Home  5  Books  5  GBEzine  5  News  5  HelpDesk  5  Register  5  GreenBuilding.co.uk
Not signed in (Sign In)

Categories



Green Building Bible, Fourth Edition
Green Building Bible, fourth edition (both books)
These two books are the perfect starting place to help you get to grips with one of the most vitally important aspects of our society - our homes and living environment.

PLEASE NOTE: A download link for Volume 1 will be sent to you by email and Volume 2 will be sent to you by post as a book.

Buy individually or both books together. Delivery is free!


powered by Surfing Waves




Vanilla 1.0.3 is a product of Lussumo. More Information: Documentation, Community Support.

Welcome to new Forum Visitors
Join the forum now and benefit from discussions with thousands of other green building fans and discounts on Green Building Press publications: Apply now.

The AECB accepts no responsibility or liability for any errors or omissions in the content of this site. Views given in posts are not necessarily the views of the AECB.



    • CommentAuthorEd Davies
    • CommentTimeJun 24th 2012
     
    At severe risk of a hijack of another thread:

    http://www.greenbuildingforum.co.uk/forum114/comments.php?DiscussionID=9243

    Posted By: SteamyTeaNot convinced about water walls yet, the SHC is good, the price is good, but have a nagging doubt about something I just can't put my finger on at the moment.

    If you do put your finger on it do describe the experience here. I for one would be interested to hear of any likely problems with such set ups.

    In the same thread:
    Posted By: tonyI have seen people use oil drums full of water -- they are best at storing heat but I would be scares of them leaking

    I too like the idea of oil drums but have some doubts about their longevity. Any thoughts on using them with some sort of inhibitor in the water, anyone?
    • CommentAuthorSprocket
    • CommentTimeJun 24th 2012
     
    Contact with other metal things would worry me a bit - causing v.fast corrosion.
    As a farm we've got a lot of galvanized stuff around - I pretty much trust that but it's generally not full of water anwhere it can do serious harm.

    I have a general deep distrust of plumbing and plumbers though. We've had three too many house-scale burst/blown mains-pressure big-clean-up very-expensive-insurance-claim disasters to be happy with a load more water anywhere I can avoid it. I might trust a well engineered and guaranteed pro setup but there's no way I would trust me or anyone else with a load of water in oil drums inside the house.

    Thinking about it, I'm quite happy that our heat pump installs are all closed-loop.
    •  
      CommentAuthorJSHarris
    • CommentTimeJun 24th 2012
     
    Given that water has a specific heat that's only around 30% greater than dense concrete or stone, is it really worth it?
    • CommentAuthorEd Davies
    • CommentTimeJun 24th 2012
     
    Water's specific heat capacity (e.g., heat capacity per kg) is a lot higher than that of concrete or stone. I think JSH is thinking of the volumetric heat capacity (heat capacity per m³).

    E.g., water's specific heat capacity about 4.2 kJ/(kg·K), stone perhaps a bit over 1 kJ/(kg·K). Density of water 1 tonne/m³. Stone maybe 2.5 to 3 tonne/m³ so water's volumetric heat capacity could plausibly be 30% higher.

    The distinction is important if a fairly lightweight structure is what's wanted, e.g., when insulation under the heat store is required.
    •  
      CommentAuthorJSHarris
    • CommentTimeJun 24th 2012 edited
     
    You're right, Ed, I took the data from the Engineering Toolbox without noting that they had transposed the imperial/SI columns between the table for fluids and the table for solids. On the solids table the imperial units are the left column, on the fluids table the imperial units are the right column. Very annoying!

    Here are the links: http://www.engineeringtoolbox.com/specific-heat-solids-d_154.html and http://www.engineeringtoolbox.com/specific-heat-fluids-d_151.html
    • CommentAuthorCWatters
    • CommentTimeJun 24th 2012
     
    Is this a good idea? I'm not so sure...

    You can only store energy in water by raising it's temperature. So lets say it's a good spring and you've heated up the water by end of june... Would you want the walls hot through july, August and September?

