Home  5  Books  5  GBEzine  5  News  5  HelpDesk  5  Register  5  GreenBuilding.co.uk
Not signed in (Sign In)

Categories



Green Building Bible, Fourth Edition
Green Building Bible, fourth edition (both books)
These two books are the perfect starting place to help you get to grips with one of the most vitally important aspects of our society - our homes and living environment.

PLEASE NOTE: A download link for Volume 1 will be sent to you by email and Volume 2 will be sent to you by post as a book.

Buy individually or both books together. Delivery is free!


powered by Surfing Waves




Vanilla 1.0.3 is a product of Lussumo. More Information: Documentation, Community Support.

Welcome to new Forum Visitors
Join the forum now and benefit from discussions with thousands of other green building fans and discounts on Green Building Press publications: Apply now.

The AECB accepts no responsibility or liability for any errors or omissions in the content of this site. Views given in posts are not necessarily the views of the AECB.



  1.  
    Hi all,

    My question is motivated by the benefit of a condensing boiler installed in an existing heating and hot water system, where hot water has to be heated to above 65 deg (legionella) and radiators operate at approx 70 deg - as not being under floor and existing. In both circumstances the boiler must heat to say 70 deg. Does this mean that condensing will only occur when the boiler is first turned on and begins to heat up the system, or can the boiler condense partially anyway even in some circumstances (e.g. when the heating return is say 40 deg). What kind of efficiency might one expect in reality (as oppossed to the usual "high"claims). WHat happens if the system is only heating water to above 60?


    Matt
    • CommentAuthorbrig001
    • CommentTimeNov 1st 2009
     
    Found this post by Water Systems (about half way down this http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=3494&page=3 page.

    Cranfield University did studies and concluded that 15% energy savings can be had by using thermal storage. A Google brings it up.

    The lower the return temperature of a condensing boiler the greater the efficiency. If you look at a gas condensing boiler graph, the boiler starts to condense at around 53C return water temperature. That is the key point. Just above and below doesn't make that much difference in efficiency. One the return temperature drops to 30C the efficiency rises sharply.

    At 65C the efficiency is 87%
    At 53C (dew-point) the efficiency is 89%
    At 30C the efficiency is 97%
    At 25C the efficiency is 98-99%
    At 20C the efficiency is near 100%

    So 10% more efficient using lower temperatures, which a heat bank gives. A cylinder heated by a coil will not get near the condensing efficiency re-heat figures of heating a cylinder directly.

    Look at this:
    http://www.keston.co.uk/downloads/pdf/cel25-b.pdf
    There is a graph here (the boiler is now discontinued)

    A heat bank using a plate heat X will give temperatures at the bottom of the store at 5C above the incoming mains temperature (see Any's post to confirm this). That could be 10-15C in the bottom of the cylinder, while 65-70C at the top. When the boiler kicks in the boiler efficiency is approaching near 100% on most of the cylinder re-heat. Have the heat bank set to 65C and the efficiency is beyond question.

    HTH,
    Bri.
    • CommentAuthorCWatters
    • CommentTimeNov 1st 2009
     
    It's worth noting that some boilers (eg Grant Oil boilers) should not be operated with a return temperature below about 40C. They advise using a mixer to maintain the return temperature above 40C.
    • CommentAuthormike7
    • CommentTimeNov 1st 2009
     
    Have I got this right? :- Non- condensing boilers had high exhaust temperatures in order to avoid condensation at ANY time, which would cause corrosion of the heat exchanger. This meant they wasted heat via the high exhaust temps, AND by failing to extract any of the latent heat available by condensation.

    Condensing boilers are resistant to corrosion, and so for a given return temperature can operate with a lower exhaust temperature, even though this may mean condensation happens only some of the time.

    So - condensing boilers are more efficient, even when they are not condensing.

    Also, am I right in thinking that some of the condensing takes place in a heat exchange between exhaust and incoming air? If so that would allow a contribution to efficiency from condensation but with a higher return temp than you might otherwise expect.

    The figures Vaillant quote for my boiler are about in line with brig001's figures above.
  2.  
    brigg001, thank you for your comments. The Keston brochure answered alot of questions for me, as clearly the condensation occurs on the incoming return just prior to the exhaust, with condensate dripping down as the temperature declines. So the point here is that as long as the incoming return is low enough - eg 40 deg then the condensing should work well.

    With regards the thermal store, the entire argument there is very confusing. I have 4 boiler systems which are all tank fed water for HW, each system stores around 450l. I have pressure/water supply constraints that limits the ability to get rid of the current system set up. So I am looking at simply changing the boilers over and want to make sure that condensation will occur. It seems that the main time condensation wont occur is when heating up water only, e.g. in summer. Each boiler I have at the moment is between 27 and 45 Kwh (gross - which I measured off the gas meters)

    I dont follow the thermal store points at all, can you outline how I might re-lay out my system, also I am interested in using a gas waste recovery system as a HW supply pre-heat. But it seems that these systems only are available for combis?

