    • CommentAuthorbella
    • CommentTimeAug 21st 2012
     
    19th century pine with sarking boards, 3 massive beams, all timbers visible internally (open roof), and rather fine – must stay unchanged. Bitumen felt + battens + slates over. Wall plate, rafter ends and sarking boards exposed externally at eaves, purlins and wall plates at gable end - all in good condition. Have PP to raise roof 200mm. High winds, rains horizontally. Small rodents make regular sorties along and through fibre glass quilt in attached, ventilated loft probably via “closed” chimneys.

    Rafters (150 or 100mm) to be added over existing sarking board but before detailed specification considering material for insulation in light of above. Options:-

    1.Mineral Wool – batts between 150mm rafters, 50mm boards over – rodents won’t eat/chew it but will they just wriggle along timbers/batt junctions? Weight an issue if >50mm board used over (hence 150mm rafters). u-value not good, ext membrane “drapped” over vertical battens so airtightness depends on vapour closed membrane over existing sarking boards but could/would rodents breech the membrane? Will wind blow through insulation?

    2. “Natural” – hemp/cotton batts between 100mm rafters, 100mm wood fibre board over – would rodents chew boards, wriggle along rafter/batt junctions and use batts for nesting material? Still bit heavy, u- value better but not wonderful, airtightness good. Use vapour-open membrane over existing sarking board?

    3.EPS – 100mm board between rafters and 100mm over – would rodents nibble away at it and use for nesting? Weight no problem, u-value best of three, airtightness could be secured but should membrane over sarking board be vapour open or closed?? Would another board be required over the EPS + another vapour open membrane? Would having membranes on both sides of new rafters, even if vapour open, be a bad idea?

    4.PUR - rejected on evidence of shrinkage

    How would you insulate this roof? Timbers deserve what is best for their longterm health.
  1.  
    Strip off the roof and put down 20cm SIP panels ontop of the massive timbers. Batten and tile.
    • CommentAuthorbella
    • CommentTimeAug 28th 2012
     
    Thanks for that thought. Gosh, yes, I can see the benefits. When you say "strip off the roof" did you mean strip off slates, battens and bitumen felt (latter currently laid direct on pine sarking boards)?
  2.  
    Yup, take everything off down to the supporting structure. In theory you could leave the sarking and bitumen if its difficult to remove or the sarking needs to stay in place.
    The sips come with a variety of finishes for the interior side. OSB, pine panelling, plasterboard etc. Depending on the distance of the roof span, the panels can be installed to be self supporting, anchored at the eaves.
    •  
      CommentAuthorfostertom
    • CommentTimeAug 28th 2012 edited
     
    Doesn't have to be SIPs - EPS over the sarking boards, breather felt, downslope battens, slates and battens.
    Are your 'beams' across-slope (purlins) or down-slope? Are your sarking boards thick and strong enough to span between them? If so, simply omit the new raftering.
  3.  
    How about a combination of mineral wool and multifoil? New generation products carry full BBA Certification, have Building Control and NHBC approval and can meet u-value requirements within the rafter space you suggest.
    • CommentAuthorbella
    • CommentTimeAug 28th 2012
     
    Thank you for those further thoughts.

    "Are your 'beams' across-slope (purlins) or down-slope? Are your sarking boards thick and strong enough to span between them?

    3 massive A-shape beams set into walls, then 2 big purlins resting on each side of A, then rafters set on wall plates + sarking over. Will not know how thick sarking is until roof off but could be hefty given the rest. SIP idea appeals because it answers concerns about effectively bolting down new coverings and securing the strength of the roof (primary reasons for added rafters), complexity of the work and rodents, all in one go. SIPS would span between existing rafters with light, strong, airtight, well insulated structure. Maybe I cannot see the downsides yet (yes, I know, cost is one).

    "How about a combination of mineral wool and multifoil?"

    Yes, that is a thought (I assume 150mm rafters, mineral wool between, multifoil over) and would be structurally secure. But creating a totally air-tight space of still-air between each pair of rafters top to bottom? Can even the best acheive that? Feels a big ask (having read previous posts on batten technique) for ordinary mortals who have a living to earn - but then how would I know never having been up on a roof!
    • CommentAuthorMike George
    • CommentTimeAug 28th 2012 edited
     
    Hi Bella, It's not as difficult as you may think.

    Have a look at http://www.euroform.co.uk/genx_applications.shtml for options.
  4.  
    I hope nobody minds if I post in here as I'm currently tackling a similar situation.

