<?xml version="1.0" encoding="utf-8"?>
	<rss version="2.0">
		<channel>
			<title>Green Building Forum - Engineered wood over limecrete floor</title>
			<lastBuildDate>Thu, 16 Apr 2026 18:49:30 +0100</lastBuildDate>
			<link>https://www.greenbuildingforum.co.uk/newforum/</link>
			<description></description>
			<generator>Lussumo Vanilla 1.0.3</generator>
			<item>
		<title>Engineered wood over limecrete floor</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16745&amp;Focus=283737#Comment_283737</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16745&amp;Focus=283737#Comment_283737</guid>
		<pubDate>Mon, 05 Oct 2020 23:22:40 +0100</pubDate>
		<author>graham_cbruk</author>
		<description>
			<![CDATA[Hi all, <br /><br />I have a conundrum... we're installing a Geocell/limecrete floor with underfloor heating. I'm planning on laying engineered wood flooring but have found conflicting advice with regard to the best approach to installing it. <br /><br />Some experts say you should lay the wood on treated battens with an air gap, whilst others say it's fine to float the wood on a breathable underlay. The downside of the batten approach is that the air will diminish the transfer of heat from the UFH, whilst the (possible) downside of the floating approach is that the floorboards will be damaged, over time, by moisture coming up through the breathable limecrete floor. However as the Geocell, is non-capillary, it's also possible that this will manage the moisture effectively below the UFH and leave the limecrete dry.<br /><br />Has anyone else had to deal with this conundrum - and if so what solution did you settle on? I'm particularly interested in the experiences of people that have had engineered wood floors down over limecrete for some years and so have real world experience of the outcomes over a decent period of time! <br /><br />Thanks in advance for any thoughts.<br /><br />Graham]]>
		</description>
	</item>
	<item>
		<title>Engineered wood over limecrete floor</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16745&amp;Focus=283740#Comment_283740</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16745&amp;Focus=283740#Comment_283740</guid>
		<pubDate>Tue, 06 Oct 2020 09:25:57 +0100</pubDate>
		<author>tony</author>
		<description>
			<![CDATA[I dont see the batten approach as a problem, the heat will still go through ,  and pipe sizing /flow temperatures /flow rates can all be optimised<br /><br />I would not like the wood to see any high moisture levels from underneath --  fail safe design for me would be dpm, sorry - ft the wood gets damp from under it will fail <br /><br />If the house is warmer than the ground then moisture vapour will move from the house into the ground , floods, spills and leaks are all risks]]>
		</description>
	</item>
	<item>
		<title>Engineered wood over limecrete floor</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16745&amp;Focus=283747#Comment_283747</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16745&amp;Focus=283747#Comment_283747</guid>
		<pubDate>Tue, 06 Oct 2020 12:12:11 +0100</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: tony</cite>I dont see the batten approach as a problem, the heat will still go through</blockquote><br />That's true but the air gap adds thermal resistance, so the heat flow calcs need to be worked out appropriately. The pipes might need to be closer together or the flow temperature increased as against a solid construction.<br /><br />One thing I would say is to make sure that the floor is very dry before laying the timber, and make sure the timber has acclimatised for many months in the room before it is laid. The alternative is gaps between boards (and/or at the edges).]]>
		</description>
	</item>
	<item>
		<title>Engineered wood over limecrete floor</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16745&amp;Focus=283757#Comment_283757</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16745&amp;Focus=283757#Comment_283757</guid>
		<pubDate>Tue, 06 Oct 2020 15:35:59 +0100</pubDate>
		<author>Ed Davies</author>
		<description>
			<![CDATA[I'd think the higher temperatures in the slab needed to get the same heat flow with the extra thermal resistance of the air gap will result in more heat losses downwards into the ground. How much difference this will make will depend a lot on the characteristics of the ground, particularly how wet it is and, if it is wet, how much the water moves.]]>
		</description>
	</item>
	<item>
		<title>Engineered wood over limecrete floor</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16745&amp;Focus=283765#Comment_283765</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16745&amp;Focus=283765#Comment_283765</guid>
		<pubDate>Tue, 06 Oct 2020 19:43:03 +0100</pubDate>
		<author>Peter_in_Hungary</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: Ed Davies</cite>I'd think the higher temperatures in the slab needed to get the same heat flow with the extra thermal resistance of the air gap will result in more heat losses downwards into the ground. How much difference this will make will depend a lot on the characteristics of the ground, particularly how wet it is and, if it is wet, how much the water moves.</blockquote><br />Should there not be insulation under the UFH or slab to prevent downward losses?]]>
		</description>
	</item>
	<item>
		<title>Engineered wood over limecrete floor</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16745&amp;Focus=283766#Comment_283766</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16745&amp;Focus=283766#Comment_283766</guid>
