Home  5  Books  5  GBEzine  5  News  5  HelpDesk  5  Register  5  GreenBuilding.co.uk
Not signed in (Sign In)

Categories



Green Building Bible, Fourth Edition
Green Building Bible, fourth edition (both books)
These two books are the perfect starting place to help you get to grips with one of the most vitally important aspects of our society - our homes and living environment.

PLEASE NOTE: A download link for Volume 1 will be sent to you by email and Volume 2 will be sent to you by post as a book.

Buy individually or both books together. Delivery is free!


powered by Surfing Waves




Vanilla 1.0.3 is a product of Lussumo. More Information: Documentation, Community Support.

Welcome to new Forum Visitors
Join the forum now and benefit from discussions with thousands of other green building fans and discounts on Green Building Press publications: Apply now.

The AECB accepts no responsibility or liability for any errors or omissions in the content of this site. Views given in posts are not necessarily the views of the AECB.



    • CommentAuthorscrimper
    • CommentTimeSep 12th 2013
     
    Talking to a builder tonight about our project, and he advised in the strongest terms against trying to put EWI on an existing 30's cavity wall (which has no current insulation).

    His opinion was that all your heat goes through the brick and simply warms the air in the cavity up, before escaping. He seemed to suggest that all the EWI firms promise that this won't be the case because the EWI will form a perfect seal, but he suggested that in reality this was extremely hard to achieve. He said he'd take 60mm of IWI over 100mm EWI in such a situation any day ...

    Thoughts anyone?!
  1.  
    He's right, you would have to fill the cavity as well.... his IWI suggestion may well be better, especially if he has seen the project in question and can way up the costs/disruptions involved.
    • CommentAuthorjamesingram
    • CommentTimeSep 13th 2013 edited
     
    I 70mm EPS EWI over a rockwall filled cavity wall about 5-6 years ago , so far no signs of negatives.
    spend quite a bit of time on sealing top and any routes into it to reduce potential moist air getting in and condensing mid structure.
    Empty cavity would, as said, just take the heat away via ventalition unless completely sealed at the top etc..

    How about filling the cavity with lean mix or similar and then EWI , suggested by Tom on GBF to give a thermal massive warm wall.
    • CommentAuthortony
    • CommentTimeSep 13th 2013
     
    I would fill the cavity for sure first then do EWI as the best option.

    Cavity fill for me would be foam, polystyrene beads or fibres as least good option. (Scared of grouts or concrete)
    • CommentAuthorSprocket
    • CommentTimeSep 13th 2013
     
    What they all said.
    You would be very surprised how much heat an unfilled cavity can leak away even if you think it is well sealed. The EWI will certainly be pretty pointless unless you fill that gap with something. If you are on a very tight budget then just the cavity fill alone will probably be more thermally effective than the EWI.

    The main concern with filling the cavity is the possibility of bridging the cavity with something that allows moisture to track across. In that respect Tony's suggested preferences look good to me too.
    • CommentAuthorscrimper
    • CommentTimeSep 13th 2013
     
    Thanks all. So ... yes ... apparently it's going to be an absolute nightmare to even attempt to fill the cavity first, so IWI it is. Despite the loss of internal space, I'm actually a little relieved ... the whole EWI thing was making me feel a little nervous anyway.

    Now - final question - I wonder if anyone out there has managed to get proper levels of ECO funding for internal wall insulation!?
  2.  
    Hi Scrimper,
    I have had cavity insulation fitted to all the houses I have owned. And have never had a problem. CIGA 25 year gaurantee on all of them. Mind you the oldest one was built in the 1960's. I am now looking at moving to our "final" resting place. I am interested in older houses and wonder if there is any particular problems with installing Cavity insulation in them. My last installation was blown in rock fibre took less than a day and cost £200. Have you contacted any insulation companies ? and have they highlighted any problem areas ?

    Richard
    • CommentAuthortony
    • CommentTimeSep 13th 2013
     
    Why is it difficult to fill. The cavities, if it is then there could be grant funding available for it.
    • CommentAuthorscrimper
    • CommentTimeSep 13th 2013
     
    HR - I'm sceptical of contacting insulation companies direct to be honest because their take on it is going to be somewhat impartial to say the least!

    Tony - can't say in detail why they are so hard to fill, but appparently it would necessitate a myriad of holes and then very difficult to ascertain whether it has successfully filled the entire cavity ... and of course, any slumping in the material then leaves gaps at the top where it is most vital!

    The other factor to consider is the speed of response to heat input .. which seems to make perfect sense, as with IWI you are going to get a more immediate effect ...
  3.  
    Posted By: scrimperand of course, any slumping in the material then leaves gaps at the top where it is most vital!


