    • CommentAuthoradwindrum
    • CommentTimeJul 13th 2012
     
    I appreciate that you can get very good figures for MVHR and that it does what it says on the tin, but I am trying to avoid the cost of buying/installing and running one while having all the complications of having another mechanical object in the house to maintain etc. Passivents (with humidity/CO2 valves/sensors) combined with lockable opening windows and a couple of extractor fans in bathroom (along with opening windows) would be a much cheaper and adequate solution for me.

    I am also a windows open person so will be conflicting with the system a lot of the time and am finding it a very grey area regards what to do to the system when windows are open.

    Heat loss seems to be the only problem, but having a log boiler it simply means more work for me rather than money.

    Am I barking up the wrong tree? Should I take the easy option and plump for the extra money and efficiency of MVHR.
    •  
      CommentAuthorjoe90
    • CommentTimeJul 13th 2012
     
    adwindrum,

    I am having the same conflict/decision. I want to build strawbale with all the renewables that I can and want to get away from "technology" with all its costs/maintenance/embodied energy. I would be interested to see what others say and see what passive solutions are available to compete with MVHR.
    • CommentAuthorGaryB
    • CommentTimeJul 13th 2012
     
    Adam

    From your description of how you heat and ventilate your home, neither option appears suitable for you.

    Passivent would save the cost of an MVHR unit but each terminal is more expensive and my experience is that there is just as much ductwork as MVHR.

    Individual room MVHR fans may be your most cost effective option.
    •  
      CommentAuthorjoe90
    • CommentTimeJul 13th 2012 edited
     
    or FIWI units as per viking house:-
    http://www.viking-house.co.uk/fine-wire-hrv.html
    • CommentAuthoradwindrum
    • CommentTimeJul 13th 2012
     
    I like the FIWI but cant help thinking it is still at the tweaking stage. I need something for life.
    The amount of ducting isnt the main issue, but the cost of the units does seem a problem. I have only read the Passivent bumph and they use comparative figures suggesting (off the top of my head) that it would cost £1500 to install a passivent system as opposed to £5k for MVHR, I will look at the individual room idea, thanks for that.
    •  
      CommentAuthorfostertom
    • CommentTimeJul 13th 2012
     
    Posted By: adwindrumHeat loss seems to be the only problem, but having a log boiler it simply means more work for me rather than money.
    That's the key thing - you're willing to provide yourself with 'no-cost' wood fuel for life, so 'waste' heat by leave windows open as much as feels right - but why stop there? - why bother with serious insulation/airtightness? - where's the dividing line?

    However, seeing you have a good supply of your own wood fuel, you could look at it as your pension, as all-fuel prices continue to rise (see nothin' yet). But you've committed yourself to burning your pension instead of selling your woodfuel output to highest bidder - as well as committing yourself to continued labour in retirement!

    Remember MHRV only gives benefit in winter - in summer you switch it off and open the windows anyway.
    MHRV requires any woodburner to be balanced flue type, otherwise the combustion air flow makes nonsense of the airtight + MHRV principle.
    With super insulation and airtightness, a woodburner, whether balanced flue or not, becomes redundant - for decorative or feelgood purpose only. You'll have trouble throttling back even the smallest woodburner - it will burn kindling for 20mins before it needs to be shut down, to avoid overheating. Used that way, it will tar up.

    Passivent can (should) be controlled by extract humidity sensors (humidity gives good correlation with smells and CO2, as the 3 reasons for ventilating). With airtightness, cold-air inlets are reqd. Are these to be unthrottled? Or rely on synchronising the manual opening of inlet windows with the extract humidity sensors? If not bothered about windows left open while the extract sensors are 'off', then why bother with Passivent at all? Pukka humidity-sensing trickle vents are available, so both inlet and extract are humidity controlled and synchronised.
    • CommentAuthorShevek
    • CommentTimeJul 13th 2012
     
    Bill Dunster designs his schemes with passive ventilation.
    • CommentAuthoradwindrum
    • CommentTimeJul 13th 2012
     
    You hit the nail on the head there Tom. I do wonder about scaling back on insulation and airtightness due to having a woodburner etc. The MVHR is the same dilemma as far as I am concerned. Money is the object as opposed to creating the best level of airtightness/insulation/MVHR which will all scale back the size of the house and finishings which are already scaled back.

