Home  5  Books  5  GBEzine  5  News  5  HelpDesk  5  Register  5  GreenBuilding.co.uk
Not signed in (Sign In)

Categories



Green Building Bible, Fourth Edition
Green Building Bible, fourth edition (both books)
These two books are the perfect starting place to help you get to grips with one of the most vitally important aspects of our society - our homes and living environment.

PLEASE NOTE: A download link for Volume 1 will be sent to you by email and Volume 2 will be sent to you by post as a book.

Buy individually or both books together. Delivery is free!


powered by Surfing Waves




Vanilla 1.0.3 is a product of Lussumo. More Information: Documentation, Community Support.

Welcome to new Forum Visitors
Join the forum now and benefit from discussions with thousands of other green building fans and discounts on Green Building Press publications: Apply now.

The AECB accepts no responsibility or liability for any errors or omissions in the content of this site. Views given in posts are not necessarily the views of the AECB.



    • CommentAuthorMike George
    • CommentTimeMay 15th 2009 edited
     
    Is anyone aware of the effect oversizing boilers has on reducing efficiency? I 'm particularly interested in the numbers.

    Eg. Assume a domestic hot water demand of 30kW. if a 40kW 90% efficient condensing boiler is installed, what is the maximum efficiency likely to be reached?
  1.  
    Hey Mike,

    Are you looking at fully modulating boilers?

    People I have been speaking to claim that the boilers they are peddling are modulating sometimes from say 30 w down to 5w and therefore claim that it makes no difference, whether that is true or not I dont know. I presume that there is an optimal running temperature to maximise the benefit of the heat exchanger vs losses in the boiler such as waste heat to heat the boiler itself and electrical consumption,...

    Matt
    • CommentAuthorMike George
    • CommentTimeMay 15th 2009 edited
     
    Hi Matt, I should have said we are talking about a combi boiler. I have heard that about modulating boilers as well. I don't know if its true either - anyone?

    Re the oversizing - As far as I know , combi boiler size is promarilly detemined by flow rate, with the other factors being constant [am I wrong?]. If I'm right, an oversized boiler cannot ever reach full capacity because there is simply insufficient flow of water! Therfore it will only ever run at part-load and not reach optimum efficiency [at full load]
    • CommentAuthorCWatters
    • CommentTimeMay 16th 2009 edited
     
    I have a Grant 46KW Condensing Oil boiler. I know oil boilers do not modulate but you can change the jet to reduce the power of the burner and that does effect the efficiency slightly. Grant quote the following figures in the manual for the 46Kw.

    1.00mm jet = 36kW = 101.5% efficient
    1.20mm jet = 41.5kw = 98.5% efficient (Default)
    1.25mm jet = 46kW = 97.5% efficient.

    At first glance it looks like oversizing and detuning might give a 3% improvement but I note that the efficiency figueres for the 36K model boiler are 101.5% for all jet sizes. Therefore there is no advantage in specifying a 46KW and detuning it to give 36KW. You coud just specify their 36KW model in the first place.

    Might be different for other makes though.

    To answer the question I suspect that running a 40kW boiler at 30KW doesn't cause much of a drop in efficiency.
    • CommentAuthorCWatters
    • CommentTimeMay 16th 2009 edited
     
    Posted By: Mike George As far as I know , combi boiler size is promarilly detemined by flow rate, with the other factors being constant [am I wrong?].


    I prefer to think of it the other way around. The max flow rate depends on the max boiler power. If you have multiple showers you may need all the flow rate you can get. Info on the web says that most people consider 15L/min to provide a good drenching shower. Around 7-8L/min is the governments idea of a low flow water saving shower. Check out the specs for the combi you have in mind. Do you need to be able to run two showers or one shower and the washing machine at the same time?
    • CommentAuthorjamesingram
    • CommentTimeMay 17th 2009 edited
     
    Mike ,
    I've wondered this also, and still yet to find a clear answer , asked lots of plumber,heating engineers, EST etc.
    getting in touch with a manifacturer probably the best/next way to go for info
    http://www.aecb.net/forum/index.php?topic=1664.msg6713#msg6713
    The EST and others suggest many domestic boilers are oversized and this reduce effiecency and increases installation costs, but offer no figures
    When using the EST whole house boiler sizing method , I've found boiler sizes for heating requirement almost
    half what your old school plumber would fit, the last example was a 4 bed detached came out at 17Kw and the plumber wanted to fit a 32Kw so we settled on 22kw.

    with regards to a modern condensing gas combi I presume they modulate when in heating mode,
    would they also in HW mode?


