Home  5  Books  5  GBEzine  5  News  5  HelpDesk  5  Register  5  GreenBuilding.co.uk
Not signed in (Sign In)

Categories



Green Building Bible, Fourth Edition
Green Building Bible, fourth edition (both books)
These two books are the perfect starting place to help you get to grips with one of the most vitally important aspects of our society - our homes and living environment.

PLEASE NOTE: A download link for Volume 1 will be sent to you by email and Volume 2 will be sent to you by post as a book.

Buy individually or both books together. Delivery is free!


powered by Surfing Waves




Vanilla 1.0.3 is a product of Lussumo. More Information: Documentation, Community Support.

Welcome to new Forum Visitors
Join the forum now and benefit from discussions with thousands of other green building fans and discounts on Green Building Press publications: Apply now.




    • CommentAuthorsinnerboy
    • CommentTimeJul 1st 2009 edited
     
    My thanks to Aradra1 who posted this here

    http://www.boards.ie/vbulletin/showt...2#post60940702


    EU - INSTITUTE FOR HEALTH AND CONSUMER PROTECTION Report No23
    Ventilation, GoodIndoor Air Quality
    and Rational Use of Energy

    8.5.2 Mechanical ventilation
    Buildings with mechanical ventilation have fan powered supply air to and exhaust air from the rooms. Supply air may be heated depending on demand but not humidified or cooled. Ventilation system may have heat recovery from exhaust air. System may recirculate also return air.Windows may be sealed or openable.These systems are common in countries with
    moderate or cold climate where air conditioning is not always needed to maintain thermal comfort most part of the year.Technical details of these systems for good performance are described in a European draft standard (CEN,prEN 13779,2003).
    Risks in the performance of mechanical ventilation include the following:HVAC-components may be dirty when installed or become dirty and release pollutants and odours;poor control of indoor temperature due to absence of cooling;low humidity in winter;noise generated by forced air flow and fans;draft caused by forced air flows.If the system has mechanical cooling the additional risk factors are introduced by cooing coils: condensed moisture in the system (e.g.cooling coils and drain pans) and potential microbial growth;biocides used to treat wet surfaces such as drain pans. In systems with air recirculation some additional risks are introduced:indoor-generated pollutants are spread throughout the section of building which
    air handling system serves; higher air velocities which increase risk of draft and excessive noise; supply ducts of HVAC-system may become contaminated by indoor generated pollutants.

    .........In mechanically ventilated buildings the ventilation air is conditioned before it is supplied to the rooms via the duct system.Because of supply and exhaust air fans the system is more flexible in respect of building design, and more energy efficient if heat recovery is used.
    However, studies in many European countries have shown that mechanical ventilation systems may cause adverse heath effects,the reasons of which are not yet well known,but the following have been suspected:air handling system is a source of pollution,moisture in air handling system causes the mould growth, system generates and transfers noise, ventilation air supply is poorly controlled, occupants cannot influence the ventilation.
    These issues have to be solved to achieve good indoor air quality.

    http://www.inive.org/medias/ECA/ECA_Report23.pdf
    • CommentAuthorsinnerboy
    • CommentTimeJul 1st 2009 edited
     
    HRV and fire

    I don't believe the risks are understood - or if they are - that they being addressed by the HRV industry

    http://www.boards.ie/vbulletin/showthread.php?t=2055385732&highlight=fire

    Be aware of some unfortunate Canadian experience with the units CAUSING fires

    http://www.bamn.org/prHRVrecall.cfm

    http://www.nachi.org/forum/f48/venma...concern-11412/

    http://www.bluemountainscourierheral.../article/61577

    Perhaps Paul in Montreal can put a perspective on the reports ?
    • CommentAuthorsinnerboy
    • CommentTimeJul 1st 2009 edited
     
    HRV units - evidence here ( thanks Cwatters for this link you posted elsewhere ) that installations aren't being maintained

    http://www.greenbuildingpress.co.uk/article.php?category_id=1&page=3&article_id=213
    • CommentAuthorsinnerboy
    • CommentTimeJul 1st 2009 edited
     
    My experience of talking to "the HRV industry" in Ireland is that the "double glazing /2nd hand car merchant" has found a new opportunity . Ask them any hard questions at trade fairs and see them spoof and flap .

