		<title>Help with ASHP and a 5 year nightmare...</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=8095&amp;Focus=122281#Comment_122281</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=8095&amp;Focus=122281#Comment_122281</guid>
		<pubDate>Tue, 08 Nov 2011 21:42:41 +0000</pubDate>
		<author>daysleeper</author>
		<description>
			<![CDATA[In 2006 we imported, from Denmark, a Trelleborg "Zero-Energy" House and built it in Devon.  It's a timber frame timber clad structure of about 220 m^2.   8m wide by 14 long ish. with the narrow aspect south (thanks planners). Mainly open plan internally downstairs.  4 Bedrooms, 2 bathrooms and a small en-suite lived in by 2 adults, 3 children and a dog.<br /><br />The house is well insulated, it has 300mm rockwool fibre batts wall insulation. Below the concrete screed is 75mm polystyrene, between the concrete and the timber floor is another 150mm polystyrene.  The internal walls and floor voids are filled with rockwool insuation.  The room in roof design has insulation of about 200mm ish and then the loft has 300- 450 mm. <br /><br />The windows are "Rationel" timber framed double glazed units.  There are no trickle vents and the house has a MHRV system. This uses about 0.06 kw/hr (60 watts or so) continuously.  <br /><br />The air tightness is not great, with the odd small gap around french doors and windows. <br /><br />The space heating is provided by an Genvex 0.8kw Exhaust Air Heat Pump, integrated with the MHRV.  This extracts from the kitchen area, utility, 1 x downstairs and 2 x upstairs bathrooms.  The heat pump then adds extra heat and "warm" air is put into 3 x vents in the lounge, 5 x in  bedrooms and 1 on the upstairs landing.  There is an additional 1KW electric duct boost heater that I don't use (long story)<br /><br />A 5kw "Scan" woodburner is in the lounge.  The chimney goes through the master bedroom as another heat source. That is an awesome bit of kit.<br /><br />Each upstairs bathroom has electric underfloor heating timed to provide about 30 mins in the morning and about 45 mins in the evening to take the chill off the tiles. (total of 2.0 Kw) <br /><br />Water heating is provided by a "Vanvex", this is an air to water heat exchanger of about 0.8kw integrated with a 185 L water tank.  It heats to 50c and once a week puts the tank temp to 60c to "disinfect".  There is a 1kw immersion heater installed as backup.  <br /><br />The problems:<br /><br />We have a huge condensation problem. Every bedroom has condensation for 4 or 5 cm up the bottom window pane on any cold night, say 7c or less.  If we turn the Genvex down to slow fan speed at night (as recommended for heat efficiency) then every window in the house is wet) so it stays on high (and noisy) speed <br /><br />The water heating system seems to take for ever (well it's only a small HP).  This leads to the strange situation on very cold winter days of the water tank taking 20 hours to recover from 20 to 50c... There is a 1kw immersion heater but then that kind of defeats the objective.  Strangely both the vanvex and genvex are located with the air ducting  coming in through one side of the house and out through the other.  This  ductwork runs though the joist void between ground and first floor.  So last winter it was sucking in large quantites of -10 air, and putting out similar amounts of  -17 air.  (cold bridge anyone?) <br /><br />The Genvex space heating system cannot generate sufficient volumes of warm air to produce an decent temperature in the house.  Although the HP can heat the outside air by about 30c, on cold days say zero or below, then the internal temp will be about 15c unless you stand next to the outlet duct at the end of the house the pump is at.  The temperature drop along the ductwork is high, in the order of 5 c or more.  Some additional insulation work has reduced this but not by much.  <br /><br />The space heating would normally start about mid october, this year we've decided to leave it off as long as possible to save money...so far still no space heating. But the temps are down ... 4c outside gives 15c in the upstairs rooms and about 18c in the lounge. So heating will have to go on shortly. <br /><br />Add onto this the cost... we use a shade over 10,000 kw/h a year.  Some playing around with an Ecoeye reckons that about half is spent on the two heat pumps.  So each pump uses about 2,500 kw/h a year.  That means each pump is running for an average of about 3,000 hrs a year.  (probably less as there is a lot of defrost cycles!) <br /><br />So what should I be doing.  I read somewhere that a domestic heating system should be able to have bedroom temps of 18c and lounge temps of 20?  <br /><br />Is this salvageable or should we rip the stuff out and start again, seriously expensive but I'm fed up with the energy use and the cold! <img src="/newforum/extensions/Vanillacons/smilies/standard/cry.gif" alt=":cry:" title=":cry:" />  Add onto this the MHRV is quite noisy and as the children get older the house use has changed from where we could light the woodburner and all be in the lounge to where we tend to be in and out more, (scouts, swimming, school etc) so a more automated system would be better. <br /><br />Any thoughts...]]>
