<?xml version="1.0" encoding="utf-8"?>
	<rss version="2.0">
		<channel>
			<title>Green Building Forum - Sports hall</title>
			<lastBuildDate>Mon, 18 May 2026 03:50:35 +0100</lastBuildDate>
			<link>https://www.greenbuildingforum.co.uk/newforum/</link>
			<description></description>
			<generator>Lussumo Vanilla 1.0.3</generator>
			<item>
		<title>Sports hall</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15453&amp;Focus=263907#Comment_263907</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15453&amp;Focus=263907#Comment_263907</guid>
		<pubDate>Wed, 13 Dec 2017 22:29:06 +0000</pubDate>
		<author>tony</author>
		<description>
			<![CDATA[Can we help me with high level spec <br /><br />U values for hall walls, floor and ceiling =?<br /><br />U-valises for outside walls of changing rooms shower areas etc, floors, ceilings internal = ?<br /><br />Air tightness target for whole building <br /><br />Heating forsports Hall, gas is available, and energy source for hot water and heating other areas?<br /><br />Ventilation strategy?]]>
		</description>
	</item>
	<item>
		<title>Sports hall</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15453&amp;Focus=263917#Comment_263917</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15453&amp;Focus=263917#Comment_263917</guid>
		<pubDate>Thu, 14 Dec 2017 17:38:49 +0000</pubDate>
		<author>barney</author>
		<description>
			<![CDATA[U values? - how low can you go without the structure becoming unfeasibly unique to design and build. I'm imagining a steel framed shed with insulated panels and blockwork to about 3m high all round<br /><br />Air tightness - aim for 2.0m3/m2/hr @ 50Pa  and probably settle for 3.0m3/m2/hr @50Pa<br /><br />Direct fired gas radiant or LTHW radiant for the sports hall -LTHW rads for the rest - or if feasible use UFH (keeps the floors dry). <br /><br />Direct Gas fired DHW with large capacity storage calorifiers (Lochinvar as an example) or plate HEX and lower capacity calorifiers so you can divert virtually all the boiler power to DHWS for short periods to create a semi instantaneous flow system. How much you store (and lose) is a function of how often you plan using the place)<br /><br />Ventilation - I'd go for a demand based (CO2 monitoring) supply and extract with a heat recovery using LTHW for pre heat and constant minimum off coil temperature(say 18C) for the hall and a smaller heat recovery AHU for the rest of the place (heated via the LTHW and using a similar strategy)<br /><br />A few big ventilators in the roof to allow much increased airflow in summer (no AHU heating enabled) for upper temperature control - you really don't want to be deploying cooling<br /><br />That said, you may need some cooling if the activities are particularly onerous and the occupancy is very high - dance studio as an example<br /><br />Regards<br /><br />Barney]]>
		</description>
	</item>
	<item>
		<title>Sports hall</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15453&amp;Focus=263919#Comment_263919</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15453&amp;Focus=263919#Comment_263919</guid>
		<pubDate>Thu, 14 Dec 2017 17:46:02 +0000</pubDate>
		<author>Nick Parsons</author>
		<description>
			<![CDATA[Is a U valise where you keep your U values if you are taking them on holiday?<br /><br />No, seriously, why would you go for higher than about 0.12? (Maybe even sub-0.1 on roof and maybe floors.<br /><br />Seems to me ventilation is the key issue. Can you adequately vent the smell of x no. sweaty athlete's with MVHR-type performance (as per Barney's point above)?]]>
		</description>
	</item>
	<item>
		<title>Sports hall</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15453&amp;Focus=263920#Comment_263920</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15453&amp;Focus=263920#Comment_263920</guid>
		<pubDate>Thu, 14 Dec 2017 18:10:55 +0000</pubDate>
		<author>barney</author>
		<description>
			<![CDATA[Pretty much no Nick - a commercial cross flow heat exchanger won't achieve the efficiency of a small domestic MVHR from one or two specialist suppliers - but will exceed the efficiency of many of the cheap MVHR units around - but keep in mind we are taking several cubic metres per second flow rate rather than a few tens of litres flow rate<br /><br />You could employ a DX heat recovery within the AHU (evaporator and condenser in the relevant air streams), but the capital cost might very well not give a huge improvement over a cross flow HEX if you are operating a variable flow rate responding to CO2 monitoring (as a proxy for air quality)<br /><br />I've just reviewed a proposal for a circa 4m3/second AHU with pretty good casing thermal performance (heat loss and bridging) and a good quality heat exchanger that achieving about 73% heat recovery at design condition  - to give an order of magnitude of what's available at reasonable cost<br /><br />Regards<br /><br />Barney]]>