		<pubDate>Tue, 06 Oct 2020 19:45:29 +0100</pubDate>
		<author>tony</author>
		<description>
			<![CDATA[yes, min 300mm eps/foamed glass]]>
		</description>
	</item>
	<item>
		<title>Engineered wood over limecrete floor</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16745&amp;Focus=283772#Comment_283772</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16745&amp;Focus=283772#Comment_283772</guid>
		<pubDate>Tue, 06 Oct 2020 21:04:16 +0100</pubDate>
		<author>Ed Davies</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: Peter_in_Hungary</cite>Should there not be insulation under the UFH or slab to prevent downward losses?</blockquote>Of course, but insulation doesn't prevent losses, only reduces them.]]>
		</description>
	</item>
	<item>
		<title>Engineered wood over limecrete floor</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16745&amp;Focus=283774#Comment_283774</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16745&amp;Focus=283774#Comment_283774</guid>
		<pubDate>Tue, 06 Oct 2020 22:04:26 +0100</pubDate>
		<author>graham_cbruk</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: tony</cite>--  fail safe design for me would be dpm,</blockquote><br /><br />Thanks Tony, but... similar to others on the site, we've bought in (rightly or wrongly!) to the idea that a (non-breathable) concrete  slab drives ground moisture to the sides and up the wall. Whether this actually happens or not has been questioned by some, but equally, from my research many experts seem to believe it does. Either way, we needed a (new) heating system and have opted for a Ground Source Heat Pump with UFH, so had to break up the uninsulated concrete slab and replace it with something; the Geocell (foamed glass) + limecrete solution ticked boxes on a number of fronts: environmentally friendly, sustainable, overcomes the "rising damp in walls" issue (if it existed). So whilst I accept that a DPM would be the safe bet from the wood's perpsective, it would also, at least partially, defeat the purpose of the breathable limecrete.<br /><br />djh and Ed: yes, I was also thinking that putting the UFH pipes closer together might be one way of countering the reduction in upward heat due to the air gap if we went with the battened solution. One to discuss with the heating engineers I guess!<br /><br />Of course the thing we don't know is how damp (if at all) the surface of the limecrete might get. As the Geocell is non-capilliary it shouldn't draw up moisture from below; so once thoroughly dried out and heated it should, arguably, be pretty dry.<br /><br />Does anyone have real world experience of either (i) wood rotting or (ii) everything being fine when engineered wood has been floated on limecrete? This is certainly my preferred solution (for heat transfer reasons) but if I go down this route I'd like to have some level of confidence that I'm not going to have replace the floor again in 10 years time!]]>
		</description>
	</item>
	<item>
		<title>Engineered wood over limecrete floor</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16745&amp;Focus=283775#Comment_283775</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16745&amp;Focus=283775#Comment_283775</guid>
		<pubDate>Tue, 06 Oct 2020 22:18:08 +0100</pubDate>
		<author>tony</author>
		<description>
			<![CDATA[I have a philosophy on moisture movement, it moves away from warmer places to cooler places. This is driven by partial vapour pressures so I am thinking that moisture will be moving downwards and outwards through your floor. <br /><br />Water is more dangerous, floods leaks and spills.]]>
		</description>
	</item>
	<item>
		<title>Engineered wood over limecrete floor</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16745&amp;Focus=283778#Comment_283778</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16745&amp;Focus=283778#Comment_283778</guid>
		<pubDate>Tue, 06 Oct 2020 22:41:53 +0100</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: tony</cite>Water is more dangerous, floods leaks and spills.</blockquote><br />But that also moves downwards, unless there's a DPM, and ceases to be a danger. And outwards through the doors in the case of floods, with the assistance of a brush.<br /><br />The Geocell is a capillary break so the limecrete should indeed dry out: but very, very slowly. Maybe a year or so? If it's possible to loose-lay the floor and live with it like that for a while, that's what I'd do. Then you can check for problems, and adjust the plank spacing, before making final fixings.]]>
		</description>
	</item>
	<item>
		<title>Engineered wood over limecrete floor</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16745&amp;Focus=283780#Comment_283780</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16745&amp;Focus=283780#Comment_283780</guid>
		<pubDate>Wed, 07 Oct 2020 06:21:37 +0100</pubDate>
		<author>tony</author>
		<description>
			<![CDATA[Any residual damp/moisture in or under the floor even from drying out will cause problems for the flooring, possible cupping, swelling and writing it off]]>
		</description>
	</item>
	<item>
		<title>Engineered wood over limecrete floor</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16745&amp;Focus=283782#Comment_283782</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16745&amp;Focus=283782#Comment_283782</guid>
		<pubDate>Wed, 07 Oct 2020 08:44:42 +0100</pubDate>
