    • CommentAuthoralec
    • CommentTimeAug 25th 2012 edited
     
    Many people love zoning, but from an installers perspective there is no way to integrate zoning on small projects (less than for example 35kws) to a boiler other than on-off controls which open and close valves. Thats all very well for the heating system but its not very kind to the boiler as these require pretty well constant flow through them, and do not tolerate the variable flows created by zoning very well. Indeed to do properly you would need a Low loss header to separate the boiler Constant flow from the heating circuit (variable flow). All this adds to the install cost with no research to suggest there is any benefit...

    Weather compensation and indoor compensation offer a useful alternative at a much lower cost. And any house under 35 kws is going to be consistently used throughout so no real benefit to zoning..

    The apparent absence of products on the market that vary the heat output of the boiler to match prevailing load conditions rather suggests that there are no benefits to zoning. Indeed weather compensation controls supplied by viessmann and vaillant rather suggest that temperature profiling ( that is not turning the system off, rather lowering the temperature for set back) is the optimal way to use the technology and probably increase efficiency.

    Stable state of a regularly occupied building with temperature profiling seems to be the optimal way to run boilers...indeed my experience is showing that this way is a win win situation for installers (simplified install ) and users (stable temperatures and increased reliability)
    • CommentAuthortony
    • CommentTimeAug 25th 2012
     
    What of the almost universal system with a diverted valve or two zone valves one for hw and one for heating.
    • CommentAuthoralec
    • CommentTimeAug 25th 2012
     
    well I was really thinking about when you have a room thermostat in each room...
    • CommentAuthorPaulJ
    • CommentTimeAug 25th 2012
     
    I agree with Alec, that in a fairly small, well insulated unit, the additional cost plus the complexity and reliability issues may make zoning pointless. Also, the end user may not choose to set up the system to optimise the benefits. A programmable thermostat and thermostatic rad valves will give users controls they can understand and if set up correctly should be fairly efficient.
    • CommentAuthorcrusoe
    • CommentTimeAug 25th 2012 edited
     
    From the Roll-your-own UFH thread:

    Zoning is a different issue. Which needs a different solution for every building. When we fitted the Mk 1 version of Honeywell's CM programmable stat range back in the late '80s, they produced research, aided and abetted by the government's own, now-famous, DOE research (1 deg C drop in temp saves 10% of your fuel bill) which said that their machines, avoiding the hysteresis caused by the on-off cycles you mention, could save upwards of 15% if used sensibly. My experience with customers ever since makes me agree.

    Note caveat about different houses needing different solutions, so no right or wrong answer. However, to pick up on a couple of points: Optimising/weather compensating controls are fine, if the customer understands them. Which, picking up on Paul's point about end-users not understanding them, may be why, when we first fitted two gens of these control in the late '80s/early '90's, the complaints came thick and fast.

    As far as flows go, modern boilers modulate for a number of reasons, and those include reducing output to match demand. No after-market black box required, though you will find several, including Danfoss' BEM 5000, but these have reduced in popularity, though NatWest fitted many to their boilers. Some solutions to flow issues: By-pass radiators (sep zone?), pressure-differential by-pass valves or open loops are just three ways of overcoming the problem of low flow.

    Honeywell aside, as far as research goes, I have monitored my own customers' installations over many years to see the effect of zoning. I cannot isolate zoning as a sole ingredient in savings, nor quantify the %, as we offered many solutions including BEMs and weather compensating systems, but zoning is certainly one factor in the mix achieving reductions of 35-40% plus. (Google Ben Shirley CAT 2008). When we won an award from WILO pumps in 2011, it was for achieving savings of 55%, including 6 separate zones, in a terraced, sub-30KW/h house. The customer is very chuffed and certainly doesn't think it an expensive waste...

    PeglerYorkshire suggest savings of 30% - their own research using their itemp programmable thermostatic radiator valve, a zone-per-room set-up.

    Perhaps I should point out that, contrary to catholic procedure, wherever possible I do not connect boiler directly to radiators or UFH, which overcomes your flow objection. Why not? For the simple reason that direct connection allows only THAT boiler to heat those radiators (low loss headers are a limited exception to this, with very limited benefit). I prefer to be able to harness 'free' heat like solar, or off-peak sources with heatpumps, and integrate these into heating whichever part of the house I shall be inhabiting at a given time.

