    Hi All

    Sorry if this is a silly question but I'm trying to work out the detailing for a warm roof design (all insulation above tafters) where the rafters overhang 500mm outside the outer wall.

    My design has both 4 and 25 degree roofs which are to be clad in a standing seam roof and both roofs are essentially the ceilings in the single storey element and room in roof element.

    I appreciate the benefits of a true warm roof and came across a system called VIEOROOF when looking at the Tata (Corus) Colorcoat Urban steel standing seam roof.

    This system has circa 240mm of Rocslab mounted above the rafters using special fixings that hold the insulation in place and provide a mounting for the metal sheet roof.

    The construction would be as per attached image (1) with standard 220mm rafters resting on the roof plate of a 150mm full fill cavity wall construction. The rafters extend 500mm beyond the outer wall to create the overhang.

    My questions are

    1. How to make this detail airtight? I presume I would have to plug the gap between the rafters as the exit the inner leaf? And then rely on the plasterboard/skim below the rafters?

    2. If the insulation is above the rafters, surely heat wil rise into to the void between the rafters and espace out through the sides? If I plugged the ends with enough insuation would this work?

    3. Would I be better off having a hybrid warm roof with insulation between the rafters and then making up the balance above? Would this help with either of the issues above?

    I’m going to attach a couple of images to help explain the above better, but please say if its not clear
    Thanks
  1.  
    You need to plug the gaps between the rafters with insulation, put a wind barrier on the outside to stop wind blowing through the insulation & an air barrier on the inside. The wind barrier should ideally be sealed to the outer leaf of the cavity wall & the sarking membrane in the roof. The air barrier needs to be sealed to the air barrier in the roof which, if you're using trussed rafters, will mean cutting it around all the ceiling joists/tie beams & sealing all these junctions with tape.

    A hybrid warm roof would help by plugging the rafters gaps with insulation, but it doesn't change the air barrier sealing issue. Using a ridge beam &/or purlins instead of trussed rafters can help because it allows you to have a continuous air barrier at the eaves without having to cut around lots of ceiling joists/tie beams. However, you'll need to think carefully about how the floor joists for the room in the roof are supported. Here's one I did earlier.

    David
    • CommentAuthorbeelbeebub
    • CommentTimeMay 15th 2011 edited
     
    Hi Crofty,

    I had a similar set of issues with my roof (going in as we speak).

    Here's a brief summary of my construction:

    The pitch of my roof is 30deg
    The walls are 100mm block, 200mm glass wool, 100mm block.

    I am using 200mm deep rafters sitting on the inner wall plate but not extending across the cavity.
    Over the top of the rafters is an 18mm OSB (grade 3, exterior) sheet layer. This is primarily for structural stability. This extends over the top of the cavity to link to a bevelled wall plate on the top of the outside blocks. It then flies past to provide the overhang. This achieves several things: It ties the tops over the block wall together for stability, it creates the eaves overhang and it makes air sealing of both the inner and outer joint easier.
    I then have a layer of breather membrane (Tyvek or similar)
    Then a layer of 50mm of Steico Universal wood wool over the top. This also acts as a water-proof layer.
    Where I have Veluxes or other roof penetrations I am putting a strip of Tyvek from the ridge down to the window/chimney etc. This is simply because it makes sealing easier as most of the products assume you have Tyvek as top layer.
    Then counter battens, battens and tiles.

    I'm insulating between the rafters with glass wool (not sure which one yet, see later). 2x2 noggins between rafters will help hold the insulation in place. The bottom of the noggins will be flush with the rafter bottoms and installed as the insulation goes up.

    A VCL will then be stapled and taped to the underside of the rafters. At this point I am intending to fix plasterboard (not foil backed) to the underside of the rafters (with the noggins catching the edges of the boards).

    You could put a service void in at this point, in which case the 2x2 noggins could probably be omitted.

    At the eaves and verge, there isn't any reason to carry the over rafter insulation much over the inner wall leaf, and certainly not over the overhang. So I am stopping the over rafter insulation above the inner wall. to make up, short deep counter battens are fitted. This stiffens the OSB overhang so that it is strong enough, the top edge of the stub counter battens also helps support the over rafter insulation and the counter battens that fit on top against "sliding" down the roof (i.e. shear of the connectors)

    Things to watch out for:

    At the rafter feet you almost certainly will need noggins as timber is far from straight and un-twisted. The noggins will also help stabilise the rafters. This means that the insulation will be interrupted at this point. I compromised by leaving a small gap at the top of the noggin, with some wool stuffed in. This reduces the thermal bridging.