		</description>
	</item>
	<item>
		<title>Help with ASHP and a 5 year nightmare...</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=8095&amp;Focus=122285#Comment_122285</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=8095&amp;Focus=122285#Comment_122285</guid>
		<pubDate>Tue, 08 Nov 2011 21:52:39 +0000</pubDate>
		<author>Timber</author>
		<description>
			<![CDATA[How air leaky is the house? Getting an air permiability test might show up some serious air leakage that could be addressed and improve matters greatly.<br /><br />As for the tech side of things, I can't offer any useful comment other than the power outputs of the heat pumps seem low for the level of heating that may be required?]]>
		</description>
	</item>
	<item>
		<title>Help with ASHP and a 5 year nightmare...</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=8095&amp;Focus=122287#Comment_122287</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=8095&amp;Focus=122287#Comment_122287</guid>
		<pubDate>Tue, 08 Nov 2011 22:03:10 +0000</pubDate>
		<author>tony</author>
		<description>
			<![CDATA[U-values for walls and ceiling?  and duct sizes?]]>
		</description>
	</item>
	<item>
		<title>Help with ASHP and a 5 year nightmare...</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=8095&amp;Focus=122288#Comment_122288</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=8095&amp;Focus=122288#Comment_122288</guid>
		<pubDate>Tue, 08 Nov 2011 22:22:20 +0000</pubDate>
		<author>daysleeper</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: tony</cite>U-values for walls and ceiling?  and duct sizes?</blockquote>  Short answer is not sure and too small... long answer is I probably have that at home and will post on Thurs night/Friday as I'm away with work at the moment...<br /><br />Supply is 125mm stepping down to 100mm at the "far" end of the house.  Extract is 125 everywhere, or at least thats what the plans say!<br /><br />Ok found the U values online...walls claimed U= 0.13  Floor u= 0.09 Ceiling 0.09.  Windows seems high though at 1.33 (and we have a lot of windows!)]]>
		</description>
	</item>
	<item>
		<title>Help with ASHP and a 5 year nightmare...</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=8095&amp;Focus=122289#Comment_122289</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=8095&amp;Focus=122289#Comment_122289</guid>
		<pubDate>Tue, 08 Nov 2011 22:55:12 +0000</pubDate>
		<author>bot de paille</author>
		<description>
			<![CDATA[You dont need to rip everything out, the ASHP is undersized and can upgraded to something beefier. 0.8Kw seems small.<br /><br /> Is the house orientated and designed to make use of solar gain, lots of glazing on the south side, little on the north etc?]]>
		</description>
	</item>
	<item>
		<title>Help with ASHP and a 5 year nightmare...</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=8095&amp;Focus=122290#Comment_122290</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=8095&amp;Focus=122290#Comment_122290</guid>
		<pubDate>Tue, 08 Nov 2011 23:01:12 +0000</pubDate>
		<author>daysleeper</author>
		<description>
			<![CDATA[<blockquote ><br />Is the house orientated and designed to make use of solar gain, lots of glazing on the south side, little on the north etc?</blockquote><br /><br />Short answer is no, windows are evenly spaced round the house, on the south wall downstairs are two sets of double glass doors and upstairs two windows.  North face ground floor has two windows and one door and upstairs has two windows. East face has 2 large, 2 small windows and a door, west face has double door and 4 sets of windows.]]>
		</description>
	</item>
	<item>
		<title>Help with ASHP and a 5 year nightmare...</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=8095&amp;Focus=122291#Comment_122291</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=8095&amp;Focus=122291#Comment_122291</guid>
		<pubDate>Tue, 08 Nov 2011 23:14:31 +0000</pubDate>
		<author>tony</author>
		<description>