    So I am clearly from a different school of thought. Doesn't make me right or you wrong or vice-versa, but I must beg to differ in the eating of this particular cake. A single slice will do me fine - I don't want to eat the whole thing. :bigsmile:

    Paul: What reliability issues did you have in mind?
    • CommentAuthorRobL
    • CommentTimeAug 26th 2012
     
    re Tony - we have an s-plan gas boiler system in our house, and I'm sure it could be more efficient. That is, if the hot could be routed through the DHW tank first, then (in winter) rads, it would give lower temp water back to the boiler keeping the condensing boiler efficient. With s-plan (or y-plan) it's hard to keep water return temps back to a boiler low and achieve high DHW tank temps. What I'm thinking of would just use one valve, and you could have either just DHW, or DHW+heating, but there'd be no heating only option, and no ABV. Any unused heat in the DHW tank just ends up in the house anyway. Could call it RobL-plan :-)

    As an aside, we had a subtle fault with our s-plan system - the ABV (auto bypass valve) was stuck on, allowing a bit of hot to bypass straight back to the boiler. I wonder how common that is - it didn't stop the system from working at all - presumably made it less efficient again by raising return temps. I only noticed it by being a bit nerdy with the central heating. I swapped it out for a new one pdq.
    • CommentAuthoralec
    • CommentTimeAug 26th 2012
     
    The best way to lower the return temperature is of course to lower the flow temperature to the minimum required...thats what compensation controls actually do, espceially weather compensation when the outdoor sensor is acting on the burner through the boiler.. (not with a mixing valve!)

    I am finding the condensing boiler (when installed with compensation controls, which after all it has to accept as part of EU legislation) surprisingly reliable... the oldest I know is 12 years old with very limited maintenance...longer running pump times, lower average operating temperatures and constant flow seem to keep the boiler well happy..

    That compares favourably with on-of controls (of which zoning would be one) that suffer from all manner of reliability issues if you listen to domestic installers....

    I do make a point of using compensation controls...because reliability and efficiency is a big issue for my clients...I am open minded to zoning...whats needed of course is zone controls that calculate optimum heat output of boilers according to requirements... probably exists in open therm versions in Germany...not yet in the UK!
    • CommentAuthorcrusoe
    • CommentTimeAug 26th 2012 edited
     
    Alec said: "I do make a point of using compensation controls...because reliability and efficiency is a big issue for my clients...I am open minded to zoning"

    Confused - errm, so why is the thread asking if zoning is an expensive waste of time?? :confused:

    Alec said: "The best way to lower the return temperature is of course to lower the flow temperature to the minimum required...thats what compensation controls actually do, espceially weather compensation when the outdoor sensor is acting on the burner through the boiler.. (not with a mixing valve!)"

    Or you could simply connect the boiler to a suitably-sized thermal store of course, meaning it stays in condensing mode fairly permanently, as mentioned on a previous thread, and according to Messrs Keston & co, saving a further 15%.

    As far as reliability goes, we fitted the first Trisave condensing boilers I believe in 1988 or so, and are on 3rd gen product now, so the jury's out for me on CB reliability.

    Robl-plan sounds like tepid showers to me....:shocked:
    • CommentAuthoralec
    • CommentTimeAug 26th 2012
     
    well I am looking to be convinced about zoning! People love it and it does seem to offer savings, but I only see pitfalls especially after installing so many compensated boilers...which offer the same savings but at lower cost!

    I have recently been called to one to replace a grundfos pump after 4 years of use... the cause, almost certainly the zoning controls that mean the fixed head pump has worn out prematurely..

    the problem with thermal stores and condensing boilers is that the turbulence mixes the water in the store to such an extent that the return doesn't stay low... great in theory but not so good in practice...
    • CommentAuthortony
    • CommentTimeAug 26th 2012
     
    and there are also the heat losses from the store itself to account for
    • CommentAuthorGreenPaddy
    • CommentTimeAug 26th 2012
     
    alec,
    you've been a strong voice for weather compensation on a number of threads, and I keep meaning to get myself gen'd up on their ins & outs - I'm guessing there are others similarly ignorant. Rather than me googling my way through stuff, could you perhaps point me to a couple of useful sites?