    Fitting veluxes with over rafter insulation can be a little bit more tricky but I think we have got it cracked, I'll let you know.

    Timbers are nowhere close to straight, you must not assume (as I did) that if the ends are at 600mm centers the middle bits will be at 600mm centers!

    With that in mind, I would urge you to consider very carefully the 4degree slope on the flat roof (assuming it's not a typo). With the variation in building tolerances, especially timber, holding a slope of 4 degrees will be difficult, resulting in low spots and ponding

    EDIT: I forgot to mention, the room-in-roof roll has been discontinued. Knapf have not yet updated any of their literature or even their sales people, but if you try to order it you can't.

    Do you have goggle sketchup? If not download it for free from google, it's really great for early stage planning. If you do, whisper me your email and I'll send a model of the roof construction over for you to fly through.

    Good luck
  2.  
    This is our flat roof solution! The roof is airtightened from the outside using silicone between the rafter and the Ply.
      Flat Warm Roof Block.jpg
  3.  
    Hi VH
    What is the purpose of the 25x25 battens inlaid into the EPS (top layer I presume to fix the ply decking, but the bottom layer?)
    How do you cut the EPS for the 25x25 inlaid battens, then how do you fix the battens into the EPS?
    Peter
  4.  
    Hi Peter

    They should be 2 x 1 battens in the drawing and their purpose is to reduce the cold bridge from a screw going from outside to inside. Some builders have used the detail as in the drawing and others have used longer screws.
    We use a hot knife to cut a groove in the EPS the same size as the batten.
      EPS on Roof.jpg
  5.  
    OK I thought that would be the reason, there remains the question as to how do you fix the battens once the slot has been cut, or is it just a friction hold which would seem a bit tenuous to hold ply decking etc.
    Peter
  6.  
    Hi Peter, Just screw into the latt through the EPS and into the rafter below, the second latt is screwed into the 1st latt through the top layer of EPS.
    On a seperate note! I got an enquiry last week from somebody wanting to build a Passive House in Budapest, do you build houses?
  7.  
    Hi VH Thanks for that, its clear now.
    On the separate note! I do not build houses, but my sons partner is a newly qualified architect and works in Budapest and her English is better than my Hungarian.
    Peter
  8.  
    Posted By: Viking HouseHi Peter, Just screw into the latt through the EPS and into the rafter below, the second latt is screwed into the 1st latt through the top layer of EPS.
    On a seperate note! I got an enquiry last week from somebody wanting to build a Passive House in Budapest, do you build houses?


    So with your first layer of EPS all your battens line up directly with the rafters below? And your picture above shows the first layer ready for the next layer (which will have perpendicular battens)?
  9.  
    Posted By: spoonandfork So with your first layer of EPS all your battens line up directly with the rafters below? And your picture above shows the first layer ready for the next layer (which will have perpendicular battens)?
    That's the way we did it.
  10.  
    Posted By: Viking HouseThat's the way we did it.


    doesn't that mean your battens will run perpendicular to the roof slope and therefore be more prone to water damage? Wouldn't it be better to run the first set of battens in the first layer of EPS perpendicular to the rafters below and then run battens parallel to the rafters in the 2nd layer of EPS? What sort of screws are you using to attach the battens in the 2nd layer of EPS to the battens in the first layer?
  11.  
    Yes, you're correct Spoon, I misread your question, here's the detail we used.
      Ext Ins TF Roof.jpg
  12.  
    We have recently had a warm roof fitted onto the main part of our house using TLX Gold foil (breathable) on top of the rafters, 25mm Celotex between the rafters and 75mm celotex under the rafters. We also have an attached building that used to be a stables and has been converted to a 'granny annexe' for my parents and we have a standard breather membrane above the rafters, 75mm between the rafters and 75mm under the rafters. With both roofs we had limited scope for putting insulation above the rafters and were lucky enough to have sufficient head height to have so much insulation beneath the rafters. In all of the rooms the ceilings are partially or fully vaulted (i.e. we can see the underside of the roof) and so a warm roof was essential. We have hit the current building reg requirements for u values with both roofs.