			<![CDATA[My house is heated entirely be solar gains, incidental losses, light bulbs, people, thermal storage, I have better windows than you and am very air tight (less than one)<br /><br />I was told that my MHRV would never be capable of transporting enough heat around the house and my ducts start at 200mm then 150 and 125 but it does, utilising a smaller heat pump 300W down to -3C when temp falls to 18C indoors by -6C<br /><br />I reckon that you should do an airtightness test and rectifications as a first point of call<br /><br />what are your fan speeds and energy use figures?]]>
		</description>
	</item>
	<item>
		<title>Help with ASHP and a 5 year nightmare...</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=8095&amp;Focus=122294#Comment_122294</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=8095&amp;Focus=122294#Comment_122294</guid>
		<pubDate>Tue, 08 Nov 2011 23:53:11 +0000</pubDate>
		<author>RobinB</author>
		<description>
			<![CDATA[Agree with Tony, worth doing an airtightness test, make sure they'll give you time to go around identifying which areas are leaking. You have quite a lot of doors by the sound of it and the long thin shape means a high surface to area ratio. So quite a lot of possibel leaky spots.<br /><br />Is the MVHR blocked at all?  Waft a thin plasic bag or cling film nearby and check they suck or blow as appropriate. We tend to put ours on the slow speed at night and have only a little condesation onthe double glazing (none on the 3G) when it's below freezing outside.  And with the low indoor temperatures you're suffering there should be even less condensation.<br /><br />From experience I'd suggest adding a  solar thermal panel would really help the heat pump out for the hot water, providing all the hot water on a sunny day and usefully pre-heating it most days.<br /><br />Again I wouldn't throw any of the kit out it does sound a bit wimpy but I'm sure you can add to it rather than starting again.<br /><br />I hope you get things sorted out soon.<br /><br />RobinB]]>
		</description>
	</item>
	<item>
		<title>Help with ASHP and a 5 year nightmare...</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=8095&amp;Focus=122295#Comment_122295</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=8095&amp;Focus=122295#Comment_122295</guid>
		<pubDate>Wed, 09 Nov 2011 00:22:54 +0000</pubDate>
		<author>CWatters</author>
		<description>
			<![CDATA[<blockquote >Water heating is provided by a "Vanvex", this is an air to water heat exchanger of about 0.8kw integrated with a 185 L water tank.<br />snip<br />This leads to the strange situation on very cold winter days of the water tank taking 20 hours to recover from 20 to 50c</blockquote><br /><br />Someone check my figures but...<br /><br />(185 x 30 x 4186) / 20 x 60 x 60 = 322 watts<br /><br />from an 800W heat pump isn't a great COP. Perhaps worth doing a more accurate test?]]>
		</description>
	</item>
	<item>
		<title>Help with ASHP and a 5 year nightmare...</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=8095&amp;Focus=122296#Comment_122296</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=8095&amp;Focus=122296#Comment_122296</guid>
		<pubDate>Wed, 09 Nov 2011 07:13:37 +0000</pubDate>
		<author>davidfreeborough</author>
		<description>
			<![CDATA[I guess you're using the Vanvex 185S. <br /><br />Which Genvex model are you using? Do you know what flow rate you need or the volume of your house?<br /><br />David]]>
		</description>
	</item>
	<item>
		<title>Help with ASHP and a 5 year nightmare...</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=8095&amp;Focus=122298#Comment_122298</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=8095&amp;Focus=122298#Comment_122298</guid>
		<pubDate>Wed, 09 Nov 2011 07:35:13 +0000</pubDate>
		<author>daysleeper</author>
		<description>
			<![CDATA[Sorry correcting last nights fatigue error, it's a Vanvex 285 V TT for the water.]]>
		</description>
	</item>
	<item>
		<title>Help with ASHP and a 5 year nightmare...</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=8095&amp;Focus=122300#Comment_122300</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=8095&amp;Focus=122300#Comment_122300</guid>
		<pubDate>Wed, 09 Nov 2011 07:56:16 +0000</pubDate>
		<author>CWatters</author>
		<description>
			<![CDATA[The brochure puts some emphasis on achieving the correct air flow rates even mixing external air into the exhaust air if that's necessary. As you have the MHRV turned down for noise reasons perhaps worth checking if it's getting enough?<br /><br /><a href="http://www.icsheatpumps.co.uk/docs/ICS_Thermacell_Data_Sheet.pdf" target="_self" rel="nofollow">http://www.icsheatpumps.co.uk/docs/ICS_Thermacell_Data_Sheet.pdf</a>]]>
		</description>
	</item>
	<item>
		<title>Help with ASHP and a 5 year nightmare...</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=8095&amp;Focus=122301#Comment_122301</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=8095&amp;Focus=122301#Comment_122301</guid>
