Home  5  Books  5  GBEzine  5  News  5  HelpDesk  5  Register  5  GreenBuilding.co.uk
Not signed in (Sign In)

Categories



Green Building Bible, Fourth Edition
Green Building Bible, fourth edition (both books)
These two books are the perfect starting place to help you get to grips with one of the most vitally important aspects of our society - our homes and living environment.

PLEASE NOTE: A download link for Volume 1 will be sent to you by email and Volume 2 will be sent to you by post as a book.

Buy individually or both books together. Delivery is free!


powered by Surfing Waves




Vanilla 1.0.3 is a product of Lussumo. More Information: Documentation, Community Support.

Welcome to new Forum Visitors
Join the forum now and benefit from discussions with thousands of other green building fans and discounts on Green Building Press publications: Apply now.

The AECB accepts no responsibility or liability for any errors or omissions in the content of this site. Views given in posts are not necessarily the views of the AECB.



    • CommentAuthorandyman99
    • CommentTime5 days ago
     
    Looking for a bit of advice please.

    Whilst starting to help my son renovate his bathroom we came across a rather unpleasant problem. The tiles on an external wall pretty much fell off and everything behind is very wet.
    Construction: this “front” wall appears to be a simple timber frame structure. From outside to in: PVC cladding - roofing felt (what I would call old style felt not a breathable membrane) - timber frame filled with fibreglass type insulation - plasterboard. The water ingress does appear to have come from the inside. The timber structure is very wet, the insulation a sodden mess and the roofing felt disintegrates as you touch it. We have an insurance assessment this Friday but I would like to understand a way forward if possible before then. I think the main structural walls are brick, left and right whilst front and back appear to be this timber frame structure. 2 rooms across the front, bathroom and bedroom. No obvious signs of a problem in the bedroom front wall. I’m wondering how fixing this would best be approached? Any ideas welcomed
    • CommentAuthorandyman99
    • CommentTime5 days ago
     
    Needs a health warning
      wetwall.jpeg
    • CommentAuthortony
    • CommentTime5 days ago
     
    Was there a vapour barrier anywhere or foil backed plasterboard?

    Nice to see you again
    • CommentAuthorandyman99
    • CommentTime5 days ago
     
    Thank-you. No nothing (unless dissolved!) Assume we dry it out and replace any obviously damaged timbers, could we insulate and put a vapour barrier on the inside? It does look a bit of a basic construction. The cladding looks fairly good but runs the whole length of the front of the house, so tricky to remove and do anything from the outside without major works
    •  
      CommentAuthordjh
    • CommentTime5 days ago
     
    The PVC cladding components on the outside will prevent outward movement of water vapour, although there may well be gaps in between that allow movement. Similarly, the roofing felt is probably impermeable and may well have fewer gaps. You didn't mention a ventilated gap behind the roofing felt. So it'd be no surprise if water has made its way from a bathroom to the outside of the wall and structure.

    A vapour barrier on the inside would help, as would a ventilation-gap/drainage-plane behind the outer cladding (PVC and roofing felt). How old is the PVC cladding?
    • CommentAuthortony
    • CommentTime5 days ago
     
    Yes, good plan,

    For the shower room/bathroom I would seriously consider fail safe design and go wetroom style
  1.  
    my assessment, (like DJH has mentioned above) would be the vapour in the bathroom has been condensing on the felt and been trapped with no ventilation void. The bedroom may have managed to avoid an issue being less vapour generation in the room, but it's still a very bad wall build up.

    The timbers look like 50x50?? Presumably you don't want to remove those, as they are supporting the cladding, which you've said you want to keep in place. It would be better to remove it and start again, but in absence of that approach, I would do the following....

    - remove the insulation/felt/mould
    - treat the timbers which are remaining, assuming they aren't completely nackered
    - ensure there is a ventilation path below and above the cladding, in the vertical voids created by the timber structure (may have to cut/drill in vents/mesh)
    - fix OSB to the back side of the existing 50x50 timbers (forms a 50mm cavity).
    - assumption again... the brick walls each side are 100/50cav/100, and the OSB layer takes you flush with the outer face of the inner brick leaf
    - add PIR insulation board against the OSB to bring the new build-up flush with the existing brick wall (may be 100mm, may be 90mm or even 80mm PIR).
    - if you've space add another layer of let's say 50mm PIR covering brick and the first layer of PIR.
    - use spray PU adhesive from a can to stick the PIR boards over the surfaces and all butt edges.
    - fit a VCL over the lot, catching the ceiling, floor, and perp walls.
    - strap out the wall with 22x100 treated offsaw timber vertically at 600 cntrs, fixing into the brickwork with concrete screws, and into the original stimber studs with timber screws (might be 180mm or longer)
    - plasterboard over.