    I my view that industry , in Ireland anyhow - and I suspect in the UK too - does not know or care about the issues I have posted in this thread .

    "Build tight and ventilate right" - a snappy Blairite sound bite - that's all . My view .

    Proceed with caution .
    • CommentAuthortomsusweb
    • CommentTimeJul 2nd 2009
     
    Anyone want to defend HRV a bit? I was starting to be converted. Are Sinnerboy's fears sensible? Or if it's installed and maintained correctly will you end up with much better air quality?
    • CommentAuthorTuna
    • CommentTimeJul 2nd 2009
     
    That first report seems to me to be pointing out areas where there may be a risk, not where products are systematically causing problems. The risks include 'the HVAC may be dirty when installed' (is that really something that can't be fixed?) and 'poor control of temperature...due to absense of cooling' (should you be suprised if a ventilation system cannot act like an air conditioner?). Hmmm...

    The vague reference to health problems is so inconclusive that I cannot take it seriously. My sister's house has a fusty old hot air heating system from the 70's and I can fully understand how that might affect the occupant's health, as might communual systems in the apartment blocks common in Europe. A modern domestic system would appear to have no obvious vector for health problems and other than the issue of humidity, shows little difference from just opening the windows. In fact, the possibility of dust and allergen free ventilation should offer better air quality?

    The only real lesson to take from that report is that if you install a ventilation system, or buy a house with one installed, you should commit to regular maintenance cycles. In that sense, it's no different from the maintenance you should carry out on your hot water system (you do get your boiler serviced on an annual basis don't you?).

    As for the fire risks.. I'm really not sure about those. In a domestic setting, proper use of smoke alarms and the relatively limited scope of a ventilation system seem to mitigate the actual risk. In apartment blocks and large institutional settings I would imagine the risks to be much more severe.

    In general, ventilation systems blow fresh air from the outside into the living areas, which would suggest that transmission of smoke through a building would be reduced in the first case? sinnerboys link seem to be a bit broken so I'm not sure how much of a risk HVAC systems play in small domestic installs as distinct from larger and communual systems.
    •  
      CommentAuthordjh
    • CommentTimeJul 2nd 2009
     
    In the UK, the official term is MVHR - mechanical ventilation with heat recovery. I don't think the issues are connected with the heat recovery, in general they apply equally to plain MV. And that is used in huge numbers of offices, public buildings and homes around the world. There's also an enormous quantity of discussion about its pros and cons. In short: "nothing new to see here, please move along". Just my opinion.
    • CommentAuthorsinnerboy
    • CommentTimeJul 2nd 2009 edited
     
    The link about fire risk is broken - so to summarise

    Any upper floor in any house must be min 30 mins fire resistant . So the typical timber floor requires a fully intact floor deck ( t+g / osb / ply etc ) and fully intact ceiling below . Where plasterboard is cut away for vent grilles - the fire resistance is lost .( This dawns on some - not all - in the case of recessed lighting too )

    A fire

    http://www.youtube.com/watch?v=TKPfkrGDv7U&feature=related

    http://www.youtube.com/watch?gl=GB&hl=en-GB&v=jQV_MJwYQ3k&feature=related

    will very quickly melt the outlet and attack the floor cavity

    Unless you fit one of these at each outlet

    http://www.scottaire.co.uk/circularvalves2.html

    The fan unit should also be linked to the fire alarm / smoke detector installation to power down .

    ( but don't bother asking anyone in the industry about this .... they'll think your mad )
    • CommentAuthorsinnerboy
    • CommentTimeJul 2nd 2009 edited
     
    Posted By: djhIn the UK, the official term is MVHR - mechanical ventilation with heat recovery. I don't think the issues are connected with the heat recovery, in general they apply equally to plain MV. And that is used in huge numbers of offices, public buildings and homes around the world. There's also an enormous quantity of discussion about its pros and cons. In short: "nothing new to see here, please move along". Just my opinion.