    Polystyrene bead cavity fill is typically injected with watered down PVA glue to prevent slumping, and to prevent it falling out when you make holes in the wall. It forms a solid mass once the glue has dried. Even if there are gaps in the fill, I think they are more than likely to be enclosed on all sides thus preventing the chimney effect that your builder is talking about. I would not consider fibre fill.
  4.  
    How wide is the cavity? I was told if it is only 25 or 30mm it can't easily be filled.
    • CommentAuthortony
    • CommentTimeSep 13th 2013
     
    Myriad of holes will all be filled and covered over by the EWI

    With IWI you loose the thermal mass and reduce comfort.
    •  
      CommentAuthorfostertom
    • CommentTimeSep 13th 2013 edited
     
    Where do they think that heat (by air convection) will escape to, from the cavity? into the loft maybe? Either fill the cavity and/or seal its top off from uninsulated loft space. If you're EWIing, unless it's too thin to be worth while, you're bound to be disturbing the eave tiling so you should have good access to the top of the wall and its cavity. If the loft is part of the insulated envelope, then no need to do either.

    Whether or not the EWI is airtight (it doesn't claim to be) is irrelevant.

    Filling the cavity with insulation is the cheapest and simplest thing anyone can do - many firms falling over themselves to do it. But inadequate on its own - additional EWI recommended.

    If it was me, I'd fill the cavity solid with weak concrete, then EWI outside that. That way, you get lots of beneficial thermal mass inside a tea-cosy of insulation.

    But one way or another, EWI is def the way to go - avoid IWI at al cost. Spend time to understand the issues and ideas.
  5.  
    Posted By: fostertomWhere do they think that heat (by air convection) will escape to, from the cavity?


    I don't think its realistic to expect the heat to build up and expect convection to carry the heat to the top and stay there - when you need heating chances are its blowing a gale and there are all kinds of air movements through gaps in pointing, around windows, everywhere.

    Agree the insulating the cavity is going the be the cheapest by a long shot, but not going to get to the same values as IWI/EWI.
    • CommentAuthorscrimper
    • CommentTimeSep 13th 2013
     
    Ouch. And just when I thought I REALLY understood it ... !

    But thanks for your input.

    There is no loft in our house ... 100% flat roof. I would have thought there was plenty of opportunity for the air to escape given that it is a 80 year old brick wall, and I've got no idea how good the cavity trays are at the top.

    100m of 6m high 100mm cavities = 60 cubic metres of weak concrete cavity fill - that's quite something! Wouldn't the wall ties possibly be compromised by such an undertaking?

    The house has a rendered finish, so aesthetically EWI is a perfect fit ... it's just the frightening cost of it, and the thought of having to deal with the cavities was starting to really put me off. But once we have vacated the property, I shall have the guys really dig around and see what state everything is in within the walls - should make things a lot clearer.
    • CommentAuthortony
    • CommentTimeSep 13th 2013
     
    What if any roof insulation have you got?
  6.  
    Hi Scrimper,
    You would probably get a good performance/cost benefit from cavity insulation. With internal insulation there could be many issues. One of which is where internal walls meet the internal cavity wall giving a thermal bridge. And external insulation is costly. One way is to have the cavity insulated (you will end up with drill holes at about 1 metre grid and extra ones around windows and doors about 25mm diameter). If these are filled and made flush with the current render then you could apply a coat of special "flecked" render coating. This is applied with basically a tray of the special weather proof coating with a rotary brush "flicking" the render coat onto the wall. I had this done one one house. I can't remember the name of this. But it may be worth getting a decent company to give a quote. This will probably give the best cost/benefit.

    Richard
    • CommentAuthorscrimper
    • CommentTimeSep 14th 2013
     
    Tony - probably precious little roof insulation. It's a 30's asphalt flat roof ...

    Richard - thanks. Sounds like a LOT of drilling. But need to find myself an impartial/independent surveyor who can really establish the viability of sorting these cavities one way or another ...
    • CommentAuthortony
    • CommentTimeSep 14th 2013
     
    Roof/ceiling insulation rates as a higher priority than anything to with walls, you probably only have plaster between you and the outside world!
  7.  
    Hi,
    Totally agree Tony. I think both cavity and roof need to be done to give a uniform insulation. If the floors are suspended then it may be easy to get insulation in there as well.

    Scrimper If you do go the cavity insulation route make sure the company is using the cavity insurance guarantee angency ( CIGA ). 25 year guarentee up to £10,000 on my last certificate. I would not worry about the amount of drilling the company that do it will probably only take 1/2 a day for that and filling and checking flues etc. My brick built home had holes drilled in the mortar at the junction between vertical and horizontal courses - these were filled with mortar. It is hard to see unless you look carefully. (not sure if injecting from the inside will be better for you depending on the amount of renovation required and if the current render is in good order )

    Good to see you have a breathing space to investigate.

    Richard
    • CommentAuthorjamesingram
    • CommentTimeSep 14th 2013 edited
     
    here's a little heat loss pic.
    •  
      CommentAuthorSteamyTea
    • CommentTimeSep 14th 2013
     
    What about a terraced, end terraced or bungalow. They will have different numbers.:wink:
    • CommentAuthortony
    • CommentTimeSep 14th 2013
     
    And a flat roof will be different.
    •  
      CommentAuthorSteamyTea
    • CommentTimeSep 14th 2013
     
    And if you have a basement or live in a flat.

