Posted By: davidfreeboroughThe 6.6 m²K/W represents the nominal thermal resistance through the centre of the expanded polystyrene pods which provide the concrete formwork and the floor insulation. This is only a nonimal value because the pods form a waffle tray pattern which greatly reduces the insulation thickness in some areas.
The 0.11 W/m²K is the average U value across the whole floor.
Posted By: djhOK, but 1/6.6 = 0.15 W/m²K is then the nominal through the insulation, but that's worse than the average across the concrete as well. That's what I don't understand. How can the best insulated bit be worse than the average?Because this is the average U value across the floor area & large portions of the floor area don't see the outside air temperature. The ground below the house will tend towards room temperature at the centre of the slab & towards outside air temperature at the perimeter of the slab. So the effective U value of an area of floor towards the centre of the slab will be a lot better than 1/6.6, while an area of floor towards the perimeter of the slab will tend towards 1/6.6. That's one reason why I prefer cast in-situ slabs over pre-cast suspended floors which require through ventilation.
Posted By: Chris P BaconI don't like the look of that system at all. I'm told that, especially with UFH, a significant portion of the heat loss it out the edge of the slab and that system appears to have no insulation in that area.It seems they've tried to make it look familiar to UK builders, structural engineers & building control officers by making it look as much as possible like a conventional raft foundation, complete with all the usual thermal bridges!
The insulated raft I am using has a thermal break between the main slab and the ring beam and further vertical insulation outside of the ring beam and then 1.5 metres of wing insulation.