    ...my electrian and I have agreed that for the artsy fartsy downlighter positions he will wire up to a fused connection or similar and I'll take it from there, placing the downlighter arrays exactly where I want them, (and then move them when the 'head of design' points out my stupidly....)

    Any environmental or other factors between 12 and 240v in this context....?


    J
    • CommentAuthorCWatters
    • CommentTimeJul 2nd 2012
     
    I'm using 230V GU10 LEDs but I think on a new install I'd go for 12V LED that use 20-24 of the 5050 form factor die and deliver >350Lm

    Installing 12V lighting is notifiable under the Building Regs unless the electrician does it. You should design the wiring to cope with the much higher current of 12V halogen just incase you sell the house and the new buyer fits these bulbs. Otherwise there is a real fire risk that could come back to you...The high current draw by 12V halogen is the reason installing 12V is notifiable where as 230V it isn't allways.
    • CommentAuthorTimSmall
    • CommentTimeJul 2nd 2012
     
    240v halogens are higher efficiency I believe than 12v ones. Both are a bit enviro-rubbish, but that having been said:

    1. Don't go nuts on the total wattage.
    2. Buy the high efficiency halogen bulbs.
    3. When dimmed, the efficiency drops through the floor, better to split them onto several switches instead, so that you can turn two thirds of them off.
    • CommentAuthorTimSmall
    • CommentTimeJul 2nd 2012
     
    Oh yeah, if you're going for LEDs, not halogens, then a low-voltage constant-current driver might be the best idea, but I'm not up to date on LED fittings etc.
  2.  
    Posted By: CWatters20-24 of the 5050 form factor die and deliver >350Lm

    ? Que...?

    (Will all be LEDs)

    J
    •  
      CommentAuthorDamonHD
    • CommentTimeJul 2nd 2012
     
    TimSmall: I just read something within the last couple of hours that for MR16-style halogens the lower voltage versions had the higher luminous efficacy due to the more compact filament.

    Rgds

    Damon
    • CommentAuthorTimSmall
    • CommentTimeJul 3rd 2012 edited
     
    Posted By: DamonHDTimSmall: I just read something within the last couple of hours that for MR16-style halogens the lower voltage versions had the higher luminous efficacy due to the more compact filament.


    Yep, looks like you're right. I must have remembered that back-to-front (although I've just spent about 10 minutes trying to get lm/W figures for GU10s and MR16s, and have failed entirely - they just don't want you to know exactly how rubbish they are - as soon as the same companies are trying to flog their LED replacements, out come the lm/W figures!).

    For LED lights, standard downlighter enclosures are generally a bad idea, because the LEDs run too hot - this seriously shortens their life, and also makes them less efficient.

    If you do have to use them, then they should be open at the back to a large cool void in order to get the best cooling (which is obviously impossible if they're in an insulated ceiling, and may make complying with fire-safety regs more difficult too).

    Unfortunately - the alternative - which is a proper fixture designed for LEDs from the drawing board (rather than a bodgy attempt to retrofit them to existing halogen fittings). Sadly, there seems to be relatively little demand for these (partly because everyone has halogen downlighter fittings already, and partly because specifiers don't understand why they are a good idea) - and this in turn keeps the price relatively high for these superior fittings...
    • CommentAuthorTimSmall
    • CommentTimeJul 3rd 2012
     
    The best bet if using conventional halogen fittings, the most efficient option is probably to use a dimable constant-current driver (instead of the conventional 12v halogen "transformer") like this:

    http://www.aurora.eu.com/ProductPages/PowerProductDetails.aspx?g=248&c=&b=5&oc=556

    (available for £30 or so).

    and use it to power a couple of strings of "uncontrolled" LED bulbs, if you can find them (probably not on reflection, the average bod would just plug them into a halogen transformer and blow them up).

