My agreed spec for the make up of the ground floor slab [ To a barn conversion] is as follows:- Mot type 1 Dpm 100mm conc 50mm cellotex Wet UFH 50-75mm screed Floor tiles
My question is :- Any advantage in increasing the 50mm cellotex to 100mm thick? Thanks.
Just wondering what the reason is for having the concrete layer? If you are going to insulate, ignoring Tony's comment for the moment on what is really required, why not replace the concrete and celotex with 150 eps?
Thanks for all your help, i have decided that Tony has the solution, which has been confirmed by 'Kingspan' tech dept. 50mm Kingspan/Cellotex with an increase around the perimeter [greatest heat loss] - 100mm. Thanks again.
Couple of points 1) I can never see why there is need for both vapour control on warm side and dpm on the cold side. All I have ever done is thick polythene on top as combined dpm/vapour control.
2) concrete and screed both react with aluminium so any spills seeps etc will naff the foil layer.
I agree with 1, but I follow their spec as I am not sure that PUR is totally impermiable. I have heard that it is not and the BBA spec seems to back this up.
<blockquote><cite>Posted By: Mike George</cite>It does not matter, either is acceptable, provided you follow their details [Detail sheet 2, figs 1&3]</blockquote>
Mike,
...well you learn something new every day, to be honest the last time I asked them it was on a commercial project w/ 5kn/m2 live floor load, perhaps it was that that scared them off.
So under slab to provide more thermal mass (I assume) but EPS or PU...?
A matter of choice dependent [for me] on the need for building up height to finish floor level.You need less PUR but EPS is nicer to use. Details here: http://www.bbacerts.co.uk/certs/17/1796i6_web.pdf
The main thing to remember with underfloor heating is that the temperature difference between inside and outside is much greater than with indoor air temperature. Secondly, you are dealing with liquids and solids, so heat transfer is greater than air-solid-air ( as in a wall. Although the earth below the slab is more or less constant in temperature in the centre, and is not very cold, the heating pipes will be between 40C and 60C depending on the systems, rather than 20C. Your heat will flow continuously into the ground without good levels of insulation. I would go towards Johan's 300mm of foamed glass.
I am at the start of removing the screed in my ground floor bathroom. Base is about 100mm thick, there is a thick polythene film then the screed about 80mm thick. The room is 3M square. one outside wall with window. As I am laying ceramic tiles on the new screed, I want to install an electric heating mat to take the chill off the floor. I realise I won't meet the latest standards for insulation, but will about 20mm of board make any real difference? I have installed pipes for a rad, and can fit one one if needed. There is also a 800watt towel rail in the system.
How about running some pipes in the screed -- a big loop in parallel with the rad and an adjusting valve near the rad? or just extend the radiator pipes under the floor for a bit.