Home  5  Books  5  GBEzine  5  News  5  HelpDesk  5  Register  5  GreenBuilding.co.uk
Not signed in (Sign In)

Categories



Green Building Bible, Fourth Edition
Green Building Bible, fourth edition (both books)
These two books are the perfect starting place to help you get to grips with one of the most vitally important aspects of our society - our homes and living environment.

PLEASE NOTE: A download link for Volume 1 will be sent to you by email and Volume 2 will be sent to you by post as a book.

Buy individually or both books together. Delivery is free!


powered by Surfing Waves




Vanilla 1.0.3 is a product of Lussumo. More Information: Documentation, Community Support.

Welcome to new Forum Visitors
Join the forum now and benefit from discussions with thousands of other green building fans and discounts on Green Building Press publications: Apply now.

The AECB accepts no responsibility or liability for any errors or omissions in the content of this site. Views given in posts are not necessarily the views of the AECB.



    • CommentAuthortony
    • CommentTimeDec 5th 2025
     
    I have been dreaming about a project that measures heat flux through walls

    The big news is that my dream is about to come true

    I would be keen to from any others who have heat flux data for walls of any type please
    •  
      CommentAuthordjh
    • CommentTimeDec 5th 2025
     
    I'd be interested to learn more about the approach. Something like the PHFS-09e heat flux sensor?
  1.  
    Didn't Historic Scotland do a lot of in situ U value testing? (I understood that it was these tests which gave rise to the amendment of the SAP assumption for an uninsulated 225mm solid brick wall from 2.1 to 1.7W/m2K).
    • CommentAuthortony
    • CommentTimeDec 15th 2025
     
    Not sure which heat flux sensor we will be using, we will install it and data log results for three days - add weather data and compare real world with as designed assumptions

    I have a few building types lined up and am about to start a list
    •  
      CommentAuthorfostertom
    • CommentTimeDec 15th 2025 edited
     
    Will be exceeding interesting.
    • CommentAuthortony
    • CommentTimeDec 15th 2025
     
    Yep
    • CommentAuthortony
    • CommentTimeJan 27th 2026
     
    Started, high level note on second property monitored

    Dot and dabbed on medium density blocks, cavity with “fluff” rendered blockwork outside skin.

    U -value as found 0.54, after retro filling in void between blocks and plasterboard with fire retarded EPS beads = 0.37

    I think this delivers a 30% saving on heating demand and has the added benefit of fewer draughts.

    Property was built in 1986 - uncertain about the as designed u-value but suspect 0.6
  2.  
    I have used this kit previously:
    https://www.buildtestsolutions.com/u-value-measurement/heat3d-infrared-thermography

    which uses the FLIR One and iPhone to monitor heat flux and establish a u-value.

    The kit was fiddly to set up (easily disturbed), but delivered results after a few days of monitoring. Generally measured u-values of older solid walls were better than 'on paper' and newer walls were a bit worse.

    We also found that the u-value varied in different spots of the wall, so you need to do a few 'takes' to get a reliable figure.
    • CommentAuthortony
    • CommentTimeFeb 26th 2026
     
    More results are being obtained

    16 year old timber framed house - 30% underperforming

    Brand new 0.1 timber frame with designed U value 0.1 measured at 0.09 likely result of careful workmanship

    1950’s cavity wall was 1.6, when filled with ‘fluff” 0.68 and after internally thermally lining it with 50mm eps/plasterboard laminate 0.34.

    The odd result was a 1960’s mansard wall with no insulation at 0.09????? Under further investigation

    More monitoring is ongoing.

    We are using a heat flux detector, indoor and outdoor temperature sensors and internal and external wall surface temperature , data logging for seven to ten days
    •  
      CommentAuthorfostertom
    • CommentTimeFeb 26th 2026 edited
     
    So what heat flux monitor are you using?
    • CommentAuthortony
    • CommentTimeFeb 27th 2026
     
    A proper heat flux pad , ÂŁ thousands
    •  
      CommentAuthorfostertom
    • CommentTimeFeb 27th 2026
     
    I'd like to look it up?
    • CommentAuthortony
    • CommentTimeFeb 28th 2026
     
    Huskeflux heatflux plate is the name of our sensor , it is connected to a data logger with the other input sensors
    •  
      CommentAuthordjh
    • CommentTimeFeb 28th 2026
     
    • CommentAuthortony
    • CommentTimeMar 1st 2026
     
    Yea
    • CommentAuthortony
    • CommentTimeMar 7th 2026
     
    Just did my house, from the data the U-value of the SW side wall of my house was 0.08W/m²/K which is much better than the design value of 0.1W/m²/K.

    The flank wall value most likely benefited from three factors that help improve the U-value, a) careful installation of the fibreglass batts with no gaps, b) using basalt fibre wall ties to reduce thermal the bridging of the more common metal wall ties assumed in the U-value calcs, and c) highly air-tight construction. But a 20% improvement on design was very satisfying to find.
    •  
      CommentAuthordjh
    • CommentTimeMar 8th 2026
     
    Congratulations :bigsmile:

    It's all stuff I'd be interested to do on my own house if it wasn't so expensive. I can't really even justify doing a repeat airtightness test just for interest, and that (I hope) is a lot less expensive.

    It's a pity there aren't (a lot) more of community ventures that share the cost of the equipment and the desire.