<?xml version="1.0" encoding="utf-8"?>
	<rss version="2.0">
		<channel>
			<title>Green Building Forum - Slab with ASHP and overnight rate</title>
			<lastBuildDate>Sat, 09 May 2026 20:45:53 +0100</lastBuildDate>
			<link>https://www.greenbuildingforum.co.uk/newforum/</link>
			<description></description>
			<generator>Lussumo Vanilla 1.0.3</generator>
			<item>
		<title>Slab with ASHP and overnight rate</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18266&amp;Focus=307835#Comment_307835</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18266&amp;Focus=307835#Comment_307835</guid>
		<pubDate>Tue, 25 Feb 2025 10:55:47 +0000</pubDate>
		<author>neelpeel</author>
		<description>
			<![CDATA[I've always thought a large 'interseasonal store' type slab and PV was the ideal way to go for a new build / extension. But...<br />- We now have tariffs with very low overnight rates (or low periods for ASHP tariffs).  These rates are much lower than you can get for PV export so if you have a battery you are actually better off exporting all of your solar.<br />- Heat pumps can give you a CoP of 4+.<br /><br />So I think the killer combo is now probably a smaller slab with UFH that is getting charged up during the Autumn overnight with an ASHP (and then topped up as required through Winter/Spring)<br /><br />In the warmer months the CoP will be highest so you could be looking at 4.5X efficiency at least.  At £0.07/kWh (IOG overnight rate for example) this would equate to only 1.5p per kWh to charge the slab.  IOG tariff gives 6hrs cheap rate each night so in theory you could be putting in 6x7kW = 42kWh each night.<br /><br />Is anyone doing this yet??]]>
		</description>
	</item>
	<item>
		<title>Slab with ASHP and overnight rate</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18266&amp;Focus=307839#Comment_307839</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18266&amp;Focus=307839#Comment_307839</guid>
		<pubDate>Tue, 25 Feb 2025 12:46:28 +0000</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[I don't think an 'interseasonal store' type slab has ever been practicable. When I was planning my build I did consider incorporating a 20,000 litre water tank inside the house, extremely well insulated and using a variable ventilation system to direct the heat losses either to the outside or inside of the house depending on the season. Inspired by things like <a href="https://jenni.ch/publications-448.html?file=files/jenni/inhalte/pdf/Publikationen/Energie_fuers_Leben_english.pdf&cid=2910" target="_self" rel="nofollow">https://jenni.ch/publications-448.html?file=files/jenni/inhalte/pdf/Publikationen/Energie_fuers_Leben_english.pdf&cid=2910</a><br /><br />I agree that the floor slab is an important part of the 'thermal mass' of a house, and that UFH is a good way of incorporating a heat emitter in a building.<br /><br />I don't think there's any question of 'charging up' the slab on a seasonal basis. You simply maintain it at a constant temperature during the year.<br /><br />I presently heat up the 'thermal mass' of our house overnight using direct electric heaters, and that plus solar gains the following day are sufficient to keep the house comfortable. Control is pretty manual at present, relying on forecasts of how cold and/or sunny it will be for the next 24 hours.<br /><br />If I was building now, I would put UFH in the floor slab and use a heat pump with some suitable tariff to keep the house warm. But it's not obvious to me what the best transition is from my current system.]]>
		</description>
	</item>
	<item>
		<title>Slab with ASHP and overnight rate</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18266&amp;Focus=307842#Comment_307842</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18266&amp;Focus=307842#Comment_307842</guid>
		<pubDate>Wed, 26 Feb 2025 09:51:28 +0000</pubDate>
		<author>neelpeel</author>
		<description>
			<![CDATA[I've often pondered about using a large tank, but I kept coming to the conclusion that a zero maintenance large slab was the better long term solution.<br />I'm in the position now where I'm looking to extend the house by 40m2 in the next year or so and trying to decide how to heat.  I already have a 7kW ASHP, 10kW of PV and a 15kWh battery so the obvious solution is UFH.  I just need to get my head around the calculations for slab size and how much heat I need to store.  The ASHP demand swings hugely from a 6 degree day to a 0 degree day due to efficiency so I think having a large 'heat bank' would smooth this out.  It should allow me to use a lower 'heat curve' and hence much greater efficiency.]]>