    Hmm, bloody halogen downlighters... Hopefully the LED market will get a bit more sensible in the next few years, but then I was saying that a few years ago.
    • CommentAuthorCWatters
    • CommentTimeJul 3rd 2012 edited
     
    <blockquote><cite>Posted By: James Norton</cite><blockquote><cite>Posted By: CWatters</cite>20-24 of the 5050 form factor die and deliver >350Lm</blockquote>
    ? Que...?
    (Will all be LEDs)
    J</blockquote>

    These are the sort I'm using ...

    http://tinyurl.com/cagtgfs

    The "5050" form factor LED refers to the package for one individual LED and looks like this..

    http://tinyurl.com/d8dqh7a

    Some of this type of downlight bulb are capable of producing > 480 Lumens according to ebay sellers.

    I've used versions made from 20 or 24 of these LEDs producing 320-450 Lumens from about 4-5W.

    They appear to be suitable replacements for 40-50W halogen provided you are aware of the wider beam angle issue. The wider wide beam angle means the light is more spread out so the spot of light on the ground below _one_ of these appears dimmer. However if you have an array of downlights the spot below one of them is illuminated by several LEDs so the required brightness returns.
  3.  
    I' m regretting downlighters, they let loads of drafts through the holes in the ceiling. Next time would choose dangling light fittings.
    • CommentAuthorTimber
    • CommentTimeJul 4th 2012
     
    IIRC most LEDs run a between 4 and 5 volts. So would it be more practical to run a high current capacity 5v lighting ring and plug the LEDs directly into this, rather than stepping down from 12v in the 'bulb'?

    I have some LED lighting in my garden. I made them from £ shop LED head torches and have a 5v supply running out to my shed. I dissassembled the LED head torch, took the circuit board out and mounted in my own housing and then an a feed to each one (on my deck, in the shed etc). I run the whole lot off a computer power supply taking a feed off the 5v output.

    Is there mileage in this for lighting within a house (obviously with higher tech LED packages)?
    •  
      CommentAuthorDamonHD
    • CommentTimeJul 4th 2012
     
    White LED forward voltage drop more like 3.3V if that's what you mean?

    Rgds

    Damon
    • CommentAuthorTimber
    • CommentTimeJul 4th 2012
     
    Yeah, that is more the number I was looking for. It has been a while since I propperly messed with electronics.

    The LED head torches that I used ran off 3 AA batteries giving a nominal 4.5v. In reality the voltage of a fresh AA is a little higher, so I was happy pushing a regulated 5v through them. So far I have had no problems with lifespan, but they are not used 24/7.

    So, going back to my previous post, if most white LED chips take 3.3v, would a regulated high current 3.3v rig be a reasonable idea. My thinking was to get away from multiple voltage regulators/transformers. Or would the losses through wires at those low voltage/high(ish) currents negate any benefit in transformer efficiency?
    • CommentAuthorEd Davies
    • CommentTimeJul 4th 2012
     
    Posted By: TimberSo, going back to my previous post, if most white LED chips take 3.3v, would a regulated high current 3.3v rig be a reasonable idea.

    No, not really. The problem is that they need to be fed a specific current rather than a specific voltage. The actual current through them is very sensitive to the exact voltage and the voltage corresponding to the right current varies slightly between devices, with age and with temperature. E.g., you might have two LEDs next to each other, one needing 3.29 V and the other 3.31 V. If you feed 3.3 V the one needing 3.31 will be very dim, not just by an amount proportional to the reduced voltage as the current will be also be greatly reduced, whereas the one wanting 3.29 V will take too much current and will likely burn out quickly.

    LED installations always have some sort of circuitry to control the current. Sometimes it's an active semiconductor circuit to form a constant current source. Other times it's just a resistor in series.

    Often that circuit can be shared between multiple LEDs in a series chain hence it's often a good idea to use a voltage a little in excess of some number of times the forward voltage drop of a single LED with that many LEDs in each series chain.
    • CommentAuthorCWatters
    • CommentTimeJul 5th 2012
     
    <blockquote><cite>Posted By: Timber</cite>IIRC most LEDs run a between 4 and 5 volts. </blockquote>

    What Ed said...

