Home  5  Books  5  GBEzine  5  News  5  HelpDesk  5  Register  5  GreenBuilding.co.uk
Not signed in (Sign In)

Categories



Green Building Bible, Fourth Edition
Green Building Bible, fourth edition (both books)
These two books are the perfect starting place to help you get to grips with one of the most vitally important aspects of our society - our homes and living environment.

PLEASE NOTE: A download link for Volume 1 will be sent to you by email and Volume 2 will be sent to you by post as a book.

Buy individually or both books together. Delivery is free!


powered by Surfing Waves




Vanilla 1.0.3 is a product of Lussumo. More Information: Documentation, Community Support.

Welcome to new Forum Visitors
Join the forum now and benefit from discussions with thousands of other green building fans and discounts on Green Building Press publications: Apply now.




  1.  
    Considering we are now looking at embodied energy and lifecycle cost etc. What would be the optimal EWI thickness to aim for in terms of cost/energy/co2?

    Standard 60s build, no insulation currently in cavity.

    Windows will be going in (within proposed EWI layer) in the next 2 months, then it will be, CWI (graphite beads).

    Thinking of EWI using EPS... Limited by space on the side walls of the house so EPS rather than fibre.

    150mm sound okay?

    Just then need to consider how to get a good 'stone sill' detail for the windows...
    •  
      CommentAuthordjh
    • CommentTimeJun 14th 2025
     
    Posted By: VictorianecoJust then need to consider how to get a good 'stone sill' detail for the windows...
    There are plenty of alternatives around. A search engine will show plenty of candidates.
    • CommentAuthorGreenPaddy
    • CommentTimeJun 14th 2025
     
    one way to look at it is...

    - start by filling the cavity with EPS beads (say 50mm) gives Uval = 0.48 ish
    - add 100mm EPS graphite on top gives Uval = 0.20 ish
    - add 150mm EPS (rather than 100mm) gives Uval = 0.15 ish
    - add 200mm EPS (rather than 150,,) gives Uval = 0.12 ish

    I seem to recall seeing Wolfgang Feist (Passivhaus) giving a lecture, which to massively paraphrase him explained that after a lot of empirical data analysis, the Uval for opaque elements should be around 0.15 W/m2K, with lots of lifecycle payback grphs etc. Very convincing.

    So, you could take that at face value, or research a bit more and see if that's been revised (as a general benchmark, ignoring that PHPP would do detailed bespoke calcs), in light the elecricity being greener than when I sat in that lecture 15 years ago (or more???).

    You'll get lots of different answers, and I'm not sure there would actually be a correct answer that stands the test of time, and vagiaries of personal finances, interest rates, climate change, energy costs, but personally I'd target 150mm, and ask the installer to quote for 120/150/180, and see what the cost diff is. Versus the mobilisation, scaffolding, render, labour, probably not a huge percentage.
  2.  
    Do you have a target value for the walls?

    I'M in agreement with what GreenPaddy said above.

    If you are thinking of cost/energy/co2 then the recent (and continuing) greening of the grid throws the long term calcs of co2 for heating up in the air. What will be your fuel for heating?

    A quick and dirty calc. using ubakus.de and making (probably not to valid) assumptions about the construction of the property gave
    100mm EWI with 50mm CWI a u. value of 0.210 and
    150mm EWI with 50mm CWI a u. value of 0.162
    Which is in line with GP above.

    IMO the key to the effectiveness of the works will be getting a good quality CWI done without any voids or air flow. Not at all easy as far as I have read about it.
    •  
      CommentAuthordjh
    • CommentTimeJun 14th 2025 edited
     
    Posted By: Peter_in_HungaryIMO the key to the effectiveness of the works will be getting a good quality CWI done without any voids or air flow. Not at all easy as far as I have read about it.
    It might be better to do the CWI before the EWI. Easier to install it, and a lot easier to check and rectify any mistakes/voids afterwards if there's no EWI covering the walls.
  3.  
    djh said: "It might be better to do the CWI before the EWI. Easier to install it, and a lot easier to check and rectify any mistakes/voids afterwards if there's no EWI covering the walls."

    Absolutely! I'd be pretty amazed if a CWI installer would do CWI 'behind' EWI, and why do it only to drill xxx number of holes in it? The 'solution' is not perfect but the thinking of insulating the cavity (even as far as insulating residual cavities in partially-filled walls) is that it almost certainly *will* leak air, and bonded EPS beads, though not a draught-stopper, are better than nothing.
  4.  
    Yes CWI going in first after the windows

    Then the EWI.

    I was just advising where the windows will sit in the 'layers'

    Heating is ASHP.

    I'll get the windows and CWI in then get some prices on 120/150 and 180. There will always be diminishing returns so finding the sweetspot in terms of U-Values v price. 0.15 sounds liek a reasonable target to aim for

    Thankyou
  5.  
    Any PV and battery going into the mix?