		</description>
	</item>
	<item>
		<title>Slab with ASHP and overnight rate</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18266&amp;Focus=307843#Comment_307843</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18266&amp;Focus=307843#Comment_307843</guid>
		<pubDate>Wed, 26 Feb 2025 10:17:33 +0000</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: neelpeel</cite>I've often pondered about using a large tank, but I kept coming to the conclusion that a zero maintenance large slab was the better long term solution.</blockquote>You need to consider the quantity of energy (heat) that you want to store.<br /><br />energy stored  =  mass of store  x  specific heat of store material  x  temperature difference<br /><br />energy required  =  heat loss rate  x  time<br /><br />The big question is what temperature difference you can achieve/tolerate if you use the slab to store heat. With a water tank you potentially have about 80 K or so.]]>
		</description>
	</item>
	<item>
		<title>Slab with ASHP and overnight rate</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18266&amp;Focus=307846#Comment_307846</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18266&amp;Focus=307846#Comment_307846</guid>
		<pubDate>Wed, 26 Feb 2025 11:12:10 +0000</pubDate>
		<author>neelpeel</author>
		<description>
			<![CDATA[It's those loss rates that I'm trying to work out just now.  And to work out what, if any, insulation I need above the slab to ensure that the losses match the room demand.  I'll maybe post my workings and theory once done.<br /><br />The 80k differential is not an option for my ASHP, which works at much lower temperatures.  It will go to about 60deg, but efficiency drops like a stone once flow temps are over 40deg.<br /><br />Gut feel says that I want the slab no more than 30deg in Winter and insulated to the room sufficiently to maintain the room at 20deg (10deg differential).  It might be that thick underlay and wood floor is sufficient insulation.]]>
		</description>
	</item>
	<item>
		<title>Slab with ASHP and overnight rate</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18266&amp;Focus=307847#Comment_307847</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18266&amp;Focus=307847#Comment_307847</guid>
		<pubDate>Wed, 26 Feb 2025 12:06:41 +0000</pubDate>
		<author>Mike1</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: djh</cite>Inspired by things like [jenni.ch]</blockquote>Yes, there are quite a few using that method in Switzerland, either for individual houses, or small apartment blocks, like this one featured on YouTube: https://youtube.com/watch?persist_app=1&app=m&v=D0wPnlQBVUM<br /><br /><blockquote ><cite >Posted By: djh</cite>The big question is what temperature difference you can achieve/tolerate if you use the slab to store heat. With a water tank you potentially have about 80 K or so.</blockquote>I agree. The tank in that YouTube video can reach 95°C - certainly rather more than you'd want your slab.<br /><br />Then the specific heat capacity of concrete is around 20% of that of water. you'd need 5x the volume of concrete to store the same quantity of heat at 95°C. Then to cap the maximum to around 30°C, you'd need to multiply that by around another 3 times - so 15 x the volume of water (actually more than that, due to the extra heat losses due to the greater perimeter).<br /><br />When you get to those sorts of volumes, a 'better' alternative, if you're clear of the water table, might be to heat the ground, and to use a GSHP, rather than ASHP. Though that would need 2 separate pipe loops - one to pull the heat from the garden (or under the drive, which is likely to be hotter) to the store, another to pull the heat from the store to the house in winter.]]>
		</description>
	</item>
	<item>
		<title>Slab with ASHP and overnight rate</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18266&amp;Focus=307848#Comment_307848</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18266&amp;Focus=307848#Comment_307848</guid>
