Home  5  Books  5  GBEzine  5  News  5  HelpDesk  5  Register  5  GreenBuilding.co.uk
Not signed in (Sign In)

Categories



Green Building Bible, Fourth Edition
Green Building Bible, fourth edition (both books)
These two books are the perfect starting place to help you get to grips with one of the most vitally important aspects of our society - our homes and living environment.

PLEASE NOTE: A download link for Volume 1 will be sent to you by email and Volume 2 will be sent to you by post as a book.

Buy individually or both books together. Delivery is free!


powered by Surfing Waves




Vanilla 1.0.3 is a product of Lussumo. More Information: Documentation, Community Support.

Welcome to new Forum Visitors
Join the forum now and benefit from discussions with thousands of other green building fans and discounts on Green Building Press publications: Apply now.

The AECB accepts no responsibility or liability for any errors or omissions in the content of this site. Views given in posts are not necessarily the views of the AECB.



    •  
      CommentAuthorfostertom
    • CommentTimeDec 7th 2007 edited
     
    Posted By: biffvernonMike George said, "I am mystified about the inner layers and ..... etc
    Oh bronco - that's just the sound of someone covering their ass!
  1.  
    so I could conduct a test using a sheet of cardboard, find that it's as good as 200mm of mineral wool and building control would have to accept it?
    • CommentAuthorMike George
    • CommentTimeDec 7th 2007 edited
     
    Posted By: Mark Brinkleyso I could conduct a test using a sheet of cardboard, find that it's as good as 200mm of mineral wool and building control would have to accept it?

    No of course not, but I think you may once again be able to rely on previously certified comparitive testing, such as that certified by TRADA. This is of course pure speculation on my part. We will have to await the new DCLG guidance to Building Control but I cannot see what else they can do.
  2.  
    Maybe Martian can clarify for us?
    •  
      CommentAuthorfostertom
    • CommentTimeDec 7th 2007
     
    Why can you never find a Martian when you need one?
    • CommentAuthorMike George
    • CommentTimeDec 7th 2007 edited
     
    • CommentAuthorMike George
    • CommentTimeDec 7th 2007 edited
     
  3.  
    I guess the next thing is to see the guidance from CLG. If it says "it's up to each BCB how to interpret this ruling", then we are no nearer a solution than we were two years ago.

    Meanwhile, what is happening with the European Technical Approval for multifoils?
  4.  
    As far as I know it is ongoing.
    • CommentAuthorPDobson
    • CommentTimeDec 9th 2007
     
    So as a result of this ruling should I try and persuade my BCO to accept Tri-iso 10 rather than thinsulex? Should I put it above the rafter or below? Still favour above even if I need to put tyvec above it - I guess if nothing else the tyvec will help protect the shiny stuff and I have another waterproof layer between me and the weather.
    • CommentAuthorPDobson
    • CommentTimeDec 9th 2007
     
    Frank – Thanks - I appreciate what you are saying but as I will be heating/living in my roof space the sort of ventilation you are describing doesn’t appeal. The tyvec will at least drop any water coming in under the tiles into the gutter. I think felt or PE film would do the same job as the tyvec in this situation but I will have to use the "official" recipe
  5.  
    Hi again PDobson, the interaction of foils and breather membranes is a sticky subject for me as various foils have diffent levels of air and vapour permeability. Some are stitched together and some are welded. My advice would be to choose a type which has some form of Certification. and follow the manufacturers technical data sheets to the letter.

    If you've managed to read this entire thread you will know that most people here do not accept that multifoils work as effectively as is claimed. I myself am still on the fence but I would use a multifoil which is welded and therefore more airtight in use. Their airtightness alone makes them worth using in my opinion.
    • CommentAuthorPDobson
    • CommentTimeDec 9th 2007
     
    I absolutly agree I wouldnt use it on its own - but a combination of Airtightness and a bit of insulation over or under the rafters - in combination with 90mm of celotex between the rafters should give me a pretty warm roof.
    • CommentAuthorchuckey
    • CommentTimeDec 10th 2007
     
