    In Cornwall Today magazine this month they ran quite a big piece on Wind Turbines, one of the guys (Danny Mageean) putting the case against WT's made the following comment:

    "The National Grid operates back-up generators to cover the sudden and unexpected loss of wind power to avoid power cuts. Last year one electricity generator admitted that for every 1MW of wind electricity penetrating the grid, there was at least 0.9MW of back-up operating. These back-up generators are gas-fuelled, producing carbon dioxide."

    The wording of this seems to me to be a bit disingenuous as surely the back-up needs to be available not operating?
    He actually makes a strong case against W.T's but some of the figures seem high eg:

    "Costs of back-up generation are estimated to rise from £18m currently to £400m in 2020"

    Really? if all this is true then the more I read about W.T's the more uneasy I become about the:

    "125m industrial white elephants changing the face of Cornwall"
    • CommentAuthorSeret
    • CommentTimeOct 22nd 2012 edited
     
    The grid does operate a certain amount of spinning reserve and backup, but this isn't entirely to support wind as you need to cover faults and maintenance anyway, not to mention following demand. The OCGTs he mentions get up and synced very fast, that's what they're there for so I wouldn't imagine they don't get used as spinning reserve and so aren't burning fuel while waiting for action. Spinning reserve involves having plants with longer response times hot but with a reduced load, so they can ramp up relatively quickly. They may not be operating at full efficiency due to the reduced load, but the amount of extra fuel consumed by that slightly lower efficiency isn't going to be huge.

    This article on the Guardian directly rebuts the claims you mention, using the magic of real data:

    http://www.guardian.co.uk/environment/blog/2012/sep/26/myth-wind-turbines-carbon-emissions
    • CommentAuthorEd Davies
    • CommentTimeOct 22nd 2012
     
    Quoted By: candlemakerLast year one electricity generator admitted that for every 1MW of wind electricity penetrating the grid, there was at least 0.9MW of back-up operating.

    That doesn't make clear whether that 0.9 MW of back up is actually using fuel for 0.9 MW or using, say, 0.1 MW's worth in order to be able to produce 0.9 MW at very short notice. Anyway, what Seret says.
    •  
      CommentAuthorfostertom
    • CommentTimeOct 22nd 2012
     
    The Guardian article is v interesting - puts to rest the 'fact' I had in mind that back-up is a necessary accompaniment to unpredictable renewable generation, until such time as major storage becomes possible e.g. by utilising the battery bank of a large national fleet of electric vehicles - at which time renewables would finally come of age.

    Now it seems that is not so - that the backup pretty much already exists, for TV tea-break spikes, and little or no new back-up is required per renewable installation.
    • CommentAuthorSeret
    • CommentTimeOct 22nd 2012 edited
     
    That's about the size of it Tom. Papers I've seen project that impact from renewables in the grid should be pretty minor up to about 20%. So a long way to go yet before it starts to become a big issue for the UK.

    After all, the grid is designed to swallow variation in demand, why should it have any real problem coping with variation in supply? Flexibility has always been a feature. As the article mentions, weather forecasting is getting a lot better, so wind can be planned for fairly well, and as we install more it only serves to even out the smaller and more unpredictable lumps.

    The grid's main headache with accommodating new renewables is providing the connections, not balancing the load AFAIK.
    •  
      CommentAuthorfostertom
    • CommentTimeOct 22nd 2012
     
    This 'myth' has been trotted out forever incl on GBF - incredible it's never been disputed AFAIK.
    •  
      CommentAuthorSteamyTea
    • CommentTimeOct 22nd 2012 edited
     
    Not read the article, in fact, never read it at all after the front cover had a picture of Portreath with the caption 'Taste the Sea'. Anyone that has been there knows that it is something else beginning with S that you can smell and taste.

    Load balancing is well understood, as is the variation in grid supply and demand.
    Now I would never claim that for every MWh of renewable (remember that it is not unlimited) supplied there is a corresponding reduction in FF generation.
    But what it can do, and does do, is allow for the grid to become overall 'cleaner', but it is early days yet and we do not have enough renewables connected to cause a problem.

