Home  5  Books  5  GBEzine  5  News  5  HelpDesk  5  Register  5  GreenBuilding.co.uk
Not signed in (Sign In)

Categories



Green Building Bible, Fourth Edition
Green Building Bible, fourth edition (both books)
These two books are the perfect starting place to help you get to grips with one of the most vitally important aspects of our society - our homes and living environment.

PLEASE NOTE: A download link for Volume 1 will be sent to you by email and Volume 2 will be sent to you by post as a book.

Buy individually or both books together. Delivery is free!


powered by Surfing Waves




Vanilla 1.0.3 is a product of Lussumo. More Information: Documentation, Community Support.

Welcome to new Forum Visitors
Join the forum now and benefit from discussions with thousands of other green building fans and discounts on Green Building Press publications: Apply now.

The AECB accepts no responsibility or liability for any errors or omissions in the content of this site. Views given in posts are not necessarily the views of the AECB.



    • CommentAuthorzak99
    • CommentTimeFeb 24th 2017
     
    Hi,

    Waterproofing a fully below ground existing basement with a plastic waterproof membrane. For the floor screed which I'd like to keep as thin as poss for head height, what would you recommend to gain a little insulation please. Guide thickness is 65mm. I've seen Isolcap which contain eps beads I think.
    Any thoughts or other suggestions please?

    Rgds
    • CommentAuthortony
    • CommentTimeFeb 24th 2017
     
    Aerogel

    I would worry about condensation forming on the waterproof membrane behind or under the insulation.

    Is the basement below the water table? Are there any plumbing or drains leaking nearby?

    How will you satisfy building regulations with that little insulation?
    • CommentAuthorzak99
    • CommentTimeFeb 24th 2017
     
    Thanks Tony,

    Its a sealed cavity draining membrane designed for the job, draining to a sump with pumps. aka Newton or Delta.

    We had a history of water in the cellar but since the clay drains were replaced with all new plastic its drying out now.

    Building regs not relevant as its a non habitable room, for storage, study etc. I'm just trying to do the best I can in the circumstances.

    Aerogel on the floor ? Below ply or something like that?

    thanks again
  1.  
    Tony said:

    ''I would worry about condensation forming on the waterproof membrane behind or under the insulation.''

    and zak99 answered:

    ''Its a sealed cavity draining membrane designed for the job, draining to a sump with pumps. aka Newton or Delta.''

    Unfortunately that does not fully answer the point. The issue is interstitial condensation, occurring on the *inside* (meant to be the dry side) of the membrane. I am in the early stages of doing my basement, and the manufacturer advised that the standard detail (floor membrane taped to wall membrane) should not be used where insulation will cool the membrane, since you end up with a pond.

    The same manufacturer's instructions actually advise that *no* insulation should be installed because of this issue, or, (if you must) a very thin layer.

    When I told them I was going ahead with 50mm XPS anyway they advised great care with a VCL, but this is not wholly straightforward as it is a cool storage area underneath a habitable (warm-ish) room. I have been meaning to start a thread on this, because, from the point of view of the 'warm house', the VCL would be on the cold side. I'll try to find time to start that thread, but in the meantime do comment, and I'll shift the comments to the new thread if it looks like digressing from the OP's points too much.
    • CommentAuthorzak99
    • CommentTimeFeb 24th 2017
     
    Whats VCL?

    Worrying info Nick. Any more info welcome as I am just about to push the go ahead button. None of the expert contractors that quoted mentioned this unfortunately.

    Any more thoughts anyone on an improved screed value?
  2.  
    Vapour Control Layer - a plastic sheet.

    More info: If you are in a high radon risk area the option of not connecting the floor and wall membranes may not be possible, in which case you thereby ensure that, if condensation does occur on the inside of the membrane, you will have a small pond!

    Ask your contractor whose membrane they will be using, ask for the manufacturer's recommendations re insulation, and for their guidance with regard to interstitial condensation risk.

    ''Any more thoughts anyone on an improved screed value?''

    Don't use a screed! I have used 35mm XPS (extruded polystyrene) with tongued-and-grooved OSB (oriented strand board) over. It's fine, as long as you buy insulation designed for floors. This is a fully-floating floor, by the way - no battens.
    • CommentAuthorzak99
    • CommentTimeFeb 25th 2017
     
    Thanks again Nick.

    As far as I can see there is not an option of not connecting the wall and floor membranes because it will leak !?? Typical makes btw are Delta or Newton, looks like a sheet of football studs.

    Good suggestion re asking the manufacturers recommendations. I did try the other day but they weren't that helpful, I'll try again.

    The only issue with not using a screed in this case is that if there is internal flooding (ie from the above bathroom). Every damn membrane pocket would fill up below the insulation and require the floor and insulation lifting, and sucking every one of the small pockets out with a wet vac !! I know from experience.
  3.  
    ''As far as I can see there is not an option of not connecting the wall and floor membranes because it will leak !?? ''

    Not so. Under the floor membrane discharges into the drainage channel directly, as does the wall membrane. I don't want to advertise, but whisper me and I will send you a link to 'my' manufacturer's drawings for the 'open' detail.

    As to the flooding from above, I recommend not having any!!