Home  5  Books  5  GBEzine  5  News  5  HelpDesk  5  Register  5  GreenBuilding.co.uk
Not signed in (Sign In)

Categories



Green Building Bible, Fourth Edition
Green Building Bible, fourth edition (both books)
These two books are the perfect starting place to help you get to grips with one of the most vitally important aspects of our society - our homes and living environment.

PLEASE NOTE: A download link for Volume 1 will be sent to you by email and Volume 2 will be sent to you by post as a book.

Buy individually or both books together. Delivery is free!


powered by Surfing Waves




Vanilla 1.0.3 is a product of Lussumo. More Information: Documentation, Community Support.

Welcome to new Forum Visitors
Join the forum now and benefit from discussions with thousands of other green building fans and discounts on Green Building Press publications: Apply now.

The AECB accepts no responsibility or liability for any errors or omissions in the content of this site. Views given in posts are not necessarily the views of the AECB.



  1.  
    Posted By: Mike GeorgeI thought the counter battening had some effect on the way in which vapour migrates to the outside air? Also there shouldn't really be any significant volume of water to run off whether membrane pulled tight or not. I'd be interested in reading a BBA which details this if you have a link as like I said it is an assumption [probably wrong] on my part
    If the membrane is pulled tight or fully supported then wind driven rain finding it's way through the tiles will not be able to run off under the tile battens. So they need to be lifted up 12mm with counter battens.

    You're not wrong, the Tyvek Supro BBA refers to this in Section 13.2 as a a drainage and "vapour dispersal space"
    http://construction.tyvek.co.uk/Tyvek_Construction/en_GB/assets/downloads/certificates/roof_bba_tyvek_supro_in_warm_non_ventilated_cold_ventilated_roofs.pdf

    David
    •  
      CommentAuthorfostertom
    • CommentTimeApr 20th 2010
     
    Funny, this thread started about gap above insulation/between rafters/below felt (which I don't like) but has migrated to batten-space ventilation (which I'm coming round to/back to, and isn't difficult to arrange at eave tho a drag at ridge).
  2.  
    Thanks David, that makes sense.
    •  
      CommentAuthorfostertom
    • CommentTimeApr 20th 2010
     
    What if it's insulation full-fill between rafters, OSB over rafters, EPS or woodfibre over that EWI-style, all breatheable, no VCL. Then no danger at all of condensation within the rafters. Over the EPS/woodfibre, 35x50 downslope battens, metallised breather felt draped, shiny side down, battens and slates over.

    What need then, for through-ventilation - which layer? Wd prefer to prevent ventilation of the under-breather space, so dust wouldn't come in to spoil the shiny surface.
  3.  
    Posted By: fostertomDavid, what's the difference between your c) and your d)?
    c) and d) [i] seem to support sinnerboy. I'm depressed!
    c) is without sarking boards/insulation & d) is with sarking boards/insulation.

    d) [i] is what I'm doing & what you would be doing with woodfibre sarking insulation. It requires batten cavity ventilation above or below the draped breather membrane, I would ventilate above the membrane for windtightness.

    d) [ii] is what you would be doing with EPS sarking insulation. It does not require batten cavity ventilation.

    David
    •  
      CommentAuthorfostertom
    • CommentTimeApr 20th 2010
     
    Thanks David, think we're getting there. But don't go thinking that EPS equals non-breatheable! Other plastic insulations yes, but EPS esp Springvale Platinum-grade whatever they call it is reasonably breatheable.
    • CommentAuthorCWatters
    • CommentTimeApr 20th 2010 edited
     
    Regarding..

    b) forming a ventilated gap between top of insulation and underside of a breathable membrane,


    It's not just some BCO that insist on a gap. Some manufacturers of breathable membrane also specify a small unventilated gap. I believe there are two issues..

    a) The first has already been mentioned - the need for drape so that rain can run down under tile battens without the need for counter battens.

    b) a possible issue with the membrane "wet clinging" to the insulation, forming some kind of chemical reaction or perhaps simply not drying as quickly as it should when wet.

    I can't find much info on b) but Celotex say...

    "With some breathable membranes, the cold side of the insulation may be placed in direct contact with the membrane (check with membrane supplier prior to specification)."

    Knauf say...

    "Knauf Breatheline is non-wicking and so can be laid in direct contact with insulation and roof boarding with no risk of moisture penetration."