		</description>
	</item>
	<item>
		<title>Sports hall</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15453&amp;Focus=263921#Comment_263921</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15453&amp;Focus=263921#Comment_263921</guid>
		<pubDate>Thu, 14 Dec 2017 18:15:01 +0000</pubDate>
		<author>ActivePassive</author>
		<description>
			<![CDATA[Bear in mind, depending on use that you probably don't want the sports hall too warm if it is generally only being used actively - 14C for example should be enough. On this basis the U values don't need to be anywhere near as high as for a domestic premises, because the deltaT will be much lower and it will need heating for a much shorter period during the winter (deltaT is probably half and the heating period half, so perhaps 25% of the heating requirement of a home on a per volume basis, depending on your ventilation strategy.<br /><br />Also, the occupancy (periods) is relatively low, I would avoid UHF, as its not that responsive in a hall, although it does have the benefit of keeping anyone sitting on the floor feeling warm. Having done energy assessments on sports halls, the UHF is often poorly controlled, and ends up being left on for too long leading to much higher than predicted energy bills.<br /><br />You could consider heat recovery on your shower water.<br /><br />MVHR may also provide to be uneconomic as it will add a significant extra cost to the build, given the volume of air which potentially needs moving, and as per my first point your heat losses are going to be less anyway.]]>
		</description>
	</item>
	<item>
		<title>Sports hall</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15453&amp;Focus=263922#Comment_263922</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15453&amp;Focus=263922#Comment_263922</guid>
		<pubDate>Thu, 14 Dec 2017 18:42:01 +0000</pubDate>
		<author>barney</author>
		<description>
			<![CDATA[Given that the dominant loss is the ventilation loss, then I would say that heat recovery is pretty much essential<br /><br />No connection to Hoval, but I used similar units on a sports hall about 2 years ago<br /><br /><a href="http://www.hoval.co.uk/blog/com/sport-halls-ventilation-how-much-fresh-air-has-to-be-provided-tips-for-planners" target="_self" rel="nofollow">http://www.hoval.co.uk/blog/com/sport-halls-ventilation-how-much-fresh-air-has-to-be-provided-tips-for-planners</a><br /><br />Regards<br /><br />Barney]]>
		</description>
	</item>
	<item>
		<title>Sports hall</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15453&amp;Focus=263924#Comment_263924</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15453&amp;Focus=263924#Comment_263924</guid>
		<pubDate>Thu, 14 Dec 2017 20:14:01 +0000</pubDate>
		<author>tony</author>
		<description>
			<![CDATA[Re U values, any comments on keeping heat out during the summer?<br /><br />Thanks for the input, all very useful]]>
		</description>
	</item>
	<item>
		<title>Sports hall</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15453&amp;Focus=263932#Comment_263932</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15453&amp;Focus=263932#Comment_263932</guid>
		<pubDate>Fri, 15 Dec 2017 07:10:00 +0000</pubDate>
		<author>gravelld</author>
		<description>
			<![CDATA[There's an article in the latest Passivhaus+ magazine about a sports hall, might be of use.]]>
		</description>
	</item>
	<item>
		<title>Sports hall</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15453&amp;Focus=263952#Comment_263952</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15453&amp;Focus=263952#Comment_263952</guid>
		<pubDate>Fri, 15 Dec 2017 14:19:02 +0000</pubDate>
		<author>TimSmall</author>
		<description>
