<?xml version="1.0" encoding="utf-8"?>
	<rss version="2.0">
		<channel>
			<title>Green Building Forum - Help! how to work out heating demand from SAP?</title>
			<lastBuildDate>Tue, 09 Jun 2026 12:08:25 +0100</lastBuildDate>
			<link>https://www.greenbuildingforum.co.uk/newforum/</link>
			<description></description>
			<generator>Lussumo Vanilla 1.0.3</generator>
			<item>
		<title>Help! how to work out heating demand from SAP?</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=9545&amp;Focus=155894#Comment_155894</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=9545&amp;Focus=155894#Comment_155894</guid>
		<pubDate>Sun, 09 Sep 2012 10:09:57 +0100</pubDate>
		<author>targer</author>
		<description>
			<![CDATA[Hi all, <br /> I am trying to work out what size air source heat punp I require for my new build. I have tried to work out the heat demand from the SAP calcs but not sure if I am doing it correctly? The house is a 2 storey ICF with appx 305M2 floor area. I have slightly better insulation spec than was specified for the SAP rating. Figures are appx walls = 0.16, windows = 0.7, roof = 0.13.  I have UFH downstairs and a PAUL heat recovery unit.<br /><br />Its a while since I worked out some figures but if I remeber I was getting a figure around 4.5KW. I recently spoke to someone about a unit and they said on the size of house I would need a 25KW unit!!!  I thought that was OTT? <br /><br />I would appreciate any help or pointers or any other ideas regards how to heat the house for that matter.  I am on the Isle of Skye so gas etc is out.<br /> I really need to get my finger out and decide what I am going to do regards heating/hot water.<br />Thanks for any input.  Cheers W.]]>
		</description>
	</item>
	<item>
		<title>Help! how to work out heating demand from SAP?</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=9545&amp;Focus=155901#Comment_155901</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=9545&amp;Focus=155901#Comment_155901</guid>
		<pubDate>Sun, 09 Sep 2012 12:36:10 +0100</pubDate>
		<author>Gavin_A</author>
		<description>
			<![CDATA[where in the country are you / what's the lowest external air temperature, and what temperature are you wanting to maintain the house at?<br /><br />are you planning to have a secondary heat source, eg a wood stove? This would allow for a smaller heat pump as the wood stove could be used to provide extra heat on the coldest 5-10% or so of days, while the heat pump did it all the rest of the time.<br /><br />Do you plan to have some form of a buffer tank? This can seriously reduce the size of heat pump you need, as it can smooth out the peaks of demand eg on first heating in the morning, so you can use a smaller heat pump.<br /><br />stuff like this is important in determining what size heat pump you'd be ok with, as well as the actualy sap estimates.]]>
		</description>
	</item>
	<item>
		<title>Help! how to work out heating demand from SAP?</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=9545&amp;Focus=155902#Comment_155902</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=9545&amp;Focus=155902#Comment_155902</guid>
		<pubDate>Sun, 09 Sep 2012 12:37:14 +0100</pubDate>
		<author>Nick Parsons</author>
		<description>
			<![CDATA[Have a search on here. This has certainly been discussed at length before.]]>
		</description>
	</item>
	<item>
		<title>Help! how to work out heating demand from SAP?</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=9545&amp;Focus=155903#Comment_155903</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=9545&amp;Focus=155903#Comment_155903</guid>
		<pubDate>Sun, 09 Sep 2012 12:56:11 +0100</pubDate>
		<author>targer</author>
		<description>
			<![CDATA[Gavin_A - I am the Isle of Skye. It never gets really cold, probably about -6-7 at worst. It's wind and rain we get not cold!!  Probably looking for 20 for a rough internal temp.<br /> I had planned on a stove but after reading some things on here about I'm not so sure.  I would need a room sealed stove as building as air tight as possible. Had been reading about the flue being a nice cold bridge. Now just thinking is it really worth the cost/effort to install.<br />Yes, planned to use a buffer tank or tank in tank.<br /><br />Nick - yes did look and that's where I originally seen mention of box - x + box - y + z = demand! or something along that kind of idea.<br /><br />Thanks for the input.<br /><br />I just felt 25KW heat punp seamed way too big. I would rather it is oversized but not massively so.]]>
		</description>
	</item>
	<item>
		<title>Help! how to work out heating demand from SAP?</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=9545&amp;Focus=155905#Comment_155905</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=9545&amp;Focus=155905#Comment_155905</guid>
		<pubDate>Sun, 09 Sep 2012 13:37:36 +0100</pubDate>
		<author>Paul in Montreal</author>
		<description>