    Putting the windows in the EWI layer and then putting the EWI on some time later could be a risk. Typically sh#t happens and you don't want to be left with windows stuck outboard of the facade face for any length of time no matter how good the sealing is. Probably best to do the EWI around the windows to a finished state (minus the final render) and then do the remainder of the EWI when you are ready.

    BTW I put and additional 20mm thick surround 200mm wide around the windows and doors (applied after the main EWI) to give a picture frame feature which I then render a different colour to the main part of the EWI, just to add a bit of interest.
    •  
      CommentAuthorfostertom
    • CommentTimeJun 15th 2025 edited
     
    Posted By: Peter_in_HungaryIf you are thinking of cost/energy/co2 then the recent (and continuing) greening of the grid throws the long term calcs of co2 for heating up in the air. What will be your fuel for heating?
    Exactly. This new calculus of optimal insulation thickness, in which embodied CO2e (the CO2e resulting from mining, manufacturing, transporting and constructing the work) is approximately twice as harmful to climate crisis and ecological collapse, as the subsequent in-use CO2e emssions, depends upon the heating being by ever-lower-carbon electricity. i.e. the building must stop burning fuel (incl biomass) and instead use electric heat pump.

    If still burning fuel, then the older calculus prevails, ideally Passive House thinking, in which fuel burning for in-use heating is drastically reduced or eliminated.
    •  
      CommentAuthorfostertom
    • CommentTimeJun 15th 2025
     
    https://tomfosterarchitecture.co.uk/cottage-magazine - scroll down to 'Eco-Building Rethought'.
  6.  
    It's jaw dropping (in a good way I suppose) how much the world has changed in the last 15 years.

    It is no longer a good idea environmentally or financially to put EWI on to a wall that already has CWI.

    The emissions of manufacturing, distributing and eventually disposing of the EWI materials, are worse now than the emissions they will ever save, and more expensive.

    15 years ago, we would never have imagined we would get to this stage!

    The magic ingredients that have changed are the electricity grid getting dramatically cleaner, plus the ability of heat pumps to multiply that benefit.


    It is taking some head scratching to get used to this change, as ultra insulation has been a huge part of GBF thinking for many years so is hard to move on from it. Some building folks are getting used to it, others will need more time to let go, and building regs are now hopelessly off the ball, 100 pages about energy and none at all about upfront carbon.




    Using the numbers above for CWi versus [CWi + 150mmEWI]:

    Additional savings for adding EWI = 0.48 - 0.15 = 0.33 W/m2C

    Annual electricity savings: 2500HDD x 24h/d x 0.33 W/m2C ÷ 1000 ÷ CoP 3 = 7kWh per m2

    Energy cost saved 7kWh x 25p/unit = £1.75 per m2

    £ cost payback time of EWI: £150/m2 ÷ £1.75

    = 90years to payback £


    CO2 emissions saved from electricity (120g/kWh reducing to net zero by 2050):
    (120-0)/2 X 25y x 7kWh = 10 kg lifetime CO2 savings per m2

    Lifecycle emissions from EPS, adhesive, render: 20-40 kgCO2 per m2 (depending which EPD you believe)

    CO2 payback of EWI: never
    •  
      CommentAuthordjh
    • CommentTimeJun 15th 2025
     
    Posted By: WillInAberdeent's jaw dropping (in a good way I suppose) how much the world has changed in the last 15 years.

    It is no longer a good idea environmentally or financially to put EWI on to a wall that already has CWI.

    The emissions of manufacturing, distributing and eventually disposing of the EWI materials, are worse now than the emissions they will ever save, and more expensive.
    Scary thoughts. How about such concepts as EROEI as well? And does/should the balance include the carbon/energy invested in the extra generation capacity required by not adding the extra insulation?
  7.  
    For aesthetics though we would like to re-render the property so makes sense to EWI at same point surely and also falls under Building regs to upgrade?

    Solar will be being installed also and maybe battery storage
  8.  
    ''For aesthetics though we would like to re-render the property so makes sense to EWI at same point surely and also falls under Building regs to upgrade?''

    Hmm, well....Not sure it does if you do CWI.

    Yes, 'Renovation of a thermal element' means adding or replacing a layer to an element, such as a wall in this case, but an unfilled cavity wall is an interesting one. The Regs assume that the unfilled cavity you have is 50mm. They then look at what U value you'd get if you put 50mm of mineral wool in a hitherto uninsulated 50mm cavity. The answer is 0.55W/m2K (against a 'base case' U value of around 1.5W/m2K. Then, because it is hard to make a 50mm cavity bigger, they make that the target.

