    • CommentAuthorfinny
    • CommentTimeAug 20th 2012
     
    I can see what you are saying but if you look at the indoor and outdoor temps I recorded above..
    Also why does a longer flue create more draw?
    •  
      CommentAuthorfostertom
    • CommentTimeAug 20th 2012
     
    Again, I edited my last (last para) just too late!
    • CommentAuthormike7
    • CommentTimeAug 20th 2012 edited
     
    Posted By: finnyI can see what you are saying but if you look at the indoor and outdoor temps I recorded above..


    "No testimony is sufficient to establish a miracle, unless the testimony be of such a kind that its falsehood would be more miraculous than the fact which it endeavours to establish" (David Hume)

    What you're suggesting would be miraculous - more likely is that you need to take the average temperature of the whole flue. and of the "outside" air. (This outside air would possibly not all be outside the building down to ground level - the path of the supply air might in a well sealed house be via an intentional vent, or at the other extreme via a bedroom window left wide open.)

    Longer flues, if taller, create more draw because the pressure difference due to the different density of the columns of warmer and cooler air is greater. If you have a skyscraper 21C inside and -20C outside the effect can be huge.

    The mechanism of the stack effect is no different in principle to the thermosyphon effect in a hot water system.
    • CommentAuthoran02ew
    • CommentTimeAug 20th 2012
     
    Maybe the effect of insulating the flue suggested by Finny has somthing to do with his point? it is somthing that i planned to do anyway, but having read all above, it sounds like room sealed or nothing
  1.  
    How do you stop the stove from being a cold radiator in the morning because cold air drops down the chimney at night?
    The room with the stove is always the coldest room in the house when the stove isn't lighting.
    People don't close chimney-roof valves before they go to bed because the stove is still smoking, and they don't set their alarm for 2 0'Clock to get up to close the valve either.

    I was in a Passive House at 9 0'Clock one cold morning, the room with the sealed stove was 15 degrees while the rest of the house was 20 degrees, the stove was 8 degrees and acted as a cold radiator.
    • CommentAuthoran02ew
    • CommentTimeAug 21st 2012
     
    Posted By: Viking HouseHow do you stop the stove from being a cold radiator in the morning because cold air drops down the chimney at night?
    The room with the stove is always the coldest room in the house when the stove isn't lighting.
    People don't close chimney-roof valves before they go to bed because the stove is still smoking, and they don't set their alarm for 2 0'Clock to get up to close the valve either.

    I was in a Passive House at 9 0'Clock one cold morning, the room with the sealed stove was 15 degrees while the rest of the house was 20 degrees, the stove was 8 degrees and acted as a cold radiator.


    As our only space heating for the entire home, i would think in the coldest months that it would be lit most of the time and with little effort and good quility logs i should be able to keep it alite through the night, as with the existing old broken fire she just requires a bit of tenderness in the morning and she away:shocked: also the more modern fires are usually so full of cast iron or ceramic that they hold heat for hours even if the do go out in the middle of the night.
    •  
      CommentAuthorfostertom
    • CommentTimeAug 21st 2012
     
    Even a small woodburner in a highly insulated/airtighted house - may overheat the house! No resemblance to an ordinary house, which likes a stove left ticking over overnight. You may find you only run the stove in short burns and let it go out. If you try to keep it in all the time, it's bound to be on v slow burn, with tar and toxic effects that have been much discussed here. Wiull be interesting to see what you find. Tho you do have a less-insulated half of the house to heat as well.
  2.  
    Forgive me as I have only quickly read the posts on this thread but any air passing over the top of the flue will cause a drop in pressure. Exacly the same as air accelerating over the top surface of an aircraft wing does. Hence the wing is pushed up. The air passing over the flue would do the same. On very calm days dont light your stove!!!!! I cant explain that one......
    My BCO told me recently that elbows are not needed anymore. My flue is vertical and works a treat, cough, cough.:shocked:
    • CommentAuthorEd Davies
    • CommentTimeAug 21st 2012
     
    Gusty's mentioned one reason there could be a draw on a flue even when the temperatures inside and outside are the same. Another could be if the inside air is moister as moist air is less dense than dry air at the same temperature and pressure.
    • CommentAuthorchuckey
    • CommentTimeAug 21st 2012
     
    if you don't have a properly engineered air intake, your fire will draw cold air along from the floor and give occupants nice cold feet. If you engineer a air vent close or behind the fire( stove) then this effect is cured.
    Frank
    • CommentAuthorCliff Pope
    • CommentTimeAug 22nd 2012
     
    " If you are building an air tight house for safety's sake you need to have an external air supply, end of story."


