Home  5  Books  5  GBEzine  5  News  5  HelpDesk  5  Register  5  GreenBuilding.co.uk
Not signed in (Sign In)

Categories



Green Building Bible, Fourth Edition
Green Building Bible, fourth edition (both books)
These two books are the perfect starting place to help you get to grips with one of the most vitally important aspects of our society - our homes and living environment.

PLEASE NOTE: A download link for Volume 1 will be sent to you by email and Volume 2 will be sent to you by post as a book.

Buy individually or both books together. Delivery is free!


powered by Surfing Waves




Vanilla 1.0.3 is a product of Lussumo. More Information: Documentation, Community Support.

Welcome to new Forum Visitors
Join the forum now and benefit from discussions with thousands of other green building fans and discounts on Green Building Press publications: Apply now.

The AECB accepts no responsibility or liability for any errors or omissions in the content of this site. Views given in posts are not necessarily the views of the AECB.



    • CommentAuthorbar
    • CommentTimeNov 10th 2009 edited
     
    Hi I have a similar situation to a previous post but did not want to jump on the back of that so here goes....

    I have been trying to review my plumbing setup since last winter but need some advice on my Solar/UFH/ Oil boiler set up as it is difficult to get advice from the various contractors who installed my system.

    My set up (as best that I can draw it) is attached where I have a buffer store supplying DHW and heating demands controlled by a single cylinder stat. This cyl stat fires the boiler frequently with DHW or heating demand when the temp drops below the preset 60deg. A picture of my buffer store is attached.

    I know from reading various posts here that I need a 2 stat setup and plan to replace the analogue thermometer at top of tank with another cylinder pocket probe stat but have the following questions

    1. For my plumbing setup e.g boiler flow/return tank positions on wiring diagram should I put a NC cyl stat down further to middle of tank to increase buffer volume? I assume the current stat I have is a NO type so I could replace the analogue thermometer at the top of the tank with this and then I would need to get a NC type for the bottom stat?
    2. My solar guy is trying to get me to buy another solar controller to act as a differential controller but I believe I just need another cylinder stat yet he says this would not work as stats he has only have a temp differential of only 3deg? Assuming I can get a NC type cylinder pocket type stat what brand/model should I get which will work in my application? I see a lot of clip on stats on net but few pocket sensor types and local plumb centre guy is not familiar with any Normally Open /normally closed type stats?
    3. I read here also about use of a relay in the wiring setup. Do I need this in optimising the set up?
    4. Would I need a mixer on the return flow to boiler from the buffer store as if bottom stat is below the
    boiler return then return temp could be too high/low for efficiency?

    Appreciate any comments to above with info/diagrams I can go back to plumb centre and electrician with to finally get the set up I need.

    bar
    • CommentAuthorCWatters
    • CommentTimeNov 11th 2009
     
    When you say...

    "This cyl stat fires the boiler frequently with DHW or heating demand when the temp drops below the preset 60deg"

    Can you clarify "frequently"? When the tank temperature falls below the set temperature the stat should call for heat and the boiler should fire continuously until the tank is above the set temperature. I ask because I thought I had the same problem with the tank stat and it turned out to be something else.

    In my case the boiler pump was too small so the boiler flow temperature exceeded the maximium set on the boiler dial (even with the dial at max). This caused the boiler to cycle on and off even though the tank stat was calling for heat constantly.
    • CommentAuthorCWatters
    • CommentTimeNov 11th 2009
     
    Re 2) I believe with a dual stat arrangement the stats shouldn't need any hysteresis/differential. Thats effectively provided by their seperation and setting.