		<pubDate>Wed, 09 Nov 2011 08:01:20 +0000</pubDate>
		<author>CWatters</author>
		<description>
			<![CDATA[Thought I recognised this topic.. <br /><br /><a href="http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=6545" target="_self" rel="nofollow">http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=6545</a>]]>
		</description>
	</item>
	<item>
		<title>Help with ASHP and a 5 year nightmare...</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=8095&amp;Focus=122305#Comment_122305</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=8095&amp;Focus=122305#Comment_122305</guid>
		<pubDate>Wed, 09 Nov 2011 08:29:55 +0000</pubDate>
		<author>davidfreeborough</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: daysleeper</cite>Strangely both the vanvex and genvex are located with the air ducting coming in through one side of the house and out through the other. This ductwork runs though the joist void between ground and first floor. So last winter it was sucking in large quantites of -10 air, and putting out similar amounts of -17 air. (cold bridge anyone?)</blockquote>Am I right to assume from the above that the Vanvex & Genvex units are independently connected to the outside air?<br /><br />I see from the other thread that the MVHR is a Genvex GE215VP TT with an OPT300 controller.<br /><br />Do you know what the air flow rate is through the MVHR &/or the house volume?<br /><br />David]]>
		</description>
	</item>
	<item>
		<title>Help with ASHP and a 5 year nightmare...</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=8095&amp;Focus=122309#Comment_122309</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=8095&amp;Focus=122309#Comment_122309</guid>
		<pubDate>Wed, 09 Nov 2011 08:47:03 +0000</pubDate>
		<author>daysleeper</author>
		<description>
			<![CDATA[Well thatâ€™s embarrassing, Iâ€™d completely forgotten about that thread when I sat down in a grump last night to write this one.  I knew I'd got involved in a discussion about it on the web before but for some reason thought it was elsewhere...I guess I only get fed up in winterâ€¦sorry! <img src="/newforum/extensions/Vanillacons/smilies/standard/shamed.gif" alt=":shamed:" title=":shamed:" /><br /><br />Both systems are independently ducted to the outside world.  If I can get digitise the plans slightly Iâ€™ll post them. <br /><br />The system is the Genvex 215l vp-tt running a 520w compressor with 2 fans of 60w eachâ€¦ The vanvex is the 285 l version with the 585w compressor.  I know weâ€™ve seen some of this before now!  I donâ€™t know the volume of airflow house volume I have at home (still in the office)  There is a distinct possibility the ducts have been under sized, the builders have pretty much admitted it as it seems a couple of houses built around the same time (in Denmark) have similar issues. Slip of a pen in the ventilation design office is suspected.  Since last winter weâ€™ve had a couple of bits of ceiling down to check and re-lag some of the ductwork. Doesnâ€™t seem to have made a huge difference. <br /><br />Weâ€™ve had the builder round with volume and flow measuring kit repeatedly to balance the system.]]>
		</description>
	</item>
	<item>
		<title>Help with ASHP and a 5 year nightmare...</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=8095&amp;Focus=122320#Comment_122320</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=8095&amp;Focus=122320#Comment_122320</guid>
		<pubDate>Wed, 09 Nov 2011 12:19:04 +0000</pubDate>
		<author>davidfreeborough</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: CWatters</cite>Someone check my figures but...<br /><br />(185 x 30 x 4186) / 20 x 60 x 60 = 322 watts</blockquote>It seems the tank is 285 litres. According to my spreadsheet, heating 285 litres from 20oC to 50oC takes 11.5kWh. With 1.365kW available from the heat pump, this should take around 8.4 hours. Its likely the cold water supply temperature is lower than 20oC, but even at 2oC it would "only" take 12.8 hours.<br /><br />Perhaps the additional time is due to the heat pump capacity dropping with outside air temperature?<br /><br />David]]>
		</description>
	</item>
	<item>
		<title>Help with ASHP and a 5 year nightmare...</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=8095&amp;Focus=122323#Comment_122323</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=8095&amp;Focus=122323#Comment_122323</guid>