    That's exactly what I was saying. A good fire in even a non-airtight house can use up oxygen faster than air can leak in through doors and windows.
    That's not saying the flue isn't drawing properly - it's saying it's drawing so well it's working like a firestorm.
    • CommentAuthorfinny
    • CommentTimeAug 22nd 2012
     
    Or.. if air is drawn through the building on its way to supplying the stove it will be available to the occupants to extract some oxygen, If its path is directly to the stove it won't. Even the cleverest stove cannot seperate oxygen from air before it enters the firebox.. As mentioned previously a 5 Kw stove will move around 10-15 cubic metres of air per hour. Recommended air changes in a building per hour are at least 1. It must follow that a well installed appliance, lit or unlit will contribute to this.
    I admit that if you are building today other options are available to you. Desirable even. I would happily see an airtight envelope with MHRV with either a well sized and installed heat pump (where low carbon electricity is readily available and locally efficient) or a wood fired heating system where well seasoned sustainably managed firewood is available.
    This scenario however only applies to a small minority of properties currently and to convert many existing ones is prohibitively expensive and sometimes more energy intensive than simply starting again from scratch.
    • CommentAuthoran02ew
    • CommentTimeAug 22nd 2012
     
    Posted By: Cliff Popeor a wood fired heating system where well seasoned sustainably managed firewood is available.


    This is our circumstance; also our heat demand is very low so little point in a full biomass boiler which requires a lot of fuel, a large plant room and high set up costs. So we have opted for a smaller log burner, plus it gives up something to stare at in the evening. i take on board your point about MVHR, airtight houses, and fires, we will most certainly have to balance the system very carefully and a direct air supply may help?
    • CommentAuthorfinny
    • CommentTimeAug 22nd 2012
     
    I think in your circumstances I would be tempted to install 5Kw or under, then test. If you were happy to have a vent with direct air feed, I would install it. Ultimately, it will be up to your installer or Building control officer, they will have to be satisfied that your installation is compliant. Speak to them first.
    • CommentAuthorBeau
    • CommentTimeAug 22nd 2012 edited
     
    "Looks and cost! we need a double fronted fire, as it services two rooms."

    I have just read this thread and noticed this line. If you do need a larger stove with a closed combustion system Romotop make a stove the can be swiveled through 180 degrees and has a closed combustion system http://www.romotop.com/fireplace-type-stoves-romotop/stromboli-01-stone
    Our local stove shop had one and they loved it but sadly we did not enough space for one.

    Hope this might help
    Beau
    • CommentAuthoran02ew
    • CommentTimeAug 22nd 2012
     
    Posted By: finnyI think in your circumstances I would be tempted to install 5Kw or under, then test. If you were happy to have a vent with direct air feed, I would install it. Ultimately, it will be up to your installer or Building control officer, they will have to be satisfied that your installation is compliant. Speak to them first.


    Thanks Finny, you have been a real help

    What are the dangers of starving the fire of air? will it just go out? or somthing more sinister? will co2 be an issue?
    • CommentAuthortony
    • CommentTimeAug 22nd 2012
     
    It will produce CO (carbon monoxide) tiny ammounts cause brain damage and headaches first if you are awake, a tiddly bit more you wont wake up ever again :sad:
    • CommentAuthorfinny
    • CommentTimeAug 22nd 2012
     
    Yes if you starve a fire of air it will go out. This would be obvious, less obvious is a fire that burns well intermittently, you might often have a window ajar or trickle vents open, which would allow adequate air to feed the fire, someone could then shut windows/vents when the fire is already lit which would cause it to smoulder potentially spilling carbon monoxide into the room. As tony says above, CO has no smell and it's effect are similar to that of drinking in the early stages of poisoning, as is the next stage of headaches, drowsiness and falling asleep. Ultimately it can prove fatal, and sadly does sometimes. It really is worth having a competent installer who understands all the implications of what they are doing and who has the experience and skills to ensure your installation is both efficient and safe. They will as a matter of course install an approved CO alarm, a legal requirement.
  3.  
    Go for an external air supply connected directly to the stove. No surprise drafts, and when the fire is out there is no gaping hole in your wall letting a draft in (as long as the stove door is closed). Excellent draw on the fire.
    I have done this with a Clearview (I have no connection with them) you can connect underneath or from the rear. They even sell flexible metal pipe for the job (I didn't buy some but i wish i had).
    I think it was one of the only stoves with an external air supply kit that would fit into the existing fireplace.

    Get a CO alarm as well.

    Our stove does the hot water and is connected to the underfloor heating, so it doesn't just overheat the room it is in but warms the whole ground floor.
    (interestingly this caused a problem with the recent EPC assessment where the software would not allow the choice of solid fuel boiler in combination with underfloor heating, it assumed you would have radiators)
      IMG_0711.jpg
    • CommentAuthorstones
    • CommentTimeAug 22nd 2012
     
    Just our own experience.

    Sub 5kw wood burner (Morso 'Badger') We fitted the external air kit was we wanted to ensure sufficient combustion air when we built our reasonably airtight home.

    The outdoor air kit is a 5" flexi pipe. The internal room vent on the stove remains closed. We get a great draw (flue extends 1 metre over ridge line) and great fire.

