    • CommentAuthorcullym
    • CommentTimeOct 12th 2012
     
    found this while doing some research. Might prove useful - I'm still trying to digest the info :-)

    http://www.greenbuildingadvisor.com/blogs/dept/musings/are-dew-point-calculations-really-necessary
    •  
      CommentAuthorfostertom
    • CommentTimeOct 12th 2012 edited
     
    That is quite an eye opener, and a lot to digest. It starts with easy for-everyman style, but soon falls into heavier stuff - inevitably.

    It seriously questions the Euler-diagram based graph-drawing programs that we (and Bldg Regs) commonly rely on. It gets closer, by manual/approximation means, to the fuller WUFI-type model, which acknowledges that 95% of the moisture moving through a building construction comes from outdoors, not solely from indoors as Euler assumes.

    The Euler-derived 'necessity' to use internal VCLs (vapour control layers) stems from that indoor-source assumption. The alternative 5:1 breathing-wall rule-of-thumb seems to work in UK climate, without VCL, and probably the Euler-type check that we still run on it is irrelevant.

    In different e.g continental Germany not maritime UK climates, experience mandates more rigorous design/analysis - hence WUFI from Germany, and products like Pro-Clima 'intelligent' external vapour control membranes (note - 'controlling', not 'blocking'), which are really overkill for UK climate.
    •  
      CommentAuthorSteamyTea
    • CommentTimeOct 13th 2012 edited
     
    Think we have covered most of this on the Irish Study. It is why I took the stats approach to the problem (and it worked on my roof (N=1)). This article touched on it by using the average (which average, I know which one I would use) for Dec, Jan and Feb as your worst case temperature. I seem to remember then I looked at the Climate Zone (called Climate Regime over here) methodology it was a pretty good descriptor of what is really happening.
    Does boil down to better insulation and airtightness though and the choice of materials, basic stuff but hard to implement.

    Tom
    I wish I understood what you mean when you talk of "Euler-derived" and "Euler-diagram", please explain, just to set the scene?:confused:
    •  
      CommentAuthorfostertom
    • CommentTimeOct 13th 2012
     
    Just googled it and it means something different from what I thought - so cancel that, and I'll find the correct term. Go back and edit all prev references to euler, for the archive?!
    •  
      CommentAuthorSteamyTea
    • CommentTimeOct 13th 2012
     
    Posted By: fostertomJust googled it and it means something different from what I thought - so cancel that, and I'll find the correct term. Go back and edit all prev references to euler, for the archive?!

    Good man, we will make a scientist of you yet. :wink:
    •  
      CommentAuthorfostertom
    • CommentTimeOct 13th 2012
     
    Yum yum
    • CommentAuthorcullym
    • CommentTimeOct 13th 2012
     
    ST do you have a link or can you provide more details on the approach you used? A lot of this is over my head at the moment but I'm working to gain an understanding of it. I've mentioned on another thread that I might have to use IWI on some walls so understanding how all this works is critical.
    •  
      CommentAuthorSteamyTea
    • CommentTimeOct 13th 2012
     
    Was while back I did it for a giggle when Mike and Damon started talking about it.

    Seem to remember that I created a matrix of humidity and temperature ranges for an area (easy enough to get that data for me), from that I calculated the probability of reaching the dew point (RH being >100%, though Ed pointed out that it can happen lower down, so may have used RH>95%).
    That then gave the ambient conditions and you can work out the probability of when those conditions exist (stratify the data by month or week or whatever time you like).
    Internal conditions were just the same, but more assumption (I have a temperature and RH data logger so mine would be spot on for my house). That gives you the probability of cause internal condensation.

