Home  5  Books  5  GBEzine  5  News  5  HelpDesk  5  Register  5  GreenBuilding.co.uk
Not signed in (Sign In)

Categories



Green Building Bible, Fourth Edition
Green Building Bible, fourth edition (both books)
These two books are the perfect starting place to help you get to grips with one of the most vitally important aspects of our society - our homes and living environment.

PLEASE NOTE: A download link for Volume 1 will be sent to you by email and Volume 2 will be sent to you by post as a book.

Buy individually or both books together. Delivery is free!


powered by Surfing Waves




Vanilla 1.0.3 is a product of Lussumo. More Information: Documentation, Community Support.

Welcome to new Forum Visitors
Join the forum now and benefit from discussions with thousands of other green building fans and discounts on Green Building Press publications: Apply now.

The AECB accepts no responsibility or liability for any errors or omissions in the content of this site. Views given in posts are not necessarily the views of the AECB.



    • CommentAuthorRex
    • CommentTimeJan 6th 2024 edited
     
    What ho one and all,

    My wife this afternoon, decided she would like to have a hot bath. Unfortunately the water was not terribly hot and I got some flak for not knowing how to boost the temp on a one-off basis.

    I have searched the instruction book but cannot find anything as useful as 'Hot Water Boost.' Most of the instructions assume that I want to boost the pressure, not the temperature. I occasionally use, the 'Party' mode, which will heat the DHW first, before heating the house to the desired increased room temp. but this time, I do not want to heat the house.

    Is there a simple way to just boost the hot water temperature and if so, how?

    Many thanks.
    • CommentAuthorJonti
    • CommentTimeJan 7th 2024
     
    Kettle?
    • CommentAuthorRex
    • CommentTimeJan 7th 2024
     
    My wife is Japanese and we have lived there in the past. Most houses do not have the hot water cylinder set-up that we have in the UK. They generally do not store hot water.

    The bath is a tub of water that gets used for a couple of days and obviously, does cool down. It is filled with cold water and has an in-line gas boiler that heats the water as needed. Like a Jacuzzi, but considerably more efficient.

    The boiler is usually just a small unit mounted on an exterior wall with the bath on the inside of the wall. No pump, just convection heats the water.
    • CommentAuthorbhommels
    • CommentTimeJan 8th 2024
     
    It depends a bit on which version of the user interface you have.
    For my Vitodens 200, the second screen has the 'energy display' where all connected devices are shown, which in my case has the hot water cylinder in there as well. There is a button at the bottom with a battery-like symbol. That is the button that starts a one-off heating cycle for the cylinder, or, presumably, the bathtub.
    • CommentAuthorSimon Still
    • CommentTimeJan 9th 2024 edited
     
    Mine is the 222-F (which is a 'storage combo' with a small tank and quick recharge) but I suspect the controller is the same. I don't think there is any way to quickly over-ride - the assumption is that you're going to have the hot water heated whenever you might want to use it. ie just set the DHW to be on from the earliest time you get up to a bit the latest time you might ever have a bath or shower.

    With a well insulated tank surely the savings from trying to predict when you want to use hot water and only heating it in those periods would be pretty small wouldn't they? And if the tank is in your (well insulated) house then any losses warm the house in any case.
    • CommentAuthorRex
    • CommentTimeJan 15th 2024
     
    Thanks for your thoughts.

    I did call the Viessmann helpline and seems that my boiler (Vitoden 200W) does not have a boost option. His suggest is to have only one DHW heating time set, from early in the morning to late at night. Then, if the systems calls for more DHW, the boiler fires up to ensure the cylinder is always up to speed.

    I used to have that but found that the boiler was spending quite a lot of time with things running, using electricity but not actually needing to heat the DHW or UFH. Don't know the actual electricity usage but when one hears the boiler making 'working' noises, it must be using electricity.

    So now I have it set for two heating periods.

    However, more extensive Googling and an in-depth read of the User Manual and I found a section entitled "DHW for a Few Hours Only." Not exactly a chapter title I would have looked up!