		<pubDate>Wed, 26 Feb 2025 12:19:28 +0000</pubDate>
		<author>neelpeel</author>
		<description>
			<![CDATA[@Mike1  - Water has over 4x heat capacity than concrete by weight, but due to lower density I think it's only about 2x by volume.  So not the huge benefit with water as first appears I think.<br /><br />As for the concrete required, my thinking for floor makeup to minimise concrete would be something like:<br />Insulation (200mm?); Hardcore/rubble (thickness as required); Concrete with UFH (150mm?); then flooring.<br /><br />Not sure if this is possible.]]>
		</description>
	</item>
	<item>
		<title>Slab with ASHP and overnight rate</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18266&amp;Focus=307853#Comment_307853</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18266&amp;Focus=307853#Comment_307853</guid>
		<pubDate>Wed, 26 Feb 2025 17:26:43 +0000</pubDate>
		<author>GreenPaddy</author>
		<description>
			<![CDATA[just some very rough numbers to get an idea of the magnitude of this endeavour. I'm taking this as an inter-day store, rather than inter-season (you won't store enough to achieve inter-season I'm thinking)...<br /><br />40m2 floor prob gives around 110m2 total of floor/roof/walls. Say Uvalue of 0.12W/m2K gives 13W/K.<br />Say another 10m2 windows at Uvalue 1.2W/m2K gives 12W/K.<br /><br />So working with 25W/K heat loss. Taking zero degC outside, heat loss = 500W<br /><br />The heat-degree-days info for your area, would let you work out how much energy you would need to keep the extension warm for a year (try this link to the met office HDD map)<br /><br /><a href="https://climatedataportal.metoffice.gov.uk/datasets/TheMetOffice::annual-heating-degree-days-projections-12km/explore" target="_self" rel="nofollow">https://climatedataportal.metoffice.gov.uk/datasets/TheMetOffice::annual-heating-degree-days-projections-12km/explore</a><br /><br />Might have this clac'd wrongly, but if your HDD is 2200, and your heat loss is 25W/K, then you'd &amp;quot;lose&amp;quot;...<br />2200x24hrsx25 = 1320kWh each year.<br />Replacing that, your ASHP would draw say 330kWh. Taking average of 22p/kWh (assume 27p and 7p), then you heating cost annually for the extension would be = £66/year.<br /><br />By setting up a system that pushed heat to the low level heavy mass at night, you might save 3/4 of that (night tariff only), let's say saving £45/year, with the risk that you might not be able to control the heat emission to the rooms very well, and indeed might be over charging the slab, which I suspect would be quite likely on a daily basis where our outdoor temps often leap 10-15 degK over night.<br /><br />If you put 50tonnes of crushed stone under the slab (0.5m thk), the stone alone would cost you £1500, never mind excavation, filling, additional insulation, additional heat pipes, design, controls, etc, etc, and the carbon footprint all that would entail. That's a 33 year payback just for the stone purchase. Prob never recover the carbon.<br /><br />I've likely screwed up the numbers somehwere, but the above might explain why not many examples exist??]]>
		</description>
	</item>
	<item>
		<title>Slab with ASHP and overnight rate</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18266&amp;Focus=307860#Comment_307860</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18266&amp;Focus=307860#Comment_307860</guid>
		<pubDate>Thu, 27 Feb 2025 10:03:39 +0000</pubDate>
		<author>neelpeel</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: GreenPaddy</cite><br /> with the risk that you might not be able to control the heat emission to the rooms very well, and indeed might be over charging the slab, which I suspect would be quite likely on a daily basis where our outdoor temps often leap 10-15 degK over night.<br /></blockquote><br />Wow, thanks for having a stab at the numbers.  Probably not far off with the heat loss.<br />Your comment on the temperature swings has got me thinking though.  I could indeed see -2deg one day and say 8deg the next so with a constant slab temperature I would be either underheating or overheating.  The room will get some solar gain too, compounding the issue.<br />And good point on the hardcore costs, etc.  Must admit I haven't run any costings yet.<br /><br />Hmm.  Maybe a thinner heated screed is the way to go after all - or sticking with radiators!]]>