    This is what is happening at the moment as an example:
    Demand: 43455MW
    11:45:00 GMT
    Frequency: 50.049Hz
    11:49:45 GMT

    System Transfers

    N.Ireland to Great Britain: -254MW
    France to Great Britain: -4MW
    Netherlands to GB: 992MW
    22/10/2012 11:30:00 GMT

    North-South: 6087MW
    Scot - Eng: 1329MW
    20/10/2012 05:02:00 GMT

    And

    fossil @ 78% 34108MW [CCGT, COAL, OCGT, OIL]
    import @ 2% 992MW [INTEW, INTFR, INTIRL, INTNED]
    nuclear @ 14% 6014MW [INTFR, NUCLEAR]
    renewable @ 2% 1000MW [NPSHYD, WIND]
    storage @ 3% 1226MW [PS]
    zero-carbon @ 16% 7014MW [NPSHYD, NUCLEAR, WIND]

    If we do get somewhere around 20% renewable penetration, and the weather forecast system totally breaks down, and we have an unexpected severe drop in temperature at night, spasmodically for weeks and weeks, then yes, we have a problem with spinning reserves (well actually we don't as they just become part of the supply).

    Spinning and hot reserves (they are different) do not have a linear relationship with capacity (anyone who lives off grid will know about this). So at the small scale you need a lot more than at the larger scale because not everything fails at the same time.
    • CommentAuthorSeret
    • CommentTimeOct 22nd 2012 edited
     
    Posted By: SteamyTea
    Now I would never claim that for every MWh of renewable (remember that it is not unlimited) supplied there is a corresponding reduction in FF generation.


    The regression line in that bloke's graphs was at about 0.9, which I suspect is in the right ballpark.
    •  
      CommentAuthorSteamyTea
    • CommentTimeOct 22nd 2012
     
    Are we talking about this chart, based on today's penetration of both gas and wind.
    Without seeing the underlying data I can't really comment on the regression line and if it is a best fit. Does seem strange that they have used a straight line though (the R^2 is pretty low at 0.25)
    Also have they used installed capacity of both the gas facilities and the wind facilities, or MWh or a mixture of both at the half hour level?
    I find it hard to believe that you need so much back up (the Cornwall Today article not the Guardian one).
      This Chart.jpg
  2.  
    Back up generation is not for a wind turbine going offline as wind is quite predictable in the short term and can easily be made up from existing pumped storage systems. What we do need spinning reserve for is the sudden loss of a nuclear or coal fired station. Another good argument for decentralized generation
    •  
      CommentAuthorSteamyTea
    • CommentTimeOct 22nd 2012
     
    What is really needed is more storage, say 5 to 10% of the peak nation's need, so about 4 to 8 GWh that can deliver at double that rate. If they can't sort the problem out in half and hour then it is time to start cutting off the supply to the extremes (so I will get hit). That way we do not have to totally replay the national grid which we would have to do with decentralised generation.

    Question is with the wholesale price being around £50 to £100 MWh, how much are we willing to pay for this safety net, double, quadruple?
    Hard decision.
    • CommentAuthorjms452
    • CommentTimeOct 22nd 2012
     
    Interesting discussion.

    I was looking for a graph of CCGT efficiency with load to go over the same point as raised in cornwall today but without much success.

    I did find this quote: "CCGT plants offer flexible operation. They are designed to respond relatively quickly to changes in electricity demand and may be operated at 50% of the nominal capacity with a moderate reduction of electrical efficiency (50–52% at 50% load compared to 58–59% at full load)."
    http://www.iea-etsap.org/web/E-TechDS/PDF/E02-gas_fired_power-GS-AD-gct.pdf

    Even this rather extreme case of (i.e a 100% to 50% rediction in gas turbine output dropping efficiency by 8%) would suggest that reducing your gas turbine output is at least a efficient as storing the energy (about 20% loses with pumped storage I believe).

    This makes the recent announcement of gas power station building make a bit more sense to me as they are cheap to build, better that coal environmentally and complent renewables - why is everyone so up in arms?
    •  
      CommentAuthorSteamyTea
    • CommentTimeOct 22nd 2012
     
    Posted By: jms452why is everyone so up in arms?