		<pubDate>Wed, 09 Nov 2011 13:23:42 +0000</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: daysleeper</cite>Well thatâ€™s embarrassing, Iâ€™d completely forgotten about that thread when I sat down in a grump last night to write this one.</blockquote><br />Hmm, so has anything changed since then?<br /><br />It seems to me that in the absence of progress towards a solution, you need to have an expert come and look at the house and its systems. Some of the engineering types in the AECB might be a good place to start looking for one. Check what the specification of everything is supposed to be, why its not working properly (design error, build error, operation error etc), and make a plan to fix it. The plan may include a solicitor, and since the sale of goods rules mention six years somewhere, IIRC, I think you should do it promptly!]]>
		</description>
	</item>
	<item>
		<title>Help with ASHP and a 5 year nightmare...</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=8095&amp;Focus=122331#Comment_122331</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=8095&amp;Focus=122331#Comment_122331</guid>
		<pubDate>Wed, 09 Nov 2011 13:49:15 +0000</pubDate>
		<author>CWatters</author>
		<description>
			<![CDATA[One possibility would be to run two experiments..<br /><br />Drain the HW and see how long it takes to reheat the tank with the MHRV on low. Then repeat the experiment with the MHRV on high/noisy flow rate. Check the exhaust really is faster and see what sort of difference that makes to the recharge time. If it makes no or very little difference then perhaps the MHRV flow rate isn't the issue?<br /><br />PS: On other forums I've come across people that have problems with their heating system (all types) and it's sometimes hard to get them to think through the problem methodically. You suggest changing one thing to see what effect it has and they change 10 things, raise a totally different problem or are unwilling to invest in basic equipment like a Â£10 digital thermometer. I'm not saying you are like this but if you recognise that behaviour in your self ... move house :-)]]>
		</description>
	</item>
	<item>
		<title>Help with ASHP and a 5 year nightmare...</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=8095&amp;Focus=122334#Comment_122334</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=8095&amp;Focus=122334#Comment_122334</guid>
		<pubDate>Wed, 09 Nov 2011 13:58:50 +0000</pubDate>
		<author>davidfreeborough</author>
		<description>
			<![CDATA[daysleeper has already said that the two systems are independently ducted to the outside world, so I don't think the DHW recovery time issue is related to the MVHR. I just want to work out whether the MVHR flow rate is set sufficiently high to manage humidity levels & carry all the available ASHP energy into the house.<br /><br />David]]>
		</description>
	</item>
	<item>
		<title>Help with ASHP and a 5 year nightmare...</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=8095&amp;Focus=122335#Comment_122335</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=8095&amp;Focus=122335#Comment_122335</guid>
		<pubDate>Wed, 09 Nov 2011 14:09:54 +0000</pubDate>
		<author>CWatters</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: davidfreeborough</cite>daysleeper has already said that the two systems are independently ducted to the outside world, so I don't think the DHW recovery time issue is related to the MVHR. I just want to work out whether the MVHR flow rate is set sufficiently high to manage humidity levels & carry all the available ASHP energy into the house.<br /><br />David</blockquote><br /><br />I agree that needs to be checked.]]>
		</description>
	</item>
	<item>
		<title>Help with ASHP and a 5 year nightmare...</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=8095&amp;Focus=122371#Comment_122371</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=8095&amp;Focus=122371#Comment_122371</guid>
		<pubDate>Wed, 09 Nov 2011 21:35:03 +0000</pubDate>
		<author>daysleeper</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: davidfreeborough</cite>daysleeper has already said that the two systems are independently ducted to the outside world, so I don't think the DHW recovery time issue is related to the MVHR. <br />David </blockquote><br /><br />The DHW is a completely separate system there is no connection between MHRV and DHW. <br /><br /><blockquote >I just want to work out whether the MVHR flow rate is set sufficiently high to manage humidity levels &amp; carry all the available ASHP energy into the house.</blockquote><br /><br />The short answer is no it's not, sort of.  The fans run at 75% normally but there seems to be little difference at 100% though going down to 25% results in condensation everywhere including unoccupied rooms. <br /> The builder's already accepted that the system can't push/pull enough air through the house to match the spec. Though they are unsure if that is the reason for the condensation.  They &quot;think&quot; the volume problem is because of undersized ducting, though in addition the house is right at the top of the volume range for the machine.  The question is what's to be done about it.  We'd rather not rip all the walls apart to get at the ducting and running the fans on high at night means the noise in the downstairs bedroom is unacceptably high.   <br /><br /><blockquote >Hmm, so has anything changed since then?</blockquote><br /><br />Yes, the acceptance from the builders side that there is a fundamental problem and a few more holes in my ceiling where ducting junctions have been inspected and re-lagged.]]>