		</description>
	</item>
	<item>
		<title>Slab with ASHP and overnight rate</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18266&amp;Focus=307863#Comment_307863</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18266&amp;Focus=307863#Comment_307863</guid>
		<pubDate>Thu, 27 Feb 2025 13:36:47 +0000</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: GreenPaddy</cite>The heat-degree-days info for your area, would let you work out how much energy you would need to keep the extension warm for a year (try this link to the met office HDD map)</blockquote>Ooh, thanks for that! Had no idea that data set was available.]]>
		</description>
	</item>
	<item>
		<title>Slab with ASHP and overnight rate</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18266&amp;Focus=307871#Comment_307871</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18266&amp;Focus=307871#Comment_307871</guid>
		<pubDate>Fri, 28 Feb 2025 08:18:54 +0000</pubDate>
		<author>GreenPaddy</author>
		<description>
			<![CDATA[&lt;blockquote&gt;&lt;cite&gt;Posted By: neelpeel&lt;/cite&gt;Hmm.  Maybe a thinner heated screed is the way to go after all - or sticking with radiators!&lt;/blockquote&gt;<br /><br />Not trying to put you off UFH at all. That is almost always my preference for clients. I always use conc slab ontop of insulation, avoiding a screed (costs&amp;carbon). UFH pipes cable-tied to the steel reinforcing mesh.<br /><br />That would give you a bit more thermal mass in the house than a screed, slower more even reaction time, and allow &quot;some&quot; storage of low tariff input from the ASHP (eg. setback starts at 6pm, and increase at 02:00-05:30, setting back again till mid-day... or some variation on that to suit). Normally setback would be over night with the uptick around 6am, thereby missing the low tariff of OIG.<br /><br />My thought would be, stick the £5k it would likely cost to build a huge thermal mass under the slab, into batteries, and keep the electrical energy as electric, to use how it would be best suited at the time of your choosing. Put the £1500 screed saving towards that too.<br /><br />This is just how I would do it. It's really good to challenge ourselves, and rethink, not just keep doing more of the same - drill baby drill<img src="/newforum/extensions/Vanillacons/smilies/standard/cry.gif" alt=":cry:" title=":cry:" /> If you were off-grid, had loads of crushed stone/rubble on the plot, loads of 2nd hand solar PV panels recycled from somewhere, and a tight budget, it may well be worth going down the route of a DIY sub-slab thermal battery store, but I suspect it would be a very niche set of circumstances that would make it viable.]]>
		</description>
	</item>
	<item>
		<title>Slab with ASHP and overnight rate</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18266&amp;Focus=307878#Comment_307878</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18266&amp;Focus=307878#Comment_307878</guid>
		<pubDate>Fri, 28 Feb 2025 11:14:47 +0000</pubDate>
		<author>neelpeel</author>
		<description>
			<![CDATA[@GreenPaddy<br />Not put off the concept of slab UFH in general, but...the more I think about it, the less it makes sense to have a radiator / UFH mix in my situation.<br />If I was starting from scratch for the house I think I would go for a slab with good thermal mass and UFH.<br />But given that the UFH only be for a small proportion of the house (just over 20%) then it would need to at a higher temperature and therefore could lead to overheating - and would be disproportionately expensive.<br /><br />The ASHP works well with bigger emitters, which was leading me down the UFH path (as well as other UFH benefits of space saving and cosy feet), but maybe cleverly building in an oversized radiator in the new space makes more sense.<br /><br />I already crank up the heating by 1.5deg overnight to utilise cheap rate and offset some of the morning usage until the PV kicks in.  Works pretty well.]]>
		</description>
	</item>
	<item>
		<title>Slab with ASHP and overnight rate</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18266&amp;Focus=307883#Comment_307883</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18266&amp;Focus=307883#Comment_307883</guid>