    No idea, not as if we are replacing coal with nuclear (which we should be doing), so we may as well replace it with gas as no other technology is available today that can do what is needed.
    • CommentAuthorMartinH
    • CommentTimeOct 22nd 2012
     
    Fossil fuel prices are rising steadily and will accelerate as peak oil nears - we will also as a nation be importing more energy in the future and as we already run a big trade deficit, I do not know how we can pay for that imported energy now - let alone in the future... Fuel security is also a major issue.

    The fuel for wind energy is free, which is quite an advantage. We need to take advantage of this resource - as the windiest nation in Europe, we would be daft not to. Sure - wind is not reliable, so other sources of energy will still be needed, but when the wind is blowing, we are saving imports and CO2 emissions too. I can't see the problem. Ok, there are the additional capital costs of the backup systems, but as fossil fuel prices rise further, that won't be a problem.

    Wind will just be part of a range of energy sources - the arguments against wind seem to make the assumption that advocates of wind turbines expect them to be the sole source of electricity, and argue against them accordingly. The article in Cornwall Today as cited is a good example.
    • CommentAuthorCWatters
    • CommentTimeOct 23rd 2012
     
    Posted By: SeretThe grid does operate a certain amount of spinning reserve and backup, but this isn't entirely to support wind as you need to cover faults and maintenance anyway, not to mention following demand.


    How can the same spinning reserve be used for several purposes when they can easily occur at the same time?
    •  
      CommentAuthorSteamyTea
    • CommentTimeOct 23rd 2012
     
    Posted By: CWattersHow can the same spinning reserve be used for several purposes when they can easily occur at the same time?

    Probably because they don't occur at the same time and in the case f renewables not without warning or as a catastrophic failure.
    Take a large coal plant, or nuclear, that generates 500 MW and compare it to 250 2 MW turbines scattered around the countryside.
    There are then two ways to calculate the chance of failure, the frequency of failure or the Bayesian method. In this instance it does not make a difference which is chosen as the problem is a single failure.
    So a single failure in the FF or Nuclear causes a 500 MW shortfall, a single failure in a wind turbine is a 2 MW shortfall.
    So you need a reserve for the large plants of probably 90% (a number of ready to go gas plants) but for a turbine you can get away with no reserve (the voltage and frequency drop would be hardly measurable out of 20 to 40 GW).
    So the chance of loosing a large installation and the equivalent amount of wind is infinitesimally small.
    •  
      CommentAuthorted
    • CommentTimeOct 23rd 2012
     
    The 'chance' of losing all wind is quite high, i.e. when there is no wind across the whole of the UK the chance will be 100%. This does happen and the fact that it is predictable doesn't remove the need for a reserve.

    But I think calling this a 'reserve' is actually the wrong way to look at wind. Wind generated electricity should just be thought of as a way of increasing the fuel efficiency of existing power stations.

    And I still don't understand why there is not more research into large scale batteries such as Vanadium Redox.
    • CommentAuthormw116
    • CommentTimeOct 23rd 2012
     
    But surely that chance is predictable - wind forecasts tend to be fairly accurate, so it can be planned into generation in the same way that maintenance at other types would be? My understanding is that spinning reserve is there to cope with sudden changes in demand - be it user-led (kettles on halfway through Coronation street) or generator led (e.g. Drax tripping out).
    • CommentAuthorEd Davies
    • CommentTimeOct 23rd 2012
     
    Also, even if there is an un-forecast drop in the wind it won't, on a country-wide scale, happen that quickly. A block of air 1000 km × 500 km × 100s of metres thick doesn't just stop instantly. It's a good reason to spread the turbines around, though. I'm not sure how fast gas power stations can be spun up but my impression is that it's pretty quick, much less than an hour or so, as opposed to coal or nuclear which is much slower.
    •  
      CommentAuthorSteamyTea
    • CommentTimeOct 23rd 2012
     