    There is a possibility of using a combi with a thermal store and doing away with hot water tanks. Interested in seeing some alternatives, ideally would be nice to see an ideal layout diagram.

    The other spanner in the works is that I intend to put in solar HW at some point.

    Matt
    • CommentAuthorwookey
    • CommentTimeNov 2nd 2009
     
    The thermal store argument goes like this: With a conventional boiler coil you are limited in how much heat transfer occurs in the coil. So if you put in water at 70C it might come back at 50C, thus limiting condensing efficiency gains. With a directly-heated thermal store you put hot water in the top of the store whilst taking cold (20c?) water out of the bottom. Exactly how well this works depends on how much your boiler will raise the temp in one pass (and is often complicated by having a TMV to mix return water in order to able to set the ouput temp to top of tank to (e.g. 70C)). But the basic point is that with direct heating the return water will usually be much colder than it is when heating via a coil. This is actually apoint about direct/indirect heating, not cyclinder/thermal stores per se, it's just that a store is often heated direct.

    I think you are right that summer operation is probably least efficient. Which helps make solar a good idea. Of course winter operating being efficient does require a low-enough return temp from the CH. Is it, in practice?
    • CommentAuthorbrig001
    • CommentTimeNov 2nd 2009
     
    Sorry, I think I may have caused confusion by copying Water Systems' post verbatim. Thermal stores need good mains water pressure which I don't think you have.

    Your efficiency will be lower in summer, but even at 60 deg C return to the boiler, you are in the region of 90%, which will be much better than you are getting now.

    Bri.
  3.  
    Hi,

    Its worse with oil as the dew point is 47 deg and realistically the max temp rise you can achieve throught eh boiler jacket is 20 deg. so thats an outlet temp of 67 deg. Problem is if you check the brochure specs you'll find many that quote 50 deg as the min return temp.
    many europeon oil boiler configuration use the thermal store and the return water mixer. In the uk we tend to operte boilers in a very uncontrolled way. If you can balance to achive a 20deg rise throught the boiler, you wont get a 20 deg drop throught eh rads so the mean temp climbs and climbs until it cuts on high temp then you are back into the cycling mode. Probably 99% of instalations have the boiler - radiator load un-balanced.

    Cheers
    Mike up North
    • CommentAuthorCWatters
    • CommentTimeNov 2nd 2009 edited
     
    Further to that..

    Residential OIL boilers don't modulate, when the burner is lit it's allways full power. So you can have a situation where the boiler is running flat out feeding just one rad (TRV on the rest are off) or one UFH loop. The return temperature soars, the flow temperature soars and it starts cycling on and off to keep the flow temperature within limits. Typically that limit is set by a dial on the boiler. The dial on an oil boiler doesn't control the burner power it controls how hot the flow gan get before the boiler starts to rapid cycle.

    If you have a thermal store that can provide power without firing the boiler. Only when the thermal store cools does it fire the boiler up. If set up right with the right speed pump the boiler can run flat out until the store is upto temperature with no cycling.

    Gas boilers generally can modulate their burners so this is less of an issue for them but you still want to be sure that the boiler isn't oversized.
  4.  
    Posted By: CWattersIf you have a thermal store that can provide power without firing the boiler. Only when the thermal store cools does it fire the boiler up. If set up right with the right speed pump the boiler can run flat out until the store is upto temperature with no cycling.

    Gas boilers generally can modulate their burners so this is less of an issue for them but you still want to be sure that the boiler isn't oversized.


    Good point. Thermal stores and fixed rate burners, gas or oil, go together well. Have two cylinder latched in stats for anti-cycling.

    Oil boiler have a larger heat exchanger water jacket than modern gas boilers. Some are so large they are like small thermal stores, so much so a plate heat exchanger can be slapped on the side and the thing is an instant combi, with the reserve of heat in the heat exchanger acting as a nice heat buffer giving initial high

    A good thing about a thermal store is that does not care about the size of the boiler. I assisted a friend with an oil installation. He had a small commercial oil boiler offered to him near dirt cheap. I said take it. It was way oversized for his house. It was I think around 110kW to 150kW - we sued 35mm flow and return pipes from the boiler to the store. He had the room for it in an outhouse. I suggested a thermal store with two anti-cycle cylinder stats. The boiler would kick in and re-heat in no time at all. Then it would stay off for along time while the CH drip fed heat into the house for the store. He never ran out of DHW even with a few body jet showers and two teenagers using them at the same time. When the cylinder was down on heat and the cylinder stats called in the boiler, the power of the boiler was pumping heat into the store faster than the heat being extracted.

