Home  5  Books  5  Magazines  5  News  5  GreenPro  5  HelpDesk  5  Your Cart  5  Register  5  Green Living Forum
Not signed in (Sign In)

Categories



Green Building magazine

Green Building magazine

New - Spring 2012 edition.

View the current issue.
Subscribe now.
Magazine homepage.
Browse back issues.





Vanilla 1.0.3 is a product of Lussumo. More Information: Documentation, Community Support.

Welcome to new Forum Visitors
Join the forum now and benefit from discussions with thousands of other green building fans and discounts on Green Building Press publications: Apply now.




    • CommentAuthorjms452
    • CommentTimeJul 2nd 2010
     
    I appreciate that there has already been some discussion on this and have read the various posts. I have had a (pricy) quote from an installer of one of the big propriety systems and felt that although they could do all materials and finishes they were essentially pushing the easiest system for them rather than the best for me (i.e. 50mm phenolic to ‘just’ meet building regs in the minimum, easiest-to-fit, thickness).

    The Property
    In Hertfordshire
    Detached Victorian house which is solid brick wall.
    There are lots of fitting on internal walls of the house including a fairly new kitchen so we are happy with the external over internal choice.
    We are happy to end up with a white ‘cottage’ at the end of this so can cope with the change in character but would like to avoid it looking like a house which had insulation bolted on the outside (i.e. blends seamlessly into the eaves etc.).
    The eaves overhang by 4-5” so while we appreciate that more insulation is better we don’t want to go to the point where we need to extend the eaves or add lots of prefab trim.
    We are lucky to have no evidence of any, even minor, rising damp issues.
    There is also already quite serviceable UPVC double glazing.
    The loft is insulated with 300mm mineral wool.
    The only suspended floor is insulated with 150mm mineral wool, the rest of the floor is solid.

    Questions
    From the previous posts I have read recommendations about creating ventilated gaps between the insulation the wall of the house and even mention of internal gutters etc. Given that the quote we have had so far for 50mm PU bolted onto the wall and masonry-paint/silicone-render is just over £15k creation of such a complex structure seems like it will be financially non-viable. Are these recommendations belt and braces for driving rain conditions or are such precautions really valid?

    What are your thoughts on the best system? By best I’m not that fussed about the difference between stopping 95% and 99% of the heat flow but care greatly the about the lifetime and the general performance of the system in 20 years time and to a lesser degree the breathability. I am coming to the conclusion that 80-100mm or so of XPS bolted onto the walls covered in a ‘breathable’ silicone render might be the best compromise – Any alternative suggestions?

    I would also like to reuse the current windows but reposition these to be at the level of the insulation to avoid cold-bridging/pricy-insulated-detailing around the windows. However I am likely to fit new, higher-performance, windows within the life of the EWI. I am struggling to find details of window repositioning and ease of replacing the windows in future once EWI is in place? The installers say that I’d need a glazier to reposition the windows but they couldn’t provide a spec for the position/fixings. I can’t imagine glaziers knowing a lot about positioning windows within EWI and at worst would immediately void the warranty of the EWI by drilling fixing holes into the EWI. What routes have other members taken with this issue?

    Would also love to hear any success-stories/lessons-learnt from similar EWI projects, recommended installers or systems etc.

    Thanks

    John
    • CommentAuthorjamesingram
    • CommentTimeJul 3rd 2010 edited
     
    Hi john,
    seems like you've answered a lot of your own questions

    Eaves of 4-5" restricts your insulation depth to say 100mm max , depends on the look you wont , small soffit always look at bit odd to me.
    either go for a breatherable system ; rockwall slab, woodfibre insulation or similiar with lime of arcylic render
    or non breathable Phenolic / XPS / PUR with arcylic , sand cement or lime render
    EPS seems to fall somewhere inbetween , hardly breathable ?

    Renders can be through colour or arcylic top coat or just painted the old fashion way

    Through colour or arcylic top coat seems to make seense to me , as hopefully this will last longer

    Windows detailing seems to suggest insulating the external revels with as thick as you can onto the window frames will get you round some of the thermal bridging, so leave them where they are.

    I'm no expert but have some experience installing and fixing various systems
    so I'd go for, as you say, 80mm-100mm
    Best to reduce heatloss , 100mm Phenolic with arcylic top coat , meshed one coat or meshed multicoat systems
    Breatherable option , 100mm woodfibre(NBT) or rockwall with through colour lime render and mesh
    as to life perfomance there's so many varibles its hard to say. I guess we'll have to trust the manifacture claims !

