Home  5  Books  5  GBEzine  5  News  5  HelpDesk  5  Register  5  GreenBuilding.co.uk
Not signed in (Sign In)

Categories



Green Building Bible, Fourth Edition
Green Building Bible, fourth edition (both books)
These two books are the perfect starting place to help you get to grips with one of the most vitally important aspects of our society - our homes and living environment.

PLEASE NOTE: A download link for Volume 1 will be sent to you by email and Volume 2 will be sent to you by post as a book.

Buy individually or both books together. Delivery is free!


powered by Surfing Waves




Vanilla 1.0.3 is a product of Lussumo. More Information: Documentation, Community Support.

Welcome to new Forum Visitors
Join the forum now and benefit from discussions with thousands of other green building fans and discounts on Green Building Press publications: Apply now.

The AECB accepts no responsibility or liability for any errors or omissions in the content of this site. Views given in posts are not necessarily the views of the AECB.



  1.  
    Do any cost or performance problems arise were I to reduce the max water temperature of my GCH from the current 70C to about 45-50C?

    The background is:

    - Mixed central heating system - UFH except for rads in bedrooms.
    - Boiler spec is 25C to 90C CH water output temperature range at high efficiency.
    - We have quite generous provision of rads. Currently we only use one out of two in each occupied bedroom, and that minimally.
    - There seems to be plenty of heating capacity available in the boiler (Coopra Compact 25Kw Combi in a recently eco-refurbed house) except when heating from a week of absence when it takes a day or so to catch up.
    - I've already dropped the temp from 82C to 70C since we arrived with no apparent problems over the winter.
    - My preference is to adjust room stats and water temp rather than reprogramme time clocks.

    I can't see anything that should prevents me experimenting.

    Any comments would be welcome.

    Ferdinand
    • CommentAuthortony
    • CommentTimeMar 16th 2014
     
    In the end if you drop it too low then in very cold weather the house won't get warm enough, I would go ahead and keep reducing it.
    •  
      CommentAuthorSteamyTea
    • CommentTimeMar 16th 2014
     
    The physics of it is quite simple, the problem is getting the data/performance curves.
    Thing is you are already half-way to getting all the data you need. Try reduce the water temp by 5°C at a time until you get unacceptable performance. Read the gas meter daily so you know how much you have used, keep a log of room and external temperatures. Then plot temperature difference against usage for each water temp.
    • CommentAuthormarkocosic
    • CommentTimeMar 16th 2014
     
    Drop it right down to 35C and work your way up again as winter sets in. You should be running it as low as possible in order to improve efficiency and varying the flow temperature throughout the year in accordance with the weather. The benefits of 50/30 over 80/60 are marked. 35/30 doesn't have much over 50/30 though.

    Decent controls - weather compensation - do this automatically in response to external temperature but are alien to most gas safe registered plumbers who masquerade as engineers capable of designing heating control systems. The boiler almost certainly has the connections for them/opentherm/0-10V control.

    Intermittently running at a higher temperature to "boost" the heat after a week away is fine. There is a tradeoff between lower flow temperature to improve efficiency vs the expense of increased losses due to increased time at temperature due to the increased warmup time. I wouldn't worry about it too much.

    You should also be adjusting the start time on the time clock in order to ensure that the house is up to temperature when required but not a moment earlier. Again decent controls do this "optimum start" time automatically but are alien to most plumbers. (you set the time that you want it 'at temperature' rather than the time you think that you need the heating to come on at in order to get up to temperature)

    It's warmup time that will get you eventually, rather than the ability to maintain temperature. You'll notice more favourable temperature gradients in rooms with radiators when the flow temperature is lower: the hot air doesn't shoot quite as high up towards the ceiling quite as fast as it does at 70C!

    Who specified and commissioned the current system? Were they given explicit instructions to minimise warmup time without the slightest regard for energy efficiency? Or simply a failure to give a stuff?
    •  
      CommentAuthorSteamyTea
    • CommentTimeMar 16th 2014
     
    Posted By: markocosicWere they given explicit instructions to minimise warmup time without the slightest regard for energy efficiency?
    That's an interesting question, it may go back to us having a fire in a cave after hunting and gathering as the Middle Eastern sun sets.
  2.  
    The tale is not complicated: 82C is the default temperature and the previous people liked to run the place hot, though I think they had not made too much effort.

