    • CommentAuthorjockass
    • CommentTimeOct 29th 2012
     
    Firstly hello all,

    I have recently moved into a 1960s detached bungalow. Air quality is really poor and as an allergy sufferer i am looking to install a mvhr system primarily for air quality reasons. I am going to be installing the unit myself as we have really good access in the loft and eaves to install the unit and relevant ductwork. I am looking for some recommendations on appropriate units to install for my property and also some suggestions on where to purchase the ducting. The property has 4 bedrooms, 2 bathrooms and a shower/utility room (kitchen plus 3 wet rooms). The floor area is 140m2 and i calculate the volume to be 318m3. There are three of us in the house.

    In terms of the ducting i am considering the airflow pro flexible ducting for ease of installation but if others here with first hand experience recommend rigid ducting i will go for it.

    Any suggestions gratefully received

    Cheers
    Chris
    • CommentAuthorRobinB
    • CommentTimeOct 29th 2012
     
    Posted By: jockassairflow pro flexible ducting

    It's not a flexible as you might think! Worth having a feel before you go down that route.
    • CommentAuthorchriskemp
    • CommentTimeOct 29th 2012
     
    but easier to maintain airtightness/reduce leaks in the duct runs.
    you will need plenum boxes too dont forget.

    rigid duct work is cheaper, but shall take you far longer to screw, tape and silicone seal each joint.
    either way make sure the ductwork is insulated if a cold loft/roof void.
    • CommentAuthortony
    • CommentTimeOct 29th 2012
     
    I would not use anything other than rigid ducting.
  1.  
    why flexible ducting for a bungalow? Its a much easier installation in a bungalow and you get a lot less air pressure losses with rigid ducting preferably round and not too small, say 125mm diameter. You can get this type of ducting from Screwfix. I can't review the Screwfix ducting, haven't used it bought mine from the MVHR firm for a lot more money.
    We have got the Itho MVHR system, a Dutch system, which we are pleased with. It also incorporates the cooker hood waste heat.
    • CommentAuthorchriskemp
    • CommentTimeOct 29th 2012
     
    <blockquote><cite>Posted By: tony</cite>I would not use anything other than rigid ducting.</blockquote>

    Although the airflow semi-rigid is easier for a diy install, and wont crush like normal flexi
    • CommentAuthorjockass
    • CommentTimeOct 29th 2012
     
    I will happily look at both options - surely screwfix is not the cheapest for ducting. Anyone know any other suppliers that are well priced.

    The units i have been looking at all have 125mm spigots so would look to use that throughout and minimise bends and runs where possible. Does anyone have experience of the airflow dv72 unit? it looks to be pretty basic and for my needs (better air quality) might be one worth considering.
    • CommentAuthorGaryB
    • CommentTimeOct 29th 2012 edited
     
    I agree with Tony - don't use flexible ducting, it increases the specific fan power of the system amd costs much more to run.

    Choose your MVHR system carefully - check that the model proposed has an EST Best Practice specific fan power (SFP) - heat exchange efficiency is what the manufacturers focus on but SFP is the really important one. Similar duty units can have the same HR efficiency but one unit can use 3 times the energy of the other. These are 24/7 operation so take care in the selection.

    SAP software packages have access to the full database and can give an accurate assessment of the energy used (and saved).

    The Itho models mentioned by Chippyclaus in his post above are amongst the best performers, but other brands such as Vortice and Xcell are also good. Don't settle for anything worse than 0.6 W/l/s. BTW, you could double the SFP by using flexible ducting - it's a complete false economy.
    • CommentAuthorGaryB
    • CommentTimeOct 29th 2012
     
    Jockass:

    The Airflow DV72 model you have been looking at has an SFP of 0.79 and 89% HEx Efficiency. Not bad, but could be better.

    Regards

    Gary
    • CommentAuthorGaryB
    • CommentTimeOct 29th 2012
     
    The DV71 is a dog however, not to be touched with a bargepole.