    How about you do some research of the various systems , talk to the suppliers , then try and find a local plasterer/renderer with some interest/savy and get together and sort out a solution , even on a day rate for time and materials you may well get the price down from your quote ( depend on how big you house is) be good to get it below £100m2

    hope this is of some help

    some links
    EWI good pratice guide
    http://www.azobuild.com/downloads/GPG-external%20wall%20insulation%20MK.pdf
    http://en.wikipedia.org/wiki/External_wall_insulation#External_Wall_Insulation_Systems
    http://www.natural-building.co.uk/news/2010/nbt-launches-pavawall.html
    http://www.inca-ltd.org.uk/
    http://www.wbs-ltd.co.uk/refurb_drawings.htm
    http://www.netweber.co.uk/external-wall-insulation-systems.html

    report on longterm perfomance
    http://www.ibp.fhg.de/literatur/fachz/Roz2.pdf
    • CommentAuthorjms452
    • CommentTimeJul 5th 2010
     
    Hi James,

    Thanks for your thoughts.

    Your comments make me thank that rockwool may be worth more of a look as it seems like it should last virtually indefinetly, and had the potential to dry out if it ever got wet. I will also have another look into EPS as my reading seem to show a moderate degree of breathability.

    For your comment about window detailing and insulating the reveals won't this make it near impossible to remove the existing windows in future? It seems to me that if the EWI is just over the exterior faces of the walls (and not in the reveals) then the windows can be moved out giving a more simple construction and minimal thermal bridging. The only issue is what exactly do you fit the windows too! 8)
    • CommentAuthortony
    • CommentTimeJul 5th 2010
     
    Hang them out there on brackets
    •  
      CommentAuthorfostertom
    • CommentTimeJul 6th 2010
     
    e.g L's of 30x5 Batstrap screwed to the outside wall face and projecting outward, there screwed to the perimeter face of the window frames - e.g. 2x down each jamb and 2x across the top - @ about 900c/cs The cill can often hang there if nec if that helps with detailing when there's nothing solid to rest it on or screw it to. That way, the window hangs in space outboard of the old wall face, ready to bring the EWI up to the sides of, and lap across the outside face of (jambs and head) as far as poss without fouling the opening light or hinges. It does wonders for effective insulation, to 'suspend' the windows within the insulation zone, well away from contact with anything internal (which is what the old wall becomes - part of the internal environment).
    • CommentAuthorjms452
    • CommentTimeJul 8th 2010
     
    @Jamesingram

    In the complete guide to solid wall insulation (Christopher Pearson):
    Rockwool – negligible vapour resistivity – i.e. excellent;
    EPS – allows moisture vapour to pass through – but not quantified.

    Do you have a quantifiable number for the vapour permeability (or lack of it) of EPS?
    Does anyone have any idea of what permeability is needed?
    I've seen this topic go round and round on previous EWI posts and noticed that all the materials seem to sing their strengths but it all seem to be qualitative! i.e. breathable 'enough' is sufficient and you will then reach diminishing returns.

    I worked through the costs per m2 and came out with approximately:
    50mm Phenolic + plain render finish + masonry paint = £60/m2 50mm Phenolic + plain render finish + white silicone render= £65/m2.
    Not quite as pricy as I thought from your £100/m2 benchmark.

    @tony & fostertom

    Thanks for the simple solution. Do you know if this is routinely done or is it a pragmatic route to the theoretical ideal? i.e. I notice it doesn't seem to be included in the standard detailed drawings etc...

    Appolgies if I seem overly cautious - I am an experimental scientist, so like hard evidence, and don't fancy turning my house into an experiment.
    • CommentAuthortony
    • CommentTimeJul 8th 2010
     
    I met a great guy the other week who is a surveyor in the garden of England who regularly specifies 200mm eps for ewi.

    I cant see any good reason to do it with a lower U value than that would give. central europe it is best practice and very common.
    • CommentAuthorjms452
    • CommentTimeJul 8th 2010
     
    'I cant see any good reason to do it with a lower U value than that [200mm EPS] would give'

    How about wanting to keep the look of the house as the eaves only come out by 5"?
    80mm XPS has already reduced the solid wall u value of more than 2 to less than 0.33 so we have stopped 85% of the heat loss. 200mm XPS would involve a lot of work to make 85% into 92% and by then the windows, window reveals, foundations and ventilation will be the limiting points.