    I have whacked it down to 40C and will take it from there.

    Thanks

    Ferdinand
    • CommentAuthorJonti
    • CommentTimeMar 17th 2014
     
    Be interesting to see how it works out.

    Jonti
    • CommentAuthorfuncrusher
    • CommentTimeMar 17th 2014
     
    Most ch systems are over-sized and not economically optimum. There are two fundamental reasons for this. Firstly, they are designed to meet extremely cold weather, yet for the bulk of the heating season the demand is a tiny fraction of that. Secondly, cold customers are quick to complain to installers if the ch system is inadequate, but never complain if it is over-sized. So the installer has an inherent incentive to over-size.

    The end result is rads that are too big and, worse still, boilers which are far too large. Keep in mind that boilers like most thermodynamic devices (inc all engines) are designed to run most efficiently at a particular parameters.

    In general it is more economic to have a system which will meet heating requirements in all but coldest weather, and, when that occurs, do some peak lopping with either an extra jumper or some high cost electric heater, or an open fire.

    One other factor: you need to consider response time. That's a bit like acceleration performance in a car. Over-size engine gives huge acceleration but poor mpg overall. A complicated aspect.
  3.  
    Hi,
    I had the default temperatures set on my boiler when installed. I had a problem with the temperature overshooting. I use mark1 humanoid control system. It works very well. I worked out the over heating was due to the water/radiators/pipework could contain 10 kWh of energy if the water temp was high. Some years ago I knocked the water temperature down (top of radiators are about a max of 47 C measured with an infra red thermometer). I have run like this for about 4 years all seasons. At this time of year when it's chilly inside I just "click the stat on" and turn it off after 10 minutes. Leaving the stat to "overshoot" because of hysteresis just costs energy and causes the temperature over shooting. On very cold days then the heating does need to be on for longer. However at this time of year just putting the boiler on until the radiators are warm/hot saves gas and electricity for the pump.

    Richard
    •  
      CommentAuthorSteamyTea
    • CommentTimeMar 17th 2014
     
    Is it worth timing the system from cold to hot, would that give you an idea of how long the system takes to respond and lets you know how much energy is in the system that may be going to waste.
    • CommentAuthormarkocosic
    • CommentTimeMar 17th 2014
     
    An 82C default is sad, isn't it Ferdinand.

    Weather compensation will address overshoot with hysteresis stats too; you're turning down the proportional element in the control loop.

    "Oversize" radiators aren't a problem. "Oversize" boilers are rarely a problem, unless paired with "undersize" radiators. (cycling on the water flow temperature is bad; cycling on the house thermostat is ok unless it is absurdly (<10 mins) quick, but that is rarely the case. 30% of rated output is often a more efficient operating point than 100% of rated output too: the boilers are overdriven to get their maximum outputs, particularly in domestic hot water mode for a combi.
    • CommentAuthormarkocosic
    • CommentTimeMar 17th 2014 edited
     
    Easier to time the house then set a weather compensation slope/curve.

    (follow the commissioning instructions provided with all decent boilers/controls - not difficult unless you have the patience, pride in workmanship, and reading skills of a mainstream gas safe installer)

    Attached: readout that you get with relatively dumb controls (£99.99 Owl Intuition) that only do on/off. (the boiler is a state-of-the-ark noncondensing Baxi that only does on/off control and isn't economic to replace) The slope is easy to see though, and tweaking the flow temperature manually every quarter gets most of the benefit at minimal cost.
  4.  
    It has taken about 3 goes to make the reduced max temperature stick, but it is now saying 33C return temp.

    Reflecting, I wonder if there will be extra load on the pump.

    The floor temp of my downstairs bathroom floor surface temp has dropped from about 27C (which is the normal figure to date) to 22C since I turned the temp down. The upstairs bathroom is currently up to 30C floor surface temp, presumably waiting to catch up.

    I might even gird my loins and do a daily temp / gas / elec readings.