    They ( MVHR / HRV ) are not used in large number in houses in UK/IRL yet .
    • CommentAuthorsinnerboy
    • CommentTimeJul 2nd 2009 edited
     
    Posted By: tomsuswebAnyone want to defend HRV a bit? I was starting to be converted. Are Sinnerboy's fears sensible? Or if it's installed and maintained correctly will you end up with much better air quality?


    Tom - I am not attacking HRV ( MVHR ) .

    I am saying there are risks . If you are a self builder and informed - that's fine . If you are a disinterested tenant however ... Well we live in a "set and forget" culture . Filters won't be replaced . Filters ARE NOT being replaced People will get sick .

    I can "see" before too long Paxo on BBC2 getting stuck into some industry spokesman / environment minister ....
    • CommentAuthorCWatters
    • CommentTimeJul 5th 2009
     
    Posted By: tomsuswebAnyone want to defend HRV a bit?


    We've had ours in for two years and it does give the house a fresh feel. No condensation not even in the bathroom. Towels seem to dry more quickly. I'd definitly put one in again but I'd want a better job done of the installation.
  1.  
    I'm planning to use MVHR as an element of a low energy renovation of
    my house.

    To gather information I have looked at the websites of manufacturers
    of what I perceive as high quality systems (eg. Drexel und Weiss,
    Paul, Zehnder Comfosystems). In their native territories they appear
    to operate as one-stop-shops for whole MVHR systems with a design
    service, their own range of air distribution products, air inlets and
    outlets, and other accessories. For example, Zehnder Comfosystems
    have their own ComfoTube duct system with a smooth, hygenic lining
    (Clinside). One of their brochures shows a miniature chimney sweep's
    brush to clean it.

    My impression of the UK market is that suppliers use a MVHR unit,
    possibly badge engineered to their own branding, with a ducting system
    from another manufacturer. I'm not sure if this is because of UK
    specific regulations or for other reasons.

    While it is relatively easy to find sales literature on a wide variety
    of MVHR systems I have yet to find a good review of MVHRs and the
    features that are appropriate for the UK climate. Something that
    would answer questions such as these:

    * What is required for fire safety; frost protection; humidity
    control (enthalpy heat exchanger); cleaning and routine
    maintenance?

    * Does the MVHR control system need to be aware of wet room use?

    * Does the MVHR control system need to interact with the cooker
    hood?

    * Will a ground loop (brine or air) provide a useful amount of
    cooling in a UK heatwave?

    I would rather be in the position where I could specify the MVHR
    system requirements rather than being sold a system that suits a sales
    person's requirements!

    There is some useful information in this forum and the AECB Forum
    (http://www.aecb.net/forum) has more technical information.

    Anyone know of a good, up-to-date MVHR review?
  2.  
    Posted By: sinnerboy
    Unless you fit one of these at each outlet

    http://www.scottaire.co.uk/circularvalves2.html" >http://www.scottaire.co.uk/circularvalves2.html


    Posted By: sinnerboy (in " MVHR with humidity recovery?" thread)
    2. Insist that all ceiling inlet outlets are fitted with fusible link dampers - intumescent collars do not work


    I'm confused by these comments as both fusible links and intumescent collars depend on heat to activate them. Granted, the fusible links may be quicker in operation. Isn't the major risk in fires from smoke and other combustion products that may be spread through ducting for some time before heat activated devices operate?
  3.  
    Posted By: john_connett'm confused by these comments as both fusible links and intumescent collars depend on heat to activate them. Granted, the fusible links may be quicker in operation. Isn't the major risk in fires from smoke and other combustion products that may be spread through ducting for some time before heat activated devices operate?
    Over here, where HRV and ducted air heating systems are common, no-one uses fusible links or intumescent collars in residential applications. If you want to be extra careful, link your smoke detector to the power supply of the HRV so it is shut off if smoke is detected.