			<![CDATA[&lt;blockquote&gt;&lt;cite&gt;Posted By: targer&lt;/cite&gt;I just felt 25KW heat punp seamed way too big. I would rather it is oversized but not massively so.&lt;/blockquote&gt;<br /><br />That is massively oversized for your climate and build-type. My virtually uninsulated house of 267m2 heated area only requires about 15kW at an external temperature of -23C.<br /><br />You're better off using a program like hot2000 to calculate the heatload <a href="http://canmetenergy.nrcan.gc.ca/software-tools/hot2000/84" target="_self" rel="nofollow">http://canmetenergy.nrcan.gc.ca/software-tools/hot2000/84</a><br /><br />Paul in Montreal.]]>
		</description>
	</item>
	<item>
		<title>Help! how to work out heating demand from SAP?</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=9545&amp;Focus=155907#Comment_155907</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=9545&amp;Focus=155907#Comment_155907</guid>
		<pubDate>Sun, 09 Sep 2012 14:16:15 +0100</pubDate>
		<author>WillInAberdeen</author>
		<description>
			<![CDATA[Our house is 170ish m2 heated area, 1800s granite, so nowhere near as insulated or airtight as yours despite ongoing  efforts. We have 16kw Ashp which is plenty big enough.<br /><br />various parties tried to size the ashp from calculated loads, but in the end we went with 16kw cos it was only few hundred quid more than the 11 kw model.<br /><br />One installer proposed an ashp sized to match the total capacity of all our radiators, which are oversized, so that proposal was for very big ashp.<br /><br />Beware ashp ratings are quoted at standard +7 oC outside temp. At real winter temp, they will actually deliver about half their name plate rating, depending how cold it gets.]]>
		</description>
	</item>
	<item>
		<title>Help! how to work out heating demand from SAP?</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=9545&amp;Focus=155919#Comment_155919</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=9545&amp;Focus=155919#Comment_155919</guid>
		<pubDate>Sun, 09 Sep 2012 17:15:05 +0100</pubDate>
		<author>kotpat</author>
		<description>
			<![CDATA[Hi<br /><br />Please find the Microgeneration details - which advise you should not use the SAP's to design the heatloss, but to use <br /><br />the microgeneration have a excel spreadsheet tto large to attache<br /><br />email kotpat@btinternet.com and will send you a copy<br /><br />kotpat]]>
		</description>
	</item>
	<item>
		<title>Help! how to work out heating demand from SAP?</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=9545&amp;Focus=155921#Comment_155921</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=9545&amp;Focus=155921#Comment_155921</guid>
		<pubDate>Sun, 09 Sep 2012 17:22:17 +0100</pubDate>
		<author>targer</author>
		<description>
			<![CDATA[Thanks Kotpat, will email. Cheers]]>
		</description>
	</item>
	<item>
		<title>Help! how to work out heating demand from SAP?</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=9545&amp;Focus=155926#Comment_155926</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=9545&amp;Focus=155926#Comment_155926</guid>
		<pubDate>Sun, 09 Sep 2012 19:09:33 +0100</pubDate>
		<author>RobinB</author>
		<description>
			<![CDATA[Based on what you're said it seems 25kw  OTT. For similar spec house - ICF, similar windows etc. but just under 200m2  in West Yorkshire we are using a 5kw ASHP.  We do have a small air-sealed stove but don't actually need it to keep warm.]]>
		</description>
	</item>
	<item>
		<title>Help! how to work out heating demand from SAP?</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=9545&amp;Focus=155978#Comment_155978</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=9545&amp;Focus=155978#Comment_155978</guid>
		<pubDate>Mon, 10 Sep 2012 09:12:30 +0100</pubDate>
		<author>qeipl</author>
		<description>
			<![CDATA[Targer,<br /><br />After I built my house I recorded the energy use over a week and compared it with the SAP figures and my own calculated figures. According to SAP I should have used twice the amount of energy that I actually used whereas my own spreadsheet was within 10% of reality. As others have said, don't use SAP.<br /><br />If I set the temperature difference to 30C (minus 10 outside; 20 inside) my home-made spreadsheet comes up with a heat loss of 59.3W/m^2 for my house which has higher u-values than yours (0.18) and is a stupid shape (only 100m^2 but high ratio of external wall & roof to volume).<br /><br />Multiply 305 (your floor area) by 59.3 gives a total heat loss of 18kW. Your house should be less than that.<br /><br />I'm on Skye as well so weather conditions should be similar.<br /><br />My house is heated primarily by the sun.<br />From May to September the UFH doesn't run at all.<br />In April/October an 800W air to water heat pump collects solar energy from inside the house and redistributes it via UFH as required.<br />This works even in the depths of winter if the day is sunny enough.<br />In the proper cold and dark I have a 10kW solid fuel boiler in my workshop (so no cold bridge out of the house) that heats rads in two rooms from where the heat pump takes warm air and redistributes via UFH.<br /><br />I don't know of anyone on Skye who relies solely on an ASHP. Most people have a stove of some sort (possibly for aesthetics as much as heating). I'd always want some sort of back-up in case the heat pump failed. Maybe a big immersion heater in your buffer tank would do the job.<br /><br />Hope that helps,<br /><br />Malcolm]]>