    I want persuading that I, me, myself and I will benefit financially from applying these things.

    The frame seems to cost about £1000-1500 per 0.1 U-value reduction (wall) beyond 0.16. I lose a bedroom to get it down to 0.12.
    • CommentAuthoradwindrum
    • CommentTimeJul 13th 2012
     
    Regards switching it off in summer, there is the issue of microbial growth in the ducting.
    Bill Dunster and Kevin McCloud too.
    • CommentAuthordjh
    • CommentTimeJul 13th 2012
     
    adwindrum wrtoe: "there is the issue of microbial growth in the ducting".

    I don't know anything about it, so I googled. The first hit I got was

    http://www.ors.od.nih.gov/sr/dohs/Documents/HVACDuctCleaning.pdf

    "The industry claims that cleaning ductwork can improve indoor air quality, control molds and other allergens, enhance heating, ventilating, and air‐conditioning (HVAC) system performance, and reduce energy costs. Yet there is little scientific evidence to support these claims, and poor duct cleaning practices can actually cause or increase air quality complaints."

    That from NIH - does anybody have any equally credible statement that there is a problem?
    •  
      CommentAuthorfostertom
    • CommentTimeJul 13th 2012
     
    Posted By: adwindrumthe issue of microbial growth in the ducting.
    Bill Dunster and Kevin McCloud too.
    wouldn't want them growing in my ducting.

    Awadukt and other u/ground pre-heat air intake systems' ducting looks like ordinary uPVC drain pipes but is expensively made with silver mould inhibitors. Are these more liable to mould because u/ground/colder?
    • CommentAuthorchriskemp
    • CommentTimeJul 13th 2012
     
    Bill and kevin use mech systems by the way, on their new projects.
    What airtightness sre you aiming for?
    Do you have nternal wetrooms?
    • CommentAuthoradwindrum
    • CommentTimeJul 14th 2012
     
    Am aiming for under 1 for airtightness. And will have 2 internal wetrooms.
    Do you have any details or links for the new mechanical systems they are using?
    • CommentAuthorchriskemp
    • CommentTimeJul 14th 2012
     
    The Triangle in Swindon as part of Hab Oakus (Kevin's own Co) is using Vent Axia Kinetic plus.
    Bill has/is developing a heat pump with mech vent at the moment as his wind cowls wont work on airtight dwellings.

    You would be very remiss to use passive on such an airtight building.
    for one you will have to punch loads of holes all over the place to any kind of stack effect, which will create draughts (by definition). and you will lose heat (if you actually get the stack effect to work).

    Also, pretty certain that below 3m3 MVHR is necessary, sensible and suggested.
    (read mandatory)

    with regards wet rooms, you will need mech vent to comply with building regs as you dont have a window to open. internal wet rooms need mech vent now.

    MVHR will also improve you sap score on an airtight dwelling.

    There is an old adage - "Build tight-ventilate right"!
    • CommentAuthoradwindrum
    • CommentTimeJul 14th 2012
     
    You may well have sold me there. Thanks a lot Chris and Tom.
    • CommentAuthorchriskemp
    • CommentTimeJul 14th 2012
     
    for prices search service vent
    • CommentAuthorGreenPaddy
    • CommentTimeJul 14th 2012
     
    adwindrum,

    with MVHR, you'll become less of an "open windows" person. I personally dislike overly warm/stuffy houses, but since I built my own highly insulated/airtight house, I almost never open the windows (actually regretting the extra cost of having quite a number of opening windows, having expected to be using them like in a traditional house). I now advise clients to minimise the number of openers - just one per room.

    A log burner may well over heat the house, if it's of a sensible size visually (say 6 or 7 kW) but since you have free logs, why not go for a log boiler stove, and get your DHW too (DHW may well be a greater energy requirement than your heating - annually). My experience is that the house does not overheat, with the log boiler stove on, though be careful to choose one which is weighted to heat-to-water rather than heat-to-room, eg. 12kW total, with 2kW to room & 10kW to water.

    And even with a well insulated house (0.12 W/m2K type level you've mentioned), you will certainly still need heating, al-be-it to a much lesser extent. The MVHR will NOT move the heat around the house adequately if the logs are the only heat source, nor can you get enough heat into the air if it's injected into the MVHR ducting.