		<pubDate>Tue, 04 Mar 2025 08:05:40 +0000</pubDate>
		<author>GreenPaddy</author>
		<description>
			<![CDATA[&lt;blockquote&gt;&lt;cite&gt;Posted By: neelpeel&lt;/cite&gt;But given that the UFH only be for a small proportion of the house (just over 20%) then it would need to at a higher temperature and therefore could lead to overheating - and would be disproportionately expensive.&lt;/blockquote&gt;<br /><br />Not sure I understand the logic for the statement. The extension will have room stat(s), so why would it be more of an overheating concern than any other UFH system. If you've got your ASHP heat curve set a bit higher, cause the rads are undersized, then yes, the ASHP will not be quite as efficient, but adding more rads to the extension in lieu of UFH won't improve that. The UFH will control the inlet temp to the loops, so the UFH pipes may not even see that higher temp. The ASHP will modulate back if it sees a higher return temp.<br /><br />The heat loss for the rest of the existing house will be reduced, by virtue of the extension covering some of the orig ext walls. So it may be that you can reduce the ASHP heat curve anyway, as the rads have less work to do.]]>
		</description>
	</item>
	<item>
		<title>Slab with ASHP and overnight rate</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18266&amp;Focus=307900#Comment_307900</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18266&amp;Focus=307900#Comment_307900</guid>
		<pubDate>Fri, 07 Mar 2025 11:47:46 +0000</pubDate>
		<author>WillInAberdeen</author>
		<description>
			<![CDATA[The new space will be insulated to building regs, so might need much less heating than we're used to. So not very big radiators at all, even at low flow temperatures.<br /><br />GreenPaddy calculated 500W, which a couple of minimal £40 / 600mm radiators will supply at low flow temperature. They'll look pretty lonely in a 40m2 space! "Oversized" rads are only for uninsulated rooms with multi kW heat losses.<br /><br /><br /><br />On heat storage: slabs and fills are good for daily heat storage but useless for interseasonal stores. If you are into numbers you can modify the daily Thermal Admittance method to work out how much a slab will store in a year. It depends on the heat capacity, but also the conductivity of all the layers which heat has to flow inward and outward through. <br /><br />Basically if the slab is thick enough to store seasonal amounts of heat, then it gets so thick that the heat cant flow in/out fast enough.<br /><br /><br />EG, heat can flow around 100mm into most solid floor materials during a 12h-12h day-night cycle, there are thermal admittance websites you can play with this.<br /><br />That stores about 0.1m x 2000kg/m3 x 1kJ/kg x 0.6 ÷ 3600 = 0.03 kWh/m2/K, so enough heat to gain and lose a few degree per day in a well insulated house, that's ok. Less if we use the walls as storage as well.<br /><br />But if we wanted to store a 6month-6month summer-winter cycle of heat, we'd need much more fill (like 30 metres). But heat can only flow about 2 metres deep in that time, so we could not charge up the store fast enough just by heating it from the top.<br /><br />Alternative solutions are to run layers of pipes every few metres deep throughout the store. Or use a very flat/wide store, like a garden or field (eg with a GSHP). Or heat the store to 100+ degrees. Or store lots of hot water (higher heat capacity, can be pumped). All are a bit more costly!]]>
		</description>
	</item>
	<item>
		<title>Slab with ASHP and overnight rate</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18266&amp;Focus=307905#Comment_307905</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18266&amp;Focus=307905#Comment_307905</guid>
		<pubDate>Sat, 08 Mar 2025 10:44:23 +0000</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[As WiA says, you need more plumbing to do interseasonal heat storage. The newly built place where I worked used a borehole ground-source heat pump for its heating in winter, and during the spring, summer and autumn it used the same heat pump for cooling, rejected the unwanted heat into the ground around the boreholes ready for next winter. There's a firm called ICAX that's been mentioned here before that does something similar - <a href="https://www.icax.co.uk/Underground_Thermal_Energy_Storage.html" target="_self" rel="nofollow">https://www.icax.co.uk/Underground_Thermal_Energy_Storage.html</a> - and there are water-based schemes such as those like the Jenni system I mentioned earlier.<br /><br />So a very brave choice for a retrofit, and likely to prove expensive.]]>