		<author>GreenPaddy</author>
		<description>
			<![CDATA[For UFH that does not reject its heat into the floor effectively, you can end up with the supply and return temps at the HP being very similar, so the HP shuts itself down before sufficient energy has been emitted to the rooms. I've seen this a couple of times on projects I've been asked to visit after the "experts" couldn't get the heating to work, blaming the HP as being at fault. One was exactly as you described with an air gap from pipes to a wooden floor.<br /><br />I'm wondering if the premis of high vapour movement and timber floors is not at odds? Thin timber boards will suffer a certain amount of vapour. Is that tolerance level above or below the vapour transfer levels you have in mind. No idea how you could ever know what those numbers might be, as there are so many varying factors on either side of the floor boards.]]>
		</description>
	</item>
	<item>
		<title>Engineered wood over limecrete floor</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16745&amp;Focus=283784#Comment_283784</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16745&amp;Focus=283784#Comment_283784</guid>
		<pubDate>Wed, 07 Oct 2020 10:12:24 +0100</pubDate>
		<author>Ed Davies</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: graham_cbruk</cite>djh and Ed: yes, I was also thinking that putting the UFH pipes closer together might be one way of countering the reduction in upward heat due to the air gap if we went with the battened solution. One to discuss with the heating engineers I guess!</blockquote>That might address the concern GreenPaddy has with transmission of heat into the slab but still, once the system's at equilibrium the whole top of the slab will be at pretty much the same temperature which will determine the heat losses downwards. The spacing of the pipes will make little difference to that.<br /><br /><blockquote ><cite >Posted By: GreenPaddy</cite>I'm wondering if the premis of high vapour movement and timber floors is not at odds? Thin timber boards will suffer a certain amount of vapour. Is that tolerance level above or below the vapour transfer levels you have in mind. </blockquote>Exactly, it seems weird to put down a sub-floor with the intention that it'll transmit water upwards then lay a finish floor across the top which might or might not be damaged by that.<br /><br />I've no idea what would be a good vapour-open finish floor, though.]]>
		</description>
	</item>
	<item>
		<title>Engineered wood over limecrete floor</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16745&amp;Focus=283821#Comment_283821</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16745&amp;Focus=283821#Comment_283821</guid>
		<pubDate>Fri, 09 Oct 2020 08:43:39 +0100</pubDate>
		<author>graham_cbruk</author>
		<description>
			<![CDATA[GreenPaddy and Ed: thanks for your comments.  I'm not entirely sure I follow them completely but my comments back are:-<br /><br /><blockquote ><cite >Posted By: Ed Davies</cite><blockquote ><cite >Posted By: GreenPaddy</cite>I'm wondering if the premis of high vapour movement and timber floors is not at odds? Thin timber boards will suffer a certain amount of vapour. Is that tolerance level above or below the vapour transfer levels you have in mind.<br /><br />1) Yes, I'm using engineered wood which I believe should be tolerant of some level of vapour movement - but I have no idea what or how I would ever measure it, so that seems a bit academic.<br /><br /></blockquote>Exactly, it seems weird to put down a sub-floor with the intention that it'll transmit water upwards then lay a finish floor across the top which might or might not be damaged by that.<br /><br />I've no idea what would be a good vapour-open finish floor, though.</blockquote><br /><br />2) well, yes, elsewhere in the house I'm laying limestone flags which obviously won't suffer any issues from damp (that I'm aware of - someone might tell me otherwise!), but lots of people have, I'm sure, used wood over limecrete successfully (otherwise where are all the people saying "NO - don't do it" ?!). I think I'm going to take my chances with the underlay - though will discuss further with the heating engineers later today...]]>
		</description>
	</item>
	<item>
		<title>Engineered wood over limecrete floor</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16745&amp;Focus=283825#Comment_283825</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16745&amp;Focus=283825#Comment_283825</guid>
		<pubDate>Fri, 09 Oct 2020 13:41:24 +0100</pubDate>
		<author>owlman</author>
		<description>
			<![CDATA[Had you looked at Schluter Ditra or similar, de-coupling mats. I know they are intended for tiling over indeed I've used them frequently but they MAY?? allow the engineered floor to be floated over them.]]>
		</description>
	</item>
	<item>
		<title>Engineered wood over limecrete floor</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16745&amp;Focus=283826#Comment_283826</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16745&amp;Focus=283826#Comment_283826</guid>
		<pubDate>Fri, 09 Oct 2020 16:31:29 +0100</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: owlman</cite>Had you looked at Schluter Ditra or similar, de-coupling mats. I know they are intended for tiling over indeed I've used them frequently but they MAY?? allow the engineered floor to be floated over them.</blockquote><br />I think Graham's idea is to have a breathable (vapour permeable) construction, not another vapour barrier? Hence the Geocell and limecrete plus engineered timber and limestone flags.]]>