    The way that the generation market works at the short term level is though half hour auctions of capacity and hour and a half before delivery. Even solar can be predicted at that level with very good accuracy.
    There are some rules that allow renewables to take precedence over FF generation even if the cost is higher.
    The big generators (King Coal and Nuclear) are generally on long term contract for base load and a proportion of daily variability. Gas sits in the middle, some is used for base load, but not constantly, some is used for daily variation that is not dealt with by the Coal and Nuclear, some is on standby (about 20 minutes to half an hour needed) and some is on hot standby (about 6 to 10 minutes) and more is on spinning reserve (about a minute or less). Then there is the diesel CI generators that are scattered around the country that can come in within a few seconds s well as load shedding though the TRIAD system (all those supermarkets freezers, every little helps).
    On top of this is the legislation that controls the voltage and frequency that is allowed to be delivered. We do not have 230V at 50Hz only, it varies constantly but averages out at that (well the UK domestic supply is closer to 240V for historic reasons).
    If there was a catastrophic failure in generation, all that happens is that local substations disconnect, shedding more load to stabilise the voltage and frequency (they know what each major substation is drawing and can quickly work out which ones to disconnect and in what order, just the same as you would do at home if putting on the washing machine, tumble dryer, kettle and microwave blew a fuse).

    So this 'intermittent' is a red herring from the anti-wind brigade and does not stand up to scrutiny. If it was true we would be having constant problems every day, today would be a good example, little wind and misty, so no wind or solar to speak of, but my power is still on. 241V and 50.01Hz, spot on.
    • CommentAuthorCWatters
    • CommentTimeOct 23rd 2012
     
    Nobody is claiming that changes in output due to day to day changes in weather can't be predicted. What's more concerning are reports that rapid changes in total output are more frequent than expected..

    http://www.jmt.org/assets/pdf/wind-report.pdf

    "The frequency of changes in output of 100MW or more over a five minute period was surprising. There is more work to be done to determine a pattern, but during March 2011, immediately prior to publication of this report, there were six instances of a five minute rise in output in excess of 100MW, the highest being 166MW, and five instances of a five minute drop in output in excess of 100MW, the highest being 148MW."

    http://www.ieawind.org/annex_XXV/PDF/Task%2025%20Paper_Bremen_final20090814.pdf

    "From both the experience and results from studies performed, a significant challenge is the variability of wind power within 1–6 hrs. Frequency control (time scale of seconds) and inertial response are not crucial problems when integrating wind power into large systems at the present time, but can be a challenge for small systems (like Ireland) and will become more of a challenge for systems with high penetration in the future."

    The amount of short term reserve needed seems to vary a lot but I agree it's not a large percentage...

    "The estimated increase in short term reserve requirements in the studies has a large range: 1–15 % of
    installed wind power capacity at 10 % penetration (of gross demand) and 4–18 % of installed wind power capacity at 20 % penetration. Time scales used in the estimation explain much of the differences in results:

    • If only hourly variability of wind is taken into account when estimating the increase in short term reserve
    requirement, the results are 0.5–4 % of installed wind capacity or less, with penetrations below 10 % of gross
    demand.

    • When 4 hour forecast errors of wind power are taken into account, an increase in short term reserve requirement of 4–5 % of installed wind capacity has been reported, with penetration levels of 5–10 % of gross demand."

    "The highest results in Fig 4 are from a study where four hour variability of wind (not forecast error), combined with load forecast error, results in 15 % reserve requirement at 10 % penetration and 18 % reserve requirement at 20 % penetration of gross demand"

    So somewhere between 1 and 18%.
  3.  
    C Watters

    Well you can ignore that first report as it is so out of date, ie generation capacity 2008 compared to 2012. Even the pumped storage is misleading due to a major part being offline for repairs. Now all back up and running the figures for 2012 could be quite interesting with the new capacity coming onstream.
    • CommentAuthorjms452
    • CommentTimeOct 24th 2012
     
    Posted By: CWattersNobody is claiming that changes in output due to day to day changes in weather can't be predicted. What's more concerning are reports that rapid changes in total output are more frequent than expected..


    Posted By: CWatters"The frequency of changes in output of 100MW or more over a five minute period was surprising.