    Currently re-roofing an old solid masonry Georgian farm house as an emergency job - old roof crumbled, so full strip off back to A frames and purlins, 150x50 new rafters, 12mm OSB, then was thinking of 50mm EPS. Client has no money to do any more for now, but my thinking was it would be criminal to re-roof without putting something above the sarking. However, then I started thinking some more...

    I had a question about the compressive strength of the standard 50mm EPS sheets one would purchase at the local merchants, as I wanted to confirm that this (70kpa) was acceptable under a counter batten and slate roof. The response came back that this EPS was not suitable in this application as it doesn't have any fire-retardent. Could anyone point me in the right direction? Do I need to be purchasing a particular flavour of EPS for use above sarking?

    Also, I am aware that being limited to 50mm outside the sarking I am potentially limiting the roof as to what could then ultimately be placed between the rafters without risking condensation, so could anyone clarify for me, if I went with 50mm EPS above the sarking, and then a fully vapour open insulation between the rafters (something wooly?) - i.e. maintaining a fully breathable structure, am I still at serious risk of condensing, and should I therefore consider scrapping the external insulation idea altogether as I can't go any thicker and it may ultimately hamper what I can do between and below the rafters?

    I also had some head scratching about eaves detailing on to solid masonry walls, but more of that later if you like.

    I hope that makes sense.
    •  
      CommentAuthorfostertom
    • CommentTimeFeb 7th 2013 edited
     
    Sounds good. Compressive strength is fine for downslope battening over. Who says fire retardant is necessary? - routinely done similar without.

    EPS is reasonably vapour permeable, so you could later add any amount more of insulation below, and your initial above-sarking EPS shouldn't be resistive enough to create interstitial condensation. By rule of thumb the inboard vapour resistance should be 3 or 5 times stronger than the outboard resistance so ideally your later inner insulation should have stronger resistance than the initial outboard EPS, or else there should be a weak vapour barrier somewhere inboard. But you'd prob get away with it if the later inboard insulation was no less resistive than the initial outboard. - which means the later shd be EPS too, not sheep wool or anything less resistive.

    Use grey/silver 'Platinum' EPS, not the white stuff - much better insulation for pro-rata price. Don't use any other type of plastic insulation - all the others are vapour impermeable. XPS (coloured stuff) is no better insulation than Plat EPS, costs much more and is impermeable.

    Is it a vented loft under, or room-in-roof with plaster lining under the rafters? Will there be a bathroom or other water vapour generator?

    Does the roof have parapet gables, or chimney stacks or other things that the roof has to be flashed against? i.e. is there a restriction on how high you can jack up the roof's top surface? If not, then why stop at 50 thk insulation? 100 over and 150 between rafters would be top-spec. Glue it to the OSB with spray contact adhesive, not more than 30% coverage, otherwise you'll seal off your breatheability. Foam fill the EPS edge joints as you go.

    Make the OSB into your airtight (but vapour breatheable) membrane by gluing the joints. 9 OSB3 would be fine, all joints supported on a rafter or nogging, bubble-glued and screwed @ 150c/cs (polyurethane expanding gap filling glue as sold for glueing T&G chipboard flooring). Good to glue it to the rafters too. Or T&G OSB, which makes it 18thk - then edges won't need noggings.

    What pitch is the roof? - affects how many/what kind of long fixings of downslope battens you need, thro the EPS and OSB. Make sure they all hit a rafter and don't merely puncture the OSB airtight membrane.

    I use reflective type breather felt, 'draped' over, not flat under, the downslope battens. Shiny side down- adds worthwhile extra reflective insulation. Draped to not quite touch the EPS, joints well taped to keep wind from blowing on the EPS.
    • CommentAuthorSaint
    • CommentTimeFeb 7th 2013
     
    Springvale seem to offer the very solution using their products Warmsqueez and Warmsark in combination. http://www.springvale.com/products/platinum-warmsark/index. These products are "graphite enhanced" Neopor EPS so the thermal conductivity is OK, Springvale is a reputable company. Polystyrene raw material prices have seen massive hikes in the last 6 months so you can expect this to be reflected in insulation prices soon if not already.
  5.  
    Thanks Tom, thats just the reassurance I was after..