    It does take an External Temperature sensor:

    "This temperature sensor must be an NTC with a resistance of 12 kOhm at 25C".

    The instructions tell me to set "minimal flow temperature", "slope" and "flow temperature at outdoor temperature of 20C".

    Interestingly there is a mini something on the wall (may well be a thermocouple) in our lobby to outdoors (unheated porch between 2 double glazed doors to outside and inside), with a cable coming back to the boiler spot but not connected. That may mean that it was tricky to configure or didn't work well :-).

    F
    • CommentAuthormarkocosic
    • CommentTimeMar 17th 2014
     
    40/33 will have the boiler condensing very nicely indeed. :-)

    Outdoor temperature sensor wouldn't work well in a porch; more insulated than one might think and too sensitive to solar gain. North wall is good.

    Sounds like cold feet will limit the minimal flow temperature. Given that it was "fine" at 70C throughout winter, try your 40 at 20C and 70 at -5C outdoor temperatures - a fairly standard looking curve. Viessmann's charts are pretty:

    http://www.willsoden.com/6pp.pdf

    Evidence says that 1.7 is fine. If you can drop to 1.2 ish (55C flow temps even when cold out) then you'll get that boiler condensing very nicely almost all of the time.

    Pump load: the heating will run for longer at the lower temperature, increasing the electricity consumption of the pump. Is it internal or external to the boiler? A-rated? (saves £25/year, allegedly)
    • CommentAuthorborpin
    • CommentTimeMar 17th 2014
     
    I know I've asked the question before but do not feel there was a good answer; at what point is a condensing boiler most efficient. I know it must vary by manufacturer slightly but the basic science is common. So heating a Thermal store, I have a diverting valve which ensures minimum temp to boiler is 45C.

    When running, as measured by sensors attached to the outside of the pipes, return to boiler is 51C and flow is 64C. There is some discrepancy here though as the boiler reports a higher temp of 68C (digital output on front) and the tank sensor (in a proper temp sensor pocket) is showing a temp more akin to the boiler temp.

    If you take the losses (or inaccuracies) to be broadly proportional, the boiler (which runs at 75% for first 15 min I have discovered i.e. not modulating), is increasing the water temp by 13C during this time. I can crank the boiler up so that after these 15 min, the flow temp is a couple of degrees higher. The boiler switches off when the tank thermostat says enough. This is set to about (as it is analogue) 55C.

    I wonder if the boiler is at it's maximum efficiency at 75%, if so I need to vary the output temp at the boiler so that there is no step after 15 minutes. I can easily live with the TS being at a lower temp, I just want to maximise efficiency of the boiler.
  5.  
    Pah. The bunny boiler appears to have reset itself again to a higher temperature.


    Outdoor temperature sensor wouldn't work well in a porch; more insulated than one might think and too sensitive to solar gain. North wall is good.


    As ever, it is complicated :-o. What I called a "porch" is actually a 10ft by 3ft brick corridor with a dg door at one end facing North. It does not get very warm.

    If the point of a well-insulated house is to decouple the inside from the outside thermally, how much benefit is obtained from an External Sensor?

    Ferdinand
    •  
      CommentAuthorSteamyTea
    • CommentTimeMar 17th 2014
     
    Posted By: ferdinand2000If the point of a well-insulated house is to decouple the inside from the outside thermally, how much benefit is obtained from an External Sensor?
    Same as using one in a high thermal mass house I suspect (which just cools your house down as far as I can tell). Shall have to ponder that.
    • CommentAuthormarkocosic
    • CommentTimeMar 17th 2014
     
    Borpin - the return temperature limiter is designed to heat the top of the store to a high temperature quickly, rather than heating the entire store to a lower temperature which isn't as useful for DHW. The boiler will supply heat more efficiently at a lower return temperature.

    A few boilers run at 75% for a set time before modulating down. (and throw a right hissy fit if they're in a pushing through a bypass against closed TRVs and can't hit 15 minute runtime before hitting the water temperature limit stat) As far as I'm aware this is a strategy to, err, "optimise their performance" for emissions testing purposes. Definitely not gaming the test cycle. (the 15 minute runtime at 75% output matches the NOx emissions test IIRC) The function can be disabled except with some Vaillant models IIRC. Fitting radiators and pump that are appropriately (>boiler output) sized solves the problem.