    A sphere has the greatest volume to surface area ratio so that would be the best shape for a thermal store. If you put a thin flat tank in the walls you need insulation both sides? On the outside to stop heat loss in winter. On the inside to stop heat loss in summer?

    I can't see it has any advantages.
    •  
      CommentAuthorSteamyTea
    • CommentTimeJun 24th 2012 edited
     
    Right, my views:

    You want to get the interior of your house at a stable temperature, say 21°C
    One way to do this is to just heat/cool the air as it comes into the house. If it gets too hot or cold, you either change the flow rate or the size of the heater/cooler. Air has a SHC of 1 J.kg^-1.K^-1 (lets not get bogged down with varying humidity).

    Another way is to heat or cool some thermal mass. So to keep the air at 21°C, you have to heat the thermal mass to above that temperature, cool it to below that temperature when the air is too hot. The rate of transfer will be affected (or is it effected) by 3 properties of the thermal mass, its mass, the surface area that is in contact with the air to be heated and the thermal properties, this is nicely described by thermal inertia J·m−2·K−1·s−1/2.
    Plain old stone (granite) has a VHC of about 217 kJ.m^-1.K^-1, and a conductivity of about 2.8 W.m^-1.K^-1.
    So that will be about 780 J·m−2·K−1·s−1/2.
    Say the air that needs to be heated needs 10 kWh a day, that will be 3.6 MJ that needs to be transferred to/from the wall.
    Heat transfer is most effective when half the energy from the hotter has transferred to the colder. So let us say that there is a 6°C (HDD 15) temperature rise needed to keep the air at 21°, the wall will need to be 16°C above the internal air temperature, so 36°C (quite warm for a wall, but manageable and not so different from UFH).
    So to work out the mass of thermal mass needed we need to know the wall area and the lass of air to be heated.
    Lets say that there are 3 tonnes of air and the wall is 5 m long and 5 m high, 25 m^2, but transfers energy from both major surfaces (lets ignore edges to keep things simple), so 50 m^2.
    The wall has to be able to release at least 3.6 MJ so that the mean temperature of the air stays at 21°C.
    The wall starts releasing energy at 36°C and at a rate of 780 J·m−2·K−1·s−1/2.
    So for a wall of 50 m^2 that is 39 kJ·K−1·s−1/2
    When it gets to half way between 21°C and 36°C it must have delivered enough energy to have supplied the air with 3.6 MJ (or 10 kWh).
    So that is 39 kJ·K−1·s−1/2 x 7.5°C or 292.5 kJ.s^-1/2

    Now 3 tonnes of air need to be heated and that requires 3.6 MJ per day or 3.6 MJ per 86400 s (3.6 MJ.86400s^-1).
    3.6 MJ.86400s^-1 / 292.5 kJ.s^-1/2 =41.67
    As I had dropped the M^2 and kg units earlier but have specified that this to heat 3 tonnes of air, I have to put the units back in. So that is near enough 42 tonnes of granite.
    Granites has a density of about 2.8 tonnes per cubic metre, so that will be 15 m^3 of granite. 15 m^3 / 25 m^2 = 0.6 m
    So your granite wall be 5 m wide, 5 m high and 0.6 m thick to store enough energy to stabilise 3 tonnes of air in a house at 21°C when there is a 6°C temperature difference.

    To be honest I am not sure if this is right, though it does seem to make sense and granite walls are often about 2 foot thick down here. I may also have made heavy weather of the calculations, but that was mainly because I was working it out as I typed, it is probably easier to introduce the mass of air and the temperature difference right at the beginning, but that would assume that the equations/values for thermal inertia, volumetric heat capacity, thermal conductivity and density were known.
    More than willing to be put right on my maths/thinking though and shown a simpler way to calculate the heat transfers as I have not taken any airchanges into account, I just made the assumption that the air needs heating, not why it needs heating.
    But just out of interest to heat 42 tonnes of granite from 15°C to 36°C would take 370 MJ or 100 kWh.
    • CommentAuthortony
    • CommentTimeJun 25th 2012
     
    less incidental gains, people, solar gains,
    in my house it already works so it can work
    • CommentAuthorskyewright
    • CommentTimeJun 25th 2012 edited
     
    Posted By: SteamyTeaAnother way is to heat or cool some thermal mass....I just made the assumption that the air needs heating, not why it needs heating.