    SFP of 3.03 for 3 wetrooms, 6 times worse than the best units available. Efficiency of 91% doesn't compensate for this miserable performance.
    • CommentAuthorjockass
    • CommentTimeOct 29th 2012
     
    Yes indeed - it is the dv72 that i am looking at - still might be a bit of a mongrel but affordable!
    • CommentAuthorchriskemp
    • CommentTimeOct 29th 2012
     
    Controls are more important than SFP with regards retrofit, especially if fitting to help with allergies and Aq.

    Go for unit with summer bypass, humidity sensors and the option for air quality sensors (which can be damn expesnive)
    Also look into filter options. Which means you may wish to oversize the system to overcome increased resistance of better filtration.

    Id rec VA kinetic all day long.
    • CommentAuthorGaryB
    • CommentTimeOct 29th 2012 edited
     
    The best I can find on the database for 3 wet rooms plus kitchen is 0.43 so the DV72 is not a mongrel!
    • CommentAuthorjockass
    • CommentTimeOct 29th 2012
     
    Thanks guys - .79 for k+3wetrooms so looks ok. Is there any guides for ducting out there other than what common sense would dictate?
    • CommentAuthorGaryB
    • CommentTimeOct 29th 2012
     
    Chris's recommendation of Vent Axia Kinetic is another good range, the Kinetic Plus models are best in class.
    • CommentAuthorGaryB
    • CommentTimeOct 29th 2012
     
    • CommentAuthorjockass
    • CommentTimeOct 29th 2012
     
    Thanks Gary - some light bedtime reading
    • CommentAuthordocmartin
    • CommentTimeOct 29th 2012 edited
     
    Lindab have branches in various areas. Eventually I used them for all the ducts, grilles and air valves that I needed after the intial batch I got from a MVHR manufacturer had to be added to and the layout modified as the job proceeded. For my next project I went to them for everything except the MVHR unit and cooker hoods. If you have a local branch that is convenient compare their prices. I got a 25%+ discount when I ordered the bulk for the second job.
    Second the suggestion from chippyclaus that a bungalow is a lot easier, even with no experience. I also have fitted 2 Itho cooker hoods directly to the MVHR systems; you may be aware that this has caused a lot of discussion on this forum in the past ( I note that you only joined GBF 9 hours ago).
    Not sure how many 125mm spigots there are on your intended unit; several members have recommended oversizing the MVHR and the ducts to reduce noise and power consumption. Some units with the capacity you would need for your home have 150mm or even 200mm spigots.
    For the 2 systems I have installed, I found that the most suitable location for the MVHR limited the choice of models. For instance, for a loft installation some need a surprising amount of headroom to remove the heat exchanger with the unit in situ.
    • CommentAuthorRobinB
    • CommentTimeOct 30th 2012
     
    Posted By: GaryBThe DV71 is a dog however, not to be touched with a bargepole.


    Gary, what makes it so, please?

    It just looks like a baby verson of the DV72 which we have and which seems to work OK.
    • CommentAuthorGaryB
    • CommentTimeOct 30th 2012
     
    RobinB

    Yes it seems to be a smaller version of the DV72 which is EST compliant. I haven't studied the unit in detail but I note it is operating at its limit with 3 wet rooms and the poor SFP suggests an inefficient fan (possibly high speed) designed to meet the pressure drop requirements of a ducted system at minimum cost.

    As a rule, the closer an MVHR system operates to its maximum capacity, the higher the SFP. I prefer to specify units which operate in the middle of their range as this gives a good balance between SFP and cost. They tend to run quieter, too.
    • CommentAuthorborpin
    • CommentTimeOct 30th 2012
     
    Posted By: GaryBThe DV71 is a dog however, not to be touched with a bargepole.

    SFP of 3.03 for 3 wetrooms, 6 times worse than the best units available. Efficiency of 91% doesn't compensate for this miserable performance.
    I investigated this unit and the SPF in SAP Q is misleading as it was (I believe) tested with and F3 filter which, as it is a finer filter, affects performance!

    I have some significant reservations on these SPF figures.
    • CommentAuthorborpin
    • CommentTimeOct 30th 2012
     
    Posted By: GaryBI agree with Tony - don't use flexible ducting, it increases the specific fan power of the system amd costs much more to run.
    Once and for all, this ducting is semi-rigid not *flexible*. There is a significant difference.
    • CommentAuthorborpin
    • CommentTimeOct 30th 2012 edited
     
    Posted By: GaryBAs a rule, the closer an MVHR system operates to its maximum capacity, the higher the SFP. I prefer to specify units which operate in the middle of their range as this gives a good balance between SFP and cost. They tend to run quieter, too.
    I'd agree with this. I was originally speced the DV72 but turned it down as actually it would have needed to operate at to higher speed all the time. A big uni running more slowly is a better solution.
    • CommentAuthorGaryB
    • CommentTimeOct 31st 2012 edited
     
    Hi Borpin

    <blockquote><cite>Posted By: borpin</cite><blockquote><cite>Posted By: GaryB</cite>The DV71 is a dog however, not to be touched with a bargepole.

    SFP of 3.03 for 3 wetrooms, 6 times worse than the best units available. Efficiency of 91% doesn't compensate for this miserable performance.</blockquote>I investigated this unit and the SPF in SAP Q is misleading as it was (I believe) tested with and F3 filter which, as it is a finer filter, affects performance!

    I have some significant reservations on these SPF figures.</blockquote>

    An F3 filter has a pretty low resistance to airflow and low efficiency. I understood that all MVHR filters were F grade. I normally specify F7 (80-90% efficiency) for an office environment, F5 is 40-50% efficiency, so F3 is not impressive.

    I checked out the Airflow ducting and yes it is semi-rigid with a smooth inner layer. This was not clear in the OP, just the term 'flexible' was used. The Airflow brochure does not quote the actual resistance factor but does state that in a complete installation the ducting is equivalent to a rigid system.

    I suspect that the pressure drop for a given flowrate is slightly higher than rigid duct but the bends will be long radius compared to the short radius fittings used in a rigid system. None of the installers on the 172 MVHR systems we have designed have used semi-rigid duct or even offered it as an alternative, so there must be a cost penalty compared with rigid.
    • CommentAuthorborpin
    • CommentTimeOct 31st 2012
     
    If you tick HTML it will quote correctly.

    I was mistaken it is a F7 filter. Most units I have looked at come with a G4 filter as standard with some offering a F7 as an option. Not stating this is a flaw in the SAP rating.

    The Airflex Pro ducting wins for me as it is 75mm OD so I can get it round the back of my Oak Frame. I also think it will be significantly quicker to install and with long bends nice and quiet.

    YMMV
    • CommentAuthorGaryB
    • CommentTimeNov 3rd 2012
     
    Hi Borpin

    Thanks for the tip re quoting via html - never did understand that before!
  2.  
    All of the above seem to be talking sense. Fan power, control - both key issues. Try looking at the Passivent GenAiration system. Uses low power (SFP) MVHR unit but is fully automatic - so you don't have to press a switch to boost it. Also, it uses semi rigid ducting to make installation easier.

    I fitted it in my bungalow, was really easy and is working fine.

    GaryB is right about the extra cost of the ducting but for me I preferred to pay that bit more than trying to mess around with rigid ducting, especially in my loft with trying to make sure I don't fall between the rafters.
  3.  
    Posted By: borpin
    The Airflex Pro ducting wins for me as it is 75mm OD so I can get it round the back of my Oak Frame. I also think it will be significantly quicker to install and with long bends nice and quiet.


    Reading up on it the other advantages are supposed to be -
    - maintains integrity of airtightness (not relying on glued joints/duct tape)
    - avoids sound transmission between rooms

    What sort of cost increment are we talking about and are there any other disadvantages?
  4.  
    Posted By: Simon StillWhat sort of cost increment are we talking about


    Yes please me too.

    Why won't all these companies list prices in their web sites; is it that there is room for 'negotiation' or they just want a foot in to 'the sell', given you have to speak with them to find out costs?
    • CommentAuthorRobinB
    • CommentTimeNov 5th 2012
     
    Posted By: Simon Still- avoids sound transmission between rooms
    This is true but we have airflex pro ducting and we do get a little noise from the unit itself. Poorly laid out perhaps?
   