		</description>
	</item>
	<item>
		<title>Help with ASHP and a 5 year nightmare...</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=8095&amp;Focus=122403#Comment_122403</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=8095&amp;Focus=122403#Comment_122403</guid>
		<pubDate>Thu, 10 Nov 2011 10:42:18 +0000</pubDate>
		<author>davidfreeborough</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: daysleeper</cite>The builder's already accepted that the system can't push/pull enough air through the house to match the spec. Though they are unsure if that is the reason for the condensation. They "think" the volume problem is because of undersized ducting, though in addition the house is right at the top of the volume range for the machine. The question is what's to be done about it. We'd rather not rip all the walls apart to get at the ducting and running the fans on high at night means the noise in the downstairs bedroom is unacceptably high.</blockquote>How bad is the condensation? Is it running down the windows onto the window sill? Does is evaporate on its own in the morning or does it need to be wiped away? If it's pooling on the window sill then I would say you need to do something about it.<br /><br />Can you reduce the amount of water vapour being released in the house? Do you cook on gas? Would you consider moving to a halogen or induction hob? Do you dry washing in the house? Could you put washing outside until it is almost dry & then bring it inside to remove the last few percent of water? <br /><br />If you've done everything you can to reduce water vapour being released in the house then you need to check that the condensation isn't due to cold spots. Do you notice significant variations in temperature around the house? Does the condensation collect in areas which are colder than others? Can anything be done to increase the temperature in these areas?<br /><br />Once you've been through these options then you're left with increasing the ventilation rate &/or the distribution of heat coming from the MVHR unit. Has the MVHR unit been properly commissioned, i.e. has the flow been checked & adjusted at each extract/inlet vent? Is the temperature drop along the ducting within specification? Are all of the ducts lagged with at least 50mm mineral wool? Is the pressure drop along the ducting within specification? Is all of the ducting low loss rigid ducting, or do you have some flexible ducting?<br /><br />If you can get answers to these questions then you can decide whether to reject the MVHR unit as not performing to specification &/or reject the builders installation as not fit for purpose.<br /><br />David]]>
		</description>
	</item>
	<item>
		<title>Help with ASHP and a 5 year nightmare...</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=8095&amp;Focus=122475#Comment_122475</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=8095&amp;Focus=122475#Comment_122475</guid>
		<pubDate>Thu, 10 Nov 2011 20:14:09 +0000</pubDate>
		<author>daysleeper</author>
		<description>
			<![CDATA[<blockquote >How bad is the condensation? Is it running down the windows onto the window sill? Does is evaporate on its own in the morning or does it need to be wiped away? If it's pooling on the window sill then I would say you need to do something about it.</blockquote><br /><br />Bad, see photo from last winter. <br /><br /><blockquote >Can you reduce the amount of water vapour being released in the house? Do you cook on gas? Would you consider moving to a halogen or induction hob? Do you dry washing in the house? Could you put washing outside until it is almost dry & then bring it inside to remove the last few percent of water?</blockquote><br /><br />We are fully electric so cook on Induction.  There is a washing machine and condensing tumble dryer. <br /><br /><blockquote >If you've done everything you can to reduce water vapour being released in the house then you need to check that the condensation isn't due to cold spots. Do you notice significant variations in temperature around the house? Does the condensation collect in areas which are colder than others? Can anything be done to increase the temperature in these areas?