			<![CDATA[High efficiency + high volume MVHR set:<br /><br /><a href="http://www.recair.com/voluminous.php" target="_self" rel="nofollow">http://www.recair.com/voluminous.php</a><br /><br />... just uses lots of domestic MVHR blocks (this is the company that makes the heat exchange blocks in about 75% of the high-efficiency domestic units by multiple suppliers).<br /><br />Small, high-SCOP mini-splits for auxilliary rooms and changing rooms?<br /><br /><a href="https://www.carltonsales.co.uk/mitsubishi-electric-zen-msz-ln25vgr-air-conditioning-system-natural-white.html" target="_self" rel="nofollow">https://www.carltonsales.co.uk/mitsubishi-electric-zen-msz-ln25vgr-air-conditioning-system-natural-white.html</a> (there's also a 3.5kW version in the same range).<br /><br />Given the low delta-T needed for the main space, may be low-temperature HP UFH there too?<br /><br />Definitely go for shower water heat recovery if possible, and low flow heads - personally I like this one:<br /><br /><a href="https://www.ebay.co.uk/itm/272946979261" target="_self" rel="nofollow">https://www.ebay.co.uk/itm/272946979261</a><br /><br />Some sort of dynamic modelling might be worth considering for overheating etc.]]>
		</description>
	</item>
	<item>
		<title>Sports hall</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15453&amp;Focus=263970#Comment_263970</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15453&amp;Focus=263970#Comment_263970</guid>
		<pubDate>Fri, 15 Dec 2017 17:58:47 +0000</pubDate>
		<author>Doubting_Thomas</author>
		<description>
			<![CDATA[The Mayville Community Centre by Bere (admittedly a retrofit) might be a worthwhile reference: <a href="http://www.bere.co.uk/projects/mayville-community-centre-passivhaus-retrofit-85-savings" target="_self" rel="nofollow">http://www.bere.co.uk/projects/mayville-community-centre-passivhaus-retrofit-85-savings</a><br /><br />I seem to recall that they used bulk air-heating as this was compatible with the passivhaus fabric targets and allowed for the intermittent use patterns - i.e.  a quick blast in the morning when people arrive and then allow the building to cool down at other times.<br /><br />The biggest challenge in most Sports Halls that I've worked on was actually acoustics - can't have many soft absorbent surfaces at the level of noise generation. Admittedly these were schools where lessons will take place in the hall, but worth considering nonetheless. The solution could end up helping other problems if you, say, lined the hall in a perforated timber that also concealed conventional radiators for instance.<br /><br />Diffuse and constant light is another thing that can be overlooked. The Sport England guidance on this is actually quite good. Again from memory, games like Badminton are particularly sensitive to decent lighting to the point where artificial light may be the only way to achieve the uniformity required to let you actually perceive the shuttlecock. May not be relevant depending on the context, but give it some thought as you'll no doubt want to keep windows to a minimum anyway for heat loss reasons.]]>
		</description>
	</item>
	<item>
		<title>Sports hall</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15453&amp;Focus=263979#Comment_263979</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15453&amp;Focus=263979#Comment_263979</guid>
		<pubDate>Sat, 16 Dec 2017 00:02:40 +0000</pubDate>
		<author>Rick_M</author>
		<description>
			<![CDATA[I assume DT's comment above is missing a 'too' - you can't have too many absorbent surfaces? And I agree; it's really difficult to hear teachers/coaches in sport halls due to the echo. I've never used a sports hall where this wasn't the case, I think you have to experience it to realise how much of a pain it is. I agree lighting is obviously important but natural light has always been a big plus in my experience.]]>
		</description>
	</item>
	<item>
		<title>Sports hall</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15453&amp;Focus=263981#Comment_263981</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15453&amp;Focus=263981#Comment_263981</guid>
		<pubDate>Sat, 16 Dec 2017 08:57:35 +0000</pubDate>
		<author>Nick Parsons</author>
		<description>
			<![CDATA[Rick_M, I am not sure it *is* missing a 'too'. I think D_T means that 'you can't have' (that is, it is not, because of the nature of the building - the need for windows, perhaps, or the need for hard surfaces  to bounce things off walls - *possible* to have) 'many soft surfaces.... But in terms of noise control, I agree with your point that (if it is possible to incorporate them), you can't have too many sound-absorbent surfaces. (On the other hand an acoustics engineer may come along shortly to tell us that you *can*!)]]>
		</description>
	</item>
	
		</channel>
	</rss>