    The more insulated the house the flatter the weather compensation curve Ferdinand and the less useful weather compensation becomes. At near passive house levels you'll be sat at minimum most of the time. It's most valuable in a "typical" shitty semi with undersized radiators that needs the full flow temperature in the depths of winter just to maintain temperature.
    • CommentAuthorborpin
    • CommentTimeMar 17th 2014
     
    Posted By: markocosicBorpin - the return temperature limiter is designed to heat the top of the store to a high temperature quickly, rather than heating the entire store to a lower temperature which isn't as useful for DHW. The boiler will supply heat more efficiently at a lower return temperature.
    It is not a return temp limiter (implies Max temp) it is a diverter (in that it sends the water round the loop until it reaches the set temp of the diverter that then closes) and yes I *fully* understand that (I designed that part in not my "expert") and is not the question I asked.

    I asked what is the most efficient flow/return temp differential/combination for a condensing boiler. Seems no one actually knows!

    If the 75% is done to optimise the NOx emission test, it implies it is running cleanest at that setting. However, is that the most efficient as well?

    Boiler was deliberately sized to keep up with 2 showers.

    BTW the valve has made a marked difference to the time the boiler runs in a day (reduced it). In addition, elsewhere we discussed mixing/blending valves for TS. I had accidental proof that what I have works. After some work, the motorised valve was left unplugged and I only noticed it when I realised the boiler was short cycling!
    • CommentAuthorRobL
    • CommentTimeMar 18th 2014
     
    Here's an article from the USA on boiler efficiency:

    http://m.hpac.com/heating/small_boiler_efficiency

    It's got a nice graph in it, showing efficiency versus return water temp at different power levels.
    It shows that best efficiency is achieved at low return temp, with lowest power level.

    Odd in a way, that most gas boilers don't make it easy to set this- I set a mid flow temp on ours, and a low flow on the pump, so the return temp is low. Bit of a faff though - if I tweak the boiler flow temp down too low, the boiler power required is less than 25%, and it modulates.... best efficiency is found just above the point it modulates I think.
    It would be easier to set the boiler flow temp low, pump fast - but doing this I get tepid DHW, and all rads are same temp( we have an old school 1 pipe system, so low flow makes downstairs rads hotter than upstairs, just as we want).
    • CommentAuthorCWatters
    • CommentTimeMar 18th 2014 edited
     
    Some boilers shouldn't be operated with a return temperature below 60C (for example some Grant oil boilers). I believe that's because it increases corrosion in the boiler. The installation instructions say to fit a mixer to keep the return temperature over 60C during start up when the water in the rads is cold.
  6.  
    Posted By: RobLHere's an article from the USA on boiler efficiency:

    http://m.hpac.com/heating/small_boiler_efficiency" rel="nofollow" >http://m.hpac.com/heating/small_boiler_efficiency

    It's got a nice graph in it, showing efficiency versus return water temp at different power levels.
    It shows that best efficiency is achieved at low return temp, with lowest power level.


    I'm struggling the units in that article, I'm afraid (with an engineering degree :-).

    "small condensing boilers, both floor-standing and wall-hung models with inputs of up to 500,000 Btuh"


    What's a Btuh in terms of input to a boiler? Or is there a missing slash? It's like a Kilowatt (Hour-squared).

    According to me that has the same Dimensions as a Joule-Second, and I'm struggling with the concept.

    Equally, further down:

    "In this example, there is a 400,000-Btu heating load and two boilers, each with 200,000 Btu, to serve the load. One way to control these boilers is to simply stage them"


    What is the meaning of a heating load in BTUs (or Joules or Kwh)? Since when has a "load" been measured in terms of total energy, ignoring time during which it is being delivered?

    Or am I just being obtuse?

    Ferdinand
  7.  
    Hmmm.

    Even though I have my Maximum Flow Temp set to 40C now, I'm spotting it sometimes going higher for a relatively short period - to say 65C then quite quickly back down again.