    All interesting, but (& I may well be missing the point) isn't it more the idea that provided the only effective thermal interface is with the house interior (i.e. no losses from the mass directly to the outside) the mass simply(!) absorbs & releases heat whenever its temperature is below or above the temp of the house air. The greater the mass, the greater the inertia in the system and so, as tony said in
    http://www.greenbuildingforum.co.uk/forum114/comments.php?DiscussionID=9243
    Posted By: tonyThe more the merrier and the longer and better it will work so long as it is inside the thermal envelope.

    With the properties of the thermal mass affecting how swiftly the mass exchanges heat with the interior at any given temp difference.

    Once an initial equilibrium[1] has been reached does the presence of the mass add anything at all to the energy input required by the house?


    [1] During which phase the mass will be being 'actively' heated (or in a hot climate, cooled) by whatever is being used to maintain the indoor air temp, of course.
    •  
      CommentAuthorSteamyTea
    • CommentTimeJun 25th 2012 edited
     
    Posted By: skyewrightabsorbs & releases heat whenever its temperature is below or above the temp of the house air

    Maybe, almost, not quite, I think.

    Thermal inertia is the volumetric heat capacity divided by the conductivity. So the shape of the thermal mass is important as well as the mass.

    The way I imagine it is that as a wall is warming, some heat from the room travels further and faster into the wall than other heat. That will be the higher temperature heat. As it travels into the wall it looses 'speed' because of the resistance, caused the wall storing that heat. Overall the same amount of energy is stored but the higher the temperature difference the faster it can store a larger proportion of that heat (from the room).
    When it comes to the wall releasing that heat back into the room, what was the higher temperature heat (the excess) is now buried deeper in the wall, but at a lower temperature than what is nearer the surface (even though that more recent heat may have come from a lower temperature difference).
    As heat can only travel from hotter to colder, what was older excess heat in the room, but is now stored deeper in the wall, and at a lower temperature than the wall surface, it has to wait until the surface of the wall is at a lower temperature than the inside before it can be released to heat the room.

    Another way is to think of it as a pendulum, but one where the return swing is inversely proportional to the initial swing.
    The quicker you move it to the right, the slower it will return to the left.

    So this is why wall thickness and surface area becomes important as well as the mass and temperature differences.
    • CommentAuthorskyewright
    • CommentTimeJun 25th 2012 edited
     
    Posted By: SteamyTeaSo the shape of the thermal mass is important as well as the mass.

    Yes. I'd intended to mention that too in along with "thermal proprties". Thanks for adding that clarification.

    Another way is to think of it as a pendulum, but one where the return swing is inversely proportional to the initial swing.
    The quicker you move it to the right, the slower it will return to the left.

    Nicely put. :bigsmile:

    So filling all (the normal thickness, or just a little more) stud walls with thermal mass (dry sand ?) might be better than having one big thick wall of equivalent thermal mass in the middle of the house?
    •  
      CommentAuthorSteamyTea
    • CommentTimeJun 25th 2012
     
    Posted By: skyewrightNicely put

    After writing the nonsense about heat buried in wall and waiting for the right time to come back out to play it just came to me what is happening, though it is only a 2 dimensional description with 1 variable.
    Filling stub walls with stone chips may be better still as it allows air movement (from a fan if you want to).
    • CommentAuthorCWatters
    • CommentTimeJun 25th 2012
     
    Increasing thermal mass will indeed help reduce temperature changes due to external input but the title of the thread talks about "thermal storage".
    • CommentAuthorskyewright
    • CommentTimeJun 25th 2012 edited
     
    Posted By: CWattersIncreasing thermal mass will indeed help reduce temperature changes due to external input but the title of the thread talks about "thermal storage".