    I always design houses with the MVHR ductwork as part of the structural/layout consideration (eg. running ducts parallel to floor joist), so that installation is simplified. So £5000 sounds a bit on the high side, since parts will be about £2000 - it's not a 3 week install.

    Make sure you oversize the MVHR unit, so it's not running at a high fan speed, as they become more noisy, and the energy consumption rises sharply as flow rates increase. The SAP apendix Q spec's which define MVHR units in terms of being "adequate for kitchen plus a number of wetrooms" is nonsense, so be wary of that. When you do the air flow calcs, you find that the units spec'd for "kitchen & 7 wetrooms", are only adequate for a house with kitchen and 3 wetrooms, for example.

    Bottom line (in my experience), target Uvalues of 0.12W/m2K, really focus on cold bridging and air tightness, use MVHR, only employ someone to design the house who can demonstrate they have experience of "low energy houses" and who consider the house shell & heating & ventilation & hotwater as a complete, integrated package. It needn't be complicated, just well thought out.

    Hope something in that helps.
    • CommentAuthoradwindrum
    • CommentTimeJul 14th 2012
     
    Thanks for that Greenpaddy.

    I currently run a logboiler which I will be transferring to the newbuild but did like the look of the indoor versions that you describe. Our designer is experienced in low energy houses and has been directing us down your route. I think that I am just a luddite and struggle with the concept of designing a house that doesnt need much heating and that the costs involved in getting down to U-values of 0.12 with airtightness below 1 to include MVHR, could well be spent elsewhere ie a room for each of my 3 kids.

    Perhaps I should reach for those targets and drop the wood burner in the house which would realistically only be a comfort feature and cost £1500 to buy and install?

    On the comfort front with a house such as you describe (minus your log burner), is a uniform temperature house without any radiant heat source (fire/rads) rather sterile? Or is it just damn comfortable and not something you think about? I look forward to not having to dash from the shower to the duvet etc but I dont want to lose that glow of fire on my face on a winters evening.
    • CommentAuthorGreenPaddy
    • CommentTimeJul 14th 2012
     
    adwindrum,

    my house sits happily at 19oC +/-2oC, and is a very homogenous temp throughout the house. It generally doesn't need active heat input until external temps get well below 10oC. I tend to forget about heating now, as it always feels comfortable. I have to confess to occasionally lighting the log boiler stove, even when the internal temp is adequate, just to have the peripheral vision of flames and radiant heat, especially when it's cold & damp like this summer!! That's a purely personal thing.

    Maybe you could install the part of the stove flue through and above the roof, plug it with insulation, and then when finances allow, add the internal flue through the house and the stove?

    Can I ask what your designers estimate per square metre is for your house (ie. total build costs for everything incl carpets, but excluding loose furnitre, divided by the total habitable floor area)?
    • CommentAuthoradwindrum
    • CommentTimeJul 14th 2012
     
    We have been thinking a long time about the project but only started our first meeting with architect this week so real details need firming up, but we have 200k. I am hoping for anything above 170m2. Going for a rather trusting and flexible route of architect and his build arm of business doing a sort of turn key affair, however a giant spreadsheet is going to be formulated with everything on to which I am able to cherrypick involvement eg doing the actual work or purchasing/researching items to bring costs down. Am planning on ploughing the money into structure and leaving finishes(kitchen/bathroom) super basic with a view to improving/updating over time.
  1.  
    Hi adwindrum,

    I have had the same thoughts, per your original post and for Joe I have found the following, as the best alternative I can find to MVHR which we are exploring.

    http://www.ventive.co.uk/

    Am chatting to the guys about installing the system in our new build property - applies similar principles as MVHR, just without the 'mechanical' element. The testing and efficiency calcuations look very impressive.

    Hope this helps
    Peter
    • CommentAuthorRobinB
    • CommentTimeJul 17th 2012
     
    Posted By: adwindrumis a uniform temperature house without any radiant heat source (fire/rads) rather sterile? Or is it just damn comfortable and not something you think about?


    I wouldn't have thought it until experiencing it myself but we find it's the latter - you just feel good - not just down to the right temperature but also a comfortable humidity level and fresh.
  2.  
    Posted By: LondonEcoHouseI have found the following, as the best alternative I can find to MVHR which we are exploring.