    Re 3) I think a latching relay is required. The stats are set up so that the top one calls for heat when it's cold BUT the boiler must keep running until the bottom stat is satisfied. The problem is the the top stat will quickly be satisfied and that mustn't turn the boiler off.
    • CommentAuthorbar
    • CommentTimeNov 11th 2009
     
    Hi CWatters
    The current pocket stat has a 3 deg differential and so when the boiler is timed 'on' the thermostat switches the boiler on every once in a while [not sure of exact time period] but would guess every 10~20 minutes depending on demand when UFH and DHW calls for water as the temp in tank drops below the preset 60deg. The boiler is doing what it is supposed to do but thats why I need the two stat set up to reduce cycling ferequency.
    I think the position of the bottom stat on the tank is also critical as believe it is up too high at present and I need to increase the buffer volume in my 600/200l tank
    I have difficulty in finding pocket stat which is NC type to put at middle of tank [and move the current NO type up to the top] what should i be asking for in heatmerchants?
    I will check up on 'latching relay '
    would i need the mixer valve to ensure return temp to boiler is >40 deg? I may have the situation where return temp is high as the return flow pipe location would be at same area as bottom stat which is calling for 65deg. Will this effect efficiency as i know if return too low then risk of damage to boiler?
  1.  
    Hi, yes the twin stats are set to differenet temps can be anywhere between 10-20 deg at least. The absolute values do not matter so much except that the upper is set cooler ie a Normally Open contact closes on cooler water to fire the boiler, conversly the lower stat Normally Closed conatct opens on rising temp to switch the boiler off ie full of hot water. Alternativelt there are controllors that are the similar as solar differntial units to do this based on 2 temp probe inputs
    Cheers Mike up North
    • CommentAuthorbar
    • CommentTimeNov 11th 2009 edited
     
    Hi Mike
    Do you know of any 'pocket sensor' stats off hand that i could use which are NC/NO type, i.e make/model

    any comments on my proposed stat positions or need for a mixer valve on the return circuit from my wiring diagram?

    thanks
    bar
    • CommentAuthorCWatters
    • CommentTimeNov 11th 2009
     
    I think I would build it without a mixer and see what return temperature you get. If it's too hot then add a mixer.

    I think you need two normal stats (eg types that go OC when hot) and a latching relay... The top stat is normally hot so will normally be OC. When the top stat cools it will go SC and will turn the relay ON. The bottom stat is normally cold so will normally be SC. The relay stays ON until the bottom stat gets hot and goes OC. The bottom stat removes power to the relay turning it OFF...or something like that.
  2.  
    Hi, yes thats fine either way works so long as its off at the bottom and on at the top and there is a reasonable differential.
    Alternatively just buy a boxed oil boiler + accumulator on/off controller.
    Oil boiler + large thermal store is quite common (except in UK) so fo9lk are surppised to find that you can buy off the shelf differential temp controllers to do this - much simpler

    see ww.lkacaso.se/en/LK-Acaso/Products/Differential-temp-controls/Termomat-3

    Cheers

    Mike up North
    • CommentAuthorbar
    • CommentTimeNov 12th 2009
     
    Hi Mike
    the acaso system looks good but on contacting them they do not supply to public so not sure on budget price?

    Think I may go for another probe stat same as i already have and get electrician to wire them up NC/NO with a relay?
    Is there a wiring diagram for this setup available or is it standard stuff -excuse my ignorance

    How easy is it to de-pressurise an unvented system? i.e to fit the new thermostat in the tank?
  3.  
    Hi,
    Ok they used supply, that must be since the takover by a new parent company
    The stats should be fitted into pockets, so you dont need to empty it, but you would if you needed to fit a pocket.
    Electrician will be able to wire it if you can specify exactly what you want.
    Cheers mike up North
    • CommentAuthorbar
    • CommentTimeNov 12th 2009
     
    seems I may need to empty it as need to fit pocket :-(

    came across the Honeywell L6188 imersion stat and thought this would do the job for top stat but it is a high limit stat. Would ideally like a low limit stat which closes on drop of temperature so not have to do relay setup?
    Anyone know of any?
    • CommentAuthorbar
    • CommentTimeDec 17th 2009 edited
     
    Ok an update..
    I eventually upgraded my solar controller so that I can use a program which controls the boiler/feed pump via two sensor probes on the tank. I also installed a TMV on the return flow set to 45°.