    See the I-V curve down here. Once you go past Vf they behave like very low value resistors. Problem is that no two LED have exactly the same Vf although if they are from the same batch it might be close. Slight change in Vf = big change in current and power unless supplied by a constant current device.

    http://en.wikipedia.org/wiki/Light-emitting_diode
    •  
      CommentAuthorfostertom
    • CommentTimeJul 5th 2012 edited
     
    My first time, and not seen them fitted yet but we're using http://www.aurora.eu.com/ProductPages/LampProductDetails.aspx?g=7822&c=&b=136&oc=84 LED swivelable downlighters (also avail fixed) £36 + £9 driver. Why do anything else now these have come of age?
    • CommentAuthordjh
    • CommentTimeJul 6th 2012
     
    Posted By: fostertomMy first time, and not seen them fitted yet but we're using http://www.aurora.eu.com/ProductPages/LampProductDetails.aspx?g=7822&c=&b=136&oc=84 LED swivelable downlighters (also avail fixed) £36 + £9 driver. Why do anything else now these have come of age?

    Because ">55 Lumens per Watt output allows compliance with the Building Regulations" is still only about half of state-of-the-art commercially available LED lamps.
    • CommentAuthorsnyggapa
    • CommentTimeJul 6th 2012
     
    Posted By: fostertomMy first time, and not seen them fitted yet but we're usinghttp://www.aurora.eu.com/ProductPages/LampProductDetails.aspx?g=7822&c=&b=136&oc=84" rel="nofollow" >http://www.aurora.eu.com/ProductPages/LampProductDetails.aspx?g=7822&c=&b=136&oc=84LED swivelable downlighters (also avail fixed) £36 + £9 driver. Why do anything else now these have come of age?


    exactly what i was waiting for, exactly 9 months too late!

    maybe once my MR16 12v LEDs start to blow I could consider replacing them with constant current devices, one string at a time...
    •  
      CommentAuthorfostertom
    • CommentTimeJul 6th 2012
     
    Posted By: djh">55 Lumens per Watt output allows compliance with the Building Regulations" is still only about half of state-of-the-art commercially available LED lamps.
    Oo dear, so these are cheap and nasties? Now I'm fully concentrating, cd someone remind me of the lm/W hierarchy - incandescent; LV halogen; CFL; linear fluorescent; typical LED; state-of-art LED? thanks
    •  
      CommentAuthorDamonHD
    • CommentTimeJul 6th 2012
     
    Incandescent ~ 13lm/W
    Latest commercial LEDs ~ 100lm/W
    •  
      CommentAuthorfostertom
    • CommentTimeJul 6th 2012
     
    and the ones in between, if anyone would be so kind?
    • CommentAuthorCWatters
    • CommentTimeJul 6th 2012 edited
     
    Looks like 230V 5W 400L GU10 are now down to around £3.50-£4 compared to £7-£11 this time last year..

    http://www.ebay.co.uk/itm/Best-price-for-20pcs-GU10-4-5-5W-24-5050-SMD-LED-light-450Lm-180-Warm-White-UK-/180852631499?pt=UK_Light_Bulbs&hash=item2a1ba827cb
    • CommentAuthorCWatters
    • CommentTimeJul 6th 2012
     
    <blockquote><cite>Posted By: fostertom</cite>and the ones in between, if anyone would be so kind?</blockquote>

    There is a table here..

    http://en.wikipedia.org/wiki/Luminous_efficacy#Examples_2
    •  
      CommentAuthorfostertom
    • CommentTimeJul 6th 2012
     
    Great - thanks
    •  
      CommentAuthorfostertom
    • CommentTimeJul 16th 2012 edited
     
    Despite the comments, on reflection I think that http://www.aurora.eu.com/ProductPages/LampProductDetails.aspx?g=7822&c=&b=136&oc=84 are prob a gd deal for now - tho not state-of-art, are affordable, very shallow depth, cool running, IP54, swivleable or fixed, sparkling effect unlike CFL equivalents, and lm/W as good as any CFL. Ours are being installed today I think - will see the effect next week.
  4.  
    ...soooo....