    If your insulation is air tight, I would have thought that it is waterproof, so it would catch any water blown in, so it must terminate in the gutter to shed this. From what I have read foils need a 25mm air gap over them, so I reckon the total system is :- slates/tiles, battens, sarking cloth (into gutter), counter battens, foil, rafters infilled with foam, vapour proof membrane, ceiling material. WOW!
    Frank
  6.  
    I'm just in the process of putting 50m of Kingspan in the roof and between 60m and 50mm of kingspan between the floor boards ... I've also putting a layer of thinsulex in under the rafters. I'm going to batten down the thinsulex in 1 meter blocks ... it will be baggy inbetween which seems to match with the recomendation to let it 'hang' rather than totaly batten it down.

    any other advice?
  7.  
    I'm fascinated by the multi-foil saga and the different points of view on this thread.

    What I can't get my head around is the European assessment procedures that multi-foils will now be subjected to. As far as I can tell, there are three separate EU activities taking place:

    i. Common Understanding of Assessment Procedure (CUAP) tied in with the European Organisation of Technical Approvals (EOTA). The reference is:
    141. Thin reflective insulation product intended to be used as thermal insulation complement in the construction envelope
    Final EOTA: March 2007
    http://www.eota.be/html/etawhoutetag.htm

    ii. CEN TC89 WG12 – Standardisation of the assessment of the thermal performance of products based upon or utilising reflective or low emissivity layers.

    iii. CEN Workshop 36 - Evaluation of Thin Multilayer Reflective Insulation Products by in situ Testing.

    The latter of these is, I believe, a workshop set up by the multi-foil manufacturers, the results of which could influence the decisions of the other two. However the workshop doesn't in itself have any binding regulatory effect.

    In the business plan to CEN Workshop 36 there's a footnote that reads as follows:

    'The Workshop will liaise with CEN/TC 89 “Thermal performance of buildings
    and building components” and in particular its WG12, and the European
    Organisation for Technical Approval (EOTA).

    'Both CEN/TC 89 and EOTA have made studies on reflective insulation
    products. However EOTA has decided to suspend its study of in situ testing and
    to maintain reliance on the existing ”Hot Box” or “Hot Plate” test methods.

    'CEN/TC 89/WG12 has embarked on a wide ranging study of insulation products having a reflective surface, or surfaces. Whilst WG 12 will include a review of in situ testing it has made no commitment to produce an EN on in situ testing of thin multilayer reflective insulation products. At the present the only test methods recommended by CEN/TC 89 are the existing “Hot Box” or “Hot Plate”.'

    http://www.cen.eu/cenorm/businessdomains/technicalcommitteesworkshops/workshops/n002adoptedbusinessplancenws36.pdf

    Am I reading this wrong, or doesn't this mean that the comparative in-situ testing preferred by the multi-foil manufacturers has already been dismissed by the EOTA and will probably be dismissed by CEN?

    So in terms of the UK derogation period granted to multi-foils, are we waiting on the results of the workshop, run by the multi-foil manufacturers themselves? Even though the EOTA and CEN are likely to ignore the results?

    I hope this posting makes sense, and people can follow my drift (told you I was confused). Any information / illumination would be great.
    •  
      CommentAuthorrichy
    • CommentTimeDec 12th 2007
     
    Why cant they just build 2 semis, one insulated with actis, the other with kingspan and check the heating bills against each other at a given temperature?
    • CommentAuthorCWatters
    • CommentTimeDec 14th 2007
     
    As I understand it the foil insulation relys in part on airgaps either side of the foil established during installation to reduce conducted losses. These still air gaps won't exist when the foil is tested in isolation in a heat box but would exist if tested in-situ. ..or have I missed something in this complex case?
    • CommentAuthorbiffvernon
    • CommentTimeDec 14th 2007
     
    And those still air gaps won''t exist in a real building either if the gap is more than a couple of centimetres. Convection will start up and move the heat. Of course one could stop that by filling the gap with something woolly. :wink:
  8.  
    The recommended gap is 25mm in most cases and can be achieved in a real building, providing the job is done properly, which is an issue regardless of insulation type. Also the spaces between the layers of foil are filled with something woolly. Actis make one with sheeps woll don't they? Others use polyesters or suchlike.
    • CommentAuthorbiffvernon
    • CommentTimeDec 14th 2007
     
    You will get convection in an empty 25mm gap - so what is the gap for?
    • CommentAuthorworkaholic
    • CommentTimeDec 14th 2007
     
    The air gap above the multifoil was, I had always assumed, to prevent the foil touching the breather membrane and causing wicking.
  9.  
    Posted By: biffvernonYou will get convection in an empty 25mm gap - so what is the gap for?