    Don't get me wrong: I would love to be able to specify double the thickness for a small extra cost but due to the existing construction there is a clear breakpoint.
    • CommentAuthorjamesingram
    • CommentTimeJul 8th 2010 edited
     
    See link below for a table of Vapour Permeability (r) of a range of materials (page 2) in this article making the case for Breathable constructions and the breathability of insulation products
    EPS 150 MNs/gm

    http://www.natural-building.co.uk/PDF/Breathability-Matters-response-to-Kingspan.pdf

    If you go the non-breathable route, using the lower lambda value insulations, you might as well increase insulation thickness ( say 80mm phenolic) . As discussed on other threads, insulation cost is only a small percentage of the overall cost when keeping to a thickness that doesn't require additional works
    •  
      CommentAuthorfostertom
    • CommentTimeJul 8th 2010 edited
     
    Springvale Platinum EPS (and poss anything made from BASF Neopor) has lower water vapour resistance than that 'generic EPS' 150 MNs/gm figure, as well as better insulation than generic EPS.

    Posted By: jms452... and by then the windows, window reveals, foundations and ventilation will be the limiting points.
    indeed, they will dominate, and going to 200, far from diminishing returns, allows these detail areas to be tackled - esp the massive losses thro window reveals if trying to make do with leaving extg windows in extg location.
    • CommentAuthorSaint
    • CommentTimeJul 9th 2010 edited
     
    Tom, the notion that EPS is vapour permeable, "breathable", showing little resistance to the passage of water vapour even if using Neopor is contrary to what Springvale says in its literature and even in its BBA where it quotes "significant resistance to water vapour transmission" http://www.springvale.com/ni/uploads/bbacertificates/platinumwallshield_bbacertificate.pdf see 11.1

    In the coldstore industry where EPS wall and ceiling panels were once the norm the very suggestion that EPS was more vapour permeable than XPS and therefore more reliant on the performance of the sealant between joints in a high vapour drive environment would send the EPS manufacturers into a state of apoplexy
    • CommentAuthorjms452
    • CommentTimeJul 9th 2010
     
    @Jamesingram

    Wow, the best quantitive data I've seen on the topic, thanks.

    My main concern was that a small, previously unimportant, fault in the DPC becomes exacerbated by the loss in breathability and/or there is a leak/fault at some point and I need the structure of the building to dry.

    From those figures I get a loss of 2 Kg/day through the 80mm EPS at 20C 50% humidity differential which seems resonable especilly as is ROM the same as brick.

    Do you have any ideas about silicone render and the effect of masonry paint?
    I would guess that the silicone would be better?
    • CommentAuthorjms452
    • CommentTimeJul 9th 2010
     
    just found the link below when looking for the breathability of silicone render (p4 - option B).

    http://issuu.com/the_building_centre/docs/8864_pdf7

    This gives the vapour resistance of 'FRA grade' EPS as 6.9MNs/gm. That's about 20 fold less than the figure used by the www.natural-building.co.uk/PDF/Breathability-Matters-response-to-Kingspan.pdf article.
    • CommentAuthorjms452
    • CommentTimeJul 23rd 2012
     
    Posted By: jms452

    I worked through the costs per m2 and came out with approximately:
    50mm Phenolic + plain render finish + masonry paint = £60/m2 50mm Phenolic + plain render finish + white silicone render= £65/m2.
    Not quite as pricy as I thought from your £100/m2 benchmark.


    Going through a second round of quotes for a different smaller (£25m2) job to the same house came up with the following costs:

    Weber contractor 1 - £165/m2
    Weber contractor 2 - £148/m2
    Wetherby contractor 3 - £94/m2

    all for 10 yr warranties in 80mm phenolic with acrylic render and silicone finish. exc VAT and Cills

    The contractor who I previously mentioned at £65/m2 is now the £148/m2. They said something about funding (?) through the manufacturer for jobs doing more than 70% of the wall area allowing this previous low price.

    Though I would post actual prices to avoid setting a potentially unachievable goal for others.
  1.  
    Uggh, but not remotely surprised. Not all high prices though; one of the guys on my Eco Refurb course last year was London-based, and doing 60mm phenolic for £90/m2.
    •  
      CommentAuthorikimiki
    • CommentTimeSep 7th 2012
     
    So,

    (1) Is there excess demand for EWI installation (relative to the base of contractors who are in the industry) ?
    (2) Are they anticipating a surge in Green Deal induced demand, and putting their prices up accordingly in advance ?
  2.  
    Not wishing to highjack the thread but there is a general relevance to window detailing within external insulation.
    Any suggestions as to how you would detail support for a window unit positioned outboard of masonry that weighs somewhere close to 800 kg. Window approx 2 m x 3.7 m, triple glazed 8 mm toughened glass to all panes. Or am I stuck with locating within the masonry envelope possibly located within a load bearing insulation collar.
  3.  
    Sky hooks?

    Or resin-anchored L-bkts to masonry on all 4 sides with insulation/render oversailing the frame? But 800kg..... ?Oversize frame so that a bit of the depth sits in the masonry?