    I'm sure I've seen other references that imply a potential issue. So perhaps best check that the insulation and membrane are compatible before putting them in contact with no gap.
    •  
      CommentAuthorfostertom
    • CommentTimeApr 20th 2010
     
    Good point. Luckily the construction I've been describing lifts the breather felt off the continuous EPS insulation, draped over 35x50 downslope battens. However, since the dawn of such constructions, both slab-insulation manufs and breather manufs have most often preferred the breather flat on the insulation, downslope battens over that. I remember thinking that looked suspect when I first saw it.
    • CommentAuthorsinnerboy
    • CommentTimeApr 21st 2010 edited
     
    From BS 5250 2002 - As Amended 23 Dec 2005

    "Roof coverings and batten spaces
    Research has shown that moisture conditions in the space between the outer roof covering and the underlay
    are dominated by the external environment, the air openness of the outer covering and the vapour openness
    of the underlay. If an HR " ( underlay has a water vapour resistance greater than 0.25 MN·s/g. ) " underlay is used there will be relatively little moisture transfer from within the building to the batten space. In the case of an LR " (underlay has a water vapour resistance of less than or equal to 0.25 MN·s/g.) " underlay more moisture will be transferred: in order to avoid a build up of moisture in the batten space it is good practice to ensure adequate air movement through the void between the outer covering and the underlay. Most traditional unsealed slating and tiling methods are sufficiently air open. "

    There you go Tom . Your POV is reinforced here .

    " Should it be necessary to determine if the roof covering is sufficiently air open, it should be tested using a
    rig as described in Annex L of BS 5534:2003 but with equipment designed to measure low pressure
    differences down to 2 Pa. If the airflow at 2 Pa is, or could be reasonably expected to be, greater than 7.8Ar (in m3/h, where Ar is the effective test rig area in m2) the roof covering will allow sufficient air movement in the batten space without additional ventilators.

    If the airflow is not, or could not reasonably be expected to be, greater than 7.8Ar (in m3/h), it is necessary to provide either:
    a) ventilation openings to the batten space which are equivalent to a continuous slot 25 mm wide in the eaves and 5 mm wide at the ridge and 25 mm counterbattens; or
    b) ventilation openings to the roof void or air void below the underlay as specified in 8.4.2.2.3.
    In case of uncertainty, the air tightness of the roof covering should be tested, as above, or ventilation
    openings to the batten space or loft installed. "

    So - if in doubt - test as described above ( as if ! ) or provide vent slots / strips into the batten void .
    • CommentAuthorsinnerboy
    • CommentTimeApr 21st 2010 edited
     
    Sidenote .
    At a seminar presentation by roof slate supplier a couple of years back a speaker cautioned about the use of the lighter breather membranes ( which are more "flag-like" than the old bitumen based felts are /were ) when used below states

    If used with battens only and IF allowed to overly sag between rafters - then in high winds suction forces can cause the light membrane sag to "belly up" . Then the slates are simultaneously subjected to suction forces over and positive forces under - the slates can be ripped off the roof. According to the speaker some failures did occur when breathing felts were first used .
  4.  
    Posted By: CWatters
    b) forming a ventilated gap between top of insulation and underside of a breathable membrane
    It's not just some BCO that insist on a gap. Some manufacturers of breathable membrane also specify a small unventilated gap. I believe there are two issues..

    a) The first has already been mentioned - the need for drape so that rain can run down under tile battens without the need for counter battens.
    This is a good point. However, counter battens achieve this without the risk of unwanted air movement below the sarking membrane, while allowing the insulation to protect the full depth of the rafter. So I would always use counter battens.

    Posted By: CWattersb) a possible issue with the membrane "wet clinging" to the insulation, forming some kind of chemical reaction or perhaps simply not drying as quickly as it should when wet.
    Most breathable sarking membranes are classed as "non-tenting". So liquid water will not pass through if in contact with another surface & there will be no surface tension type effects. Any breathable membrane which is classed as suitable for use with sarking boards/insulation will be non-tenting. There are some punctured-polyethylene based products which may be vulnerable to this, but I wouldn't use them & you've got to question how good they'd be at protecting the rafters they're in contact with from liquid water.