    Paul in Montreal.
    • CommentAuthorsinnerboy
    • CommentTimeJul 8th 2009
     
    Look at the You Tube videos I posted and observe the stated temp rises . And how quickly that happens .
    Look at the temp settings at which fusible links activate

    Fusible links act significantly faster than intumescent collars . I say that having read fire test certificates . The fusible link will act within minutes of the outbreak of fire . Intumescent collars will not . They will not seal up untill well after ferociously hot combustions gases have entered into your floor cavities . And killed you .
    • CommentAuthorsinnerboy
    • CommentTimeJul 8th 2009 edited
     
    Posted By: Paul in MontrealOver here, where HRV and ducted air heating systems are common, no-one uses fusible links or intumescent collars in residential applications. If you want to be extra careful, link your smoke detector to the power supply of the HRV so it is shut off if smoke is detected.

    Paul in Montreal.


    Posted By: sinnerboyHRV and fire

    I don't believe the risks are understood - or if they are - that they being addressed by the HRV industry

    • CommentAuthorsinnerboy
    • CommentTimeJul 8th 2009
     
    I queried an installer as to why fusible links were not a default selection . Cost of ordinary ceiling outlet €25.00
    Cost of fusible link outlet €40.00 . Every little helps . Him that is .
  4.  
    The majority of houses in North America (particularly the US) have forced air heating systems. These carry 10x the volume of air that an HRV system does. If there were serious fire issues with this type of heating system, then we'd be hearing about it in the news all the time. Not that there are no risks, but the mitigation of the risk is a set of good smoke detectors. That's the compromise that's used.

    I couldn't find any references to the dangers of forced air heating/cooling systems with respect to fire in residential construction.

    With a good smoke and/or CO detector coupled to the HRV's fan control, I really don't think the risk is any worse than an open window (which also increases the rate of spread of fire and smoke).

    Paul in Montreal.
    • CommentAuthorsinnerboy
    • CommentTimeJul 8th 2009 edited
     
    Can not agree . Smoke detectors are no compromise . Look carefully at the American youtube clip to see this in the most graphic format .


    http://www.bamn.org/prHRVrecall.cfm

    http://www.nachi.org/forum/f48/venma...concern-11412/

    http://www.bluemountainscourierherald.com/courierherald/article/61577

    Can you put a perspective on these reports ?
  5.  
    I've seen many videos of house fires. The one common element is polyurethane foam in furniture as the biggest risk. Oh, and chip pans. I've seen the recall notices about the HRVs you mention above - but I haven't seen any reports of actual fires over here caused by them, let alone enhanced by the system. As I said, most people have forced air heating/cooling and the duct sizes and air volumes transported are much larger. Best way to reduce house fires is to ban smoking indoors and the cooking of chips. Washing machines are also a surprisingly large source of housefires (water + electrics is not a good combination) as are dishwashers, particularly those which have heating elements from drying which can set plastic items on fire etc. You're correct that air ducts are a risk, but this has to be set in proportion to everything else. Without a smoke detector, you're toast, as it were, no matter if you have an HRV or not. I suspect it's fear of the unusual as such systems are rare in the UK - just like many people here are terrified of gas stoves because they associate gas with explosions. And, of course, houses do explode due to gas leaks - probably more than burn down due to HRV enhanced fires.

    Paul in Montreal.

    p.s. I have both gas stoves and forced air heating / cooling (in one house) as well as all three in the other
    • CommentAuthorsinnerboy
    • CommentTimeJul 8th 2009 edited
     
    You have outlined common risks as to how fires start . I am talking about containment of the outbreak .

    Without smoke detector(s) you don't comply with min b regs .

    I insist - the risks are real and simply preventable . So far advocates of HRV have yet to face up to this
    • CommentAuthorsinnerboy
    • CommentTimeJul 8th 2009 edited
     
    Posted By: john_connett
    * What is required for ; cleaning and routine maintenance?


    Canadian advice here

    from the Canada Mortgage and Housing Corporation recently, on what you need to do to keep your MVHR (which they refer to as HRV) systems tickety-boo.

    MAINTAINING YOUR HEAT RECOVERY VENTILATOR (HRV)

    Your heat recovery ventilator (HRV) can help make your house a clean, healthy living environment, while keeping fuel bills down. But your HRV can't do all this without your help.
    It only takes seven simple steps to keep your HRV happy…

    The Seven Steps to a Happy HRV

    First turn off the HRV and unplug it.