    Then it is just a case of matching the two:

    Ambient, Internal
    Yes,Yes
    Yes,No
    No,Yes
    No,No

    Disregard the probabilities of No,No, as there is no risk at all there, and the Yes,Yes as you can't do anything about that (except change lifestyle/ventilation/insulation/materials). Then start looking at the probabilities of the other 2 and, assuming you know the Thermal Inertia (how long does it take to change temperature) of your house/wall you can see if any of the conditions match i.e. is it cold enough behind the plasterboard (or where you deem the problem may be) to cause condensation for both the internal and external conditions (that is the worse case).
    What you should end up with is the fraction of time that condensation may happen. Compare that to the times it will not happen (or times that it is a set temperature above or RH below a safe level) and then assess the risk. If it happens, for say, 30 percent of the time, you probably have a problem, it if 2% of the time, you probably don't.
  1.  
    Bit I struggle with:
    I'Ll try to explain

    Just because theres a point in the walls which is below DP, means vapour will condense, but doesn't mean water will build up. Because if theres a route to a point with even lower water vapour pressure (like outside) then the water will re evaporate and diffuse outside.

    I dont understand how DP calcs take account of this, i suspect they just say (if below DP then fail) which seems bit simplified.

    Example: lath and plaster stone walls. The vapour resistance (stone) is outboard of the thermal resistance (air gap) so water should condense. But there are enough paths for the water to evaporate and diffuse to outside through mortar and air leaks.

    I' m not expert / qualified in this, explanations would be welcome!
    •  
      CommentAuthorSteamyTea
    • CommentTimeOct 13th 2012
     
    Posted By: WillInAberdeeni suspect they just say (if below DP then fail) which seems bit simplified

    That is exactly how I see it too. Why choice of material is so important.
    Does not change the probability of it happening, though changes the risk. None of us actually worry about condensation rotting the window panes, though we may worry about the wooden frames.

    So there are at least 2 risks here, how often liquid water forms and when it does damage can if cause.
    • CommentAuthorcullym
    • CommentTimeOct 13th 2012
     
    Speaking of liquid water how do you then take into account moisture on the exterior from say rain. Is it assumed that this would just dry to the outside?
  2.  
  3.  
    Great link Will. I particularly like the pic where someone has insulated the nails
    • CommentAuthortony
    • CommentTimeOct 13th 2012
     
    I think that that is North American based research and problems.....
    • CommentAuthorMike George
    • CommentTimeOct 13th 2012 edited
     
    Yes North America, but the criticism of the prediction method is just as relevant here isn't it? It's basically saying that a build up of condensation which occurs at the dew point (which may be within insulation for example) will subsequently re- evaporate and continue to migrate until it comes up against a more significant barrier.

    Of course this depends where the VB (or VCL) is. It could be the vinyl surface of a painted wall which has been internally insulated, or a rich waterproofed cement layer of external rendering
    • CommentAuthorcullym
    • CommentTimeOct 13th 2012
     
    Ok so I managed to find some data on Weather Underground for my area. I've created a matrix for Air Temp, Humidty and Dewpoint. I've used the daily averages for these. If I understand you correctly SteamyTea the areas marked in red in the attached pdf are the external conditions I need to worry about.
    •  
      CommentAuthorSteamyTea
    • CommentTimeOct 14th 2012
     
    Looks like it. Are the numbers the 'count' of days that dew can form or the temperature that dew forms?
    • CommentAuthorcullym
    • CommentTimeOct 14th 2012
     
    The numbers are the temps that dew forms. I've modified the sheet since and set up a pivot table which shows the count. I've filtered out the RH below 95 and took out the year grouping. Data is only from Oct last year to yesterday. I have to see if I can find another weather station with more data.
    PDF of updated sheet attached. I presume I should do something similar for indoor but I have no actual data for this. What would you suggest to use for an approximation? I think it would be a good time for me to get some of those iButtons. The next 3 - 4 months is heating season in our house so it would be a good time to capture the data.
    •  
      CommentAuthorSteamyTea
    • CommentTimeOct 14th 2012
     
    Yes get some iButtons, they take the guessing out of it and can be used for all sorts of experiments.

