			<![CDATA[Hi there,<br /><br />I am currently building  t/f house which will have 180mm of Warmcell insulation and 300mm to the roof.  The floor will be 100mm of Kingspan or Celotex, sitting on the concrete slab with ufh and 65mm of screed.<br /><br />We are currently at the first fix stage with the plumbing going in very soon.<br /><br />My builder is good but I think that regarding some aspects, I am working outside his comfort zone.  He is telling me that the next stage will be insulation and drylining, before slab insulation, ufh and screed.  I think it should be the other way round.<br /><br />Similarly, he maintains that the staircase should be installed so that it is sitting on the slab; in his opinion, it should be installed before the g/f insulation and screeding.  I feel that it should be installed after the g/f screed and may be after the floor finish is laid.<br /><br />Since I have never built a house before, I am somewhat uncertain as to the correct order.  But I feel I am right and his way could be creating a lot of problems down the line.<br /><br />So what is the suggested order of doing things?  I know there is not 'right or wrong' but I would be grateful for some suggestions.<br /><br />Many thanks,<br /><br />Rex]]>
		</description>
	</item>
	<item>
		<title>Correct order of doing things</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4254&amp;Focus=57728#Comment_57728</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4254&amp;Focus=57728#Comment_57728</guid>
		<pubDate>Fri, 10 Jul 2009 09:53:44 +0100</pubDate>
		<author>Timber</author>
		<description>
			<![CDATA[Rex<br /><br />Re ground floor<br /><br />I assume you have the TF kit sat on the floor slab, you will then be installing insulation and screed around it?<br /><br />If that is the case, if you don't dryline first, you will need to provide timber noggings between the studs in order to stop the screed pushing the dpm or whatever into the stud voids and to pic up plasterboard edge support.<br /><br />If you dryline first, then this is not an issue. It is also easier to detail the vcl/dpm/dpc lap and junction for air tightness if you drylin first. <br /><br />However, either way is possible.<br /><br />I must warn you, however, If your consruction is as above, with the kit sat on the slab, you must be really really really really really careful of the internal load bearing and non load bearing walls. If they are sat on the slab, when you install the insualtion and screed they will be burried below internal finished floor level. If you ever have a leak or something like that, water can pour down into that trench formed by the timber frame. Because the timber is surrounded on three sides by dpm etc, then the moisture cannot easily disipate and can quite easily stay there for an extended period of time. This can lead to decay of the timber sole plates and bottom of the studs. Bad news if it is a load bearing wall.<br /><br />As for the stairs, it depends what type of stairs it is. If it is a normal domestic timber stairs, that should be installed after the screed is laid.<br /><br />Timber]]>
		</description>
	</item>
	<item>
		<title>Correct order of doing things</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4254&amp;Focus=57732#Comment_57732</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4254&amp;Focus=57732#Comment_57732</guid>
		<pubDate>Fri, 10 Jul 2009 10:34:59 +0100</pubDate>
		<author>tony</author>
		<description>
			<![CDATA[Traditional methods do not take into account air sealing or insulation.<br /><br />Do all service penetrations early, make sure all insulation goes in all joined up with no gaps and that you air sealing barrier is impossible to damage during construction.<br /><br />It would be possible to put a small piece of insulation in under the bottom of the stairs and join to it later.<br /><br />watch out for thermal bridging.]]>
		</description>
	</item>
	<item>
		<title>Correct order of doing things</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4254&amp;Focus=57770#Comment_57770</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4254&amp;Focus=57770#Comment_57770</guid>
		<pubDate>Sat, 11 Jul 2009 08:01:35 +0100</pubDate>
		<author>Rex</author>
		<description>