		</description>
	</item>
	<item>
		<title>Help! how to work out heating demand from SAP?</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=9545&amp;Focus=155994#Comment_155994</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=9545&amp;Focus=155994#Comment_155994</guid>
		<pubDate>Mon, 10 Sep 2012 11:38:14 +0100</pubDate>
		<author>targer</author>
		<description>
			<![CDATA[Hi Malcolm,<br /><br />Thanks for the reply.<br />That sounds a lot better than 25kw!<br />Unfortunately my house was not designed to have any real solar gain.  The house at present has been plastered and the internal temps are around 16.5 with humidity of 85!  I am keen to get the MVHR up and running.<br /><br />Are you below the road at Drynoch by any chance?  I take it you are using an ecocent? I spoke with esp and they said someone on skye was using one very sucessfully?  They did say I could try and link it into my PAUL unit but I have yet to discuss this with the supplier. <br /><br />I have to admit the stove was more for asthetics than purpose as you say and that's what makes me think is it really worth the effort.<br /><br />Cheers<br />Willie]]>
		</description>
	</item>
	<item>
		<title>Help! how to work out heating demand from SAP?</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=9545&amp;Focus=156047#Comment_156047</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=9545&amp;Focus=156047#Comment_156047</guid>
		<pubDate>Mon, 10 Sep 2012 17:51:19 +0100</pubDate>
		<author>qeipl</author>
		<description>
			<![CDATA[Yes, I'm in the wooden shed at the end of the loch, and yes, I had the first ecocent on Skye (I think).<br />I haven't investigated how it works with MVHR but Nick at ESP seems to be pretty clued up - I'd be happy to follow his advice.]]>
		</description>
	</item>
	<item>
		<title>Help! how to work out heating demand from SAP?</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=9545&amp;Focus=156048#Comment_156048</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=9545&amp;Focus=156048#Comment_156048</guid>
		<pubDate>Mon, 10 Sep 2012 18:13:25 +0100</pubDate>
		<author>DarylP</author>
		<description>
			<![CDATA[Targer,<br /><br />Box 39 in SAP2009 should be January's heat loss (normally the biggest). (W/k)<br />Multiply this by the degrees of heating required (-3 to +21 = 24 degrees), and this gives you the load in Watts.<br /><br />Your heating system should be designed to need to meet this demand.<br /><br />Cheers...<img src="/newforum/extensions/Vanillacons/smilies/standard/smile.gif" alt=":smile:" title=":smile:" />]]>
		</description>
	</item>
	<item>
		<title>Help! how to work out heating demand from SAP?</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=9545&amp;Focus=156053#Comment_156053</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=9545&amp;Focus=156053#Comment_156053</guid>
		<pubDate>Mon, 10 Sep 2012 20:33:51 +0100</pubDate>
		<author>Dantenz</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: Gavin_A</cite>Do you plan to have some form of a buffer tank? This can seriously reduce the size of heat pump you need, as it can smooth out the peaks of demand eg on first heating in the morning, so you can use a smaller heat pump.</blockquote><br />Not sure I understand or agree that a buffer tank, which is usually fairly small in capacity of 100 litres or so can reduce the size of the heat pump.  My understanding is that heat pump buffer tanks are mostly used for system hydraulics and flow rate purposes and being of such relatively small volume offer very little in the way of thermal storage.]]>
		</description>
	</item>
	<item>
		<title>Help! how to work out heating demand from SAP?</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=9545&amp;Focus=156056#Comment_156056</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=9545&amp;Focus=156056#Comment_156056</guid>
		<pubDate>Mon, 10 Sep 2012 20:46:44 +0100</pubDate>
		<author>Nick Parsons</author>
		<description>
			<![CDATA[Heat pump buffers are as big as you make them. Yes, many suppliers suggest 100 ltr, but one installer I know won't use less than 300 ltr. If you are looking to buffer heat so as to benefit from E7, you'd want more than that, I think.]]>
		</description>
	</item>
	<item>
		<title>Help! how to work out heating demand from SAP?</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=9545&amp;Focus=156064#Comment_156064</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=9545&amp;Focus=156064#Comment_156064</guid>
		<pubDate>Mon, 10 Sep 2012 21:17:56 +0100</pubDate>
		<author>Dantenz</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: Nick Parsons</cite>Heat pump buffers are as big as you make them. Yes, many suppliers suggest 100 ltr, but one installer I know won't use less than 300 ltr. If you are looking to buffer heat so as to benefit from E7, you'd want more than that, I think.</blockquote><br />From memory I think I'm right in saying that buffers tanks are sized at around 10 litres per kW output of heat pump  and thermal stores upwards of 50 litres per kW.]]>
		</description>
	</item>
	
		</channel>
	</rss>