    The best way to keep the rafters dry is to keep them warm (do not insulate below, insulate to full depth & use sarking insulation) & not allow them to come into direct contact with air which may cause condensation. By keeping a non-tenting breathable membrane between the rafters & the ventilated air gap as in d), you prevent liquid water from condensation of the ventilating air coming into contact with the rafters. This has got to be a good thing.

    David
  5.  
    Posted By: sinnerboySidenote .
    At a seminar presentation by roof slate supplier a couple of years back a speaker cautioned about the use of the lighter breather membranes ( which are more "flag-like" than the old bitumen based felts are /were ) when used below states

    If used with battens only and IF allowed to overly sag between rafters - then in high winds suction forces can cause the light membrane sag to "belly up" . Then the slates are simultaneously subjected to suction forces over and positive forces under - the slates can be ripped off the roof. According to the speaker some failures did occur when breathing felts were first used .
    This is a good point, but its not a reason to use old bitumen based felts. Breathable membranes are rated for wind loading &, if there's any concern about getting the drape right, the membrane can be pulled tight & counter battens fixed on top.

    David
    •  
      CommentAuthorfostertom
    • CommentTimeApr 21st 2010
     
    Very good, everyone. Getting some clarity here (I think!).
    • CommentAuthortony
    • CommentTimeApr 24th 2010
     
    I was hoping for some answer as to if a ventilation gap of less than 50mm would be OK in a cold roof

    My thinking is like this

    "They" work out that a 20mm is OK then double it and add 10mm before telling us 50mm?
  6.  
    No, I think its its probably bue to 'the 50% rule' which states that 50% of the surface area of timber should be open to evaporation [at least where non-breathable insulations are used] More discussion of this on page 1 here http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4698&page=1
    • CommentAuthortony
    • CommentTimeApr 24th 2010
     
    Then the only rafter sizes that work for that rule are 50 x 50 and 35 x 65 !!
  7.  
    I don't follow you? In the case of a 50 x 100 rafter. 50mm [say PUR] insulation between would cover 100mm rafter surface area plus 50mm on the inside face. This leaving 150mm open to the air gap. Ie 50%.

    I'm not sure but this is where I think the requirement originates though perhaps it has been relaxed somewhat to allow for greater thickness of insulation between wider rafters. I think the the reason for the gap though is a good one where materials such as PUR between are used.
    • CommentAuthortony
    • CommentTimeApr 24th 2010
     
    the top of the rafter is covered isn't it?

    if breathable then on top then yes -- biggest rafter 100x50.

    Lots or even most rafters are bigger than this.
  8.  
    Yes you're right. Just my thought on where this originated.
    • CommentAuthorsinnerboy
    • CommentTimeApr 24th 2010 edited
     
    From Page 32 of BS 5250 2002 - As Amended 23 Dec 2005

    "Figure 16 — Pitched roof — Small ventilated void above insulation and a type HR underlay"

    "Problems from interstitial condensation are unlikely to occur provided that a well sealed ceiling is provided
    and vented voids at least 25 mm deep at the centre of the drape are maintained between the insulation and
    the underlay. It is important those airpaths remain unobstructed during the life of the building: particular
    attention must be paid to potential restrictions at eaves, at changes in roof slope, at valleys and hips, and
    at changes in construction details where such a void may be difficult to achieve. Obstructions such as
    dormers, roof windows, compartment walls, fire-barriers, or changes in pitch create separate voids in the
    roof slope.
    Ventilation openings should be provided to each void, at both high and low level, to allow free air movement
    through the gap between the insulation and the underlay.
    a) Low level openings should be equivalent in area to a continuous opening of not less
    than 25 mm × length at eaves; and
    b) High level openings should be equivalent in area to a continuous opening of not less
    than 5 mm × length at the ridge or hips. Where there is no cross communication between each
    roof slope, 5 mm should be provided on both sides of the ridge"

    So from that I would say that if working with (by that I mean retro fitting insulation below ) a bitumen felt the critical dimension is 25mm below the lowest part of the drape of that felt - as opposed to 50mm down from top of rafter

    Not sure if this helps .... 50mm below the rafter or 25mm below the felt drape should result in the same face of insulation location .
    • CommentAuthorwookey
    • CommentTimeApr 24th 2010
     
    Very informative thread. Well done all. Moving back to the summary of possible ventialtion requirements in various pitched roof constructions and the principles we just collectively (largely) agreed on, can we consider the case where the construction is a flat roof? How do options a-d change?