    I know the materials are not particularly environmentally sound, but we are hoping that the energy they save will make up for the energy used in their construction.
    • CommentAuthorrhamdu
    • CommentTimeJun 21st 2011
     
    Another warm-roof question which I don't think is answered anywhere above (sorry if I missed it):

    The builders have put a warm flat roof over our loft room, with 90mm PIR above the rafters. We are adding 50mm PIR between rafters (making it a 'hybrid' warm roof). What do we do at the last rafter each side?

    (1) bring the insulation down the face of the rafter to join up with the wall insulation?
    (2) leave the rafter bare to keep it 'warm' (at the expense of some heat loss through the thermal bridge)

    To complicate things, neighbours on one side have a loft room (with a weathered joint between the two flat rooves). On that side, it's hard to say what conditions the last rafter will be exposed to.

    On the other side there is a dormer cheek with tiles, membrane, and OSB so the last rafter will be relatively cold and well ventilated.
    • CommentAuthorwookey
    • CommentTimeJun 22nd 2011
     
    Are the rafters hard up against gable walls at the ends? Often there is some space for foam in the gap so there is at least some insulation on the outside. A picture would help...
  13.  
    Posted By: Viking HouseYes, you're correct Spoon, I misread your question, here's the detail we used.
      http:///forum114/extensions/InlineImages/image.php?AttachmentID=2017" alt="Ext Ins TF Roof.jpg" >



    are you tempted to add an airtight layer above the EPS? tape the joints between the sheets / another barrier?
    • CommentAuthorTimber
    • CommentTimeJun 23rd 2011
     
    Some of you lot really need to brush up on your definitions of warm and cold roofs!

    If the roof is being clad with standing seam metal system you have the following options.

    Warm roof:
    Standing seem metal roof
    Hairy chest wing membrane
    rigid insulation materail to whatever thickness also incorporating a carrier system for the roofing
    Vapour control layer
    Sarking board (optional)
    Rafters
    Plasterboard.

    The gaps where the rafters bear onto the wall should be filled with a rigid foil faced insulation board to link the roof and wall insulatino together. All gaps should be foamed, masticed and taped.


    Colf roof:
    Standing seem metal roof
    Carrier system forming a ventillation void of 50 mm. This could be timber, metal or whatever
    breathable roof membrane
    INsulation above rafters if required (should be breathable)
    Insulation between rafters (could be breathable or non breathable)
    Insulation below rafters if required (idealy non breathable)
    vapour control layer
    plasterboard.

    Hope that helps in some way.
    • CommentAuthorBSteven
    • CommentTimeAug 7th 2011
     
    Based on the above definitions, anything with a cavity between the insulation layer and the outer skin would not be classed as a warm roof?

    We are planning a new warm roof (I think/hope) for our renovation in New Zealand as follows:
    1:20 fall
    metal tray roofing (Dimondek 400 tray, width 200mm, 45mm high rib, sheets clip together -2 trays/sheet)
    roof batten
    counter batten (structurally fixed to rafters)
    100mm celotex with taped joints (2x50mm, offset joints, NZ distributor only imports 50mm sheets)
    15mm ply sheathing (bracing plus support for celotex)
    exposed rafters @ 1200 spacing

    We are planing to build "clip on" eaves, so the wall and roof insulation (both celotex) will be able to be sealed together at the roof/wall junction with no penetrations through the insul boards (except for fixings)

    Does this qualify as a warm roof?
    • CommentAuthorMike George
    • CommentTimeAug 7th 2011 edited
     
    Yes.

    A warm roof is simply a roof with ALL of the insulation outboard of the STRUCTURAL element. [In your case, the rafters]. There can be many variations to Timber's example above, including the inclusion or omission of vapour control layers/barriers and breather membranes. The choosing of these dependent upon the other materials physical properties. Not least their vapour permeability.

    The definition however is based upon the location of the Insulation within the roof make up.
    • CommentAuthorShevek
    • CommentTimeJan 26th 2012 edited
     
    Super impressed with your details Seamus. With the flat roof detail below do you slope the whole structure/ceiling to form any fall required? And what do you do if you need to connect solar thermal or PV panels on top of this construction? Any recommendations on membrane material?
    Posted By: Viking HouseThis is our flat roof solution! The roof is airtightened from the outside using silicone between the rafter and the Ply.
      Flat Warm Roof Block.jpg
    • CommentAuthortony
    • CommentTimeJan 27th 2012
     
    no need to silicone or seal over nail heads, with a poly layer you wont need to silicone the joins in the osb.

    like the idea of additional insulation inboard.