    • Step 1: Clean or Replace Air Filters
    Dirty or clogged filters can lower ventilation efficiency. Try to clean your filters at least every two months. Filters in most new HRVs can be easily removed, cleaned with a vacuum cleaner, then washed with mild soap and water before being replaced. Older units have replaceable filters. If your HRV is easily accessible, this is a 5 minute job.

    • Step 2: Check Outdoor Intake and Exhaust Hoods
    Remove leaves, waste paper or other obstructions that may be blocking the outside vents of your HRV. Without this vital airflow, your HRV won't function properly. During winter, clear any snow or frost buildup blocking outside vents.

    • Step 3: Inspect the Condensate Drain
    Check to see if your HRV has a condensate drain, a pipe or plastic tube coming out of the bottom. If it does, slowly pour about two litres of warm, clean water in the drain inside the HRV to make sure it's flowing freely. If there's a backup, clean the drain.

    • Step 4: Clean the Heat Exchange Core
    Check your HRV owner's manual for instructions on cleaning the heat exchange core. Vacuuming the core and washing it with soap and water will reduce dust which can build up inside the core.

    • Step 5: Clean Grilles and Inspect the Ductwork
    Once a year, check the ductwork leading to and from your HRV. Remove and inspect the grilles covering the duct ends, then vacuum inside the ducts. If a more thorough cleaning is required, call your service technician.

    • Step 6: Service the Fans
    Remove the dirt that has accumulated on the blades by gently brushing them. Most new HRVs are designed to run continuously without lubrication, but older models require a few drops of proper motor lubricating oil in a designated oil intake. Check your manual for complete instructions.

    • Step 7: Arrange for Annual Servicing
    Your HRV should be serviced annually. If you are not comfortable doing it yourself, contact a technician accredited by the Heating, Refrigerating and Air Conditioning Institute of Canada. Make sure the technician you call has been trained by the manufacturer of your HRV.

    Check Your HRV Balance: the Garbage Bag Test
    HRVs need to be balanced, with the fresh air flow matching the exhaust flow. If you do not know if the HRV was balanced when installed or if you have changed or added HRV ducts, you may want to check the balance with the following simple procedure. This rough test will take about 10 minutes.

    Use a large plastic leaf collection bag, typically 1.2m (48 in.) long. Untwist a wire coat hanger. Tape the wire to the mouth of the bag to keep it open. You now have a garbage bag flow tester. Go outside to where your HRV ducts exit the foundation.

    • Step 1:
    Crush the bag flat and hold the opening tightly over the exhaust hood. The air flowing out of the hood will inflate the bag. Time the inflation. If the bag inflates in eight seconds or more, go to Step 2. If the bag inflates in less than eight seconds, turn the HRV to a lower speed, and repeat the test. Then go to Step 2.

    • Step 2:
    Swing the bag to inflate it and hold the opening against the wall around the HRV supply hood. The air going into the HRV will now deflate the bag. Time the deflation. If your HRV is balanced, air going into the HRV will balance the air coming out of the HRV. The inflation and deflation times should be roughly equal. If you find that the bag inflates twice as fast as it deflates, for instance, your HRV is unbalanced. If you can see no problem with the filters that would cause such an imbalance, you should call a service person to test and adjust your HRV.

    Please don't ignore your HRV. Just a little bit of your time is all it takes to keep it running smoothly.

    • April or May
    — Turn dehumidistat (the adjustable control on many HRVs which activates the HRV according to relative humidity) to HIGH setting or to OFF.

    • September or October
    — Clean core
    — Check fans
    — Check condensate drain
    — Check grilles and ducts in house
    — Reset humidistat (40%–80%)
    • CommentAuthorTuna
    • CommentTimeJul 8th 2009
     
    Sinnerboy - you seem to be conflating two separate risks.

    The articles you link to are talking about a product recall for a specific set of MHRV units that pose a fire risk due to a manufacturing defect.

    Yet you talk about MHRV units increasing the spread of fire.

    Those are two different issues - with two different solutions, and clearly two different levels of risk.
    • CommentAuthorsinnerboy
    • CommentTimeJul 8th 2009 edited
     
    They are separate risks . I'm not conflating anything . Assuming that manufacturers no longer produce defective and hazardous goods there remains the matter of the installation .