		</description>
	</item>
	<item>
		<title>Engineered wood over limecrete floor</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16745&amp;Focus=283828#Comment_283828</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16745&amp;Focus=283828#Comment_283828</guid>
		<pubDate>Sat, 10 Oct 2020 01:02:21 +0100</pubDate>
		<author>owlman</author>
		<description>
			<![CDATA[I must have read this wrong then?<br /><br />From Schluters website:-<br />c) Equalisation of vapour pressure<br />The interconnected air channels between the cavities on the underside of the SchlÃ¼terÂ®-DITRA 25 matting remain open. This allows moisture in the substrate to evaporate, therefore neutralising vapour pressure.]]>
		</description>
	</item>
	<item>
		<title>Engineered wood over limecrete floor</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16745&amp;Focus=283840#Comment_283840</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16745&amp;Focus=283840#Comment_283840</guid>
		<pubDate>Sat, 10 Oct 2020 14:39:31 +0100</pubDate>
		<author>graham_cbruk</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: djh</cite>I think Graham's idea is to have a breathable (vapour permeable) construction, not another vapour barrier? Hence the Geocell and limecrete plus engineered timber and limestone flags.</blockquote><br /><br />Thanks for the suggestion owlman but djh is right on both counts: we want a breathable floor and Ditra appears to be a waterproof membrane, so unfortunately a non-starter for us.]]>
		</description>
	</item>
	<item>
		<title>Engineered wood over limecrete floor</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16745&amp;Focus=310285#Comment_310285</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16745&amp;Focus=310285#Comment_310285</guid>
		<pubDate>Tue, 24 Feb 2026 06:21:24 +0000</pubDate>
		<author>CraigF</author>
		<description>
			<![CDATA[Hi Graham. I’ve been reading through the chat above. How did your timber floor finish perform on the limecrete and did you have any issues? I’d be really grateful for any information from you or other members as we’re going through a similar dilemma. Thanks.]]>
		</description>
	</item>
	<item>
		<title>Engineered wood over limecrete floor</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16745&amp;Focus=310287#Comment_310287</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16745&amp;Focus=310287#Comment_310287</guid>
		<pubDate>Tue, 24 Feb 2026 10:41:10 +0000</pubDate>
		<author>fostertom</author>
		<description>
			<![CDATA[With non-capillary Geocel under it, why do we fear "moisture coming up through the breathable limecrete floor"? Yes the limecrete's initial mix water needs time to substantially react (hydrate) with the lime (not so much 'drying out', if the mix water was correctly proportioned) but absolutely no water should subsequently 'rise' through the Geocel from the ground. Spillage, and raised water table/flood, excepted.<br /><br />Yes, plenty of future water vapour travelling down through the wood floor, breather, limecrete - but that's harmless until/if it condenses as water. That won't be within the limecrete, as that's near enough room temp, or above with UFH. Condensation may happen within the lower reaches of the Geocel, where as liquid, without contrary upward capillary attraction, it will fall by gravity to the subsoil.<br /><br />The subsoil surface will be the all-seasons, reliable 'condensing plate' removing quite a large proportion of the house's internal vapour generation, as well as moisture entering through windows in some seasons and/or reverse-permeating through walls etc. What is important is that this subsoil-surface condensation can readily drain away to somewhere by gravity. What you don't want is the Geocel zone to act like a bathtub slowly filling with condensate.<br /><br />If ground water table periodically rises into the Geocel zone, insulation value will temporarily suffer, but all is well as long as the water can drain away when the water table drops back. If the water table rises higher than that, it's called Flood!]]>
		</description>
	</item>
	<item>
		<title>Engineered wood over limecrete floor</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16745&amp;Focus=310291#Comment_310291</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16745&amp;Focus=310291#Comment_310291</guid>
		<pubDate>Tue, 24 Feb 2026 16:18:35 +0000</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: fostertom</cite>What you don't want is the Geocel zone to act like a bathtub slowly filling with condensate.</blockquote>Indeed. I was very concerned about this risk when we built so I put a spare piece of drainpipe vertically underneath a mini access chamber cover, down to nearly the bottom of the 2 m deep hardcore-filled hole that sits underneath our house (to prevent clay heave from trees). There's also a French drain around the house. Never seen any sign of water when I put a dipstick down the drain pipe.<br /><br />In one room (so-called bin store) we actually have geocel underneath flagstones on top of the hardcore. Never seen any problems there either.<br /><br />Oh and I'm still very pleased with the bamboo flooring we used a lot on the ground floor in the house. It supposedly doesn't care much about water and is very stable compared to timber. I used it in the bathroom of our previous house.]]>
		</description>
	</item>
	
		</channel>
	</rss>