    Tricky.
  4.  
    Nick, your last comment was along the lines I was considering. Extend the depth of frame back into the masonry opening and locate it within a insulation collar, Foamglas or similar. Also wondered if a continuous length of angle section resin bolted beneath window with load bearing insulation above and window sitting atop.
    •  
      CommentAuthorfostertom
    • CommentTimeSep 7th 2012
     
    Does the cill member need continuous support, or does it have beam strength so that vertically securing just the jambs would suffice? Because the jambs are easy - the side members of a ply/board box would have excellent shear strength to support the frame jambs even well outboard of masonry. That would work as long as the box's top and bottom members weren't expected to vertically support the frame head and jambs. If the cill needs support, then as above, plus some fabricated steel cantilever brackets at intervals under the cill - as long as the undercill masonry will resist the outward overturning force of the brackets.
  5.  
    Tom, no particular requirement for continuous support to cill, this will in itself be sufficiently robust as a section. Just acutely aware of the weight of these damn things !
    • CommentAuthorjamesingram
    • CommentTimeSep 8th 2012 edited
     
    Posted By: ikimikiSo,

    (1) Is there excess demand for EWI installation (relative to the base of contractors who are in the industry) ?
    (2) Are they anticipating a surge in Green Deal induced demand, and putting their prices up accordingly in advance ?

    Not that up on it , but
    1) doubt it
    2) seem suppliers etc. are expecting green deal to increase number of projects and are sending out useful product info in preperation , as to cost material all round seem to be up a touch.
    Supply and fit prices will depend on number of those in the running , if lots jump on to it, if it look like there's going to be a boom in EWI, then price may well drop with competiton .
    A far as I'm aware supply and fit price range from £65-150+++ m2
    •  
      CommentAuthorikimiki
    • CommentTimeSep 8th 2012 edited
     
    I am somewhat wary of entrusting our house to these outfits, insofar as it's very difficult to monitor and control the quality of their work in real time, while after the fact it's all concealed and sealed beyond inspection by the render!
    • CommentAuthorjamesingram
    • CommentTimeSep 8th 2012 edited
     
    find a local builder/plaster you trust and get them to do it , nothing complicated about it , so no need for so called specialist, if you dont fancy them. Though a honest specialist team will probably give you a cheaper better job purely because they're more fimilar with the product.
    cheers Jim
    •  
      CommentAuthorfostertom
    • CommentTimeSep 8th 2012 edited
     
    Isn't that true of v many building processes? Esp as Architect, making weekly site visits! A lot hangs on selection and trust of the 'right' contractor/subcontractors - and ultimately on enforceable contractual descriptions of work if faults discovered later (if you have a taste for litigation!). It's a miracle how it generally turns out OK-enough.

    It's a conundrum without a watertight answer. Right now I'm considering tenders - two firm-price tenders for the work as voluminously specified, and one 'fair estimate' of what a cost-plus contract might come to (unsurprisingly, the lowest of the 3 figures). The fair point made by the cost-plus man was that it removes all temptation to cut corners, which a fixed-price in theory promotes. First thought is 'speak for yourself' - an insight into that man's conduct when on a fixed-price. Despite all that, I'm not dismissing the cost-plus proposal, because I was impressed by that man's apparent eco-knowledge, enthusiasm and track record, which I would check out further before going that route. So we 'feel our way into' a solution - but it all takes time and can't be formularised.
    • CommentAuthorjamesingram
    • CommentTimeSep 8th 2012 edited
     
    "Though a honest specialist team will probably give you a cheaper better job purely because they're more fimiliar with the product." , just added this while you were typing Tom.
    Not really a miracle , Building to me is quite a robust process ( no need for motor racing tolerance) so an average quality job is probably sufficient, but still good to strive for above average to get the benefit of increased longevity, performance and esthetics ,if the budget allows
    •  
      CommentAuthorfostertom
    • CommentTimeSep 8th 2012
     
    And I added more while you were typing!
  6.  
    "First thought is 'speak for yourself' - an insight into that man's conduct when on a fixed-price."
    Even the most noble trademen will have a certain point at which they'll revert to self protectionism :smile:
  7.  
    As to choosing between tenders , I think trusting ones intuition usually seems to work.
    I do a fair bit of 'fair estimate' work , it takes alot of the pricing/loss making pressure off and allows me to concerntrate the work side rather than the money making side. Truth is I usually make more on price work
    as I have to stick a % lump on for arse covering, dont like it though , can be a stressful distraction.
    •  
      CommentAuthorfostertom
    • CommentTimeSep 8th 2012
     
    Thanks James, that's helpful.
   
The Ecobuilding Buzz
Site Map    |   Home    |   View Cart    |   Pressroom   |   Business   |   Links   
Logout    

© Green Building Press