Posted By: RexI have sent an e-mail to the Swedish manufacturerHave you got the correct manufacturer? Looks like they could be Finnish?
Posted By: Mike1Certainly that looks like the control panel. The MVHR manufacturer is apparently Norwegian, with a Swedish factory, according to https://www.flexit.no/en/about-flexit/about-us/ and an American domain for email export@flexit.com !Posted By: RexI have sent an e-mail to the Swedish manufacturerHave you got the correct manufacturer? Looks like they could be Finnish?
https://www.onninen.fi/en/onnline-control-panel-energy/p/AHN331
Posted By: RexReplacement stats are available from Sweden/Norway, but will continue to monitor before replacing.
Posted By: GreenPaddyThe MVHR manuf will have bought the stat from a stat manuf, just as you can.
Posted By: RexCannot find anything that resembles my current stat base. As the second will fit but the face will not protrude into the air flow, am I likely to encounter any difficulties?I can't imagine that a 2mm projection would make a great deal of difference. However I can see a couple of stats that do project - the Fagor Brandt 283311AAC and 95X0080 (may be the same product) - which I assume are normally closed as they're also safety thermostats, but not sure what their dimensions are. For example https://spares2repair.co.uk/fixed-value-thermostat-limiter-safety-80o-fagor-brandt (available for ¼ of that price in Europe). Zooming in that looks like 16A 250V AC too, though that may be a 4 in brackets on the Ampage?
Posted By: Rexthe most common stat is 10/250AC but my current is 16/250AC.That will be 16A 25V AC current, the maximum it can safely handle
Posted By: RexWhat happens if I fit a 10/250AC?If your HVMR unit is running at 230V and protected by a breaker of 10A maximum (I'd guess it may be 2A?), it should be fine.
Posted By: WillInAberdeen While you have it out, put it in the cold kitchen oven. Turn the oven on to its lowest setting so it slowly warms up. Every minute, measure the oven temperature with a thermometer and check if the stat has tripped yet. Stop when it does, and note the final temperatureThe 80â° safety stat is there to prevent a fire/meltdown if the fan airflow ever got blocked/stopped whilst the heater was energised. The other stat is the everyday on/off control that decides if heating is required today depending on the weather, test it in your freezer. There is no guarantee that either one still works at the original specified temperature, until you test...!
You can use this info: a) to check if the stat is tripping at a sensible temperature or **if the fault lies elsewhere**, and b) to search for an equivalent stat.
(And - obviously - stop before anything melts!)
Posted By: WillInAberdeenEven if not needed for heating the house, the preheaterPreheaters can never heat the house, because their heat is immediately exchanged with the outgoing air! They are, as you say, to eliminate the possibility of condensation freezing within the MVHR unit, either within the heat exchanger or possibly on the fans or ducts. PH-certified MVHR units are required to use pre-heating rather than varying the ventilation rates. A post heater can be used to heat the house.
Posted By: RexI am assuming that something like this
manual-reset-thermostat/1211154-thermostat-80-closed.html