    The above was installed recently however I now have the situation where the boiler cuts On/off frequently which was the whole idea of making this change to eliminate this!
    Some info
    -feed pump has 3 settings and cycling occurs on all 3 settings
    - boiler [grant vortex 26-36KW] is set at 31kw (0.85 nozzle)
    - boiler stat set to max
    I have a sensor on boiler flow and the burner cuts in at 58° and off at 62°
    The Solar Controller seems to be working correctly with the tank sensors as I can manually adjust the off temp to switch the burner off but when the tank is calling for heat the boiler is cycling
    Help appreciated..
  4.  
    Hi,

    two stats control the boiler on and off. Top stat = boiler on set to say 50 deg so boiler does not come on untill water ant less than 50deg is present at this top stat.
    the lower stat is boiler off and is set to open at say 70deg so when the hot water has come down this fat the tank is full and the boiler is off.

    cheers
    mike up north
    • CommentAuthorbar
    • CommentTimeDec 17th 2009
     
    HI Mike
    The stats are setup correctly for ON/Off as you mentioned above i.e top stat =On , bottom stat - off but the tank never gets to heat up to bottom stat temp as the boiler cycles on/off.
    I know Cwatters mentiopned before that it could be the pump size but I think this is OK but maybe wrong? Could it be the boiler stat faulty as it is cutting on/off at 58/62°
  5.  
    Hi, sorry for the quick answer - doing too much at once. I would check with grant about the boiler stat. I suspect it is switching at a lower than expected temp. Usually for most boilers the hottest setting is around 80-82 deg. Hence it should always be set to max and the store bottom stat at least a few degrees less but probably best at say 75 deg so it will always switch off on the store stat. These stats are not that accurate and have a couple of degrees of hysteresis so don’t get the settings too close. However, I suspect (anecdotally) that the max on the grant is 70 ish. I think this is so that they maintain condensing and meet the very high eff they always quote. Check with them what it is set at. It may be that the boiler stat is over ruling the store stats.
    Cheers Mike up North
    • CommentAuthorbar
    • CommentTimeDec 17th 2009 edited
     
    Hi Mike
    I checked with Grant and boiler max is 70°, just dont understand why its cutting out at 62° then? Technical guy actually mentioned that it is possible to adjust this stat [removing spring from behind dial at front panel] to increase the max themp to 80°. The boiler does seem to override the tank stat as it is still calling for burner on yet boiler switches off!

    On thinking more about my situation i think one issue is theat becuae it is a tank in a tank and the top /bottom stats are on the opposite side of the flow/return pipes that they are getting miss readings hence the boiler cutting out [but then I have a mixer to reduce the return temp to the boiler??
    Because of stagnation in the tank in tank setup I may never get to reach the lower temp stat value. I may have to put a pump at the bottom drain tap exit connected back to top of tank to get circluation going in the tank and allow bottom stat to achive its temp?
  6.  
    Hi well that sorted one point, you may just have a low stat just a bad un, can you do a sketch, and what tank is it? any diagrams?

    cheers

    mike up north
    • CommentAuthorbar
    • CommentTimeDec 17th 2009
     
    Tank is KSE-1 600/200 , only one solar coil. . Plumbing diagram is above [above tank picture in original post)except I not have a TMV valve on return flow before feed pump and the burner/feed pump are controlled by the differential controller tank stats
  7.  
    Hi,
    Make sure the bottom stat is 5 deg less than the boiler max, so if it is only 62deg at the boiler try top =45, bottom = 55 deg to see what happens. But just as a test. With the grant set to 70 max the realistic top store temp is 65 deg.
    The TMV into the boiler RAISES the temp to 45 deg so it must be less than this. The boiler then adds say 20deg and it comes out at 65 deg. You could run 55-75deg excepting the top limit on the grant and the dew point of oil is 47deg so running 45-65 will always ensure condensing. Try what grant suggested and defeat the boiler stat. This is a little dodgy as all control is with the store. If this works fit a pipe stat on the out let set to say 80+ and feed the boiler supply through it so you have some high temp protection.
    However i still suspect the upper stat is overuling the lower stat and thus running till the boiler stat operates.