    So you have 42 days where the conditions where met, or about 11% of the time, pretty low and considering that it is not 42 consecutive days there is probably not much of a problem from ambient humidity turnign to water.
    •  
      CommentAuthorfostertom
    • CommentTimeNov 2nd 2012 edited
     
    Posted By: SteamyTeaTom
    I wish I understood what you mean when you talk of "Euler-derived" and "Euler-diagram", please explain, just to set the scene?:confused:" alt=":confused:" src="http:///forum114/extensions/Vanillacons/smilies/standard/confused.gif" >
    Posted By: fostertomJust googled it and it means something different from what I thought - so cancel that, and I'll find the correct term
    It's Glazer not Euler - oh well, 'er' 40% right
    • CommentAuthorSprocket
    • CommentTimeNov 2nd 2012
     
    Tom, "Euler" ?.. for the sake of the angles maybe?
    Is there something about your background (that I don't know about) there?
    Sounds very 3D :-/
    You're not one of those simulation people are you? ;-)
    •  
      CommentAuthorSteamyTea
    • CommentTimeNov 2nd 2012
     
    Posted By: fostertomIt's Glazer

    You will have to enlighten me as it is not a technique I am familiar with.
    • CommentAuthorEd Davies
    • CommentTimeNov 3rd 2012
     
    Googling "Glazer diagram" suggests "Glaser diagram". First sensible hit for that is to a Google Book which says:
      glaser.png
    •  
      CommentAuthorfostertom
    • CommentTimeNov 3rd 2012 edited
     
    I dunno - I saw Mark Siddall say Glazer on http://www.aecb.net/forum/index.php/topic,3689.0.html so I knew that must be it!
    • CommentAuthorMike George
    • CommentTimeNov 3rd 2012 edited
     
    Chopped from a conversation I've been involved in here http://www.linkedin.com/groupItem?view=&gid=3612272&type=member&item=171377696&qid=fad9e01b-d3b0-448f-b9ff-f6046a03b65d&trk=group_most_popular-0-b-ttl&goback=%2Egmp_3612272

    The Glazer method is that used for most simple Condensation Risk Analyses.

    Referring to the Glaser method s, BS EN 13788 states:

    'This standard gives calculation methods for:

    a) The internal surface temperature of a building component or building element below which mould growth is likely, given the internal temperature and relative humidity–the method can also be used to assess the risk of other surface condensation problems.

    b) The assessment of the risk of interstitial condensation due to water vapour diffusion. The method used assumes built-in water has dried out and does not take account of a number of important physical phenomena including:

    • the dependence of thermal conductivity on moisture content;
    • the release and absorption of latent heat;
    • the variation of material properties with moisture content;
    • capillary suction and liquid moisture transfer within materials;
    • air movement through cracks or within air spaces;
    • the hygroscopic moisture capacity of materials.

    Consequently the method is applicable only to structures where these effects are negligible.'

    In terms of simulating such conditions Hygrothermal simulation (such as WUFI) is a more accurate method for evaluating the combined risk of water and vapour transfer within such wall structures.

    ‘European standard EN 15026 provides minimum criteria for simulation software used to predict one-dimensional transient heat and moisture transfer in multi-layer building components exposed to transient climate conditions on both sides. The standard lists model equations and pertinent material properties which shall be used for computing heat and moisture transport phenomena. These model equations allow for the following storage and transport phenomena:

    • heat storage by the dry materials and the absorbed water,
    • heat transport by moisture-dependent thermal conduction,
    • latent heat transfer by vapour diffusion,
    • moisture storage by vapour sorption and capillary forces,
    • moisture transport by vapour diffusion,
    • moisture transport by liquid transport (surface diffusion and capillary flow) and the following boundary conditions:
    • indoor and outdoor temperature,
    • indoor and outdoor humidity,
    • solar and long-wave radiation,
    • precipitation (normal and driving rain),
    • wind speed and direction.

    So a much more accurate method of evaluation.

    Hope this helps