Home  5  Books  5  GBEzine  5  News  5  HelpDesk  5  Register  5  GreenBuilding.co.uk
Not signed in (Sign In)

Categories



Green Building Bible, Fourth Edition
Green Building Bible, fourth edition (both books)
These two books are the perfect starting place to help you get to grips with one of the most vitally important aspects of our society - our homes and living environment.

PLEASE NOTE: A download link for Volume 1 will be sent to you by email and Volume 2 will be sent to you by post as a book.

Buy individually or both books together. Delivery is free!


powered by Surfing Waves




Vanilla 1.0.3 is a product of Lussumo. More Information: Documentation, Community Support.

Welcome to new Forum Visitors
Join the forum now and benefit from discussions with thousands of other green building fans and discounts on Green Building Press publications: Apply now.

The AECB accepts no responsibility or liability for any errors or omissions in the content of this site. Views given in posts are not necessarily the views of the AECB.



  1.  
    Hi there,

    About to start conversion of a Church into a 3/4 bed dwelling (~200m2) - it's grade II listed. I must decided on my heat source and method of delivery. The building may not be occupied all the time (we work away a lot), so I'd like a fairly responsive system (an hour or so to 'feel' the difference is OK). I want to use a heat pump to supply the heating (outside scope of this thread). We'll also have a 9kW double-sided wood stove for really cold periods.

    We're doing our best with insulation - floors - 0.16W/m2K (may get to 0.12), roof - 0.2W/m2K (may end up slightly better), walls first 1.1m - 0.3W/m2K, but then 600mm solid stone up to first floor height. So we could exceed Regs in a few places, but those solid walls present a problem (decorative stone reveals with not much plaster depth ~10-20mm). Not bad for something built in 1896 though (I'm still thinking where I can make improvements - suggestions please?).

    I'm deliberating my options (and have been for many months!). I've warmed (pardon the pun) to idea of warm air heating but as mentioned in the posts on this forum - there is little use of it in the UK (predominantly due to non-requirement for air-conditioning in the summer) - so makes making an informed decision tricky.

    I must install a MHRV system as I cannot modify the existing components (e.g. stained lead windows with no openers) to satisfy Regs, so am considering coupling a heat pump coupled to this and utilising the ducting to supply my heating too. I see this as offering the same advant of UFH in terms of non-occupation of wall space (i.e. rads). I should be able to route the ducting within the new constructed elements.

    Just wondering if anyone can offer some advice/observation/experience on this and what to look for/think about when specifying the system.

    Any comments greatly appreciated. I do not want to chicken-out on a potentially better solution due simply to lack of confidence - but given the amount of money involved............

    Cheers,

    Phil
    • CommentAuthortony
    • CommentTimeAug 27th 2010
     
    what is your heat loss in Jan/Feb?

    I suspect that it will be so high that the air ducts would need to so big that they wouldn't fit into the new walls/floors.

    I cannot see any heating system getting it to feel warm within an hour! The air will warm up fast but the fabric will still be cold and so you may still feel cold even with the air at 24C due to radiation losses.

    A monster grain drier might do it.

    Probably a mobile phone call to switch on the heating the day before you return would be a better plan

    I would aim at U values below 0.1 everywhere if it was mine and use aerogel to the window reveals and secondary dg if allowed inside,
  2.  
    Cheers Tony. A few omissions - secondary glazing is also going in - oak frames with low E dg.

    By 'feel' the difference, I mean a shift towards warm not stabilised warmth. The analogous situation/example in my house with my combi and wet rad. system would be that you 'feel' it starting to warm within about 10-15mins of the boiler starting up - admittedly it takes a good bit longer to get up to 'full' heat.

    I'm still working on reducing U-values but with such an old building and the grading options are somewhat limited, 0.1 is just a dream for me!

    Grain dryer is an interesting idea - but I'd specifically need/want a heat pump.