    The physical principles and surroundings (inside/outside) are just the same. The only change is the angle and the outer covering(s), and the major point that without a significant slope air movement rates may be much reduced (no warm air rising/cool air falling), and arranging ventialtion at both ends is very difficult anyway.

    Normally there will not be tiles and thus no battens, but some type of membrane. Either old fashioned waterproof/vapour-proof felt, or more newfangled materials which are all waterproof but may or may not also be vapour-tight. (e.g. cefil (vapour permeable), sarnafil (not sure), polisystem (vapour tight)).

    My reading of all the above for this context suggests
    a) Don't do it - even worse idea on flat roofs than pitched ones.
    b) I'd generally prefer to avoid this construction too but do we reckon a gap is still needed for b[ii]?
    c) I don't think this ever occurs as a flat roof design effectively always has sarking boards.
    d) This is the interesting case as that's the sensible way to build a modern flat roof. Does anyone think that a ventilation gap is still useful here? I've never seen a design where one is fitted, whether the sarking insulation or meberane is vapour-tight or not. Clearly the gap for drainage is not relevant, but the comments about vapour dispersal still apply, and of course the upper membrane is going to be much more airtight than tiles.

    So for a pitched roof a ventilation gap for d[i] was suggested/recommended. For d[ii] it is not needed. For a flat roof we don't have a gap in either case. Is that because without battens there is no need for ventilation to protect the battens themselves? Or perhaps because there is really no such thing as d[i]. Even the 'vapour permeable' flat-roof membranes are in fact not very permeable really, so we are always in case d[ii] in practice?

    Thoughts?
    • CommentAuthortony
    • CommentTimeApr 24th 2010
     
    Now for the hilarious bit!!! -- if you want to extend it to flat roofs what about walls!"!!!!
  9.  
    d) for a flat roof is in effect a "warm deck" construction. The recommendation here is to keep all of the insulation above the joists & deck. The deck will typically be of non-vapour open plywood with a vapour control layer on top. The insulation on top needs to be rigid to support the waterproof covering, so typically it will be non-vapour open rigid board insulation. So, as you say, this is in effect equivalent to d)[ii]. Ventilation is not required because it's easy to make airtight, the rate of vapour transfer is extremely low & there's nothing on the cold side of the insulation that's vulnerable to decay.

    You could in theory use vapour open woodfibre board insulation giving a construction equivalent to d)[i]. However, this would require the creation of a ventilated cavity above the insulation & a "cold deck" to support the waterproof covering. I would have concerns about the ability to get effective ventilation at the centre of the roof leaving the battens, deck & insulation vulnerable to decay. So, if I had to have a flat roof, I would use d)[ii].

    David
  10.  
    Posted By: tonyNow for the hilarious bit!!! -- if you want to extend it to flat roofs what about walls!"!!!!
    I'm glad you mentioned walls!

    No one questions the need to sheath a timber framed wall, but I'm often asked why it's necessary to fit rigid sarking boards to a roof. In many respects a roof is a timber framed wall leant over at an angle & I don't know why you would build it any less well than a wall. In fact, wind speeds are higher in the roof & it is more exposed to the weather, so if anything it should be built more robustly. Similarly, no one questions the practice of ventilating the outside face of a timber frame sheathing board or suggests ventilating the inside face of the sheathing board instead, but these questions are often asked in the context of a sarking board.

    I think these are both historical hangovers. During the post-World War II house building boom, timber was in short supply, so sarking boards were replaced by tiling battens. A cold roof structure allowed the most structurally efficient roof trusses to be used. However, over time it was realised that this structure should be ventilated to avoid moisture build-up. Hence the ventilated cold roof.

    Other parts of Europe without the same shortage of timber, continued with warm roof constructions, rigid sarking boards & batten cavity ventilation.

    David
    • CommentAuthortony
    • CommentTimeApr 24th 2010
     
    All that didn't answer the question about why walls dont need to ventilated did it.
    •  
      CommentAuthordjh
    • CommentTimeApr 24th 2010
     
    For flat roofs don't forget that there is an alternative possible construction that avoids the whole question of ventilation gaps: an inverted roof. i.e. top-down - weather protection (gravel, greenery etc), insulation, waterproof membrane, rigid sheathing, structure, internal lining if desired.