</blockquote><br /><br />Temperature variation around the house is a problem, but particularly the bedrooms where we suffer the worst condensation are the coldest rooms.<br /><br /><blockquote >Once you've been through these options then you're left with increasing the ventilation rate &/or the distribution of heat coming from the MVHR unit. Has the MVHR unit been properly commissioned, i.e. has the flow been checked & adjusted at each extract/inlet vent? </blockquote><br /><br /> The installer has been round and round and round rebalancing and setting up. <br /><br /><blockquote >Is the temperature drop along the ducting within specification? Are all of the ducts lagged with at least 50mm mineral wool? Is the pressure drop along the ducting within specification? Is all of the ducting low loss rigid ducting, or do you have some flexible ducting?</blockquote><br />Temp drop has been out of spec, thus the extra work re-lagging.  Pressure drop seems ok but the overall pressure is low, all the ducts are rigid and sit in insulation, but how thick that is I'm not sure. <br /><br /><blockquote >If you can get answers to these questions then you can decide whether to reject the MVHR unit as not performing to specification &/or reject the builders installation as not fit for purpose.<br /><br />David</blockquote><br /><br />Well new fans and software coming next week.  Not convinced and I suspect neither is the UK rep.]]>
		</description>
	</item>
	<item>
		<title>Help with ASHP and a 5 year nightmare...</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=8095&amp;Focus=122479#Comment_122479</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=8095&amp;Focus=122479#Comment_122479</guid>
		<pubDate>Thu, 10 Nov 2011 20:27:43 +0000</pubDate>
		<author>Paul in Montreal</author>
		<description>
			<![CDATA[Just to jump in here late. The insulation specs you have sound similar to Tony's house (and the overall area is about the same). I did heatload calculations for him and they came in at 4.3kW with 21C inside and -3C outside. You say your heatpump is 0.8kW - is that output power or input power? If that's output power that's way way too small for your house, even though it is well insulated. Once you take incidental gains into account, you'll still be in the 3kW ballpark for a delta-T of 24C - with half that delta-T (which is where it seems you are now) - you would still need 1.5kW. If 0.8kW is the input power of your heatpump, I doubt the output power would be much above 1.4kW on average - so still too low. Your internal temperature figures suggest this is the case.<br /><br />Since your internal temperatures are so low, it's no wonder there is condensation as the surface temperatures of your windows have no chance of being above the dew point - no matter how good your ventilation is - at 7C outside the RH is probably close to 100% anyway in the UK and with all the occupants I'd bet the dewpoint temperature is 12-14C. You need to increase your internal temperature to at least 20C I'd say - then you might be OK. HRV systems are not really designed to moved heat around as the duct work is too small to do so effectively without noise. I have a GSHP with air delivery and the main trunk is 600mmx300mm!<br /><br />I suspect that such a house as yours works OK in a cold climate with the wood burner in use as the outside air in such climates is way drier than in the UK.<br /><br />Paul in Montreal.]]>
		</description>
	</item>
	<item>
		<title>Help with ASHP and a 5 year nightmare...</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=8095&amp;Focus=122482#Comment_122482</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=8095&amp;Focus=122482#Comment_122482</guid>
		<pubDate>Thu, 10 Nov 2011 20:45:53 +0000</pubDate>
		<author>daysleeper</author>
		<description>
			<![CDATA[Thanks Paul,<br /><br />It's worse than that,  the ASHP input is only 520w !]]>
		</description>
	</item>
	<item>
		<title>Help with ASHP and a 5 year nightmare...</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=8095&amp;Focus=122483#Comment_122483</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=8095&amp;Focus=122483#Comment_122483</guid>
		<pubDate>Thu, 10 Nov 2011 20:52:37 +0000</pubDate>
		<author>Paul in Montreal</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: daysleeper</cite>It's worse than that,  the ASHP input is only 520w !</blockquote> The output could be around 1kW then - which sounds about right given your internal temperatures and my guesstimate of the actual heatloss of your house. I suspect if you can raise the internal temperature of your main living area to 20-21C, you'll probably end up with bedrooms that are warm enough that the condensation level will be significantly reduced. How much do you use the woodburner?<br /><br />Paul in Montreal.]]>