    Phil
    •  
      CommentAuthorSteamyTea
    • CommentTimeAug 27th 2010
     
    Its calculation time :bigsmile:

    First things you need to do is calculate your overall heat losses (overall/average U-Value).
    Then calculate the volume of air that needs to be heated.
    The the temperature differences (degree days).
    From that information you can easily calculate the amount of energy (Joules) needed to heat.
    Then decide how many air changes you need or in effect the leakiness of the building. Take into account the effects of the MHRV on airchanges.
    Now that you know how much air is leaving the building, how much heat is going through the walls and windows/doors it is relatively simple to work out the size of the heater needed.

    Two things to remember is your peak load (the coldest nights) and the time that the building is occupied (number of hours you are actually in it). The reason for this is to allow the heater to run at maximun efficiency, you do not really want it 'cycling'. The occupancy hours will tell you how fast you need to heat the building up i.e. if it is empty 8am-6pm you may want to heat if faster than if it is constantly occupied.

    You obviously understand how U-Values work, air changes are similar but the units are different. U-Value is in Wm^-2K^-1 but the air changes is in Joules per second, Js^-1.
    A Watt is a Joule per second, Js^-1

    Failing all that, get the tape measure out, work out your areas and volumes and post the data up here and then we can all have a go at working it out, I am sure we will end up with different numbers for you. :devil:
  3.  
    Thanks SteamyTea.

    Will give it a go!

    I had planned to do this to ensure my system will deliver what I need (my worst nightmare). I've done very rough stuff using online calculators - but realise the limitation of this (t'was more so to have an idea of the potential size of system required - ~17kW was the result - but I purposely made it the worst case scenario for our approach).

    I have had a quote on a system. They've offered to perform some heat loss calcs - so it'll be good to see how the two figures compare!

    Phil
    •  
      CommentAuthordjh
    • CommentTimeAug 27th 2010
     
    I believe there are issues with using a heat pump to heat a building from cold. I don't know enough to suggest anything other than to ask your question on the AECB forum.
  4.  
    I would be very dubious about trying to use warm air heating in this case. Your ground floor insulation levels are very poor, especially for the top half of the wall. I also suspect you will find it very hard to make the building airtight, resulting in significant loss there too. You absolutely need to do the calculations.

    Air does not have a very high heat carrying capacity - much less than water - and to provide the level of heat you will need you're almost certainly going to need large amounts of air flow, resulting in very large ducts, big fans and almost certainly lots of air currents. This is unlikely to be easy or comfortable and could be noisy.

    You also have huge thermal mass, so if you are going to allow the structure to cool down then you will need a lot of heat to start to warm it back up. Hot air is unlikely to do this quickly.

    The air flow will be massively more than you need for normal ventilation, so I wouldn't link it to your MVHR system unless you want it to be very expensive. You would also need very large heat exchangers to get the heat into the air, which will introduce quite a bit of resistance to the air flow. You would need PassivHaus levels of insulation and airtightness to get away with this - and you look to be far from these levels.

    UFH could be a good option, but the response time is not always fast, especially with your level of thermal mass. Your heat losses will probably make it prohibitively expensive to keep the whole house up to temperature all the time.

    Your best bet is almost certainly a radiator based system, but this generally needs high water temperatures and is probably not compatible with a heat pump. Maybe oversized radiators running at a lower temperature, but this conflicts with your desire to not have too much wall space occupied. Perhaps skirting radiators?

    I would be inclined to go for an even larger wood stove than you currently assume but this will depend on your heat loss calculations. You could consider a large boiler linked to your heating system as well - double sided boiler stoves do exist.

    The last option is to hang some jumpers near the entrance to put on when you take your coats off!