    I 'range rated' my own 28kw condensing combi boiler to around 10kw (my rad requirements) when in central heating mode by reducing the inlet gas pressure, the installation manual had instructions and a graph for this purpose ,In HW mode I believe it still gives its full output ?

    cheers jim
    • CommentAuthordelboy
    • CommentTimeMay 18th 2009
     
    I've heard of gas & oil boilers having efficiencies of over 100% before, but I've never understood how that works.

    Can anyone explain the maths behind that?

    Cheers
    • CommentAuthorjamesingram
    • CommentTimeMay 18th 2009 edited
     
    Delboy, sounds impossible to me, how could you get more than 100% energy out of something unless it was coming from somewhere else?
    in the case of a GSHP the extra energy comes from the ground which inturn comes from the sun
    but the energy stored in gas is just what it is. ?
    Ive no idea really . be interested to know also
    • CommentAuthorDantenz
    • CommentTimeMay 18th 2009
     
    Impossible for a boiler to run at 100% efficiency, that would mean no losses and and all of the input energy i.e. gas is directly turned into heat - achieve that and we have perpetual motion. Combi boilers are pretty much always oversized when it comes to the heating load because the high output is needed for the hot water flow rate. Boilers are also traditionally oversized because they are used for spike or intermittent heating. Oversizing of fully modulating boilers doesn't really matter as the controls look at the flow temperature and modulate the output down when the set point flow temp is being approached. The boiler then matches it's output to the system load. However, the downside is that from initial switch on the boiler will run at maximum output which will give a very rapid heat up of the system and when the return water temp. exceeds 52'C the boiler will no longer run in condensing mode. To get the most from a condensing boiler in "the perfect world" either the boiler needs to be undersized or the radiators oversized - the boiler needs to be working hard to maximise the running time in condensing mode i.e. return water temp below 52'C. Sorry, can't give you any figures as to efficiency but what I can say is that it will always be less than the quoted SEDBUK rating. I would suggest a minimum efficiency of 5 % below SEDBUK.
  2.  
    Thanks all, the figures do seem very elusive don't they? I suppost the manufacturers are not going to be quick to advertise any negative effect on efficiency so it doesn't look like there's an easy answer to this one. The client is determined to oversise their boiler - perhaps they will learn the hard way.
    • CommentAuthorjamesingram
    • CommentTimeMay 18th 2009 edited
     
    how about showing them the EST whole house boiler sizing guide ,let them work it out themselves with this
    there is a online version
  3.  
    They did use an online schematic - not sure which one. The point I am trying to get across to them is that it is the hot water demand which determines the combi boiler size as it is a greater demand than the heating. Or am I missing something?
  4.  
    sorry, forgot about the combi bit ,
    Do modern combi boiler modulate in heating mode , if so then its not such a problem as Dantenz mentions
    (do they modulate in HW mode ?)

    Any idea Dantenz?
    • CommentAuthorMike George
    • CommentTimeMay 18th 2009 edited
     
    Yes, that's the question isn't it- Dantenz?
    • CommentAuthorjamesingram
    • CommentTimeMay 18th 2009 edited
     
    http://www.worcester-bosch.co.uk/homeowner/products/gas-fired-boilers-and-systems/greenstar-27cdi/literature
    Have a look at the tech/spec on page 6-7
    "central heating mode ,the boiler initially fire at minimum output before modulating upwards to meet the actual system requirements"
    "hot water mode electronic controls modulate the boiler output downwards to ensure HW temperature remains between 40-60oC"

    From the manifacture gumf, but it looks like this combi does modulate in CH and HW mode
    also note the minium max outputs in both modes on page 4
  5.  
    Nice one James.
    • CommentAuthorDantenz
    • CommentTimeMay 18th 2009
     