			<![CDATA[Many thanks for your relpies.<br /><br />Timber,<br /><br />You have given me cause for concern!  Yes, it is a trad t/f build; sole plates onto the g/f slab with a dpc below the first sole plate.  There are sufficient sole plates to build up to the finished floor level.  There is then another noggin for the bottom of the drylining board to attach to.  Or to put it another way, there are five layers of 180mm x 80mm timber sitting on the slab.<br /><br />I figured the plan will be, insulation, dpm over the top and taped up the soleplates, ufh pipework and then screed.  I hear what you say regarding the soleplates being in a 'trench' and a (hopefully not) future water ingress, but what is the solution?<br /><br />The stairs will be normal.  Am thinking of MDF frame which will have the bamboo tread cover to match the rest of the g/f floor finish.  I presume the screed at the base of the staircase will be sufficiently strong to not 'dent' the insulation over time?<br /><br />Tony,<br /><br />As mentioned above, the build-up will be insulation, dpm, ufh, screed and final floor finish.  I figure the stairs at the bottom will sit on either the screed or the final floor, so there should not be a 'break' in the insulation.]]>
		</description>
	</item>
	<item>
		<title>Correct order of doing things</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4254&amp;Focus=57787#Comment_57787</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4254&amp;Focus=57787#Comment_57787</guid>
		<pubDate>Sat, 11 Jul 2009 15:11:37 +0100</pubDate>
		<author>CWatters</author>
		<description>
			<![CDATA[Screed under the stairs will be fine but plan the UFH pipe layout carefully. Places to omit UFH pipe include:<br /><br />Under the bottom of the stairs (it needs fixing down)<br />Around the WC pans and basin pedestals and possibly under the bath (same reason)<br />Under the fridge/freezer.<br />Under a floor mounted boiler.<br /><br />Real fires also need attention. Some types need a constructional hearth so no insulation or UFH allowed under the screed there. If it's a stove with legs chances are it's rated not to raise the hearth above 100C so you can put flamable insulation underneath the screed.  This type of stove only needes a slab of something to stand on (eg tiles, 20mm granite or even glass).<br /><br />If you have a wooden floor some companies say not to put rugs on top or it can damage the floor.  <br /><br />Aside: I favour shower trays and enclosures over wet rooms but I hate the pedestal most builders put under the shower. With a bit of planning you can have the tray either flush with the tiled floor or resting on it. Well worth the effort in my view. Take a look at top access traps with metal domed covers from Eurobath.]]>
		</description>
	</item>
	<item>
		<title>Correct order of doing things</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4254&amp;Focus=57817#Comment_57817</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4254&amp;Focus=57817#Comment_57817</guid>
		<pubDate>Sun, 12 Jul 2009 09:53:59 +0100</pubDate>
		<author>Timber</author>
		<description>
			<![CDATA[Rex, wow, that is ALOT of sole plates!<br /><br />Do you have a similar setup on the external walls as well? <br /><br />As for what to do, there is not a lot you can do now really, other than make sure that the trench is not fully water tight, so that if water does get in there it can drain away under the insulation and away from the timber. <br /><br />And just remember that the sole plates are burried. If you have a major (or minor leak) just keep an eye on the sole plate moisture contents. If it stays above 20% for too long, there may be problems.<br /><br />Make sure that the moisture content of the sole plates (core using a hammer probe) is below 20% before the screed is poured. If over 20% you are trapping a lot of moisture in the wood right from the outset. <br /><br />The way to get round this is to construct dwarf walls for the tf kit to sit on to get it up to FF level. its a bit of a faf, but a much much more robust solution. Or build a structurally insulated foundation system. <br /><br />Best of luck<br /><br />Timber]]>
		</description>
	</item>
	<item>
		<title>Correct order of doing things</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4254&amp;Focus=57847#Comment_57847</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4254&amp;Focus=57847#Comment_57847</guid>
		<pubDate>Mon, 13 Jul 2009 08:01:07 +0100</pubDate>
		<author>Rex</author>
		<description>
			<![CDATA[Again, thanks for the replies.<br /><br />CWatters,<br /><br />No problems there, UFH will only be routed in open areas.  Apart from any other reason, there is no point in heating under the bath, etc.<br /><br />Timber,<br /><br />Bit late now for the dwarf walls but is that the 'normal' way with t/f.  My t/f company wanted a poured concrete slab as that is easier to 'gun' the sole plates onto.  They then built up using more of the same wood, to get to final floor level.  Surely a dwarf wall could crack when the nails are  fired in.  <br /><br />Of course, the sole plates could have been bolted, but I have never seen that in the UK, only in Japan where they have earthquakes!<br /><br />As for drainage channels, have not considered that.  Good idea, but since the slab is flat, where to drain to and how?<br /><br />Rex]]>
		</description>
	</item>
	<item>