    When the lower stat operates it removes the boiler supply.
    When the upper stat closes to operate the boiler the lower stat must also be closed (other wise there would be nothing to open when the hot water comes down to it).

    cheers
    mike up north
    • CommentAuthorbar
    • CommentTimeDec 18th 2009
     
    Well Mike I pulled off the plastic boiler thermostat cover on front panel to reveal a ' limit spring' which i removed as advised by Grant. After doing this the boiler cycling stopped and where previously the flow temp was upto 62° it now climbed upto 76° before shutting down.
    I checked with Grant and they said that the boiler safety is not compromised as still have the high level stat safety at 111° to cut out boiler and also the efficiency is not effected as only effected by 0.5 percent at 75°.
    I still have the problem that the burner switches off because of max limit (now 76°)rather than off by bottom probe temp setting. I had to turn bottom temp stat down to 33° in order to turn the boiler off as the top of tank was 72° and bottom was hanging about 33- 35°!
    Due to tank in tank setup as mentioned before in addition to the temp probe locations on the other side of tank to the inlet/outlets ports that I never get to raise the lower tank temps by much. I am now looking at plumbing a circluating loop pipe from bottom of tank to top controlled by a slow setting pump [tied into boiler pump electrics] which would help draw down the hot water to bottom of tank when boiler on, helping to raise the bottom store temps and realise the proposed 45-65 setup?

    On steep learning curve of my heating system but slowly making progress I think
    • CommentAuthorCWatters
    • CommentTimeDec 18th 2009 edited
     
    Bit late to this thread but it's Interesting. My Grant will go upto 75-80C flow and I've not had to remove a limit spring. Perhaps this is a newish addition.

    When yours shuts off at 76C what's the return temperature?

    If you are getting a large temperature rise across the boiler (eg 40C return and 76C flow) then I'd have a look at the pump speed. Basically an oil burner has a fixed output power so the faster the water goes through the boiler the lower will be the temperature rise.

    You shouldn't lower the return temperature below 40C. In fact most systems have a mixer to prevent the boiler return going below 40C. (aside: This mixer has come up twice on the forum thie week already. Funny how that happens).

    I am now looking at plumbing a circluating loop pipe from bottom of tank to top controlled by a slow setting pump


    Deliberately stiring the tank shouldn't be needed.

    Is it possible the boiler is cycling so fast that the average power is too low to heat the store on a cold day. That's what happened to me first winter.

    My boiler is the 36/46 now fitted with the smaller 1mm nozel so 36kW. The original pump supplied with my DPS store was a grundfos UPS 25-60-130 and I changed it to a UPS 25-55-180 which has about twice the flow of the original. Note this wasn't a drop in replacement - the last three digits are the width. The original was 130 and the new one 180mm.

    I can't be sure pump speed is your issue but if you see a large temperature rise across the boiler when it's all at the peak of a cycle that would be my first suggestion.

    PS What part of the country are you in? My UPS 25-60-130 is going spare. Low milage!
  8.  
    Hi,
    Actuallly CW you mentioned this one before in a thread at least a year ago about this as I'd said before I thaught it was 70 ish deg. I'd been questioning the suitability of pairing a grant boiler with a thermal store on this basis.

    It may be the tank is stirred up the bottom stat is supposed to be the higher setting ie say 70 deg so will open to switch the boiler off when the layer of hot water (76deg) arrives from the top downwards. Thus for 76 deg out the boiler would ideally be getting water at about 55deg from the TMV.
    It may you are just horsing it through to much.

    Most boiler manf will only sanction a 20 deg rise as standard, some will agree upto 30 when into a fixed load like a store and with a loading valve.

    Cheers Mike up North
    • CommentAuthorbar
    • CommentTimeDec 18th 2009
     
    temp rise is 15-20 rise from return but as in other thread my TMV rises after a period upto 60°. Pump is -130 'width' with 3 settings, mine is on setting 3. Condenser Boiler power I believe is OK at 31kw as told better having boiler working for heat rise rather than too powerful.

    By the way based in Eire!
    • CommentAuthorCWatters
    • CommentTimeDec 18th 2009
     
    Hi Mike,

    It seems to manage a bit more than 70 but not quite the 80 claimed in the manual (Unless they measure it inside the boiler).