    Whatever you do you'll probably need a large heat source, so don't assume a small heat pump if you're wedded to this route.
  5.  
    I can speak from experience here. I live in a 200m2 house with stone walls and not much insulation in them. I heat with forced air that's supplied by a GSHP. I don't have an HRV as the air leakage is such that it's not required. My heatloss at -23C outside is 15kW and the heatpump supplies 11kW - to make up the difference for worst case conditions (which occur less than 2% of the time), there's an auxiliary resistance heater. The airflow required to deliver that amount of heatis 1450 cubic feet per minute (684 l/s) - this is obviously much larger than an HRV requires. However, over here it's standard practice to use the forced-air heating ducts as the supply for the HRV, the extract side uses its only, much smaller, ducts.

    The largest ducts we have are 24"x10" rectangular ducts and the smallest branches are 6" round ducts. Most of these are hidden in wall and ceiling spaces, except for the large trunks which are in the basement (which is not designed as a finished room). There's no problem with "resistance to air flow" in the heat exchanger - this is all built into the heatpump and the coil is about the size of a large car radiator. One certainly doesn't need passivhaus levels of insulation and airtightness to use forced air heating - it all works fine so long as you have sufficient airflow to supply the amount of heat required - with the airflow level I mentioned the temperature rise of the air is about 14C above ambient - so if your room temperature is around 70F, the air from the heating system is coming out in the low 90s. Because this is a relatively low delta-T, you don't actually feel any drafts at all (surprising but true).

    In general, heatpump systems are not designed for fast response - though with a good adaptive thermostat you should be OK as they can be programmed to give a reasonable rate of increase in temperature per hour without energizing the auxiliary heat. In our case, we leave the thermostat set at the same temperature year-round (as I work from home) and let the system run as necessary to maintain the temperature. On the odd occasions we have let it get cold (transition from summer to the heating season) - the warm air makes it feel warm pretty quickly in my experience.

    Hope this helps,

    Paul in Montreal.
  6.  
    OK, I bow to Paul's first hand experience. If it works for him under similar conditions and -23C then it'll work here.

    Do note the size of the main air ducts though - these will have to be an integral part of the design, rather than an afterthought unless you want to go for the industrial look.
    •  
      CommentAuthorSteamyTea
    • CommentTimeAug 28th 2010
     
    When it comes to cold weather and heat pumps Paul knows his onions, better at sums than me too:cry:
  7.  
    Posted By: SteamyTeahen it comes to cold weather and heat pumps Paul knows his onions, better at sums than me too


    Thanks for the vote of confidence! Any system is only as good as the design and installation that's behind it - if the calculations are done properly, there's no reason why a forced-air heating system should not be quiet, effective and economical to run. One certainly doesn't need passivhaus-levels of insulation - though, of course, if you do, the heatload is reduced and hence the capital cost of the heating equipment can also be reduced (together with the running costs). Ironically, though, paying more for high-efficiency heating appliances in a low-load application can have the perverse effect of not being cost effective since the potential for savings (through the higher efficiency) is diminished because the absolute consumption figures per year are reduced. This is the same diminishing returns that extreme amounts of insulation also incur. It's always worth doing a proper cost-benefit analysis to see what the appropriate trade-off is. That's what engineering is all about :)

    In my case, it wasn't cost effective to install a heatpump that would meet 100% of the worst-case winter heating load as the increased capital costs of the equipment and deeper borehole required would work out at more than the cost of running auxiliary straight resistance heat for the 2% of the time these would be required - the engineering compromise in my case was to size the heatpump at around 80% of the peak heatload - the breakeven point being around 25 years of operation (which is the typical lifespan of the heatpump itself). A good installer will certainly help quantify these trade-offs.

    Paul in Montreal.
  8.  
    Guys - thanks for the comments and advice.

    Apologies for the delay in picking up this again - I was on the hunt for a caravan on Friday night and onsite yesterday.

    Paul, I am very encouraged by your experience thanks for sharing this.