		<title>Correct order of doing things</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4254&amp;Focus=57849#Comment_57849</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4254&amp;Focus=57849#Comment_57849</guid>
		<pubDate>Mon, 13 Jul 2009 09:26:24 +0100</pubDate>
		<author>Timber</author>
		<description>
			<![CDATA[Poured concrete is much easier to shot fire the sole plates to, however you can also shot fire into blockwork upstands! Engineering brick is another option. Sole plates can be shot fired, plastic plug and screw fixed or bolted. Shot firing or plug and screw fixings are the most common and popular. <br /><br />This issue with burried sole plates is still one that I am fighting! A lot of companies still build in the same way as your project. I personally have seen the issues that can arrise with burried sole plates, and so try and diswade people from doing it that way. Plus with upstand you can gain better level threshold details, as it brings the internal finished floor level down (or can do!) All structural timber must be 150 mm above external ground level, so if your slab is 150 above, then you lay another 150 of insulatino and screed, internal FF level becomes at least 300 mm  above. <br /><br />As for the drainage, the water won't really drain anywhere, but at least less of it will stay around the sole plates.<br /><br />Out of interest, were all site cut ends of sole plates brush treated with preservative? The sole plates will be presevative treated, but the treatment only penetrates a few mm, so when you cut a length of timber on site, it exposes an untreated end. These untreated ends are very vulnerable to drawing up moisture and decay. All site cut ends should be either brush treated with presevative or dunked in a bucket of the stuff.<br /><br />I would suggest going round all cut ends and treating with a good preservative (that is compatible with the origional treatment used) and making sure all the timber is protected as well as possible.<br /><br />Don't stress about it too much, hundreds of thousands of tf houses and flats will have been built like this, but it is far from an ideal detail. Always remember when building with timber is to protect it from moisture, but let it breathe! <br /><br />Timber]]>
		</description>
	</item>
	<item>
		<title>Correct order of doing things</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4254&amp;Focus=57996#Comment_57996</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4254&amp;Focus=57996#Comment_57996</guid>
		<pubDate>Wed, 15 Jul 2009 08:17:11 +0100</pubDate>
		<author>Rex</author>
		<description>
			<![CDATA[Timber,<br /><br />Again, thanks for your comments.  <br /><br />No, I do not think the cut ends were treated.<br /><br />I guess it would be an idea to moisture check the sole plates as it house was erected in December/Jan and did not have any roof covering for some time.  When the snows / rain came, the sole plates of course held considerable quantities of water in place.  I was not happy at the time and did talk about the sole plates getting saturated with the T/F company, but they (of course) gave me their assurance; which I am cynical enough to know that it means nothing.<br /><br />However, the t/f company have gone into liquidation, so there will be no come-back.<br /><br />I have heard about wrapping 1&quot; polystyrene in plastic and building a barrier around the slow plates so the after the insulation and screed has  gone down, this can be removed to create an air gap.  Is this practical?  <br /><br />There is a likelihood that I will not worry too much about this as if a flooding occurs, the damage will be considerable.  We have planned to use Warmcell insulation, and if that gets wet, I assume it will all have to be removed.<br /><br />Given that HMG are so concerned about organizing every aspect of our lives including how houses are built via the Building Control regs, I am now surprised that block soleplates are not an obligation for t/f house construction.  <br /><br />Next time, it will be better!<br /><br />Rex]]>
		</description>
	</item>
	<item>
		<title>Correct order of doing things</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4254&amp;Focus=57997#Comment_57997</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4254&amp;Focus=57997#Comment_57997</guid>
		<pubDate>Wed, 15 Jul 2009 09:16:44 +0100</pubDate>
		<author>Timber</author>
		<description>