    could you use thick poly under the osb? then it would be visible on the inside and repairable.
    • CommentAuthorborpin
    • CommentTimeJan 27th 2012
     
    Posted By: Mike GeorgeA warm roof is simply a roof with ALL of the insulation outboard of the STRUCTURAL element. [In your case, the rafters]. There can be many variations to Timber's example above, including the inclusion or omission of vapour control layers/barriers and breather membranes. The choosing of these dependent upon the other materials physical properties. Not least their vapour permeability.
    So what do you call a roof with some insulation outboard of the rafters and sarking and some inside the rafters sarking?
    • CommentAuthorborpin
    • CommentTimeJan 27th 2012 edited
     
    http://www.kingspaninsulation.co.uk/Products/Kooltherm/Kooltherm-K7-Pitched-Roof-Board/Overview.aspx page 5 of the PDF shows 18mm sarking but would this work with OSB?
  14.  
    Posted By: borpinSo what do you call a roof with some insulation outboard of the rafters and sarking and some inside the rafters sarking?
    This is what some call a hybrid warm roof.

    Although Mike's definition is the text book one, an area for potential misunderstanding is with the way the roof is ventilated. A roofer will often refer to any pitched roof where the ventilation goes below the sarking membrane/board as a cold roof & any pitched roof where the ventilation goes above the sarking membrane/board as a warm roof.

    So I've taken to calling my chosen build-up "a hybrid warm roof with ventilation to batten cavity".

    Tiles;
    Tile battens;
    Counter battens (ventilation to eaves & ridge);
    Breather membrane (taped);
    22mm T&G woodfibre sarking board;
    400mm mineral wool between I beam rafters;
    18mm T&G OSB3;
    Vapour control layer (taped);
    Plasterboard.

    Posted By: borpinpage 5 of the PDF shows 18mm sarking but would this work with OSB?
    This looks like the standard Scottish way of laying slates where the norm is to leave 3mm gaps between square edge sarking boards. Large sheet sarking materials are normally specifically excluded from the BBA certificates of breathable membranes which allow this approach.

    Even with cut timber you may have issues with a building control officer in England/Wales. So if you need the OSB for structural strength then either place it below the rafters (where it will be kept warm) or put breather membrane & counter battens on top to form a ventilated drainage space between slates & breather membrane/OSB.

    David
    • CommentAuthorborpin
    • CommentTimeJan 27th 2012 edited
     
    Posted By: davidfreeboroughThis looks like the standard Scottish way of laying slates where the norm is to leave 3mm gaps between square edge sarking boards. Large sheet sarking materials are normally specifically excluded from the BBA certificates of breathable membranes which allow this approach.
    Any reason for this exclusion? Breathability of the Wood? How good could you make the outer insulation layer air tight? Perhaps glue the 2 layers of insulation together or glue the outer layer to the rafters and glue or tape the joints? I'm sure it would end up pretty air tight.
    • CommentAuthorpmagowan
    • CommentTimeJan 27th 2012
     
    What about squirty foaming them together?
    • CommentAuthorborpin
    • CommentTimeJan 27th 2012
     
    Posted By: pmagowanWhat about squirty foaming them together?
    I have a thing in me that thinks a glue would be better. I am not convinced that you can get a good airtight seal in a but joint that is being effectively pushed apart. Not sure what glue would work though!
    • CommentAuthorpmagowan
    • CommentTimeJan 27th 2012
     
    Apparently there is a low expansion squirty foam. I think you need some expansion as a glue, IMO, would not fill the gaps enough. Glue tends to work when two surfaces come very tight together and I am not sure if insulation fits this description. This is only a guess, I will be gaining practical knowledge this spring (hopefully).
  15.  
    Posted By: borpinAny reason for this exclusion? Breathability of the Wood? How good could you make the outer insulation layer air tight? Perhaps glue the 2 layers of insulation together or glue the outer layer to the rafters and glue or tape the joints? I'm sure it would end up pretty air tight.
    I guess its to avoid water being trapped behind the sarking board. The existence proof of sarking boards with 3mm gaps being used in cold roofs in Scotland is probably what drives them to do something similar with (hybrid) warm roofs.

    If you don't need the OSB for structural reasons, I would use expanding foam to fit the insulation between the rafters to stop bulk air movement past the inner layer, seal the laps in the breather membrane with double sided butyl tape to form a wind barrier & fit counter battens as shown for the other detail on that page.