Posted By: tonyNo, eps is made up of polystyrene balls squashed together and there are continuous air paths between each side of the sheets and so they are vapour permeable.
Closed cell sheets are not nor ate ones covered in foil.
Posted By: Nick ParsonsXPS (extruded polystyrene) is closed cell. Effectively it does not need a VCL since the insulant is its own VCL.
Posted By: fostertom
Hold a piece of different insulants to the mouth. If you can get a good airseal, suck hard (hygene warnings apply!).
Posted By: lineweightNot a test one can really do at a specification stage!


If EPS can provide some vapor permeability as well as better performance...then it seems like it has a lot going for it.
But I've never really been able to find anything conclusive about how we should expect it to perform in real life. Are there any examples of real world tests to examine whether a thick layer of EPS can allow moisture trapped behind it to escape?
Such a test wouldn't necessarily need to prove that it performed in an equivalent way to other insulation materials - just that it was sufficiently permeable to allow, say, a reasonable level of construction moisture to escape within a time period short enough to avoid that moisture starting to cause problems
Posted By: djh
So EPS has the advantage that it doesn't rot, and the disadvantage that it isn't really hygroscopic. So it's ideal for use on the outside of organic components, so keeping them warm enough that RH doesn't get high enough for rot to start.
Posted By: lineweightAgree with all that, but with the niggling concern remaining about whether there's enough evidence to show that it will allow any trapped moisture out, where there's timber present. The concern's not about moisture resulting from interstitial condensation, but about moisture that gets introduced at construction stage, or perhaps resulting from small leaks.
Posted By: TimSmallSlightly idiosyncratic, but some useful rules of thumb here I thought:
https://buildingscience.com/documents/insights/bsi-038-mind-the-gap-eh
Posted By: djhPosted By: lineweightAgree with all that, but with the niggling concern remaining about whether there's enough evidence to show that it will allow any trapped moisture out, where there's timber present. The concern's not about moisture resulting from interstitial condensation, but about moisture that gets introduced at construction stage, or perhaps resulting from small leaks.
I believe it does allow moisture through, for the reason Tom gives, among others.
But note that if the insulation is outside the 'rottable stuff', then the moisture doesn't need to get out, because the RH should be low enough that the 'rottable stuff' won't rot. It's still much, much better if it can get out of course, and all designs should be such that it can get out, preferably in multiple ways. The source of the water doesn't really matter; it's all water.
Posted By: lineweightNot sure I follow that. Isn't it the moisture content of the rottable stuff that matters, rather thsn the RH of any air next to it?
Posted By: djhPosted By: lineweightNot sure I follow that. Isn't it the moisture content of the rottable stuff that matters, rather thsn the RH of any air next to it?
The moisture content and the RH are related by the sorption curve, with large time lags of course.
Posted By: lineweightI still don't really follow. If there's moisture in timber, yes it's related to the humidity of any air surrounding it. But if the humidity in that air can't escape because it's trapped by vapour-impermeable materials then it's just going to sit there isn't it? It doesn't really matter what temperature that part of the construction is at: the moisture is in the timber and can't go anywhere.
Posted By: djhPosted By: lineweightI still don't really follow. If there's moisture in timber, yes it's related to the humidity of any air surrounding it. But if the humidity in that air can't escape because it's trapped by vapour-impermeable materials then it's just going to sit there isn't it? It doesn't really matter what temperature that part of the construction is at: the moisture is in the timber and can't go anywhere.
Yes, if you wrap the timber in plastic. That's why you wrap it with hygroscopic and/or vapour-open materials instead.
I'm not claiming you can hermetically seal everything, add as much water as you like and everything will be fine. Sorry if I gave that impression.
Posted By: lineweightIt was this comment that I'd picked up on, but maybe misunderstood -
"But note that if the insulation is outside the 'rottable stuff', then the moisture doesn't need to get out, because the RH should be low enough that the 'rottable stuff' won't rot."