			<![CDATA[Rex - yeah definately check the CORE moisture content of the sole plates.<br /><br />They may have dried down now with the warm weather, but may still be very wet.<br /><br />Get a moisture meter and a hammer probe (two pins on a slide hammer that you can drive into the timber) and take some sample readings. All timber should be at 20% moisture content or less prior to 'filling in'.<br /><br />The removable insulation sounds like a good idea, but that may  create a thermal bridge down to the slab, so they could be removed to allow further drying, and then replaced once in service.<br /><br />The flooding statement is true!<br /><br />I would like to see warrantee bodies take this up! buiding control never will, nor building regs. I once spoke to a fairly high up technical bod at LABC, and he stated that as long as it stood up at the time of sign off, they wern't worried about longevity of some of these areas!<br /><br />Anyway, I hope I havn't scared you too much with this. chances are it will all be fine, but just try to mitigate any possible week links.<br /><br />Timber]]>
		</description>
	</item>
	<item>
		<title>Correct order of doing things</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4254&amp;Focus=58058#Comment_58058</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4254&amp;Focus=58058#Comment_58058</guid>
		<pubDate>Wed, 15 Jul 2009 17:53:45 +0100</pubDate>
		<author>James Norton</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: Timber</cite>I would like to see warrantee bodies take this up!</blockquote><br /><br />Had detailed this way myself with top of slab at +150 and frame built of slab with DPM insulation and gyvlon screed over slab, effectively inboard of the frame. Was told by my framer that Zurich and NHBC would not approve, suggested a block as comments above. <br /><br />J]]>
		</description>
	</item>
	<item>
		<title>Correct order of doing things</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4254&amp;Focus=58063#Comment_58063</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4254&amp;Focus=58063#Comment_58063</guid>
		<pubDate>Wed, 15 Jul 2009 18:16:01 +0100</pubDate>
		<author>Timber</author>
		<description>
			<![CDATA[Ironically James, this is the one area where it CAN be done, due to the wall breathing out into the external wall cavity!!!!!!!!! It is only covered over on the inside.<br /><br />It is the internal walls that are at risk!<br /><br />Plus if you put a block upstand around the external wall perimeter, it can lead to thermal bridging at the foot of the external wall!<br /><br />Timber]]>
		</description>
	</item>
	<item>
		<title>Correct order of doing things</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4254&amp;Focus=58345#Comment_58345</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4254&amp;Focus=58345#Comment_58345</guid>
		<pubDate>Mon, 20 Jul 2009 17:45:01 +0100</pubDate>
		<author>James Norton</author>
		<description>
			<![CDATA[Well that's what I though too... as for the internal walls d'you know I just hadn't thought of that! some f@#king architect I am, and on my own house!<br /><br />thankfully in my case I think the ones in questions can be made non load bearing and positioned between screed and ceiling. However if not, I came across this little chap, no idea how expensive or if it can take fixings...<br /><br />J<br /><br /><a href="http://www.foamglas.co.uk/building/foamglas_perinsul/#cell14625" target="_self" rel="nofollow">http://www.foamglas.co.uk/building/foamglas_perinsul/#cell14625</a>]]>
		</description>
	</item>
	<item>
		<title>Correct order of doing things</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4254&amp;Focus=58366#Comment_58366</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4254&amp;Focus=58366#Comment_58366</guid>
		<pubDate>Mon, 20 Jul 2009 21:07:52 +0100</pubDate>
		<author>Timber</author>
		<description>
			<![CDATA[James, making all the internal walls non loadbearing is the idea solution. Plus it allows you to chop and change rooms aroung over time if you wish!<br /><br />Not practical in all cases though - spans depending!<br /><br />That foamglas thing looks good! I have oftern thought about plastic (yeah i know) sole plate spacer!<br /><br />The other option is to go with an structurally insulated foundation system.<br /><br />Timber]]>
		</description>
	</item>
	<item>
		<title>Correct order of doing things</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4254&amp;Focus=58563#Comment_58563</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4254&amp;Focus=58563#Comment_58563</guid>
		<pubDate>Thu, 23 Jul 2009 22:03:57 +0100</pubDate>
		<author>cookie</author>
		<description>
			<![CDATA[All, Sorry not had chance to read whole thread.<br /><br />Only thing I read that I want to put my 2 pennith in is the stairs. Its not a problem to install the stairs first, this is normal good practice for safety and access anyway. if you refuse expect a bill for tempory stairs. The usual way is to noggin under the stairs. The screeder then just screeds up to and under the rest of the stairs (well a good screeder does)<br /><br />Hope that helps.<br /><br />Cookie (sorry don't have much time at the moment to answer posts)]]>