		</description>
	</item>
	<item>
		<title>Slab with ASHP and overnight rate</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18266&amp;Focus=308060#Comment_308060</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18266&amp;Focus=308060#Comment_308060</guid>
		<pubDate>Sun, 23 Mar 2025 18:27:54 +0000</pubDate>
		<author>neelpeel</author>
		<description>
			<![CDATA[One thing I maybe didn't explain...the new space will be open plan to the existing living area (wall being removed).  Also, the living area has an open staircase to the upstairs study, so the entire space/zone will be maybe 80-90m2.<br /><br />So yes, the new area will be better insulated, but my plan was to oversize any new radiators/UFH to bring down the flow temps for the whole space and hence reduce the heat curve.  UFH makes some sense in this regard, but I hadn't really done any costings as yet.<br />Also, regarding the potential overheating, there will some thermal gain in the space so I suppose a concern is that the UFH won't have the speed of response required to deal with this.]]>
		</description>
	</item>
	<item>
		<title>Slab with ASHP and overnight rate</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18266&amp;Focus=308062#Comment_308062</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18266&amp;Focus=308062#Comment_308062</guid>
		<pubDate>Sun, 23 Mar 2025 18:54:42 +0000</pubDate>
		<author>tony</author>
		<description>
			<![CDATA[Interseasonal storage has been proven in Alberta Canada where 56 houses share one store and it goes to -30C in winter all hw and heating provided by the sun! <br /><br />See disc.ca <br /><br />More difficult for single houses even in a mild climate but I have one and live without heating <br /><br />Key is - reduce heat losses first.]]>
		</description>
	</item>
	<item>
		<title>Slab with ASHP and overnight rate</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18266&amp;Focus=308063#Comment_308063</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18266&amp;Focus=308063#Comment_308063</guid>
		<pubDate>Sun, 23 Mar 2025 18:58:24 +0000</pubDate>
		<author>tony</author>
		<description>
			<![CDATA[There is a book that reviews tank based systems across Europe written 20 ish years ago <br /><br />Solar Heating Systems for Houses: A Design Handbook for Solar Combisystems<br /><br />From memory they all needed additional energy input during the winter]]>
		</description>
	</item>
	<item>
		<title>Slab with ASHP and overnight rate</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18266&amp;Focus=308066#Comment_308066</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18266&amp;Focus=308066#Comment_308066</guid>
		<pubDate>Sun, 23 Mar 2025 21:02:28 +0000</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: neelpeel</cite>Also, regarding the potential overheating, there will some thermal gain in the space so I suppose a concern is that the UFH won't have the speed of response required to deal with this.</blockquote>You're definitely overthinking things. <img src="/newforum/extensions/Vanillacons/smilies/standard/bigsmile.gif" alt=":bigsmile:" title=":bigsmile:" />]]>
		</description>
	</item>
	<item>
		<title>Slab with ASHP and overnight rate</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18266&amp;Focus=308067#Comment_308067</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18266&amp;Focus=308067#Comment_308067</guid>
		<pubDate>Sun, 23 Mar 2025 21:08:33 +0000</pubDate>
		<author>WillInAberdeen</author>
		<description>
			<![CDATA[The famous Drake Landing solar village in Alberta used pumps and pipes to store and retrieve heat at 60degC down hundreds of boreholes under a playing field. It's a good solution, but not the slab OP was considering. It worked well for a good while but unfortunately broke down and was too complex to repair, was finally converted to gas fired heating last year.]]>
		</description>
	</item>
	<item>