    for the cost conscious green builder I need to look for 12v, MR16 "5050" 450lm bulbs:

    http://www.ebay.co.uk/itm/MR16-4-5-5W-24-5050-SMD-LED-light-450Lm-180-Warm-White-UK-/180852735585?pt=UK_Home_Garden_Night_Lights_Fairy_Lights&hash=item2a1ba9be61

    in basic fittings with lots of space around:

    http://www.screwfix.com/p/robus-adjustable-round-low-voltage-downlight-brushed-chrome-12v/71123

    plus something like one of these for each 10 or so lamps:

    http://www.screwfix.com/p/240v-to-12v-350ma-9w-led-const-current-controller/66599?cm_mmc=AffiliateWindow-_-DeepLink-_-Na-_-Na&source=aw

    Now the plan was that my electrician would do the 240v wiring up to a 'transformer' position and I would wire in a 12v 'kit' with LED bulbs as part of the 2nd fix which I am doing, with him to check and test. Now we are talking constant current and lighting positions in series with cabling to suit drop, load, distance etc, I think that he may have to be involved in sort of 2nd 1st fix.

    J
    •  
      CommentAuthorDamonHD
    • CommentTimeJul 16th 2012
     
    You+sparks are embarking on what we call a learning journey these days I suspect... (The school governor lingo is getting to me.)

    Rgds

    Damon
    • CommentAuthorSprocket
    • CommentTimeJul 17th 2012
     
    100lm/w is still relatively state of the art (130 available from Philips and Cree these days but not in WW)
    You don't get it at those prices.
    The lumen figures claimed by many cheap LED lamps are clearly rubbish.
    If those ebay 5050 lamps are 100lm/W I will eat my box of cheap lamps that just didn't measure up.
    I know they are pricey but the Aurora LEDs that FosterTom pointed to are _much_ brighter and nicer light quality than the 5050SMD bulbs IMHO. They also are ventilated/heatsinked and run fairly cool - they have been proerly designed.

    I would be quite wary of anything where switchgear and LEDs are crammed into a normal halogen glass capsule just because that is what the factory happened to have lots of. It's just not a sensible LED design.
    •  
      CommentAuthorfostertom
    • CommentTimeJul 17th 2012 edited
     
    Posted By: SprocketI know they are pricey but the Aurora LEDs that FosterTom pointed to ...
    I was thinking they're quite cheap @ £35 + £9 for driver, And thanks for
    Posted By: fostertomThey also are ventilated/heatsinked and run fairly cool - they have been proerly designed.
    • CommentAuthorSprocket
    • CommentTimeJul 17th 2012
     
    Take those ebay lamps for example
    20 lamps for 72 quid is £3.60 per lamp.
    At 24 per lamp that's < 15p per LED. And that's ignoring cost of glass capsule and PSU electronics. Something tells me those are not the 100lm/w LEDs that cost several quids each.
    They are probably something like this:-
    http://uk.rs-online.com/web/p/visible-led/6935167

    Even so, 15p is still crazy cheap. It's likely these are the LEDs that failed to make spec when sorted. The ones that make >= 19.5 lm/w make spec and can be sold as such at a decent price. They don't throw the rest away though.

    But lets give benefit of the doubt. Lets say these are real full spec LEDs.
    The datasheet says typical is 24lm from 150ma at 3.5V.
    That would be over 500lm but only at 3.5 x 0.15 x 24 = 13 Watts.
    At 4.5W and 100% efficient PSU we only have 50ma per LED.
    Datasheet says that at 50ma this LED outputs 10 lm.
    So, even if they are full spec LEDS and 100% PSU we still cannot possibly get more than 240 lm.
    That is way short of the claimed 450 lm (which is very suspicously the magic 100 lm/W).
    And that 240 lm is also spread over 180 degrees because the SMD LEDs have no lens.

    Compare that with a 50W halogen that typically outputs 900lm. And most of that projected forwards thanks to a reflector. The cheap LED doesn't come close in luminous flux.

    It is a lot to ask of an LED but the relatively expensive 7W Aurora and Philips LED lamps with heatsinks, ventilation and lenses enclosing the LED do come fairly close to 50W halogen in performance and light quality. You get what you pay for. The ebay SMD specials surely are a bargain for the price but I would not want people to get the idea that this is what state of the art LED lighting looks like.
   