Posted By: SteamyTeahen it comes to cold weather and heat pumps Paul knows his onions, better at sums than me too
Posted By: PhilbobagginsiiiI'm still learning here for sure, but am not quite clear on how the efficiency of the heatpump is effected by its load? Seems like I need to be undersized slightly to ensure the system is running at full capacity and therefore making maximum benefit?To get the best efficiency from the GSHP you need to make sure it's flow/return temperatures are as low as possible. This in turn means the supply air heat exchanger/coil needs to be sized to deliver the heat load required with a relatively low temperature difference across it & the ducts/fans need to be sized to deliver the required heat load at a relatively low supply air temperature (i.e. as close to the desired room temperature as possible).
Posted By: PhilbobagginsiiiHe said, we're looking at 4kW loss due to ventilation (therefore recovered by the HRV system - 95% eff.),
Posted By: davidfreeboroughTo get the best efficiency from the GSHP you need to make sure it's flow/return temperatures are as low as possible. This in turn means the supply air heat exchanger/coil needs to be sized to deliver the heat load required with a relatively low temperature difference across it
Posted By: davidfreeboroughAlternatively, have you looked at the ready integrated MVHR/ASHP systems from Genvex?
Posted By: tonyMy MHRV works OK and does everything is quiet and is the only form of additional heating apart from light-bulbs that we have.I'd like to design out our underfloor heating, but I'd like some kind of automated backup heating. Does the MVHR incorporate heating elements or an ASHP like the Genvex units?
Posted By: Paul in MontrealYour HRV will not recover this - this heat loss is due to uncontrolled ventilation, i.e. air leakage - this is above and beyond what your HRV will supply. Really, the only way to know these figures is to have a blower door test done. If your air leakage is greater than about 3ACH@50Pa, a HRV will not save you any energy at all.
Posted By: dicksterWhat about cold feet?. Presuming that you have high ceilings, won't you experience cold air falling down the inner face of the external walls and flowing to the centre to rise up again? Underfloor heating?
Posted By: PhilbobagginsiiiFor me to go forward with this system (Genvex - integrated ASHP/MHRV) I need to be sure of heatlosses as the system is only capable of 6kW at bestI guess you're taking your figures from the following spec. sheet?
Posted By: PhilbobagginsiiiI have performed my own heatloss calculations (first time!), and having reviewed my approach to insulation for the project, I can get my heatloss for the fabric down to <3.5kW (from a figure of around 9kW depending on the U-value used for the 600mm red sand stone walls).At what outside air temperature did you calculate this fabric loss? Would you like to share the numbers?
Posted By: PhilbobagginsiiiI calculated my minimum required ventilation rate to be 212m3/hr. The volume of the property is 690m3. Genvex told me they calculate this by factoring in 50% in uncontrolled losses (due to 'big old building'). From the quote I can see they spec. the MHRV system to be 0.5 ACH - so for me 345m3/hr. This gives me (690x1.5)x0.5x0.33x22 = 3.8kW (vol x ACH x SHC(air) x delta T). The bit that concerns me is the 50% addition for uncontrolled losses.The bit that concerns me is that you seem to be including the 100% which goes through the MVHR in the fabric air leakage. Perhaps this balances out because the Genvex datasheet includes the recovered heat in the available power, but I think it's clearer to separately calculate the heat exchanger performance, air leakage losses & power available from the compressor.