    The great thing about oil boilers is that you are not constrained by a gas meter and mains gas pipe size. Being such a big boiler, it still only needed the same sized oil tank as a boiler perfectly matched to the house. It never used any more oil, probably less.
  5.  
    Posted By: wookeyThe thermal store argument goes like this: With a conventional boiler coil you are limited in how much heat transfer occurs in the coil. So if you put in water at 70C it might come back at 50C, thus limiting condensing efficiency gains. With a directly-heated thermal store you put hot water in the top of the store whilst taking cold (20c?) water out of the bottom. Exactly how well this works depends on how much your boiler will raise the temp in one pass (and is often complicated by having a TMV to mix return water in order to able to set the ouput temp to top of tank to (e.g. 70C)). But the basic point is that with direct heating the return water will usually be much colder than it is when heating via a coil. This is actually apoint about direct/indirect heating, not cyclinder/thermal stores per se, it's just that a store is often heated direct.


    People do not know what a quality combi is capable of. One installation with an existing "direct" electrically heated unvented cylinder in an all electric house. They were going gas. I used a 24kW Alpha combi to heat the fresh water in the cylinder. The DHW outlet was piped to the top of the cylinder using a Surrey flange. The cold inlet was taken from the bottom of the cylinder. A bronze pump was fitted on the inlet to the combi - a Grundfos Home Booster at £112 in some places. The combi heated the DHW to 60C and put the heat at the top of the cylinder. Reheat was very rapid. A cylinder stat cut out the bronze pump when it was up to temperature.

    It was cheap way to go and really delivered the DHW. The cylinder can be downsized when doing it this way. Or left the same size if a power shower or body jets is being used. Just size up the kW combi so it is just short of using a lot, or none, of 28mm for the gas supply. It could be 30kW. Or any decent deal combi. When the cylinder is empty the combi will pump 10-11 litres/min into the draw-off, when there is heat in the cylinder the to combine to extend the size of the cylinder, using on-tap energy (the gas pipe) and the stored energy (the heat in the cylinder)

    The average plumber would have fitted a system boiler and a new indirect unvented cylinder. My way was buying just a combi, the rads and a bronze pump and in effect it made the cylinder larger.
    • CommentAuthorcrusoe
    • CommentTimeNov 3rd 2009
     
    Interesting -I didn't know about the 15% savings with a TS and condensing but would concur on the principle. Have just fitted a new Qudos 28 (Keston) with 2 x 500 litre TSs (cellar access was small) plus 2 hot water tanks and 5 solar panels. Each room is independently zoned (large rooms) with oversized rads so don;t need more than 50 C. I am hoping for nearer 50% rather than 15% - but the 15% you quote will help achieve that!

    From 30-40 store temps, there is a lot of condensate dribbling - lessens markedly at 45 and by 50 the boiler, which is 60 + by now, is modulating down and vitually dry.

    I have chosen to fit separate DHW cylinders. That's another debate in itself :neutral:
  6.  
    Hi,
    Thats an interesting combination - the modulating gas boiler + T/S. For a fixed oil boiler this woul be spot on, particulary with the lower dew point. I'm OK with separate stores / cylinders for heating / DHW. Was this to be able to always ensure condensing by controlling the boiler return temp (your control) AND to gain the solar input to either space heating or DHW?
    To get the best temp (highest) into the store you could hold the return temp at say 45 and get 60 deg out (assuming you can get a 15deg rise throught he boiler). Basically if you can control the return temp easily then you could perhaps only move out of condensing when the weather was very very cold. A simple weather compensation that allows you to design to meet normal winter conditions and occasionally deal with extremes.
    Cheers
    Mike up North
  7.  
    Water systems/Wookey,Mike, Cwatters,
    Do you have any suggestions for my particular situation:
    on average per boiler (and they are not easily linked):
    10 bathrooms
    300m2 mostly Victorian property
    poor water pressure thus loft tanks
    existing system is regular boiler heating cylinders and heating separately
    • CommentAuthorCWatters
    • CommentTimeNov 5th 2009
     
    Hotels have their own needs which I don't feel qualified to comment on. Typically customers expect aircon these days. This place ripped out their rads in favour of air con only. They claim it's greener but I can't comment..

    http://www.caterersearch.com/Articles/2009/10/16/330438/energy-saving-heating-some-like-it-hot.html
  8.  
    You are right hotels have their own needs as the customers are from all walks of life. However in many ways the problems faced are much the same as for a regular house - same/similar occupancy patterns and needs. The main difference is simply the neccessity to cater to more tastes.

    I am still interested in peoples suggestions for the hot water set-up - just think of it as a massive house with lots of bathrooms that may get used at the same time.

    The article you listed above raised the point of "super-micro double glazing " - whats that? slim-lite?
    Is that any good?

    I have just been reviewing my windows and I am leaning towards secondary glazing at the moment as the U-values achieved are pretty good - supposedly 1.7 ish with low e glass, which isnt bad. Refitting the windows seems to be highly problematic, and in fact highly expensive.