    Elements of structure must , in compliance with fire regulations - resist fire . I have already described that by simply inserting a standard vent outlet into a plasterboard ceiling - that the fire resistance of that floor is totally compromised . In the event of an outbreak of fire the ceiling outlet will melt and the fire will travel rapidly into the floor cavity .

    Flashover will occur within minutes to set the very floor structure alight - That same structure that is - in the case of a typical domestic construction - required to resist fire for 30mins . It will not resist for longer than 2 mins .

    Smoke and other combustion gases will with great force find in the floor deck over , every crack , loose fit , knot hole and expansion-gap-against-the-wall and quickly intoxicate and then kill anyone on that floor .

    So why hasn't anyone reported this ? Surely we would have heard ? Come off it . Why wait for that ?

    Again I say - simple solution . Fit fusible link fire outlets .

    And co link the motor to power down when fire detection system activates .

    But no does this . Because "no one makes us"
    • CommentAuthorsinnerboy
    • CommentTimeJul 11th 2009 edited
     
    • CommentAuthorsinnerboy
    • CommentTimeJul 11th 2009 edited
     
    http://www.cmhc-schl.gc.ca/publications/en/rh-pr/tech/96215.htm

    Canada 1999 - 10 years after HRV first appear there

    "In some installations, HRVs may not be realizing their full potential due in part to installation faults and in part to a lack of homeowner understanding. Existing information transfer mechanisms need to be improved. As many of the problems noted in the existing systems could have been prevented by proper installation, installers should be required to pass the installation and designers training programs offered by the HRAI. Installers should also be encouraged to offer HRV maintenance agreements to home owners and/or impress to them the importance of proper operation and maintenance.

    The issue of most concern is that of properly balancing HRVs. In one house, the supply fan was not functioning. The homeowners were not aware of the problem because they still heard the sound of the exhaust fan. The result was backdrafting of the fireplace and the potential for backdrafting of other combustion appliances. HRV systems should be installed with balancing dampers and permanently installed flow measuring stations. Also of great concern is that filters were found to be dirty and air intake clogged. Clearly lack of owner appreciation of the potential hazards of a poorly maintained and operated HRV is also an issue of concern. The industry should also be encouraged to develop trouble indicating devices (e.g., trouble lights) or fail safe controls to indicate component failure or overdue maintenance.

    Other recommendations for improving HRVs include limiting the use of flexible ductwork or encouraging proper design and installation. Cross-Furnace installations, which are most affected by varying the furnace speed, should also be discouraged. Circulation systems must be in operation to distribute fresh air throughout the house when an extended or simplified system HRV is in operation; controls should be provided with all such systems to allow continuous operation of the furnace fan at a low speed. (Such interlocking is now a requirement of the 1995 National Building Code of Canada.)

    In order to improve HRV system performance, the regulatory agencies should continue with the current trend towards greater regulation regarding contractor training and certification standards, and HRV system installation practice and system requirements."

    Will history repeat itself this side of the Ocean ?
  6.  
    ...all sorts of requirements for HRV in Part B...

    page 22

    J
    • CommentAuthorsinnerboy
    • CommentTimeJul 12th 2009 edited
     
    That guidance relates only to additional measures required for larger domestic properties . Fundamantally -

    do not expect to cut a hole in your plasterboard ceiling , fit a pvc item into it , and expect those above to remain safe from fire

    and if a fire should start - do not allow your hrv/mvhr system continue to supply it the oxygen it requires to really thrive
  7.  
    Posted By: sinnerboyThat guidance relates only to additional measures required for larger domestic properties


    It relates to properties with a storey over 4.5m from ground level....

    J
  8.  
    Given that other countries, such as Germany, Austria and Switzerland, have greater practical experience of the deployment of MVHRs, has this resulted in regulations or industry codes of best practice that are more stringent than the UK building regulations?

    If the ducting for a MVHR crosses floors isn't it more effective to place fire stops at the floor crossings rather than the room outlets as suggested by sinnerboy?
   