    Presumably that is the dynamics of a boiler burner that cannot be avoided, and I can't control that, so what I would need would be to measure the *return* temp to make sure that water coming back has used up as much of its heat as possible in the various conditions operating in the system created by thermostat settings etc.

    And then to set that at roughly particular sweet spot, adjusting as regularly as is appropriate.

    Ferdinand
    • CommentAuthorEd Davies
    • CommentTimeMar 18th 2014
     
    Posted By: ferdinand2000What's a Btuh in terms of input to a boiler? Or is there a missing slash? … What is the meaning of a heating load in BTUs (or Joules or Kwh)
    Without reading the article my guess would be that both of those are meant to be BTU/h. Americans are very sloppy about that. Most irritating, even more so than British electricians saying mm when they mean mm².

    1 BTU ~= 1055 J (depending on which definition you use).
    1 BTU/h = 1055/3600 = 0.29 W.
    1 W = 3600/1055 = 3.41 BTU/h
    • CommentAuthorJonG
    • CommentTimeMar 18th 2014
     
    The spike in heat maybe a periodic plate heating function to pre-heat the hot water PHE to assist with quick response,it can usually be disabled in most units.
    • CommentAuthormarkocosic
    • CommentTimeMar 18th 2014
     
    &amp;quot;It is not a return temp limiter (implies Max temp) it is a diverter (in that it sends the water round the loop until it reaches the set temp of the diverter that then closes) and yes I *fully* understand that (I designed that part in not my &amp;quot;expert&amp;quot;) and is not the question I asked.

    I asked what is the most efficient flow/return temp differential/combination for a condensing boiler. Seems no one actually knows!&amp;quot;

    A: Flow and return temperatures as low as possible. The boiler will be more efficient without your diverter/minimum return temperature valve, but will be creating heat that's of little use to you.


    &amp;quot;If the 75% is done to optimise the NOx emission test, it implies it is running cleanest at that setting. However, is that the most efficient as well?&amp;quot;

    A: lowest (continuous) output usually; 30% of nameplate. Sometimes excess air and fan power/pump power start to dominate and you're better off nearer 50%. It won't be 75 or 100%.


    &amp;quot;BTW the valve has made a marked difference to the time the boiler runs in a day (reduced it). In addition, elsewhere we discussed mixing/blending valves for TS. I had accidental proof that what I have works. After some work, the motorised valve was left unplugged and I only noticed it when I realised the boiler was short cycling!&amp;quot;

    In what scenario was the boiler short cycling? Diverter stuck to &amp;quot;full divert&amp;quot; and water going around and around the loop?


    Ferdinand - I second what JonG suspects. Definitely kill the &amp;quot;keep hot&amp;quot; setting if it's been turned on as that'll be chewing gas unnecessarily.
    • CommentAuthorborpin
    • CommentTimeMar 18th 2014 edited
     
    As you know your quoting has not worked. Highlight the text you want to quote and then hit the quote link. You can do that several times from different posts on same page.

    On short cycling, it was the motor for the 4 port blending valve on the output to the UFH that was not connected so it was dropping the top of the tank quickly (as that was where the valve happened to be) without using the lower heat first. This is a different valve to the diverter on the boiler loop.

    What I do now have is that the thermostat is too high in the tank so the boiler is not running for long enough and more often. I need to move the thermostat down a pocket (about 8") to nearer the return. It is also noticeable that the water lower in the tank is colder (which is what I expected).

    Moral, it is not simple and with out an array of temp sensors, it is impossible to know what is happening.
    • CommentAuthorborpin
    • CommentTimeMar 18th 2014
     
    @RobL - Nice graph but a query on terminology; is 'return temperature' to or from boiler?
    •  
      CommentAuthorSteamyTea
    • CommentTimeMar 18th 2014
     
    Posted By: borpinMoral, it is not simple and with out an array of temp sensors
    50 quid sorts that one.
    • CommentAuthorborpin
    • CommentTimeMar 18th 2014
     
    Yep. Seen these http://www.sheepwalkelectronics.co.uk/
   