Home  5  Books  5  GBEzine  5  News  5  HelpDesk  5  Register  5  GreenBuilding.co.uk
Not signed in (Sign In)

Categories



Green Building Bible, Fourth Edition
Green Building Bible, fourth edition (both books)
These two books are the perfect starting place to help you get to grips with one of the most vitally important aspects of our society - our homes and living environment.

PLEASE NOTE: A download link for Volume 1 will be sent to you by email and Volume 2 will be sent to you by post as a book.

Buy individually or both books together. Delivery is free!


powered by Surfing Waves




Vanilla 1.0.3 is a product of Lussumo. More Information: Documentation, Community Support.

Welcome to new Forum Visitors
Join the forum now and benefit from discussions with thousands of other green building fans and discounts on Green Building Press publications: Apply now.

The AECB accepts no responsibility or liability for any errors or omissions in the content of this site. Views given in posts are not necessarily the views of the AECB.



  1.  
    This is a picture from the space below my (1930s detached) house. A couple of months ago I insulated between the floor joists but when I went down there today was shocked to see condensation on the bottom of the insulation boards. There is no drainage outside the walls and the space floods in the winter. The ground below is still quite wet. It is always damp down there but I’ve never seen any condensation before I put the insulation in. There is ventilation, (4 x 8”x3”) but perhaps not enough. I am digging away soil from the external poured concrete foundation walls, but apart from getting this done and drainage installed asap, what can I do? Dehumidifiers? What about a polythene damp course, would that help, or just prevent the ground from ever drying out?
    • CommentAuthorChristopher
    • CommentTimeJul 7th 2023 edited
     
    Photo too big, will try to re-size
  2.  
    Picture
      5BF64F26-5A2D-46D8-A692-7C362F2111CC.jpg
  3.  
    Outside wall
      0B21C730-80F9-4CAB-9BBD-600F4255DFA8.jpg
  4.  
    Is it over all the insulation or in a particular part of the void?

    Had you taken moisture readings for all the joist ends before you started?

    A bit too late to change insulants but this may be of some use:

    "The act of insulating a suspended timber floor cools down the floor structure and may increase the risk of condensation occurring on the floor timbers.

    These risks can be reduced somewhat if there is excellent cross-ventilation below the suspended floor which can ‘blow away’ any water vapour-laden air before it can condense out.

    Nevertheless I recommend that a ‘risk management approach’ should be taken in every case before proceeding with insulation of a suspended timber floor.

    First I would suggest that you measure the moisture content of the joist ends as they enter the ‘pockets’ in the wall. Crudely, less than 18% may be good, 20% may be acceptable, but much higher may be indicative of a risk factor.

    Get an idea of the general level of moisture below the floor. Is it quite wet? Does water come in when it rains? Can you prevent it coming in? If large quantities come in (standing water) can you pump it out? Perhaps as a one-off action, or perhaps you might need a sump with a float-switch-operated pump.

    Then look and see whether there is adequate cross-ventilation. For a rectangular floor-plan the ideal arrangement is to have ventilation at each corner. In a small terraced house, for example, a 225mm x 150mm air-brick at each corner may be sufficient. However even if adequate vents exist at front and rear typical cellars impede this ventilation by means of a stone staircase. In certain cases it may be possible (though not low-impact) to knock sufficiently large holes in the central spine wall (with the correct structural advice).

    The choice of insulation material can be difficult. Some sources suggest that a breathable fibrous insulant will help to manage moisture. Others take the view that fibrous insulants are absorbent and may worsen the situation by transferring moisture to the structural timbers. Opinions vary!

    What is clear is that, if the perimeter walls are at all damp it may be advisable to fix a perimeter layer of impermeable insulation such as extruded polystyrene (XPS) to prevent other insulants coming into contact with any moisture from the walls.

    Note that polystyrene should not come into contact with the PVC sheathing of electrical cables as it may make the casing brittle. Equally electrical cables should not be ‘tucked up warm’ in insulation. If they are, consult an electrician as the electrical regulations may require the circuit-breaker to be de-rated to reduce the risk of fire".