		</description>
	</item>
	<item>
		<title>Help with ASHP and a 5 year nightmare...</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=8095&amp;Focus=122485#Comment_122485</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=8095&amp;Focus=122485#Comment_122485</guid>
		<pubDate>Thu, 10 Nov 2011 20:58:57 +0000</pubDate>
		<author>daysleeper</author>
		<description>
			<![CDATA[If we use the woodburner in anything other than arctic conditions then the lounge rapidly goes from conditions needing 2 overcoats to wearing shorts.   Seriously the woodburner punches the temperature in the lounge up to about 25c very quickly even in cold weather, problem is that heat does not travel.  The nearest intake point for the MHRV is about 7 meters away and with all the internal walls insulated there isn't much appreciable difference.  The bedroom above gains a few degrees from the internal chimney.  <br /><br />We used to use the woodburner more, like fire it up in the morning and keep it going for a few hours then again at sunset till bedtime. However, as the children have started school, and we are in and out more it has become only a weekend late afternoon/evening thing.]]>
		</description>
	</item>
	<item>
		<title>Help with ASHP and a 5 year nightmare...</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=8095&amp;Focus=122486#Comment_122486</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=8095&amp;Focus=122486#Comment_122486</guid>
		<pubDate>Thu, 10 Nov 2011 21:05:15 +0000</pubDate>
		<author>Paul in Montreal</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: daysleeper</cite>If we use the woodburner in anything other than arctic conditions then the lounge rapidly goes from conditions needing 2 overcoats to wearing shorts.   Seriously the woodburner punches the temperature in the lounge up to about 25c very quickly even in cold weather, problem is that heat does not travel.</blockquote><br /><br />I have a suggestion which you can take with a pinch of salt but it might be worth a try. Fire up the woodburner a few times until the temperatures upstairs are high enough that the condensation is reduced. This may take a few days of wearing shorts downstairs. The idea is to get all the internal surface temperatures up. Then you may find that just running the wood burner once in a while is sufficient (if you do it at the right time of day ... or somehow use slower burning wood) to keep things comfortable.<br /><br />We have a woodburner in one house that also has GSHP/forced air. Even with the much larger ducts it's difficult to distribute the heat throughout the house (as the delta-T on the air is too low for the volume moved). <br /><br />When you previously used your woodburner more, did you find lower condensation levels. Also, does the woodburner have a dedicated (external) airsupply or does it burn air from within the house? <br /><br />Paul in Montreal.]]>
		</description>
	</item>
	<item>
		<title>Help with ASHP and a 5 year nightmare...</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=8095&amp;Focus=122487#Comment_122487</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=8095&amp;Focus=122487#Comment_122487</guid>
		<pubDate>Thu, 10 Nov 2011 21:18:47 +0000</pubDate>
		<author>roserambler</author>
		<description>
			<![CDATA[If a simply solution is what you are looking for, try reducing the load on the heating system.  Your woodburner seems to have more KWs output than needed, have you thought about a back boiler on the woodburner (and / or another woodburner) and link in a few rads to it to one side of the house.  That means you could focus the heat output to a smaller area, thus more efficent, less noise and more heat.<br /><br />Only a thought.<br /><br />I would say also, 10,000kw per annum for a 220 sq m house - is that just space heating, space heating and water heating or all energy.<br /><br />Most normal houses usually need to throw 15,000 - 20,000kw for energy costs to a family home<br /><br />RR]]>
		</description>
	</item>
	<item>
		<title>Help with ASHP and a 5 year nightmare...</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=8095&amp;Focus=122488#Comment_122488</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=8095&amp;Focus=122488#Comment_122488</guid>
		<pubDate>Thu, 10 Nov 2011 21:28:02 +0000</pubDate>
		<author>daysleeper</author>
		<description>
			<![CDATA[The woodburner doesn't have an external air supply, I know I know, it really should (and has the fittings for one) but it sits on a swivel base and in an open plan room we can rotate it towards the dinner table or the seating area as required. The external air would fix it in place.  There wasn't a huge difference when we used it more regularly.]]>