    The cost-benefit argument is interesting and one that I pondered yesterday as I stared at those solid walls! Seems like there is little point in spending the extra cash on improving the floor insulation from U - 0.16 to 0.12, or putting in multifoil in the roof to come below 0.2, when in actual fact the effect of these is swamped by the solid walls. I have reconsidered the walls and probably can get a 42.5mm foam-backed plasterboard above 1.1m - this should give 0.44W/m2K. I think this be my priority. Over the coming days I'll do the calculations (or at least try) to look at the trade-offs.

    I had a brief chat with a rep. from the supplier - he'd done some 'quick' heat loss calcs (they charge £250+vat for the 'full') - and was able to discuss these over the phone with me. He said, we're looking at 4kW loss due to ventilation (therefore recovered by the HRV system - 95% eff.), leaving 9.5kW for the building (at -1ºC outside temp. and 21ºC inside). At 3ºC outside temp., the heat loss dropped 4.5kW for the building fabric losses. So if I can get some insulation in those solid walls I could be looking at some quite attractive!

    In terms of air-tightness, the secondary glazing will now not have vents, so my biggest challenge is in the form of two large oak doors that currently have a 15mm gap between the whole door and the stone frame! - I can solve this though.

    So finally, I'm still learning here for sure, but am not quite clear on how the efficiency of the heatpump is effected by its load? Seems like I need to be undersized slightly to ensure the system is running at full capacity and therefore making maximum benefit? I was advised many months ago that typically GSHP are sized 60-70% of required heat (justified by them being on all the time). I think that maybe leaving the system to run at a 'background' level may actually be better - also if the heatpump is integral to the HRV - this may be the case, as I assume the HRV unit runs continuously.

    Cheers,

    Phil
    •  
      CommentAuthorSteamyTea
    • CommentTimeAug 29th 2010
     
    Phil

    Where in the country are you? Have you been to the MET office and looked at your Temperature Regime?
    Also look up how Degree Days are used, briefly they show the amount of time that the temperature goes below or above a set temperature. They are usually calculated using the Mode (most frequently occurring) as opposed to the Mean (numeric average) temperature as this gets rid of the outliers, or the extremes that serve little purpose when working out your heat load.
    It is also worth remembering that during the day that there are other heat sources, mainly solar gain, that help to raise the temperature. Also things like fridges/freezers/cooking/hot water tanks/people also raise the temperature inside.

    Insulating as much as you can and draught proofing will make a huge improvement. I had what seemed like a little draught from my back door, maybe a 2mm gap 150mm long and fixing that means I now do not need my storage heater on in the kitchen, the fridge does all my heating.

    If you want to experiment to find out how a heat pump works, play around with an old fridge, try it at different settings and see how long the compressor is running, then stick it out in the sun (or in a hot room) and do the same thing. You should find that the compressor runs for longer as there is less of a temperature difference where the fridge gets rid of the heat. This means that the compressor runs for longer for a smaller temperature difference, or less heating for more energy use.

    Good luck with the caravan, insulate it well and keep the draughts out.
  9.  
    Posted By: PhilbobagginsiiiI'm still learning here for sure, but am not quite clear on how the efficiency of the heatpump is effected by its load? Seems like I need to be undersized slightly to ensure the system is running at full capacity and therefore making maximum benefit?
    To get the best efficiency from the GSHP you need to make sure it's flow/return temperatures are as low as possible. This in turn means the supply air heat exchanger/coil needs to be sized to deliver the heat load required with a relatively low temperature difference across it & the ducts/fans need to be sized to deliver the required heat load at a relatively low supply air temperature (i.e. as close to the desired room temperature as possible).

    If this is to work efficiently you need a single supplier/designer to take responsibility for the complete system. You're unlikely to find a supplier with experience of all this & MVHR, so you might be better keeping these systems separate. Alternatively, have you looked at the ready integrated MVHR/ASHP systems from Genvex?

    http://www.genvex.co.uk/genvexmp1.asp?pid=3432&cid=GENVEXmp1

    David
  10.  
    Posted By: PhilbobagginsiiiHe said, we're looking at 4kW loss due to ventilation (therefore recovered by the HRV system - 95% eff.),


    Your HRV will not recover this - this heat loss is due to uncontrolled ventilation, i.e. air leakage - this is above and beyond what your HRV will supply. Really, the only way to know these figures is to have a blower door test done. If your air leakage is greater than about 3ACH@50Pa, a HRV will not save you any energy at all.