    Seems that the best way is to go into Party Mode, which will heat the DHW first (before UFH), crank up the temp. and after 15-30 mins, turn Party Mode off. Alternatively, apparently, open Party Mode, do not change the temperature but do press OK to accept whatever is displayed; wait 10 or more seconds then turn PM off.

    An alternative method is to install a simpler to use immersion timer switch. The current one will do what it says on the box with a one hour boost, but with all the available heating options, it uses a back-up rechargeable battery to remember those settings. Since there is no need to have the switch powered up 24/7 for no reason, it has been off for X years, resulting in the battery loosing its charge. Turning it on kinda achieves nothing until the battery has a residual charge, then have to figure out how to set the time, date, etc, before the boost will work.

    I may be misjudging my wife, but if I find it difficult to figure out, don't think she will be able to do so.
    •  
      CommentAuthordjh
    • CommentTimeJan 15th 2024
     
    Posted By: RexAn alternative method is to install a simpler to use immersion timer switch. The current one will do what it says on the box with a one hour boost, but with all the available heating options, it uses a back-up rechargeable battery to remember those settings. Since there is no need to have the switch powered up 24/7 for no reason, it has been off for X years, resulting in the battery loosing its charge.
    I use a TimeGuard fused timer switch. Well I use two actually. It seems to work well and TimeGuard replaced one that died without a problem so I'm happy with it. It has to be switched on (i.e. not isolated) all the time in order for the timer to work and control the switched output, so it consumes some standby level of electricity. But the standby is very low (doesn't it have to be below 1 W now by law?) and clearly the timer can't work unless it has power so that's fine by me.
    • CommentAuthorSimon Still
    • CommentTimeJan 16th 2024 edited
     
    All the stuff I've seen recently says that standby losses on modern devices really are irrelevant - the regulation is sub 1W but the reality is nearly all are much much less than that.



    Posted By: RexThanks for your thoughts.
    An alternative method is to install a simpler to use immersion timer switch.

    I fitted something like this for my (demented) mother who had started leaving the immersion on all the time (after a fused spur/switch)
    https://www.tlc-direct.co.uk/Products/SMTGBT4N.html?

    But again you're into cost-benefit. It's costing you c3x as much to use the immersion to heat the water than it would to use your gas boiler and you've spent c£25+ installing a timeswitch.




    Posted By: RexThanks for your thoughts.
    I used to have that but found that the boiler was spending quite a lot of time with things running, using electricity but not actually needing to heat the DHW or UFH. Don't know the actual electricity usage but when one hears the boiler making 'working' noises, it must be using electricity.


    Do you have Weather Compensation installed on your boiler? what sort of flow and return temps are you using for the UFH? I think I posted something a few weeks back about the savings these offer - most UK condensing boilers rarely if ever work in condensing mode so are c85% efficient vs c95%.

    My UFH runs super cool (currently 0C outside, flow temp (solid/wood floor coverings) 26.5C/29.5C) and modulates the burner down (currently running at 21%) so it runs for long periods and doesn't cycle with the pumps running constantly but at low speed. I get the impression that cycling (ie firing up/down) is both inefficient and hard on the boiler - the app gives those stats in the diagnostics and mine runs at about twice the number of running hours as 'boilers starts' which the engineer was really happy about.

    the cost of running the electronics and pumps is pretty much insignificant compared to the energy of heating water - a few 10's of watts of electricity (this typical Grundfos pump maxes out at 34w https://www.screwfix.com/p/grundfos-alpha-1-15-50-60-domestic-heating-circulator-230v/483fj) whereas your boiler ). The smallest Vitodens 200 system boiler I can find is 11kW ie 11000watts.
    And of course all that electrical use generates a bit of heat anyway which isn't wasted.
    • CommentAuthorRex
    • CommentTimeJan 16th 2024
     
    The timer is question is the TimeGuard FST17A. I do have a TGBT4N installed on the cylinder in our rental maisonette. Very easy to use.