    Under-floor insulation guidance:

    https://www.gov.uk/government/publications/insulating-suspended-timber-floors-best-practice

    https://www.greenbuildingstore.co.uk/information-hub/insulating-suspended-timber-floors/

    https://www.ecologicalbuildingsystems.com/post/best-practice-approach-insulating-suspended-timber-floors

    http://www.sofiepelsmakers.com/suspended-timber-ground-floors.html

    I'd suggest your air-bricks may be a tad under-sized. I'd normally do for a minimum of 4 225 x 150s at diagonally-opposite corners.
  5.  
    Thanks for the reply and links Nick. I did not measure the moisture at the joist ends and suspect you might be correct about the ventilation being inadequate, although the issue is the amount of water remaining in the ground I think. The condensation is evenly spread on all the insulation, except for small areas (approx 1m radius) around the ventilators where it is dry.
  6.  
    Wot Nick said about getting an idea about the amount of moisture / water present during the year +1

    Given that the condensation is all over except in the location of the air bricks shows that ventilation controls the problem. Perhaps increase the ventilation (temporally or permanently) by the installation of a low wattage fan at an air brick or as an extra.
    • CommentAuthorcjard
    • CommentTimeJul 8th 2023
     
    "never seen any condensation before I put the insulation in"

    Either soaked into the wood or the heat loss from the house through the floor kept the surface above the dewpoint

    Spread out a plastic sheet on the ground; it floods every year so it isn't going to dry out anyway?
    • CommentAuthortony
    • CommentTimeJul 8th 2023
     
    I have seen this before with EPS stuck unde concrete planks, the water was so heavy that it pulled some of the less well stuck on insulation off

    1) don’t panic!

    2) monitor it for a while

    3) ask questions, is the wood damp,

    I have some solutions
  7.  
    Is “fully full the void with graphite EPS beads” one of the solutions?
  8.  
    Worth a read:
    https://buildingscience.com/documents/insights/bsi-009-new-light-in-crawlspaces

    Lstiburek is a famous building engineer from across the pond, to be fair this article is based on the climate in Maryland which is very hot and humid in the summer. He argues that the soil in the underfloor void stays close to the year-round average temperature (about 10-12⁰C in different parts of the UK, more in the US). The floors were originally warmer than that, so stayed dry, but if the floor is insulated, the lower edge of the insulation drops close to soil temperature (by heat radiation to/from the soil). So at 10-12⁰ there will be condensation whenever the air humidity dewpoint is more than that 10-12⁰, which it might be in humid summer weather.

    His proposed solution is 1) more ventilation 2) breathable floor to allow humidity to escape the build-up 3) insulation extended below the floor timbers so the timber remains above dewpoint even if the insulation doesn't.

    Reducing the humidity in the void also sounds a good idea, ours is never damp.
    • CommentAuthortony
    • CommentTimeJul 8th 2023
     
    Condensation is ugly and single minded and nasty minded. I finds places below dew-point and condenses on them

    The partial vapour pressure of the moisture in the air is the problem coupled with the temperature of a cool surface.

    Ventilation could make it worse!

    I like insulating under the joists 30mm EPS for me

    The insulation is working, it is cold on the underside.
    •  
      CommentAuthordjh
    • CommentTimeJul 8th 2023 edited
     
    Posted By: ChristopherThis is a picture from the space below my (1930s detached) house. A couple of months ago I insulated between the floor joists but when I went down there today was shocked to see condensation on the bottom of the insulation boards. There is no drainage outside the walls and the space floods in the winter. The ground below is still quite wet. It is always damp down there but I’ve never seen any condensation before I put the insulation in. There is ventilation, (4 x 8”x3”) but perhaps not enough. I am digging away soil from the external poured concrete foundation walls, but apart from getting this done and drainage installed asap, what can I do? Dehumidifiers? What about a polythene damp course, would that help, or just prevent the ground from ever drying out?
    I'm with Tony; add more insulation, especially under the joists, so they are warmer and condensation forms on the bottom of the new insulation instead. So you'll still have condensation but it will be in a place that it doesn't do any harm.

    Why does the space flood in winter? And will your new drainage stop it (where will it drain to)? I don't think a damp proof membrane on the ground will help.