    "http://www.ventive.co.uk/"
    I like the simplicity of the system, but I don't understand how it can work in windless conditions.

    According to the brochure "Ventive drives the air in both directions (extract and supply) using two forces: Passive Stack Effect (with warmer air naturally rising due to its lower density) and wind assistance" with "Heat Transfer Efficiency (up to 97%, as tested by Imperial College London)".

    If the heat recovery unit really removes the 97% of the heat in the exhaust air & transfers it to the supply air then:

    a) How does the exhaust air get drawn out of the house in wind-less conditions?
    b) How does the supply air get drawn in to the house in wind-less conditions?

    I suspect they are being economical with the truth & that Imperial College have measured the heat exchanger efficiency in a laboratory with flow rates fixed by fans.

    In any effective passive ventilation system there will always be a trade-off between using the heat to drive air movement & using the heat to warm the incoming air. MVHR overcomes this conflict by using electricity to drive the air movement, allowing maximum heat exchanger efficiency.

    David
    •  
      CommentAuthorfostertom
    • CommentTimeJul 17th 2012 edited
     
    "Pre-warmed incoming air (supply) is channelled naturally via an existing chimney void and enters the room either through the fireplace opening (with minimal alteration) or a low level vent. No electrical connections and no fans or heaters are required.
    Exhaust air exits the room via the new opening at high level, using new flexible duct and into the heat exchanger at the top of the chimney where all the useful warmth is recovered."
    See the diagrams.
    Seems to be done on a room by room basis, using extg disused chimney stack! Warm(ish) air from heat exchanger disguised as chimney pot, drops down stack and enters room at low level, where it gets warmer. It's extracted via a hole into stack made at high level, into a flex duct pulled up thro the stack to the heat exchanger. So yes, there cd be natural stack circulation - but 97% efficient? that wd mean v little temp differential to create buoyancy between cooler descending inlet and warmer rising extract - but maybe enough, with sufficiently big ducts. Cd be gd.
  3.  
    I agree that with correct detailing of ducts, etc it could work well for refurbishing leaky houses, but I don't see how it can achieve 97% heat recovery efficiency & use stack effect to drive air movement.

    David
  4.  
    Posted By: adwindrumI like the FIWI but cant help thinking it is still at the tweaking stage.
    The only tweaking being done now is optimizing the defrost cycle, everything else is working well. Here's some pics of the latest Breathing Window, 3 units will be fitted flush into the external wall of a 300m2 house this week!
      Breathing Window (2).jpg
      Breathing Window (4).jpg
    •  
      CommentAuthorSteamyTea
    • CommentTimeJul 18th 2012
     
    Could it be 97% of the heretical maximum.
    And they do say energy with no reference to temperature.

    My home made unit can go over 100% when either the unit is 'hot' and the input fan is not pumping or the outside air is hotter than the extracted air (when the sun comes out).
    •  
      CommentAuthorDamonHD
    • CommentTimeJul 18th 2012
     
    Hmm Viking, definitely thinking of getting one of those for the living room or elsewhere, for this winter or next. We definitely need to up the air-changeover rate.

    What sort of floor area is one of those units intended to service given that our living room is small?

    Rgds

    Damon
    •  
      CommentAuthorfostertom
    • CommentTimeJul 18th 2012 edited
     
    Posted By: davidfreeboroughcould work well for refurbishing leaky houses
    I don't see that leakiness helps - to contrary, would dilute the buoyancy effect - a closed air circuit is ideal.

    Posted By: davidfreeboroughI don't see how it can achieve 97% heat recovery efficiency & use stack effect to drive air movement
    That's a function of how extremely low-resistance (large-area) the ducting and heat exchanger is - and I agree an existing flue half filled with another duct doesn't seem v large. Also what about leakiness, dust, toxins in the extg flue, which is used as inlet channel?
  5.  
    Posted By: DamonHDHmm Viking, definitely thinking of getting one of those for the living room or elsewhere, for this winter or next. We definitely need to up the air-changeover rate. What sort of floor area is one of those units intended to service given that our living room is small? Rgds Damon
    1 unit/100m2 floor area.
   