    See e.g. http://building.dow.com/europe/uk/ins/invert/
    • CommentAuthorwookey
    • CommentTimeApr 25th 2010
     
    David: Putting all the insulation on the outside makes for a very fat roof construction and it seems a shame not to put any insulation in the 150-200mm provided by the roof timbers (typically taller than rafters in a pitched roof). The problem there is that we need vapour to be able to get out of this area and the ply/PUR/waterproof membrane has very high vapour resistance, and normally we want highest vapour resitance on the warm side, lowest on the cold side, so I can see why putting all the insulation on top of the ply is recommended. I'm working my way through BS5250 to get a proper understanding of this. It would be nice to have a construction without 200mm of uninsulated space in it - can we really not think of one that would be robust?

    djh: The problem I see with the inverted roof is that letting water down behind your insulation seems a great way to remove all the heat. This is a bad enough problem with air and water shifts hundreds of times more heat. The design no doubts attempts to minimise water movement behind the insulation, but some seems almost inevitable.
  11.  
    Posted By: djhFor flat roofs don't forget that there is an alternative possible construction that avoids the whole question of ventilation gaps: an inverted roof. i.e. top-down - weather protection (gravel, greenery etc), insulation, waterproof membrane, rigid sheathing, structure, internal lining if desired.
    This is essentially the warm deck flat roof with the insulation & waterproof layers swapped. In others words, with the vapour control & waterproof layers combined. In both cases the structure & deck are on the warm side of the insulation. However, as wookey says, in the case of an inverted roof the insulation will be vulnerable to heat transfer by water movement.

    David
  12.  
    Posted By: tonyAll that didn't answer the question about why walls dont need to ventilated did it.
    Timber framed walls have typically been built in the same way as warm roofs. The insulation has typically followed the line of the timber structure, the external sheathing board has been continuous & it has not been replaced by tiling battens.

    Where the sheathing board is not vapour open a vapour barrier has been used on the inside as in d)[ii]. Where the sheathing board is vapour open, e.g. woodfibre board, then typically an plywood or OSB lining board provides sufficient vapour control. This is equivalent to d)[i] & is how timber framed homes are typically built in Alpine regions.

    Both will typically have a ventilated batten cavity, but this is sometimes ommitted in d)[ii], where a shingle or hung tile finish is used.

    David
  13.  
    Posted By: wookeyDavid: Putting all the insulation on the outside makes for a very fat roof construction and it seems a shame not to put any insulation in the 150-200mm provided by the roof timbers (typically taller than rafters in a pitched roof). The problem there is that we need vapour to be able to get out of this area and the ply/PUR/waterproof membrane has very high vapour resistance, and normally we want highest vapour resitance on the warm side, lowest on the cold side, so I can see why putting all the insulation on top of the ply is recommended. I'm working my way through BS5250 to get a proper understanding of this. It would be nice to have a construction without 200mm of uninsulated space in it - can we really not think of one that would be robust?
    A vapour control layer is normally placed on the inside because it's very thin & has almost no thermal resistance. So if it's was placed anywhere other than the inside it is likely to cause condensation. Non-vapour open insulation on the other hand has a temperature drop associated with it. So we have more freedom in terms of where we put it in the build-up, but this needs to be balanced against other factors.

    Putting it between rafters helps the U value, but forces all the vapour to pass through the rafters. Putting it below the rafters reduces vapour transfer through the roof, but also reduces rafter temperatures increasing condensation risk. Putting it above the rafters has the same impact on vapour transfer through the roof, but keeps the underside of the rafters at room temperature. This is why some BBA certificates insist on putting some non-vapour open insulation above the rafters, despite it initially seeming counter-productive.

    To answer your question, I can imagine an adaption of fostertom's pitched roof build-up working for a flat roof. From the bottom:

    Plasterboard finish to rafters;
    Vapour open, hygroscopic, insulation to depth of rafters, e.g.Warmcel cellulose;
    OSB/plywood deck to rafters;
    100-150mm non-vapour open, closed cell insulation, e.g. extruded polystyrene;
    Waterproof covering.

    Note that there is no vapour control layer to the inside, because it's a form of breathing roof which breathes towards the inside. The deck will be below room temperature during winter & under some conditions there will be moisture build-up in the hygroscopic insulation & deck. However, with sufficient depth of non-vapour open insulation above this can be designed to avoid long term build up. A condensation risk analysis would be essential in each individual case.