    Regarding the running cost of the FST17A, undoubtedly minimal when not in use but I make a point of turning off anything that does not need to be on, and that includes the computers and router overnight. All the tiny residuals gradually add up.
    •  
      CommentAuthordjh
    • CommentTimeJan 16th 2024
     
    Yes, FST17A is what I have got. Computers and routers and even LED lights use a whole lot more than a timeswitch. Switching off the router overnight is supposedly bad for your connection speed, IIRC. In a year or so it will also kill your landline phones as well as whatsapp etc on the mobiles.
    • CommentAuthorSimon Still
    • CommentTimeJan 16th 2024 edited
     
    Posted By: djhSwitching off the router overnight is supposedly bad for your connection speed, IIRC.


    But ironically, it's also one of the few devices that actually has a significant standby power consumption and seemingly one of those that varies quite significantly depending on the model. This is way out of date now - 2017 - but found different routers varied between 3w and 15W when idle.

    https://www.ispreview.co.uk/index.php/2017/01/energy-usage-uk-home-broadband-routers-big-isps-compared.html/3

    though at 2017 prices that meant leaving even on 24/7 was only costing £10-15 per year to run. I guess you might save a 1/3 of that?
    •  
      CommentAuthordjh
    • CommentTimeJan 16th 2024 edited
     
    From a more recent page on the same site:
    "Consumers with modern full fibre connections don’t need to worry about this, but frequently switching-off the router on a copper based broadband line (i.e. ADSL, FTTC / VDSL2 or G.fast) could cause the Dynamic Line Management (DLM) system to assume your connection is unstable and drop the speed to compensate.

    "As a side note, a lot of network operators tend to automatically push firmware (software) updates down to their broadband routers in homes during the early hours of the morning. Completely turning off the router during this period would disrupt that and might cause you to miss vital security or feature additions."
    (from https://www.ispreview.co.uk/index.php/2022/10/clarifying-the-confusion-over-turning-off-wifi-vs-broadband-at-night.html )

    I'm on a copper connection, so don't want to turn it off. Apparently the "average" power consumption of my router is 6 W. So turning it off overnight would save me 6*7*365 => 15 kWh @ 15p = £2.25 per year
    • CommentAuthorRex
    • CommentTimeJan 20th 2024 edited
     
    A saving a £10 - 15 per year; that is a few cups of coffee which I would prefer to have than pay the ISP for no reason whatsoever.

    I am with PlusNet on just standard fibre to the cabinet and copper to the house. The guarantee 35 mbs and that is what I have been getting for the past year.

    Prior to that, I was on BT copper, paying the least expensive option and always had around 7-9 mbs and that was also turning off every night.

    I certainly don't know about turning off and signal speed disruption, but could it not be a scam to pay that little bit extra to the ISP? Should also point out that we don't use wifi for the internet nor do we have any wifi enabled devices in the house, the exception being the mobile phones. Yes, my house is not 'smart.'
    •  
      CommentAuthordjh
    • CommentTimeJan 20th 2024
     
    My £2.15 doesn't seem to match Simon's £10-15?

    Yes, when I said copper, I meant fibre to the cabinet and then copper. I get 80 Mbps down/20 up; I'm quite close to the cabinet and use VDSL.

    The turning off thing is certainly not a scam. The modem in your router has to train itself to your copper wire every time it powers up. I'm impressed by your lack of wi-fi devices :bigsmile:
    • CommentAuthorwookey
    • CommentTimeJan 25th 2024
     
    Posted By: Simon StillAll the stuff I've seen recently says that standby losses on modern devices really are irrelevant - the regulation is sub 1W but the reality is nearly all are much much less than that.

    My Vitodens100 uses 9-11W doing nothing except waiting for the controller to tell it to start. It predates the EU standby regulations I think (fitted 2008) but they only apply to plug-in kit anyway, not permanently-fitted devices IIRC. I don't know if the vitoden200 is better in this regard. My router is 6W (and my ADSL modem 4W and my (green) switch a commendable 0.4W.

    So yes boilers can use non-trivial power doing nothing. (It's particularly bad in our house as the boiler gets actually asked for heat approximately 1 day/year over the last 8 years so I mostly leave it actually switched off).
    • CommentAuthorbhommels
    • CommentTimeJan 27th 2024
     
    My vitodens, even if it has no heat to generate, runs the pumps once a day to keep the impellers lubricated ('pump creep'). The few Wh that consumes is well worth it if it extends the lifetime of the internal pump and the UFH one.