    In your case if you add the 50mm in the cavity you will have complied with the Regs. You don't then *have* to do anything else, and I suspect that if you simply rendered it no-one would be after you saying 'that should have been insulated render'. The U value target for a solid wall is 0.3W/m2K, but there is no stated U value target for the further upgrade of an upgraded (filled) cavity wall, so |I don't think it necessarily ''also falls under Building regs to upgrade?''

    This is only my take on it. I'm interested in others' views (sorry VE if this is a hi-jack of your thread).
    • CommentAuthorMike1
    • CommentTimeJun 21st 2025
     
    Posted By: WillInAberdeenIt is no longer a good idea environmentally or financially to put EWI on to a wall that already has CWI.
    For embodied carbon, maybe there's a new case for using natural IWI? I used hemp insulation in France, and the manufacturer claims that 1 hectare can take up as much as 15 tonnes of CO2 from the atmosphere (much more than a forest in its peak growth phase).

    I guess the financial payback depends on what happens to future energy prices, so harder to determine that other than for Building Regs (which, I seem to recall, use current prices).
  9.  
    Some great points being made.

    So at the point of refurb. I need to make a decision on the end goal. To EWI or not to EWI particularly as this will (hopefully) be out forever home.

    As the next logical step for us is in the renovation is the CWI then windows I need to decide where the windows are to be mounted...

    I really don't want to mount the windows in the existing location then EWI at a later date as I'd rather get them in the insulation layer.

    So... For those mathematical nerds where can I get a full calculation done or look more into the subject?

    As we are looking to renew the render (sand/cement) surely it is still more environmentally friendly to go back with EWI and thincoat render?
    •  
      CommentAuthorfostertom
    • CommentTimeJun 22nd 2025 edited
     
    <blockquote><cite>Posted By: WillInAberdeen</cite>It is no longer a good idea environmentally or financially to put EWI on to a wall that already has CWI.

    The emissions of manufacturing, distributing and eventually disposing of the EWI materials, are worse now than the emissions they will ever save, and more expensive.</blockquote>

    The latter is true, but therefore rushing to the former, and similar, risks putting into reverse the several other objectives/benefits that drive well considered programmes like PH. Saving nett CO2 is not the only objective. There's also comfort - lack of cold radiation; health due to toxin-removal via MVHR, which is another part of the package likely to be dumped by the same logic; and one other objective I'm maybe not recalling. Also cost/payback, by eliminating heating system, also affecting the 'e' bit of CO2e (and other toxic emissions).

    Better perhaps to concentrate instead on the still-unresolved rules of Life Cycle Alalysis (LCA) which still ridiculously doubts whether sequestration of bio-materials can be allowed into the calc, because their eventual fate in 60yrs time can't be guaranteed. Thereby distracting from what could be immediately maximised, to at least certainly impact the shorter-term nett emisions of CO2e, while it's super-crisis tipping-point time.

    Also some creative invention into buildings that actually absorb CO2 throughout their in-use lifetime. Edit ... which has got me thinking - that would involve substantially increasing the building's bio-mass (as in weight) during its lifetime - trees growing all over it?
    https://ethz.ch/en/news-and-events/eth-news/news/2025/06/a-building-material-that-lives-and-stores-carbon.html
    - structural implications. But how about sequestering lots of carbon in the ground under/around it - cellulose like forest or wetland, or perhaps CaCO3? It could be the picturesque mark of an old building, that it gradually elevates, as the ground expands under it! Just in time for rising seas and watercourse flood-risk and/or a defence against groundwater salination.
    • CommentAuthorMike1
    • CommentTimeJun 22nd 2025
     
    Posted By: fostertomtrees growing all over it?
    I've seen a few green roofs that are unintentionally on the ways to that!
  10.  
    Posted By: fostertomBetter perhaps to concentrate instead on the still-unresolved rules of Life Cycle Alalysis (LCA) which still ridiculously doubts whether sequestration of bio-materials can be allowed into the calc, because their eventual fate in 60yrs time can't be guaranteed.


    That's a little disingenuous - the latest RICS guidance (WLCA 2nd Edition 2024), which is effectively the UK construction industry standard, is clear that biogenic carbon (sequestration) should be reported separately from the carbon used during manufacture.


    "The sequestered biogenic carbon in sustainably sourced timber and other biomass must be considered to leave the product system boundary when it is either:

    • transferred to another product system through reuse, recycling or recovery as a secondary fuel
    • transferred to nature when emitted (as CO2 or methane) through combustion (either incineration or energy recovery processes), degradation in landfill, or emission from anaerobic digestion or composting, or
    • transferred to nature if it remains undegraded in landfill after 100 years.

    In each case, this must be considered as an emission of biogenic carbon (as CO2 or methane as appropriate) in the module in which it leaves the system."