    The house being very well insulated means that it is easy to over heat. Much more than 2 or 3 hours burining can do it. Downside is that it can act as 'the mother of all cold bridges' when not lit in cold weather. We like having a fire and the real lift it can give so are willing to live with that particular downside.

    In terms of not having an external air duct we have tried running with the outdoor duct closed and interior open. Could feel air being drawn over the floors, and noticed rapid drop in internal air quality, reduction in fore combustion, only solved by opening a window. In short, you need that extarnal air source.
    • CommentAuthoran02ew
    • CommentTimeAug 22nd 2012
     
    Great thanks all, very comprehensive
    • CommentAuthorneelpeel
    • CommentTimeAug 22nd 2012
     
    "we need a double fronted fire, as it services two rooms"

    We have a double fronted fire but wish now that I just went for a single sided (with 2nd room just seeing the rear of the fire. Double sided isn't as clean burning as you can't get the 'cleanburn' feature - at least not in the Stovax range that I bought.
    Ours doesn't pump out as much heat as some smaller single sided stoves that I've seen.
    The windows tend to need cleaning more as well as the airwash doesn't work as well.

    All depends if you need to feed from both rooms of course. Our decision was purely on aesthetics. It does look nice right enough.
    • CommentAuthoran02ew
    • CommentTimeAug 23rd 2012
     
    Great thanks all, very comprehensive Our problem may have been solved, we been recommended a "Romotop Stomboli" it has a direct air( room sealed) facility and although isn’t double sided it rotates 180 degrees, so we view it from both rooms:bigsmile: another problem solved by the community of GBF give yourselves a pat on the back.
    • CommentAuthoran02ew
    • CommentTimeAug 23rd 2012
     
    That’s a definite problem solved, by the GBF just purchased a "Romotop stomboli" (see post above for details) from www.arada.co.uk the real bonus is they are getting rid of all Romotop stock as they have lost franchise and we picked up a new £2000 fire for £1000 delivered :bigsmile: they have 2 left if anyone else is interested?
    •  
      CommentAuthorfostertom
    • CommentTimeAug 23rd 2012
     
    'this domain name is for sale'!
    • CommentAuthoran02ew
    • CommentTimeAug 23rd 2012
     
    :shamed:sorry

    Well spotted Tom. just assumed .co.uk should have put www.arada.uk.com
  4.  
    Posted By: an02ew As our only space heating for the entire home, i would think in the coldest months that it would be lit most of the time and with little effort and good quility logs i should be able to keep it alite through the night, as with the existing old broken fire she just requires a bit of tenderness in the morning and she's away, also the more modern fires are usually so full of cast iron or ceramic that they hold heat for hours even if the do go out in the middle of the night.
    So 50% of the heat goes to the room and 50% is used to stop the stove being cooled down at night by cold air dropping down the chimney. So only 50% of the heat from an 85% efficient stove ends up in the house.
    If there was an electric heater in the room and no chimney then only 43% of the kWh's would be required to keep the room at 20 degrees.

    If you build a Passive House with a 15kWh/m2.annum heating demand and use a stove to deliver the heat then the amount of kWh's used is usually closer to 30kWh/m2.annum, this is because of the cooling effect of the chimney which cools down the stove at night, people don't close the valves before going to bed because the stove is still smoking.
    • CommentAuthorfinny
    • CommentTimeAug 24th 2012
     
    <blockquote><cite>Posted By: Viking House</cite>If you build a Passive House with a 15kWh/m2.annum heating demand and use a stove to deliver the heat then the amount of kWh's used is usually closer to 30kWh/m2.annum, this is because of the cooling effect of the chimney which cools down the stove at night, people don't close the valves before going to bed because the stove is still smoking.</blockquote>

    What about a thermal mass stove of some type. Fast, clean burn, then shut down baffles keeping the heat in?
    • CommentAuthoran02ew
    • CommentTimeAug 24th 2012
     
    A valid point VH, however we cannot build to full passive standards as we have an 300 year old cottage to incorporate into our build although upgrading as best as we can EWI, triple glazing, improved airtightness, etc.
    We also have to design with some sympathy to the original structure (the cottage) i think a stove fits well. Another point is our seemingly endless supply of timber; we have a joinery workshop and a large plot which has been untended for years so much hedging timber available.
  5.  
    Posted By: finny What about a thermal mass stove of some type. Fast, clean burn, then shut down baffles keeping the heat in?
    Where are the baffles? On the stove? If so then half the heat from the thermal mass goes up the chimney.
    Other options would bo to put the stove in the sunroom and have an external quality door between the sunroom and the house that you can close when you go to bed or when the stove isn't lighting.
    or Put the stove outside the house, cover it with insulation and pipe in the heat.
    or climb up on the roof and stuff the chimney with a binbag part filled with rockwool when the stove isn't lighting, say in Nov and March!
   