    100MW change over five minutes is 1.2GW/hour

    To put the concern into perspective the grid currently handles demand climbing by about 13 GW between 6.30am and 8.30am. That’s a slew rate of 6.5 GW/ hour.
    http://www.inference.phy.cam.ac.uk/withouthotair/c26/page_188.shtml

    The storage is a different matter but this is where the CCGT come in as a cheap interim solution.
    •  
      CommentAuthorSteamyTea
    • CommentTimeOct 25th 2012
     
    • CommentAuthorGavin_A
    • CommentTimeOct 27th 2012
     
    Posted By: CWatters"The frequency of changes in output of 100MW or more over a five minute period was surprising. There is more work to be done to determine a pattern, but during March 2011, immediately prior to publication of this report, there were six instances of a five minute rise in output in excess of 100MW, the highest being 166MW, and five instances of a five minute drop in output in excess of 100MW, the highest being 148MW."

    given that the spinning reserve of the grid is designed to cope with the simultaneous and instantaneuous disconnected of 2 x 1GW generation units it should be fairly obvious that 5 minutes changes of under 10% of that level are nothing to worry about, and require virtually no additional spinning reserve to cope with it.

    When installation levels start heading towards 10 times that figure, then we may require a small proportion of additional spinning reserve to cope with it, unless other measures have been implemented such as dynamic demand controls to allow temporary demand reductions from eg fridge and freezer circuits.
    • CommentAuthorGavin_A
    • CommentTimeOct 27th 2012
     
    Posted By: jms452100MW change over five minutes is 1.2GW/hour

    To put the concern into perspective the grid currently handles demand climbing by about 13 GW between 6.30am and 8.30am. That’s a slew rate of 6.5 GW/ hour.
    http://www.inference.phy.cam.ac.uk/withouthotair/c26/page_188.shtml

    The storage is a different matter but this is where the CCGT come in as a cheap interim solution.


    I'd concede that around this point in the day there may well be a requirement to increase the fast start standby reserve* levels in case you got the slew from wind generation going in the opposite direction at the same time.

    At this time in the day though a significant proportion of the difference from trough to peak is made up in the switch of 3GW of pump storage from pumping to generation.

    It could also be mitigated for significant parts of the year by encouraging the installation of more east facing solar PV generation, or trackers.





    * I may not be using the exact current terminology here.
    • CommentAuthorGavin_A
    • CommentTimeOct 27th 2012
     
    interesting to see more details of the additional 1.2GW of pump storage SSE have in the planning process at the moment, with apparently up to 50 hours of peak generation capacity planned for each.

    That should go a long way to balancing high levels of wind penetration in scotland if / when it comes on line.

    They seem to be leaving their options open to go for smaller schemes instead, but I hope they opt instead for a full size scheme at one site only if there's not enough initial need / funds for both, which would leave the potential for the 2nd full size facility to be built at a later date.

    http://www.sse.com/uploadedFiles/Z_Microsites/Coire_Glas_Hydro_Scheme/Controls/Lists/Resources/CoireGlasPumpedStorageBriefing.pdf
    • CommentAuthorGavin_A
    • CommentTimeOct 27th 2012
     
    Posted By: CWatters"The highest results in Fig 4 are from a study where four hour variability of wind (not forecast error), combined with load forecast error, results in 15 % reserve requirement at 10 % penetration and 18 % reserve requirement at 20 % penetration of gross demand"

    So somewhere between 1 and 18%.

    It's also worth pointing out that these figures are more than double the highest figure from all the other studies, and are from a 2007 almost entirely theoretical UK study.

    ie they can be excluded entirely as being completely wrong guesses by academics who's theories have been proved wrong in practice.

    Unfortunately it seems that the lead author actually heads up a DTI working group on the subject, which may go someway to explain why the UK seemed to keep on insisting that penetration levels above 20% weren't viable theoreticall (while sticking at pentration rates an order of magnitude lower than this) even while Germany was proving they were in practice.
    • CommentAuthorGavin_A
    • CommentTimeOct 27th 2012
     
    there's something else that bugs me from that article in the way they calculate one of the measures of penetration.

    Essentially one measure is based on the level of penetration compared to the minimum demand including the impact of interconnectors, but I'm fairly sure I've seen elsewhere how this is calculated, and it assumes that the interconnector is making the situation worse not better - as if at levels of peak generation and minimal demand we'd somehow actually still be forced to import via the interconnector at peak rates.

    This is plainly nonsense, and means that despite the interconnectors being a highly effective method of reducing the impact of high levels of renewables penetration, by this measure they would actually appear to be making the situation worse not better.
  4.  
    Anyone interested in winning £20 million from DECC for a good storage idea?

    http://www.theengineer.co.uk/1014337.article?cmpid=TE01