    Thanks in advance.
    • CommentAuthorcrusoe
    • CommentTimeAug 26th 2012 edited
     
    tony said: "and there are also the heat losses from the store itself to account for "

    We have covered this ground before tony. Provided the store is within the heated envelope, the losses from the store will be much lower than the requirement of the property, ergo no waste.

    alec said: "I have recently been called to one to replace a grundfos pump after 4 years of use... the cause, almost certainly the zoning controls that mean the fixed head pump has worn out prematurely.."

    I would have to disagree here. Zoning has sweet fanny to do with it. Pumps don't like dead heads - period. For many, many years it has been pump manufacturer guidance, (unless you are on SMART pump technology) to fit a PDBP or other by-pass. Anyone not doing so is in clear breach and doesn't understand pump technology. I repeat, don't confuse zoning with cooked/cavitated pump replacements like this as it could happen anywhere a fixed head pump is wrongly installed, and is not a reason to not zone.

    alec wrote: "the problem with thermal stores and condensing boilers is that the turbulence mixes the water in the store to such an extent that the return doesn't stay low... great in theory but not so good in practice..."

    Well the practice seems to be panning out pretty well for me - see my first post in this thread. This phenomenon was pointed out in a previous thread. Read the thread and you will see that I had recently fitted a Qudos 28, suspecting, but not knowing, that it would be of benefit. The benefit was verified by Keston boilers. viz:

    General: Neccessary conditions for condensing boilers to operate optimally

    http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4771

    Not agreeing on very much here are we :smile:
    • CommentAuthoralec
    • CommentTimeAug 26th 2012 edited
     
    this is the best I can find:

    http://www.pmengineer.com/CDA/Archives/cdd55d5472298010VgnVCM100000f932a8c0

    Outdoor reset is the american for weather compensation and it refers to standard efficiency boilers.

    I agree there is little on the web about weather compensation, but it seems to be sensible to install boilers in the way they would be installed in Germany, as out door sensors are mandatory there...

    the most proactive manufacturer is Viessmann on there website there is a document about weather compensation...and they also have one that explains the benefits of this control strategy to enhance boiler efficiency...
    • CommentAuthorSeret
    • CommentTimeAug 27th 2012
     
    Posted By: tonyand there are also the heat losses from the store itself to account for


    Outside the heating season they'll be no more than a DHW cylinder anyway (in fact probably less due to the large tank size and better insulation), and inside the heating season they'll be zero. So you've got a small loss compared to a combi, but you gain a lot of flexibility, including easily adding low-carbon heat sources.
    • CommentAuthorcrusoe
    • CommentTimeAug 27th 2012 edited
     
    Couldn't have put it better myself Seret. I like sunshine in my UFH. And that's a pretty well no-carbon heat source.

    Anyone imagine how they would run district heating schemes (see concurrent thread) without zoning? :shocked:
  1.  
    Posted By: crusoeAnyone imagine how they would run district heating schemes (see concurrent thread) without zoning?:shocked:" alt=":shocked:" src="http:///newforum/extensions/Vanillacons/smilies/standard/shocked.gif" >


    Easy - District boiler house sends out hot water to each block of flats with the flow adjusted for resistance. The heated water starts at the top floor and proceeds downwards and until a few years ago there were no controls and payment was made based on the sq.M of the flat. The top floors got too hot so people would open the windows and the bottom floors could get a bit cold so woolly jumpers were employed.
    Now modifications have been made (a parallel bypass pipe on each rad. installed) so that an individual radiator can be turned off without affecting the remainder of the system. Billing is now done by inefficient heat sensors on each rad.
    No zoning - no one likes the system, its expensive to run and the owners are stuck with it as they are not allowed to opt out. :sad:
    • CommentAuthorcrusoe
    • CommentTimeAug 27th 2012
     
    Easy indeed, mine work somewhat differently. Perhaps I should have included the words 'effective and efficient' in my last sentence...:confused: