    I have researched all the different renewable sources including biomass, air source, ground source, solar thermal but thermodynamics solar panels seems to be the only one that seems like the best technology is this true?

    I live in a mid terrace facing south, south west, and have 4 bedrooms, running on gas combi bolier.
  2.  
    If you have an existing gas combi boiler then its difficult to justify anything other than the simplest/cheapest solar thermal set-up. Even that would require finding space for a cylinder & putting up with standing heat losses in winter which you wouldn't get with a combi boiler. In terms of economics alone, its not a clear cut decision.

    For a new build or retrofit off the gas network, I'd agree that you need some combination of solar thermal (for bright days) & heat pump (for dull days). However, I wouldn't trust the unsubstantiated claims of the only thermodynamic panel provider I've seen & I have concerns about the panels frosting in our more humid climate.

    I would go for separate solar thermal drainback & air source heat pump systems feeding a common hot water cylinder or thermal store. Rotex offer some interesting systems based on a drainback solar thermal store & Daikin split system air source heat pumps.

    David
    • CommentAuthorRobinB
    • CommentTimeNov 1st 2012
     
    Despite the big growth in PV I'd still go for solar thermal with a condensing gas boiler back up especially if you have already have gas central heating with radiators.

    It's a question of eliminating the things you haven't got space for or that would cause a nuisance, and pricing up the cost and benefit or the remaining options over the likely lifespan.

    Thermodynamic panels might be great but they haven't got much track record that I know of yet.

    Lots of people to help here!
  3.  
    We have been in our house for almost a year now, tried to build to passishaus standards and despite plumber, electrician and MVHR installation problems (see previous discussions if clarification needed), the thermodynamic panel is one piece of kit that i cannot fault. There is a backup immersion fitted and has never been switched on and we have had 60 degree hot water every day without fail. I have seen the panel completely white with frost and still no bother with hot water. I am in no shape or form connected to any company that sells or installs the panels, but I have no problem recommending the technology.
  4.  
    Can you point us to the previous discussions on your install?
    • CommentAuthorSilverSpray
    • CommentTimeNov 5th 2012 edited
     
    I've been trying to gather info on Thermodynamic Panels on my project blog.
    - http://www.silverspray.co.uk/tag/thermodynamic-panels/

    I've got a coastal cliff top site, so a normal air source heat excanger is going to have "fun" surviving the salty sea air. The site means ground source would be VERY expensive. So when I saw Thermodynamic Panels it seemed to be the perfect solution (for my project).

    I understand they've been in use for many years in Ireland, and even longer in Spain and Portugal.

    They are what I'm planning.

    Anyway, have a look at the notes on my blog.

    and great to hear the real user comment from "brogie2805" above.
  5.  
    Thanks - I tracked down your blog yesterday and picked up some good pointers on a few things. Some great things you've picked up on Pinterest as well. I've been meaning to start a blog for my project - must stop procrastinating about the name....

    Congratulations - yours looks like a great project in an stunning location.
    • CommentAuthorTriassic
    • CommentTimeNov 5th 2012 edited
     
    Sounds like a great system but at £5500 a bit on the expensive side? If the price were to halve I might consider it!

    I also found this information on payback times which some of you may find interesting - http://www.cernunnos-homes.co.uk/latest-news/thermodynamic-hot-water-versus-fossil-fuels/
    •  
      CommentAuthorSteamyTea
    • CommentTimeNov 5th 2012
     
    About 30 MWh of electric at 18p/kWh
    or about 18 years worth of showers for a family of 4 (not including teenagers):confused:
  6.  
    I have had one of the heating systems installed on a new build house we developed and then retained as a buy to let. Occupied for a year nearly and the tenants seem very happy (and they like to house hot!). We have supplied a few of the hot water systems and again the customers are all very happy! However installation costs are a touch high and to be perfectly honest stop the product being a sensible solution in many places with mains gas.

    They especially good if one has solar PV for the electricity they consume (PV produces enough even when its cloudy as they typically consume about 700 watts.

    That said many other companies are marketing these as being eligible for the RHI - they are not I am afraid at present - in fact MCS suspended the registration of them from the Solar Thermal category a couple of days ago - effective 18th November. Suspended as it is not really solar thermal - they may create a category or move the product to the heat pump technology but one must assume no subsidies at present!

    For my own house though I have opted for the ESP Ecocent (http://www.cernunnos-homes.co.uk/products/air-source-heat-pumps/) - similar unit cost but lower installation (no panels) and when integrated with ventilation (from bathrooms or MVHR) they are fantastic. Much better looking unit, with better controls, quieter (the Energie system is a bit noisy) .... It is classified as an exhaust air source heat pump so unfortunately not at present in the RHI ...