    If you can stop it flooding, so the only problem is condensation from the air, then it might be worth considering “fully fill the void with graphite EPS beads” as Dominic suggested. That's the ultimate in adding more insulation :bigsmile:

    Joe Lstiburek's article is useful, but it's important to remember that he's describing very different conditions to the UK, so some of his advice doesn't translate well. Use his science but draw your own conclusions.
  9.  
    We had a super humid day, a day or so ago, so may correspond to that. As per Tony and others above, the insulation face happens to be cooler than the dew point, so it's doing its job (keeping the zone above it warmer). The dew point will have been quite high on that very humid day, so any fresh air coming in to the floor void will have been adding to the condensation. That's true for probably not that many days of the year, so good ventilation is mostly a positive thing.
    Also agree with Tony & DJH about keeping the timber structure warm (ie. the joists), so if you can add some more insulation, to cover those timber bottom edges, it will help protect it.
  10.  
    @djh I hope that digging earth away from the walls and putting in drainage will keep things dry(er) below the floor, will drain to a pond in front of the house. But if the condensation is coming from the air, might still be an issue.

    @tony Got a moisture meter and checked the joists, they are certainly damp, mostly high 20s some over 30% the highest readings were nearest the vents.

    The layer of insulation below the joists sounds like it is worth doing, but presume the wood needs to dry out a bit first?
    • CommentAuthortony
    • CommentTimeJul 14th 2023
     
    Yes, let the wood dry out first, I would go for EPS under the joists as it will breathe out any moisture.

    Well done so far.
    • CommentAuthorborpin
    • CommentTimeJul 30th 2023
     
    If the insulation has condensation, then the insulation is working as it is the coldest surface.

    Where is your water table? If you dig a hole outside, does it fill with water?

    I'd be concerned that the moisture is coming up from below. What is the ground - soil/rubble?

    Did you insulate from below? The fact you can get to the joist ends suggest there is good access.

    *If* the moisture is coming from below, I'd suggest that you need to stop it. A new build would have a sheet of plastic and a concrete blind over the top.
    • CommentAuthortony
    • CommentTimeJul 30th 2023
     
    It is not damp from below that is the problem, it is moisture in the air and that can’t be stopped. Condensation forms on cool surfaces when the cool surface is at or below the dew point temperature.
    • CommentAuthorborpin
    • CommentTimeJul 31st 2023
     
    Posted By: tonyIt is not damp from below that is the problem, it is moisture in the air and that can’t be stopped.
    But I am wondering how that moisture is getting into the air. If the ground is damp, that is the source.

    Adding more insulation isn't going to stop the condensation (the surface will still be the coldest point). Unless the joists are completely sealed, it could make it worse. You suggest EPS so it will breathe but equally, the dew point could be within the insulation. At worst, directly between the 2 layers of insulation.

    I'd be trying to remove the source of the moisture first.

    It could also be that the steady state has not been reached (if recently done) so you need greater intervention initially to reduce the moisture content. If other conditions are OK, it will not return, but the 'system' cannot remove the initial excess.
    • CommentAuthortony
    • CommentTimeJul 31st 2023
     
    Dew point is generally on the outside or outside illiterate of the insulation. (The exception is with a very rare phenomenon card suer condensation)

    If the house is warmer than the ground moisture will be moving from the house into the ground, driven by partial vapour pressures being higher in warmer places.

    I once surveyed a house on the Wirral where the oversite was under a few inches of water with a wooden floor a foot above it. Lots of houses on the estate were the same due to a high water table. 1980’s and the estate was 1960’s ,no problems with the wooden floors,joists or condensation in the homes.
    • CommentAuthorborpin
    • CommentTimeJul 31st 2023
     
    Posted By: tonyIf the house is warmer than the ground moisture will be moving from the house into the ground, driven by partial vapour pressures being higher in warmer places.
    If so, then I'd like to find the source. Looked well sealed in the picture.

    It could also be damp air from before insulation that needs to be forced out to reach a new steady state.

    Still cannot see how more insulation solves it as the new surface will still be the coldest surface.
Add your comments

    Username Password
  • Format comments as
 
   
The Ecobuilding Buzz
Site Map    |   Home    |   View Cart    |   Pressroom   |   Business   |   Links   
Logout    

© Green Building Press