    But Tony, it has percentages in it so it must be right :bigsmile:
    • CommentAuthorTimSmall
    • CommentTimeSep 16th 2013
     
    Polystyrene bead (with glue) cavity fill is pretty good at reaching all voids, and has minimal slump. A couple of firms around here (Sussex) will do graphite enhanced poly beads. It's likely to be your most cost efficient way of doing things.

    I've used Soudal Flexifoam (I paid £6 per can when buying a box of 12) to seal cavities at the top and side in order to stop any air travelling through the insulation in the past.

    Before you get the fill done, take the opportunity to check for cavity wall tie corrosion - it'll be easier to remedy it (if present / necessary) before the cavity fill goes in. Oh, and get a CIGA guarentee too, ask for a few quotes and ask the surveyor some tricky questions and see how they answer.
    • CommentAuthorscrimper
    • CommentTimeSep 17th 2013
     
    Thanks Tim ... will make a note of those suggestions ... esp. re: the cavity ties.

    Out of interest - can anyone give me a rough indication how my 2 courses of 100mm brick PLUS the best modern cavity fill available would compare thermally to new build wall constructed under current regs? Do I really have to go IWI or EWI to get close?
    •  
      CommentAuthorfostertom
    • CommentTimeSep 17th 2013 edited
     
    Posted By: scrimperHis opinion was that all your heat goes through the brick and simply warms the air in the cavity up, before escaping. He seemed to suggest that all the EWI firms promise that this won't be the case because the EWI will form a perfect seal, but he suggested that in reality this was extremely hard to achieve
    Coming back to this belief, there's something wrong. We've mentioned cavity warm air escaping laterally into uninsulated loft (or flat roof voids), but he's talking about heat escaping thro an air-leaky outer skin and EWI, regardless of good thermal resistance conductivity-wise.

    So it's about heat that may be carried by bulk air movement thro the outer skin and EWI. This assumes an existing air-leaky outer skin, and saying the EWI isn't airtight enough to kill this air movement.

    Well, if the outer skin is already that air-leaky, a bit of cavity fill isn't going to cure that at all. Heat escape via bulk air movement will continue just as before - polystyrene bead fill, even with added glue, offers negligible air resistance. Urethane foam fill couldn't guarantee to be continuous either, and I'm not sure it's very airtight anyway.

    Whereas EWI, even imperfectly done, will vastly improve the wall's airtightness, compared with doing nothing about it. At best, EWI is well airtight over its open surface, the weak points being at windows etc.

    Cavity fill won't even stop the other risk, either - cavity warm air escaping laterally into uninsulated loft (or flat roof voids). To prevent that, you'd have to do something definite e.g.
    Posted By: TimSmallI've used Soudal Flexifoam (I paid £6 per can when buying a box of 12) to seal cavities at the top and side in order to stop any air travelling through the insulation in the past.
  8.  
    Hi Scrimper,
    It all depends. My recent extension was started 7 years ago. It has 75 mm cavity wall insulation(from memory) 270mm loft insulation and 100mm slab polystyrene insulation. The rest of the house is the same apart from the slab is not insulated. I calculated the wall U value of 0.15. I am not sure what the current standard is. The floor area is 100 m2 and heating bills with two adults mostly at home all day is £500/year. To achieve this in the older part of the home cost £200 for cavity insulation and £100 for the loft + a days work. I did look at how to improve this further but the cost would be very large and the savings very small. Have you a cost for EWI/IWI ?

    Richard
  9.  
    Hi Scrimper,
    Slight mistake there:bigsmile: Wall value was u value of 0.3 loft insulation at 270 mm is a U value of 0.16. Part L update in 2010 from :-http://www.homebuilding.co.uk/advice/project-tips/building-regulations/part-l The table in there wall U values were 0.3 and improved to 0.2. Lots of online U value calculators are available.

    Richard
    • CommentAuthorSaint
    • CommentTimeSep 17th 2013
     
    To hit the target U values required by Building regs you'll need roughly the same thickness in the cavity as you would do for EWI on a 9" solid wall.
    The thermal efficiency of blown in cavity fill insulation is not as good as the rigid board of course and looking at Knauf's 34 mineral wool which as the name suggests has a thermal conductivity of 0.034W/mk and say Eco Bead based on Neopor which has a thermal conductivity of 0.033W/mk a filled 50mmm cavity will achieve a U value of 0.50 W/m2K, a filled 75mm cavity 0.36W/m2K and a filled 100mm cavity 0.29W/m2K
    So most older cavity walls when filled will be well short of Building Reg requirements of 0.30W/m2K in England and Wales, 0.27 to 0.25 and better in Scotland and 0.27 in Ireland.
    There are many, the so called Hard to Treat, cavities that are significantly less than 50mm so the value of simply filling them with insulation unless its with a higher performance PUR is questionable?
   