    One point last point - either product has a slower recovery time than a gas/oil fed modern system so make sure you opt for a larger tank than the one you are replacing (typically 200 litre for smaller 4 occupants or less and 300 litre for larger homes/4 or more occupants).
    •  
      CommentAuthorSteamyTea
    • CommentTimeNov 10th 2012
     
    Posted By: cernunnoshomesThey especially good if one has solar PV for the electricity they consume (PV produces enough even when its cloudy as they typically consume about 700 watts.
    Would that not bring the price up to about £10,000 for the kit, or almost double the original price.
    • CommentAuthorwookey
    • CommentTimeNov 12th 2012 edited
     
    Interesting. A cross between solar thermal and an air-source heat pump. http://www.cernunnos-homes.co.uk/products/energie-solar-thermal/ says that it can have Cop up to 8, but typically 3.5. It also says that typical solar thermal system have a COP between 2 and 1, which sounds wrong to me, or I don't understand how they are calculating it. Mine produces between 200 and 2000W with a 12W pump and 4W permanently-on controller. That's < ~6% parasitic load which makes for a COP of around 17. A COP of 2 implies 50% parasitic load which would be shocking.

    Clearly this setup has major advantages for producing hot water even when it's not sunny, or even daylight. Quite how this works out over the year I don't know, but I reckon simple solar thermal with gas/electric fill-in is hard to beat. So yes these look quite good in comparison to fossil fuels, but that's not hard - I'd like to see a comparison with conventional ST.

    Their website also says embarrassing things like: "It takes 4.18 kW to raise the temperature of 1 litre of water by 1 degree Celsius".
    •  
      CommentAuthorSteamyTea
    • CommentTimeNov 12th 2012
     
    I think COP should be worked out on the sum of outputs divided by the sum of inputs, if it is below unity then the term changes to efficiency.
    The trouble with heat pumps is that they do not count the 'invisible' energy source, this could be the air, water, ground or solar. Add them in and you will always be below unity.
  7.  
    Posted By: SteamyTeaThe trouble with heat pumps is that they do not count the 'invisible' energy source, this could be the air, water, ground or solar. Add them in and you will always be below unity.
    Why do you care? Its usually free & zero carbon.

    David
    •  
      CommentAuthorSteamyTea
    • CommentTimeNov 12th 2012
     
    Why do I care, simple, it is the physics/mathematics behind it.
    The Joule does not distinguish how it exists, but we do. Saying that it is free or zero carbon is not always the case. If you put a heat pump into an airing cupboard to heat up your water, and I know you can get such devices, the 'invisible' energy is anything but free or zero carbon.
    If people understood the concept of heat pumps then they may be able to make more informed decisions as to their value against alternative technologies.
    As with most things there is a compromise, this may be lack of roof space, lack of room inside, lack of cash etc. Somewhere someone said that this technology works well with PV, well yes it does, but you are now into a very large roof area and a lot of upfront cash. Bolting on technology to cover a failing in another technology is not always the way forward, just look at what has happened and is happening in the automotive field, they add more 'safety' technology when the problem is really traffic density.
    A simple solar thermal system with electrical backup heating is the best way to design a DHW, and I would not care if it was ET or FP, there is so little in it that is best to go on price/looks rather than performance.
    • CommentAuthorEd Davies
    • CommentTimeNov 12th 2012 edited
     
    Posted By: SteamyTeaThe Joule does not distinguish how it exists, but we do. Saying that it is free or zero carbon is not always the case.

    The COP you should be found by dividing the valuable outputs by the valuable inputs. Otherwise-useless inputs and outputs shouldn't be counted. The fact that sometimes people are a bit misleading by ignoring this doesn't invalidate the concept, though.

    Note also that a heat pump can be useful even when all of the inputs are “valuable” and the COP or efficiency or whatever you want to call it is less than one. E.g., it can turn the heat in a lot of tepid water into heat in a smaller amount of domestic hot water.
  8.  
    ST

    I agree with your main point. I'm surprised by the number of people who don't seem to understand that the compressor input power comes from electricity & that the rest of the output power comes from the environment. However, I don't think that means we should re-define COP. Instead we need to educate people that there's more to an efficient heat pump installation than the COP.

    David
    •  
      CommentAuthorSteamyTea
    • CommentTimeNov 12th 2012
     
    Posted By: davidfreeboroughInstead we need to educate people that there's more to an efficient heat pump installation than the COP.
    Yes. I was at a meeting once and someone had said that he was going to connect the output of his heat pump into the input and get all his energy for nothing :devil:
  9.  
    Love it :tooth:
    • CommentAuthorBeau
    • CommentTimeNov 12th 2012
     
    That's a classic :bigsmile:
    •  
      CommentAuthorSteamyTea
    • CommentTimeNov 12th 2012
     
    That's Penzance Transition Town for you. They still believe in magic as well.
    • CommentAuthorRobinB
    • CommentTimeNov 12th 2012
     
    Posted By: davidfreeboroughnstead we need to educate people that there's more to an efficient heat pump installation than the COP.