    In other words, the focus is back on the impact of the material at extraction (i.e. now), and no amount of magical accounting can alter this, because the sequestered carbon is effectively 'emitted' anyway.

    Crucially though, natural materials such as wood fibre are almost always lower in initial carbon impacts than extractive industry equivalents anyway, without worrying about sequestration.

    These are all technologies that exist right now and don't require techno-fix futuristic solutions to passively absorb carbon through living facades etc. They just use low impact materials to save unnecessary heat loss. The key is using them efficiently in the hierarchy of decision making (Build Nothing, Build Less, Build Clever etc.)
    •  
      CommentAuthorfostertom
    • CommentTimeJun 23rd 2025 edited
     
    <blockquote><cite>Posted By: Doubting_Thomas</cite>RICS guidance (WLCA 2nd Edition 2024)</blockquote>Exactly, that's what it says - and it's diastrously conservative, instead of promoting a super-prime way of preventing CO2 from entering the atmosphere in the crucial coming decades, which is far from magical accounting. Fear of what may happen in 60-100yrs time (assuming no tech progress) - CO2 returns to atmosphere, rather than being 'carried forward' still sequestered) significantly discourages major things that the industry can do now. https://islandpress.org/books/build-beyond-zero#desc p40 on covers this. We need to go very significantly beyond "just use low impact materials to save unnecessary heat loss" - and we can.
  11.  
    Soooo, back to my query.

    To EWI or not to EWI, that is the question...
  12.  
    Do the EWI

    Focus on the upfront emissions created now - that's the "tl;dr" version of my post above.

    Sequestration is a distraction, the grid isn't *yet* at zero, your new heat pump, PV panels etc. will all use embodied energy, right now, to make.

    But, the embodied energy of natural materials is low enough by comparison that it's still worth trying to conserve energy where you can, especially through retrofit and reuse rather than new build. So EWI if you can do it with natural fibre and enjoy all the comfort benefits and reduced grid burden that sit outside the raw £/kWh equation (as fostertom helpfully listed above).

    If you're paying for the scaffold and labour etc. to do render anyway then the cost of the woodfibre is surely not a huge uplift.
  13.  
    Yes, I'd go along with @Doubting_Thomas. CWI will get you from around 1.5W/m2K to about 0.55 (or possibly as low as 0.4-something with graphite EPS), which deals with the 'steep part of the curve' (the first few mm has the greatest effect. Everything thereafter is diminishing returns). You could stop there, and forget EWI, in which case you have about 0.5-ish, which is 3x as good as before but not earth-shattering, and thermal bridges at every opening where they have been closed with a brick instead of (today's alternative) an insulated cavity closer. You could forget the EWI and do some 'cloaking' IWI at the openings, but as @Doubting_Thomas says, having the scaffolding up and planning rendering anyway takes you a long way towards EWI. Do not, however, underestimate the cost of enabling works (all the things you have to move, extend, tweak, in order to accommodate the EWI.

    Go for a system with 3rd-party certification, since your BCO does not *have* to believe you that it 'does what it says on the tin' without certification. Check that any certification is still in date and valid.
  14.  
    deleted duplicate posting
  15.  
    Does the whole place need re-rendering? Or will a repair where needed and repaint the house last for the next 20 years? If the latter then perhaps a cost / benefit on the EWI considering all that has been said above.

    Of course the sizing of the heat pump comes into the EWI equation.
  16.  
    It doesn't 'need it'

    But it's 60 years old and we want to modernise the property to add value also.

    So it makes sense
  17.  
    Posted By: VictorianecoIt doesn't 'need it'

    But it's 60 years old and we want to modernise the property to add value also.

    So it makes sense

    If it is sound then no reason to replace it. Pressure wash and good quality paint should suffice.

    If you decide to EWI then if the render is sound then no need to remove it, just pressure wash and EWI over.
  18.  
    The windows need replacing though for sure. Every seal has gone and they're 28 years old. So I can't work out where to locate them, in existing openings or outside and then EWI.

    I need to have an end goal in sight
  19.  
    Who would you get to do a cost/benefit analysis or similar?

    It's only a case at this stage if windows are to go within the original location or in proposed EWI layer then I can look to order up
  20.  
    A possibility (and not a C/BA):

    (I am assuming here that your windows are currently fitted in the outer skin of brickwork, not 'in check' behind the outer skin)

    Get the windows made in 18mm WBP or 'marine' ply boxes. For installation in the brick wall as it stands the raw edge of the ply can be covered by a tasteful bead set in mastic. The ply box runs right through to the inside of the inner block skin and fixings are all into the blocks. When you EWI (let's say you use 150mm, and you decide that 75mm is a good reveal) you (1) wait till the scaffold is up and (2) push the windows out as required to create your 75mm reveal, then (3) you screw the boxes in to the outer brick skin.
   