    Yes, combi boilers (gas that is) modulate in both CH & HW mode. As for the comment about it not being such a problem then I would say this. A fully modulating boiler that is better matched to the peak heating load will always return a better efficiency than one that is oversized. You have to realise that a 30 kW condensing boiler firing into a 18 kW load will run efficiently for only a short period of time, that is until the return temp reaches 52'C and then it doesn't condense anymore. On further temperature rise the burner output will then modulate down to match the load of the system albeit, still no longer condensing. This is likely to happen after only some 15 mins operation or so. Compare this to an 18 kW boiler which then operates in condensing mode for longer (perhaps 30 mins) = improved efficiency before it too modulates down. You could argue the savings against an oversized modulating condensing boiler compared to those of a correctly sizied modulating boiler are small however, there is a case to argue.
  6.  
    Hi,
    When looking at the efficiency you need to be clear wether the net or gross efficiency is quoted as one (need to look it up) refers and includes the full latent heat of the fuel exhaust gas giving all the energy up. thats why its not uncommon to see 103% quoted as the efficiency.

    Cheers

    Mike up North
    • CommentAuthorCWatters
    • CommentTimeMay 19th 2009
     
    Posted By: jamesingramDelboy, sounds impossible to me, how could you get more than 100% energy out of something unless it was coming from somewhere else?


    It's not possible for a boiler to achieve 100% or more due to the laws on COE. HOWEVER figures in manufacturers literature of 102% are valid due to the way the "efficiency" is defined and calculated...

    The problem is working out how much energy is going into the boiler. eg How much energy does the fuel contain? In the past it wasn't possible to extract the latent heat of vaporization from the flue gas - so that was ignored when calculating the energy content of the fuel. This makes it look like the fuel contains less energy than it really does and it makes non-condensing boilers look slightly better than they really are. Back then this didn't matter as the figures were under 100%.

    These days it IS possible to extract this energy (eg using condensing boilers) but we haven't corrected our assumption about the amount of energy that exists in the fuel. So the result is that some boilers appear to be just over 100% efficient.

    If we wanted to correct the problem we would have to rewrite all the manufacturers data sheets and web sites and then state if the figures were calculated using the old or new method.

    Pushing this concept one stage further... One could argue that the energy content of the fuel is a lot higher still. For example Einstien said E=MC^2 ..but we don't use that method of calculating the energy content of the fuel because it would be rather difficult to extract it in a regular boiler!
    • CommentAuthorjamesingram
    • CommentTimeMay 19th 2009 edited
     
    HI Dantenz
    Just to sum up
    In the situation described, as you mentioned keeping the return temp below 52 and oversizing the rads is the way to go with a condensing combi .
    I think we discussed something similar a while ago regard the boiler I mentioned.
    System was fitted , i must ask them what there bills are like. I think they like a hot house though.

    Cwatters , how long do you think til there fitting fusion combis in our kitchens

    cheers Jim
  7.  
    Hi,
    Just to clarify - I had to look it up
    Net eff is with the fuel burnt but exhaust is basically vented.
    Gross eff is with the fuel burnt but with all the exhuast giving up its latent heat throught eh condensation process. This is more often quote in europe on the basis that everything is condensing.
    Basically the condensing part is just that, its a waste heat recovery unit what in industry has always been called an economiser.
    Add on units to do this are begining to come on to the UK market (gas only). Oil has a much lower dew point at 47deg so to be meaningful the return temp would have to be 45ish deg, whereas with gas its about 55deg so you get a reasonably higher radiator return temp and hence a better delivery temp.
    An alternative to heating the boiler feed is to use the exhuast gas to heat the incoming combustion air. some boiler manufacturers do this.
    How complete the condensing would be is difficult to say in practise.

    I thinkl Combis always get a default lower rating becuase of their irregular operration eveen including the heat store type.

    Cheers, Mike up North
    • CommentAuthorDantenz
    • CommentTimeMay 20th 2009
     
    Whether or not a condensing boiler is running in condensing mode, be it oil or gas, the efficiecy will ALWAYS be better than that of a standard efficiency boiler.