    Posted By: davidfreeboroughTo get the best efficiency from the GSHP you need to make sure it's flow/return temperatures are as low as possible. This in turn means the supply air heat exchanger/coil needs to be sized to deliver the heat load required with a relatively low temperature difference across it


    Standard rule of thumb over here for forced air systems supplied by a heatpump is that you need a temperature difference of around 14-16C between the supply and return temperature. Any less than that and the supply air feels cool (and you'll notice drafts) - any higher than that and it will also feel drafty as there will be too much of a difference between the supply air and the room temperature. This is why many people complain that forced air systems are uncomfortable - if you heat the air with gas or oil, you get a much higher temperature rise and the difference with the room temperature is noticeable.

    Posted By: davidfreeboroughAlternatively, have you looked at the ready integrated MVHR/ASHP systems from Genvex?


    This will never work for the heatloads we're talking about here - the airflow is an order of magnitude too low.

    Paul in Montreal.
  11.  
    We're in Cumbria, about 10 miles from Penrith.

    I will have a look up the temps. for the area and factor this in. Using modal avg. as opposed to mean makes sense.

    The explanation using the fridge makes sense in terms of reducing the time that compressor is running, but it's not entirely clear to me how this translates to an ASHP - as the inverse of the conditions mentioned? Sorry if I'm a bit slow - I understand the principle of operation (really), I'm trying to become fluent in its thinking from a practical perspective though.

    David, thanks for the suggestion, Genvex are indeed the people I'm currently talking to - i.e. integrated MVHR/ASHP.

    Thanks.

    Phil
    • CommentAuthortony
    • CommentTimeAug 29th 2010
     
    If you have MHRV then you dont need or want trickle vents in the windows.
    • CommentAuthorCWatters
    • CommentTimeAug 29th 2010
     
    All I know about warm air heating is that we (the UK) went through a phase in the 1970(?) for installing it in newbuilds. My friend had one back then and hated it. I believe warm air heating was abandoned by builders soon after because it was unpopular.

    Our MHRV system is virtually silent (It appears to be the room grills themselves that makes any remaining noise not the ducts or the fan unit) but I suspect it would be too noisy at the higher flow rates needed for heating.
    • CommentAuthortony
    • CommentTimeAug 29th 2010
     
    My MHRV works OK and does everything is quiet and is the only form of additional heating apart from light-bulbs that we have.
  12.  
    Posted By: tonyMy MHRV works OK and does everything is quiet and is the only form of additional heating apart from light-bulbs that we have.
    I'd like to design out our underfloor heating, but I'd like some kind of automated backup heating. Does the MVHR incorporate heating elements or an ASHP like the Genvex units?

    David
    • CommentAuthortony
    • CommentTimeAug 29th 2010
     
    They can do and with low and very low heat demand MHVR can do it all -- mine does

    I was warned that the ducts would be too small but my heat demand is extremely low
    •  
      CommentAuthorSteamyTea
    • CommentTimeAug 30th 2010 edited
     
    Phil
    If you understand the basic I will not elaborate more, will just add confusion. We each find our own way of understanding heat pumps, the Carnot cycle and latent heat of evaporation.

    Hopefully the attached file is the regime for where you are. Met Office data, 22 year means and anomolies.
    Must check to see if you really are wetter up there than here. (Edit:Just checked and I get 0.4mm more, what a turn around for the records)
    •  
      CommentAuthordjh
    • CommentTimeAug 31st 2010
     
    I can confirm that forced-air heating systems work well, in the right circumstances. My first house was fitted with a gas-fired one. I bought the house new about 1980. There was some noise but not enough to disturb me. The main benefit was that it made the house feel warm very quickly, precisely because it wasn't heating the structure first. I was living alone at the time so the house was empty most days.