    Good question- I do not know why manufacturers specify 25mm specifically, though I think it is because they have achieved the best in-situ results with 25mm.

    On a related note, what is the otimum gap in a sealed DG unit? 20mm? Is this because convective currents will begin after this? How much heat energy is lost as a result of the additional 5mm Care to have a stab at a % loss?
    • CommentAuthorbiffvernon
    • CommentTimeDec 15th 2007
     
    No. But there are graphs published that show a bell shape with U-value plotted against gap size. It's a rounded peak at about 17mm. There's not a lot of difference between 15 and 19mm but once convection sets in above around 20mm U-value drops off steeply. Hence the industry standard of 16mm gap, with wider gaps only used where noise reduction is the priority. That's for argon fill. For krypton the narrow gap side of the graph is steeper showing that this gas is more appropriate where narrow units have to be used. I've no idea who did the research or how good it is.

    Regarding the gap above multifoil, I guess the 25mm came about because of the need to avoid physical contact with a good heat conductor that would negate the low emittance of the last foil layer. 25mm is probably arbitrary, owing more to being 'about an inch' than anything to do with physics, which requires only that the gap is more than one infra-red wavelengths.
    •  
      CommentAuthorrichy
    • CommentTimeDec 15th 2007
     
    I've used multi foil above the rafters and below and that 25mm might be constant at the rafters, but it can be anything from 40mm to zero mid span. You are overlapping the edges so the thickness of the stuff is doubled at those points.
  10.  
    The multifoil phenomenon continues apace.

    I was in B&Q today (for my sins), and I saw an insulation material consisting of a foil layer, about 10mm of some sort of hemp (looked a bit like cheap carpet) and then another foil. Insert joke about what they did with the rest of the hemp here.

    Amazingly, according to the manufacturers, this is equivalent to 200mm of mineral wool. It doesn't even have any of the magic inner layers!

    I did not actually look at the price, sadly. However, I remain confident that it will have been ludicrously high.

    If you want a reflective layer, why not use agricultural mylar? I'm sure this is cheap, particularly in whole-house quantities.
    It certainly is in the US; I can't find a UK online supplier but farmers will know of one.

    Wrap two layers with something (or nothing) in the middle. Easy, surely?

    Incidentally, you can then use the off-cuts to grow your own hemp, thereby making a double saving!
    • CommentAuthorbiffvernon
    • CommentTimeDec 17th 2007
     
    Well that's an interesting post, passivhausfan. This product must be worth a second look becasuse having foils either side of fluffy stuff makes sense from the physics. It's the internal layers of foil that are magic so leaving them out merely brings one down to earth.

    Agricultural mylar. I've not heard of that but it makes a lot of sense. Where can we get it? (What do farmers use it for?)
    • CommentAuthorTuna
    • CommentTimeDec 17th 2007
     
    It's just a thought, but surely external foil layers (like the B&Q stuff) are most susceptible to conduction sucking away the heat, not only though the material itself, but also along the plane of the material (ie. in an area surrounding the contact point at which conduction occurs)? I'm assuming that the foil is conductive to heat? In which case, any point of contact with the outermost foil layers will be worse than it would be for a non-conductive insulant?

    I'm not trying to make a point for or against multifoil, but the B&Q stuff did make me think that surely it would be more effective to produce something with the reflective/conductive layer sandwiched between the insulating stuff, so that point contact is with an insulant rather than a conductor of heat? Or is it just a manufacturing convenience to have the insulation held together by a sheet of something stronger?
  11.  
    Most tables tell us that an air gap 25mm+ gives a 0.2 R-value, so with 25mm each side of insulation the product would benefit from an additional 0.4R, which was presumably included in the R5 claimed for Actis multifoil.
    • CommentAuthordavid
    • CommentTimeDec 17th 2007
     
    Aluminium coated mylar for agricultural and domestic use is available from,
    www.apollo-energy.com/welcome/
    It has BBA Certification
   