    Please educate me further! What more is there? Price, serviceable life come to mind but I don't think that's what you're getting at.
    thanks
    RobinB
    •  
      CommentAuthorSteamyTea
    • CommentTimeNov 12th 2012
     
    There is usage patterns, heating rate, storage, relationships between temperatures and COP (always makes me wonder why people want to use them at night), noise (if ASHP). and a few more I am sure.
    • CommentAuthorRobinB
    • CommentTimeNov 12th 2012
     
    Posted By: SteamyTeaalways makes me wonder why people want to use them at night)
    E7
    • CommentAuthorSteveZ
    • CommentTimeNov 12th 2012
     
    In the past, I have tried to decide on this very topic and the simple answer seems to be using off-peak electricity for DHW. Usually DHW costs are estimated to be around 25% of the house energy needs so you can put an approximate cost into your calculations. Bearing in mind that I have an oil combi, not mains gas and since I would have to install water storage and immersion heater(s), at the moment it just isn't worth the expense or the trouble. When the boiler and/or storage tank dies, the replacement heating will give me the same problem as this post poses

    If the original poster also needs a storage tank and plumbing installed by a tradesman, I'd be inclined to stick with the gas combi-boiler, especially if it is fairly new and presumably efficient
    •  
      CommentAuthorSteamyTea
    • CommentTimeNov 12th 2012
     
    Would have to work out the costs, both in cash and pollution to find out if it is worth running an ASHP, of different sorts at night. Oddly enough I am just running through the last 3 years weather data, but not sliced it into hours yet, takes long enough to just get it sorted into days. I think that it is this sort of thing that David was getting at when he talks of education.
    • CommentAuthorRobinB
    • CommentTimeNov 12th 2012
     
    First hard winter in the new house we ran ASHP on E7 and forced it to run mostly at night. After that winter I decided it would be "greener" to run it when the air temperature was highest so ditched E7 and had it run the heating when the sun is on it (and later when we got the PV it is most likely to be generating).

    Like a bad scientist I changed more than one variable and can't say for certain if it was financially advantageous. Thank heavens for ST who records things properly and can give us real information!

    For DHW I have it come on for a couple of hours later afternoon, giving the solar thermal a chance to do it's best first.

    This relative disregard for when we actually want the heat and hot water is only sensible in a well-insulated building.
    •  
      CommentAuthorSteamyTea
    • CommentTimeNov 12th 2012
     
    All comes down to how large your HP and thermal store is as to whether it is better to run it at night or no.
    Though I do urge everyone with this sort of technology to monitor it to find the sweetspot for them.
  10.  
    Posted By: RobinBPlease educate me further! What more is there? Price, serviceable life come to mind but I don't think that's what you're getting at.
    I was getting at the issues already raised by ST (where does the heat come from) & the issues you go on to discuss (like patterns of usage versus temperature, heat load of a low energy building). Its an important benefit of low energy buildings that they maintain their temperature well, so we can be more flexible in delivering the energy when its cheapest.

    Another one I would add is delivery temperature: the COP may well look good at 35 degrees C flow temperature, but many heating systems are designed for much higher delivery temperatures. So either you run at that higher flow temperature with a lower COP or you run the circulation pump for longer with the risk that the heat pump compressor short cycles.

    However, the most important has to be how the use of the heat pump is coordinated with solar thermal. It doesn't matter how many ST panels you install if the DHW tank or thermal store is always fully heated by the heat pump at 9am. This leads to the trade-off you've been dealing with. You want to maximise the opportunity for solar thermal during the day while also running an ASHP in the day when the air is relatively warm & also making use of Economy 7.

    We tend to take our baths/showers in the early morning, so the best strategy I can come up with is as follows:

    08:00-18:00 Solar thermal dedicated to DHW
    10:00-16:00 ASHP dedicated to space heating
    16:00-18:00 ASHP provides DHW top-up
    01:00-08:00 ASHP provides DHW & space heating with DHW priority

    David
    •  
      CommentAuthorSteamyTea
    • CommentTimeNov 12th 2012 edited
     
    E10 may be the answer, just to throw something else into the mix, but when we get smart meters then we will all be on E48, or is that a cream to keep your fingers soft.

    Here is a chart for the min temps and mean daytime solar intensity (sounds odd but they are daily averages) for near me.
    Ignore any value that is actually sitting on the x-axis as they are null values (and I just can't get Excel to ignore them and leave a gap).
    Trick is to now try and match the PV potential to the heat load.