		<title>Slab with ASHP and overnight rate</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18266&amp;Focus=308072#Comment_308072</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18266&amp;Focus=308072#Comment_308072</guid>
		<pubDate>Tue, 25 Mar 2025 15:14:15 +0000</pubDate>
		<author>neelpeel</author>
		<description>
			<![CDATA[&lt;blockquote&gt;&lt;cite&gt;Posted By: djh&lt;/cite&gt;&lt;blockquote&gt;&lt;cite&gt;Posted By: neelpeel&lt;/cite&gt;Also, regarding the potential overheating, there will some thermal gain in the space so I suppose a concern is that the UFH won't have the speed of response required to deal with this.&lt;/blockquote&gt;You're definitely overthinking things.&lt;img src=&quot;/newforum/extensions/Vanillacons/smilies/standard/bigsmile.gif&quot; alt=&quot;<img src="/newforum/extensions/Vanillacons/smilies/standard/bigsmile.gif" alt=":bigsmile:" title=":bigsmile:" />&quot; title=&quot;<img src="/newforum/extensions/Vanillacons/smilies/standard/bigsmile.gif" alt=":bigsmile:" title=":bigsmile:" />&quot;&gt;&lt;/img&gt;&lt;/blockquote&gt;<br />Possibly...but today for example...<br />House at 19.5deg this morning, then lots of sun and by midday the sunroom (which will be replaced by my extension) is sitting at 26deg and the rest of the living space is at 23.5deg (door open to allow heat through).  By this time the ASHP has adapted and radiators are cold - so no overheating and no 'wasted heat'.  In these shoulder months I'm now thinking that lag due to thermal mass of a slab (albeit thinner) might be counter-productive and an unnecessary cost.]]>
		</description>
	</item>
	<item>
		<title>Slab with ASHP and overnight rate</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18266&amp;Focus=308086#Comment_308086</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18266&amp;Focus=308086#Comment_308086</guid>
		<pubDate>Thu, 27 Mar 2025 09:59:02 +0000</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[If you want to reduce heat coming into the building there are several possibilities:<br />(1) make the windows smaller<br />(2) use solar glass<br />(3) increase the shading<br />(3a) brise soleil<br />(3b) external shutters<br />(3c) external planting<br /><br />Increased thermal mass generally helps moderate temperature peaks]]>
		</description>
	</item>
	<item>
		<title>Slab with ASHP and overnight rate</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18266&amp;Focus=308397#Comment_308397</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18266&amp;Focus=308397#Comment_308397</guid>
		<pubDate>Sat, 10 May 2025 13:29:15 +0100</pubDate>
		<author>neelpeel</author>
		<description>
			<![CDATA[I'm back to thinking about this.  I've been doing some costings on timber floor vs concrete and there's not much in it, depending on thicknesses.<br /><br />@Greenpaddy, you said &amp;quot;I always use conc slab ontop of insulation, avoiding a screed (costs&amp;amp;carbon). UFH pipes cable-tied to the steel reinforcing mesh.&amp;quot;<br /><br />What thickness of reinforced concrete slab do you tend to go for?  What is the minimum I could get away with?<br />Is a screed required to get the floor level if fitting wood flooring on top?]]>
		</description>
	</item>
	<item>
		<title>Slab with ASHP and overnight rate</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18266&amp;Focus=308404#Comment_308404</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18266&amp;Focus=308404#Comment_308404</guid>
		<pubDate>Sun, 11 May 2025 14:47:40 +0100</pubDate>
		<author>GreenPaddy</author>
		<description>
			<![CDATA[the slab would normally be 125 to 150 thk, though a smaller room could get away with 100mm. Struct Eng'rs usually spec A142 steel mesh, but I use A193, as it's more robust to walk on for adding UFH pipes and pouring the conc. That should be flat enough to glue wood flooring directly to, if the surface is floated. Have done this lots of times on projects over the years. Be aware, you do need to allow the misture content of the conc to drop, before applying the floor fininsh, though you can apply a liquid DPM, to retard the misture liberation, and lay the floor sooner.<br /><br />Half a day to DPM/Insulate/mesh, couple of hours for fit UFH pipes, then a couple of hours to pour conc, with a follow up float of the surface. Quick, simple, get on with the rest of the project.]]>
		</description>