    Indeed. Sorry for the digression.
    In that case there is a need for a mass that is isolated from the household environment, but from which heat can be extracted when desired.

    Given that, might ST's "stone chips" through which air can pass have advantages over a water wall?

    However I suppose stone chips inside insulated walls would be not a million miles from the classic underfloor "rock box" approach & I have a vague feeling of reading about unease regarding build up of nasties over time with those?

    Getting back to water. I'd been assuming a water wall as something that was essentially a curiously shaped tank, but an insulated water wall with allowance for passage of air (or some other heat transfer mechanism such as circulating pipes) sounds a bit like much flatter version of a solar closet?
    http://www.ece.vill.edu/~nick/solar/solar.html
    •  
      CommentAuthorSteamyTea
    • CommentTimeJun 25th 2012
     
    And insulated water wall with an air passage would be similar to a fish tank with bubbles blowing though it.
    Or a shower, if you think of the water as bubbles.

    Here is a bit about thermal inertia in buildings:
    http://www.telefonica.net/web2/josepsolebonet/index_archivos/Workshop_Thermal_Inertia.pdf
    • CommentAuthortony
    • CommentTimeJun 25th 2012
     
    Skyright you ask, "Once an initial equilibrium[1] has been reached does the presence of the mass add anything at all to the energy input required by the house?"

    No but it allows more thermal storage of incidental and solar gains WITHIN a comfortable temperature range

    Also smooths out temperature swings, ie the thermal inertia is large -- I like both = nice even temperatures in the house
    •  
      CommentAuthorSteamyTea
    • CommentTimeJun 25th 2012
     
    From my understanding of it (and I think I have made a school boy error in the calculations by not using mass at the begin, though the concept is the same), if you have too much mass, you never get to store the energy quick enough. Seems to me that going under size on the mass is the most effective method, bit like going undersize on an inverter, you can discard the very rare occasions when it is too hot, or very cold, These outliers add very little.
    Though that Telefonica Workshop paper does say that it works best in a very well insulated house, which possibly has good airthighness. The test house is in Madrid though, a very different climate regime to ours.
    Tony, do you log your house temperature on an hourly basis? Could line it up with some weather data and gauge really what is happening.
    • CommentAuthortony
    • CommentTimeJun 25th 2012
     
    Temperatures change so slowly that hourly would be too painful!

    I do log temperatures

    As I see it once the mass is warm there is so much of it that it takes ages to change, my heat losses are very small. 100W for the whole house in October (my ventilation heat loss is my biggest loss)
    •  
      CommentAuthorSteamyTea
    • CommentTimeJun 25th 2012 edited
     
    Hard to tell what is really happening at any sampling rate over an hour, even an hour is a bit crude, can lead to large error margins.

    What should happen when working out how much thermal mass to incorporate into a house is to decide on the maximum temperature swing that is permitted, then work backwards to find out how much mass is needed. This is one advantage of water, it is easy to increase the quantity, and sometimes even easier to reduce it.
    Water also behaves differently at room temperature than timber, rock or brick as convection currents can, in effect, increase the surface area that is used to transfer the heat. Though the high VHC means that a lot of energy has to be transferred before a rise/drop in temperature is noticed.
    I still think that low mass, well insulated and controlled ventilation/heat recover is the way to go in the UK.
    • CommentAuthorEd Davies
    • CommentTimeJun 25th 2012 edited
     
    I'm with Tony on this: if the goal is even temperatures then I can't see how extra thermal mass at that temperature can be detrimental to the day-to-day operation of the house.

    Things get a bit more complicated when the thermal mass is heated (e.g., from solar thermal) when you need to tune the connection between the thermal mass and the house fairly carefully.

    Tony, what does that 100 W include? The actual amount of heating you need to apply (above those for incidental gains such as lighting, cooking, leakage from the DHW tank, whatever) or the amount of heating needed to keep the house warm if it was not otherwise using any human-supplied energy? I assume, for example, that solar gain is not included in the 100 W. Also, any idea what your average heat losses are over, say, a chilly January?