    It was actually the manufacturer who responded to my initial email enquiry regarding the compressive strength, to say that their standard EPS 70 (the stuff off the shelf in the local yard) was not suitable for external, due to no fire retardant - which did strike me as odd, as by the time that lack of fire resistance would become an issue the roof would effectively be gone? Even if it did burn, it would only result in the battens sinking on to the OSB below? I'm not sure if this is just a liability limiting response?

    There are a few challenges with this job, the first being that it was fairly unplanned, the original roof was probably 200+ years old, and basically just powder held together by wood worm and fungus. Due to a sequence of events outside my control it was now or never to rip it all off, which means I haven't really had time to get all the materials I would like organised (being "off shore" it takes time and planning to get the things you need without paying through the nose if they are anything other than standard fair). The other problem is that there is no money and being water tight is the only priority for the client. I will be paid eventually, but it could be a while so I'm just trying to strike a balance between the best thing to do for the long term future of the house and its occupants vs. not going bust!

    Architecturally there are also some restrictions, chimney stacks, gable detailing, etc, so 50mm is the best we can hope for in the current situation. I was just trying to figure out if I was going to be doing more harm than good in my enthusiasm to get something on it while we had the chance. I have no idea if it will be insulated in my lifetime, almost certainly not by the current owner, so I was just trying to make sure I did the best for whoever eventually comes to finish it off. Roof is aprox 34 deg, was thinking just to use a standard heavy gauge screw 150mm, down through batten, EPS, OSB (12mm SmartPly - off the shelf). Current configuration is rooms in roof, no bathrooms, but then the house hasn't changed much in the last 100+ years, so there isn't really any bathroom to speak of. Eventually I would assume some sort of bathroom between the two main rooms (in the same bay as the stairwell), but again this is an emergency measure I'm just trying to make the best of.

    So given the inboard to outboard resistance rule of thumb, if the rafters were eventually filled with more EPS, then a foil backed insulated plaster board, the condensation risk would be fairly low?

    With regards the eaves detailing, I have rafters coming down on to a timber wall plate set over a new RC wall beam, the original roof was just laid in to the rubble at the top of the roof, no wall plate, no straps, just sitting there for 200 years. Any suggestions on the best way to terminate rafters and insulation over a solid masonry wall 600mm thick?

    Rafters and OSB is already on (OSB sealed with silicone), it was a race to get it all done in a week, its just what to do next...

    Is there much advantage to spray glueing the EPS on to OSB?

    Not likely to find foil backed membrane in the local merchant, any tips? I'm a membrane on to sarking man usually, then counter batten over, what do you think is the advantage of draping?

    Many Thanks,

    James.
  6.  
    If you have sarking boards/insulation & counter battens then the only advantage of draping the membrane is that it allows you to face the shiny side down so that its less likely to collect dirt & degrade over time. If not using a shiny membrane then its best to lay it directly over the sarking boards/insulation & under the counter battens as this gives best windtightness.

    Some argue that this is not as watertight as water can more easily penetrate the counter batten fixings. However, draping allows water to more easily penetrate the tile batten fixings & there are generally more of these. If this is a concern then fit the membrane directly over the sarking boards/insulation & the counter battens over 50mm double sided butyl tape.

    David
    • CommentAuthorSaint
    • CommentTimeFeb 7th 2013
     
    THe fire retardant is just that. It does not make the EPS fireproof. Its good practice to use the FRA grade where large volumes of the product are to be stored together e.g. obviously at the stockists but also on site. It is certainly advisable where large areas of the foam are exposed during construction. Roofing would be a very good case. Once the construction is finished there's no reason it would be anymore of a risk or contributor in fire than any other plastic foam
  7.  
    We renovated the roof of our 18th century mill with TLX Gold (a breathable multifoil combined with a membrane) on top of the rafters, kingspan rigid board between and below the rafters and then plasterboard.
    •  
      CommentAuthorfostertom
    • CommentTimeFeb 7th 2013
     
    At 34 pitch, such screws prob fine - lots of, as cantilevers to resist all slate/tile weight sliding down the roof. Also fix opposing battens together where they meet at apex. Spray glueing the EPS keeps it in place meanwhile, and allows its edge joints to be foamed, which enables full potential of insulation without multiple open or micro-gap convection by-pass weak spots. If not shiny breather, then yes, flat on the OSB. Foil backed pbd is a total vapour barrier, so is overkill if you want the whole to be breatheable construction. If not breatheable, i.e. with strong inboard VCL, then you might as well use impermeable higher performance plastic insulation e.g. Cellotex. EPS gives best bang for buck even tho thicker, but if thickness is constrained ...