    Posted By: Paul in MontrealYour HRV will not recover this - this heat loss is due to uncontrolled ventilation, i.e. air leakage - this is above and beyond what your HRV will supply. Really, the only way to know these figures is to have a blower door test done. If your air leakage is greater than about 3ACH@50Pa, a HRV will not save you any energy at all.


    I'd also second what Paul says about HRV and airtightness. At that level of airtightness MEV (mechanical extract ventilation) is more cost effective.
    • CommentAuthordickster
    • CommentTimeAug 31st 2010
     
    What about cold feet?. Presuming that you have high ceilings, won't you experience cold air falling down the inner face of the external walls and flowing to the centre to rise up again? Underfloor heating?
  13.  
    Posted By: dicksterWhat about cold feet?. Presuming that you have high ceilings, won't you experience cold air falling down the inner face of the external walls and flowing to the centre to rise up again? Underfloor heating?


    I have high ceilings (10 feet) downstairs in my house and it doesn't seem to be a problem. The duct layout is such that the return air vents are situated away from where people would be sitting. Careful vent placement and airflow design is key to making a forced-air heating system comfortable. We get very good mixing of the air with very little stratification - this means that the floor temperature is close to ambient - even more so as the basement under the ground floor is also heated. I was surprised to find that, for example, when seated at the dining table, which is only a couple of feet from a supply vent, the candles on the table don't flicker when the heating system is running. Everyone who visits our house always comments on how comfortable it feels.

    It can be quite a challenge to integrate underfloor heating and forced air as the control responses of the two systems have quite different time constants and so it can be an interesting problem to program these for comfort.

    Paul in Montreal.
  14.  
    Can I just add a few more comments.

    Going back to the start of the topic, I think I am now fairly confident with the correct design and installation a forced-air heating system could work well - so thanks for sharing your views and experience (in particular Paul). And that in my personal view it's a great way to heat, simply not generally given a fair view due to poor designed 70's systems. For me to go forward with this system (Genvex - integrated ASHP/MHRV) I need to be sure of heatlosses as the system is only capable of 6kW at best. I also need to determine the flows for delivery of this heat, as I only have those associated with the MHRV at the moment.

    I have performed my own heatloss calculations (first time!), and having reviewed my approach to insulation for the project, I can get my heatloss for the fabric down to <3.5kW (from a figure of around 9kW depending on the U-value used for the 600mm red sand stone walls). The effect of those walls was huge!

    Heatloss due to ventilation is proving a little more complicated - especially as the definitive way would be to pressure test - but this cannot be done now as we're only just starting the work so don't have a finished building to test, yet I need the data to specify the heating system!

    Using the guide in the regs, I calculated my minimum required ventilation rate to be 212m3/hr. The volume of the property is 690m3. Genvex told me they calculate this by factoring in 50% in uncontrolled losses (due to 'big old building'). From the quote I can see they spec. the MHRV system to be 0.5 ACH - so for me 345m3/hr. This gives me (690x1.5)x0.5x0.33x22 = 3.8kW (vol x ACH x SHC(air) x delta T).

    The bit that concerns me is the 50% addition for uncontrolled losses. Surely I can reduce this - e.g. effective draught exclusion on doors, secondary glazing will not have trickle vents, continuous bead of dry wall adhesive, proper sealing of vapour membranes in floors, roof and walls etc. This is something I should look into. We are essentially putting a new house inside an old structure so I should be able to implement some reasonable measures to limit this.

    Phil
    • CommentAuthortony
    • CommentTimeSep 1st 2010
     
    dream on!!!
  15.  
    Phil,

    read back to Paul's earlier post. He has a 200m2 property and he needs close to 700l/s to get adequate heating (OK at -23C).