    Any idea how quickly your house would cool in a cold winter with no external power or metabolism? I'm imagining around 1 °C per day. Is that ridiculous one way or the other?
    • CommentAuthorEd Davies
    • CommentTimeJun 25th 2012
     
    Posted By: SteamyTeaHard to tell what is really happening at any sampling rate over an hour, even an hour is a bit crude, can lead to large error margins.

    The Hockerton houses drop from summer temperatures to around 17 °C at the end of February or whenever. I can't imagine you'd need hourly monitoring to follow that.
    • CommentAuthorRobL
    • CommentTimeJun 25th 2012
     
    I have experience of low thermal mass house construction, and I'm not a fan - I think thermal mass is king!
    This house has brick walled bedrooms downstairs, SIP living/kitchen upstairs. In the morning in November it was chilly upstairs, but when the sun comes out the temperature rockets - and by mid-day it's too hot. The result is that heaters get switched on and off, then windows opened & closed. The place needs a bigger "capacitor" to stop the wild fluctuations.
    It's very well insulated (triple glazed throughout, modern scandinavian design), but due to low thermal mass is actually awkward to live in.
    •  
      CommentAuthorSteamyTea
    • CommentTimeJun 25th 2012 edited
     
    Are there other factors that could have affected it, such as a large south facing roof (assuming it is room in roof).
    And do you think that a large pile of bricks or a 45 Gallon barrel of water would have reduced this.
    I live in a low mass place, not ideally orientated to catch the sun, but it is very really too hot, and very really too cold. Even got some data somewhere to show how stable it is.

    I think the trouble is that it is very hard to compare identically designed houses, side by side.
    • CommentAuthorRobL
    • CommentTimeJun 25th 2012
     
    Hi ST
    It has lots of large south facing windows, which I guess let in lots of low November sun. And yes, I think a few barrels of water would do wonders.
    It's a holiday cottage - so I can't really make these sort of adjustments :-)
    • CommentAuthorEd Davies
    • CommentTimeJun 25th 2012 edited
     
    At least one interesting spreadsheet on Tony's site. Some reading required.

    ETA: done some reading now. To partly answer one of my own questions above, in the very cold weather at the end of 2010 in a period of a few hours over a week (171.5 hours) ending 2010-12-10T17:59 his total electrical consumption was 384 kWh for an average of 2239 W. He seems to have a floor area of 240 m² so that's 9.33 W/m² - less for actual heating as such.
  1.  
    <blockquote><cite>Posted By: RobL</cite>Hi ST
    It has lots of large south facing windows, which I guess let in lots of low November sun. And yes, I think a few barrels of water would do wonders.
    It's a holiday cottage - so I can't really make these sort of adjustments :-)</blockquote>

    By the sounds of it, you need some serious exterior shading more than anything.
    •  
      CommentAuthorSteamyTea
    • CommentTimeJun 25th 2012 edited
     
    Posted By: Ed Daviesso that's 9.33 W/m²

    One of the things that the GBF Energy use thread seems to be showing is that houses with a larger floor area use less energy per m^2. So not always a good gauge.
    Still low though.
    • CommentAuthortony
    • CommentTimeJun 25th 2012
     
    average heat loss in January/February is said to be by calculation 700W

    I have never added more than 300W average though the calculations do not take into account my thermal store.
    • CommentAuthorCWatters
    • CommentTimeJun 26th 2012
     
    Given that sunshine entering windows lands on the floor...would that be a better place to put water tanks for the purposes of increasing thermal mass?
    •  
      CommentAuthorSteamyTea
    • CommentTimeJun 26th 2012
     
    Water tends to end up on the floor, so probably a good idea :wink:

    Extra floor based thermal mass may mean that you need to have stronger floors, and almost by definition that means they will be heavier.

    If you really want to use water for stabilising the internal temperature, you really need to go to an active system, usually called central heating.:bigsmile:
   