    I experimented with slowing the original pump down and problem got worse. It seems that with a largish boiler and a smallish store there seems to be a fine line to tread between..

    a) Too slow a pump.. Causes the rise across the boiler to be too large, maxing out and causing cycling.

    b) Too fast a pump.. You loose stratification in the store. The return temperature starts to rise, possibly too much for the boiler to be in condensing mode.

    With the original pump I was definitly seeing a). The faster pump made a quite a big improvement but I started to see b). Reducing the boiler power by fitting a small jets again made it easier to get it operating between these two problems. The manual says the boiler is more efficient on the smaller jet as well.

    It seems clear the store it too small for my boiler or possibly the boiler it too big for the house.
    • CommentAuthorCWatters
    • CommentTimeDec 18th 2009
     
    Posted By: bartemp rise is 15-20 rise from return but as in other thread my TMV rises after a period upto 60°. Pump is -130 'width' with 3 settings, mine is on setting 3. Condenser Boiler power I believe is OK at 31kw as told better having boiler working for heat rise rather than too powerful.


    Ok so probably not a slow pump. I'd try dropping the store temperatures by 5C to see if that drops the peak boiler return temperature and allows the peak boiler flow to remain below 76C
  9.  
    Hi, Where abouts on the diagram do you have the stats? what are the measurements from the bottom up wards to the stats and the in/out connections?

    Did you consdier Warmflow at Lisburn for a boiler??
    Cheer
    Mike up North
    • CommentAuthorbar
    • CommentTimeDec 19th 2009
     
    Hi
    I got a small pump installed yesterday to help circulate the heat to bottom of store as heat not gettin to bottom of store and not helped with location of probe stats on oppisite side of tank in tank and now the boiler never cycles but can run for 1hr plus with a flow of 60-67deg as depending on demand for UFH etc the tank stats are set to 50 top 'on' and 60 bottom 'off'. After adjusting the boiler thermostat to increaseflow upto ~80 and the circulating pump the system is doing what is should via the differential solar controller program. The tmv valve hasn't climbed above 52deg since the circ pump installed. Pumps and boiler are all controlled by the tank stats.
    Although the boiler is running in condensing mode practicly all the time do I need more power or is it normal for bad setup to have it run to 1-2hrs constant during peak demand times?
    Have boiler installed 3yrs now Mike never considered Warmflow as Grant condenser was recomended to me back then.
    • CommentAuthorCWatters
    • CommentTimeDec 20th 2009
     
    Very surprised that stiring the store stopped the boiler cycling. Can't see how that works at all. Would have expected the exact opposite :confused:
  10.  
    Hi, me not why that is helping although the figures seem to be what would be expected.

    Although that seems to be working it does seem to defeat logic. The original low temperature at the bottom suggests the layer of hot incoming water was not getting down that far (in order to switch off the boiler) hence the boilers own stat taking over on high temp. I think what you are doing in stirring it up is simply slowing things down. Its quite a high powered boiler so with a lowish flow the temp rise within the boiler would have been quite rapid forcing the boiler to cut out before the store water got that far down, or settled into the period where the hot/cold interface layer is progressing down the cylinder.
    Looking at the diagram of the buffer the inner T in T does extend down quite a long way inside. Often they are fatter at the top with a much thinner section dropping down to near the bottom. The cold feed dip tube goes right the way down so you introduce the potable cold water in as low as possible. This help maintain the balance of hotter at the top and cooler at the bottom, also if you have a solar coil this would be wrapped around this lower section to place it close to the cold potable water.

    I’m still interested to see where you have the flow ins and outs and the temp probe points relative to each other measuring up from the floor level.

    Cheers

    Mike up North
    • CommentAuthorbar
    • CommentTimeDec 21st 2009
     
    Hi Mike see attached for tank in tank inlet/outlet dimension against the sensor positions
    I guess under the current setup I will need to adjust the parameters in summer when no heating required where I can maximise solar DHW heating of tank.

    Appreciate comments on setup
   