    You're talking about 345m3/hr, which works out to ~96l/s, or around seven times less that Paul's system is capable of, for a house that is probably around half as big again.

    SHC of air at 20C is 1.005kJ/kg.K
    Density of air at 20C is 1.205kg/m3
    Heat capacity is 1.005*1.205kJ/m3.K = 1.211kJ/m3.K
    1m3=1000l so heat capacity is 0.001211kJ/l/K
    1W=1J/s so heat carrying ability is 0.001211kW per l/s per K

    At your estimated ventilation of ~96l/s, this gives 0.116kW per K

    Assuming an ambient of 20C, the maximum air temperature you could use for heat is 50C, which gives a 30C delta. Overall, this only just hits the 3.5kW you estimate for the fabric losses (which I suspect is optimistic), and you haven't even included the uncontrolled ventilation losses yet.

    You really don't want the air temperatures up as high as 50C, as Paul suggests, so you need to be looking at higher flow rates (at least twice and probably much more).

    Trying to tie warm air heating and MVHR together in a single system is a bold move in anything that isn't approaching PassivHaus levels of losses. Pushing this much air through the MVHR runs the risk of very dry internal air in the winter. By keeping the heating separate from the ventilation you can separately control temperature and air quality.

    If you detail correctly then you should be able to get the air tightness to a good level, but you will need to be very careful and paranoid about every penetration through the envelope. Think very carefully about what will be your airtightness layer around the whole structure and how all the different elements will connect up. Think also about how the different elements will move over time and how you can still ensure high levels of airtightness in 5 years (and more) time. If you do not think this through carefully you will fail.

    Also, are you sure you have taken into account all your thermal bridges?
    •  
      CommentAuthordjh
    • CommentTimeSep 1st 2010
     
    What Mark said.

    The key point is that a forced-air heating system recirculates air inside the house, so it can have much higher flow rates with no losses in a heat exchanger and no change in the humidity. It also has larger ducts than an MVHR system.
  16.  
    Posted By: PhilbobagginsiiiFor me to go forward with this system (Genvex - integrated ASHP/MHRV) I need to be sure of heatlosses as the system is only capable of 6kW at best
    I guess you're taking your figures from the following spec. sheet?

    http://www.totalhome.co.uk/images/GE%20Premium%203%20Iss%205.pdf

    The compressor output power is quoted as 2.7kW. So the rest of the 6kW must be coming from the heat recovery. I assume that's why the 6kW is only available when the outside air temperature is -15 degrees C.

    Posted By: PhilbobagginsiiiI have performed my own heatloss calculations (first time!), and having reviewed my approach to insulation for the project, I can get my heatloss for the fabric down to <3.5kW (from a figure of around 9kW depending on the U-value used for the 600mm red sand stone walls).
    At what outside air temperature did you calculate this fabric loss? Would you like to share the numbers?

    Posted By: PhilbobagginsiiiI calculated my minimum required ventilation rate to be 212m3/hr. The volume of the property is 690m3. Genvex told me they calculate this by factoring in 50% in uncontrolled losses (due to 'big old building'). From the quote I can see they spec. the MHRV system to be 0.5 ACH - so for me 345m3/hr. This gives me (690x1.5)x0.5x0.33x22 = 3.8kW (vol x ACH x SHC(air) x delta T). The bit that concerns me is the 50% addition for uncontrolled losses.
    The bit that concerns me is that you seem to be including the 100% which goes through the MVHR in the fabric air leakage. Perhaps this balances out because the Genvex datasheet includes the recovered heat in the available power, but I think it's clearer to separately calculate the heat exchanger performance, air leakage losses & power available from the compressor.

    Anyway, the heat exchanger serves only to reduce your ventilation heat losses. Even if it's perfectly efficient, the compressor alone will need to provide all the power to compensate for fabric heat loss & fabric air leakage. For the units I was looking at, 2.7kW is all that's available to cover the sum of these.

    David
   