get wood thick and deep enough to cope with a 4.5m span. The living room is currently about 7 meters long but the room definitely used to be 2 rooms and I'm 99% certain that the dividing wall was constructed from a single layer of bricks. I assume that the brickwork which used to support the dividing wall still exists under the floor boards and I could use this as my sleeper wall. I will pull up some more floor boards this weekend to explore what's down there.

    Tony: there certainly are air vents in the external wall entering what I assume is the under-floor space. But given that the joists touch the ground, I doubt the underfloor space is ventilated especially effectively. Many thanks for the info about woodworm not eating dry wood; I didn't know that so I was a bit baffled about why the joist was rotting AND the floor board showed evidence of woodworm. But now it's much clearer!
    • CommentAuthorDavipon
    • CommentTimeJan 9th 2009
     
    dan_aka_jack hopefully here's a picture of dwarf walling for your info.

    My joists were in as bad a state as yours so I replaced all ground floor.Your existing spans should be ok if not changed from original.Any deeper timber for joisting will mean a higher floor level or lower bearing,so bottom of joist deeper in ground.
    You ideally need a clear space below joists for air movement & to stop moisture transfer.Joist should sit on timber plate on mortor bed on dpm on mortor on brick work.
      P25-03-07_10.12.jpg
  14.  
    Great picture! Yikes, that must have been a lot of work! (By the way, how did you manage to embed a photo into your post?)

    My problem is that who ever built my ground floor couldn't be bothered to build proper suspended timber floors; instead they just laid the joists directly on top of the soil! The existing joists are too thin to cope with the span without being supported by the soil.

    http://xlk.org.uk/ext_images/house/DSC_0079.jpg

    So I have to remove the joists and dig down anyway... so hopefully I can use whatever sized joists I want (I assume using larger joists just means that I have to dig further and use the correct metal supports) and I'll use metal supports to hold the ends of the joists (if that's acceptable?)
  15.  
    Where is FGL in relation to FFL ? if the floor level is well above ground level then there is less of an undermining issue, if not it might prove a difficult void to ventilate and you'll need to investigate the foundations... engineers.... big hole in you living room for ages... etc. Are you sure suspended timber is the best option in this case...

    J
  16.  
    Good point.

    The house is built on a slope but the ground floor of the house is on a single horizontal plane. So the floor level at the front of the house is probably about 2m above ground level but the floor level towards the back of the house is quite possibly slightly under ground level.

    So do you think it's possible that I could disturb our foundations if I dig the floor out by 15cm? Is a solid cement floor a better option? I suppose it's impossible to tell without seeing the building up close and personal.
    • CommentAuthorDavipon
    • CommentTimeJan 9th 2009
     
    Joist hangers aren't usually a feasable solution in older houses as the bricks are usually a soft composition & tend to crumble under loading.If you dig about under the soil you may find that it's loose debris on top of a lean mix oversite (concrete base)This can act as a surface to prop good joists from while you renew timber on bearing points,it might be easier(figuratively speaking)to put in extra strip footings & bearing points than faff about with deeper joists,cheaper timber costs too.Apologies for misspelling on mortar!
   