    You might have to replace windows cills as internally the wall will now be deeper. Catch window reveals (and cills) with 25mm PIR all around and plasterboard over if that doesn't prevent window opening or look too daft with no window frame left.

    Whatever method you use, the key is venting the back of the cladding.
    • CommentAuthorandyman99
    • CommentTime5 days ago
     
    Indeed no ventilation gap. Cladding is original to the house, built I believe in the 80's. Thank-you everyone, key point I understand is ventilation to outside / how to include this in any solution. I've no idea at the moment what will be insurance claim as opposed to what we can do ourselves, but this information is very useful in discussions with assessor, hopefully on Friday.
    • CommentAuthortony
    • CommentTime5 days ago
     
    I have noted before that although roofs need to be ventilated, there no building regulations requirement for any ventilation in walls

    Pretty rare to see problems like this too.
  2.  
    I was a bit surprised to see your note (Tony) about no regs v's cavity for cladding ventilation. I know the Scottish reg's, but not the English (though generally very similar).

    Checking Doc C...5.15 onwards - explains that a ventilated and draining cavity is required for external framed walls, and a VCL internally, as I read it, and matches the Scottish Regs which I know pretty well.

    Some scenarios might get away with insulation against the cladding, but being PVC plus felt, vapour's completely trapped, and being a high humidity room, it's pretty likely there'll be rot in the timbers.
    •  
      CommentAuthordjh
    • CommentTime4 days ago
     
    Posted By: tonyI have noted before that although roofs need to be ventilated, there no building regulations requirement for any ventilation in walls
    What is Part C para 5.17 about then? :

    "5.17 Any framed external wall will meet the
    requirement if the cladding is separated from the
    insulation or sheathing by a vented and drained
    cavity with a membrane that is vapour open, but
    resists the passage of liquid water, on the inside
    of the cavity (see Diagram 11)."
    • CommentAuthorphiledge
    • CommentTime4 days ago
     
    The wall construction looks very similar to my daughters where there's a masonry gable either side of the house and a timber stud wall between the gables to form the front and rear walls that support the lower edge of the roof. One major difference is my daughters has a skin of OSB on the outside to give structural racking resistance.

    A couple of years ago we stripped the cladding to insulate between and over the outside of the studs and fitted new cladding with a 25mm drainage/ventilation gap. When we stripped the exterior walls to the ensuite and family bathroom there was no evidence of damp even though there was no moisture barrier on the inside. I don't think the lack of a moisture barrier on the inside necessarily leads to excessive moisture within the wall.

    Was the tiled exterior wall part of a shower enclosure? If so then I'd suspect moisture ingress from splashing through tiles/grouting rather than vapour ingress condensing within the wall.
    • CommentAuthorandyman99
    • CommentTime4 days ago
     
    >philedge

    Sounds a vey similar construction. Yes the wall was tiled (around a bath). My son took the tiles off but said they came off very easily, so ingress here is certainly high on the list as the culprit. The cladding does appear to be a fairly complete barrier and less likely to allow the level of water ingress we have. I'm back today.
    Subject to opinions of the assessor, my current thoughts are:

    strengthen timber structure where necessary
    create some vertical ventilation throughout the timbers (drill some holes!)
    insulate (celotex?) leaving 25mm gap to cladding
    OSB /vapour barrier, but on inside wall
    I think the timbers are at least 3x2 so should be able to use 50mm insulation.
    Wondering if there's a way to put in a few vents to outside
    •  
      CommentAuthordjh
    • CommentTime2 days ago
     
    Posted By: andyman99Wondering if there's a way to put in a few vents to outside
    PVC cladding vents seem to be easily available. Just replace the bottom and top cladding planks?
    • CommentAuthorphiledge
    • CommentTime1 day ago
     
    To vent the 25mm cavity behind the cladding we ran a length of stainless plasterers skim angle bead along the top and bottom of the vertical battens. Once the cladding is on the cavity is closed to all but the smallest insects but nicely vented.

    I appreciate it's a load of extra work but if you're reworking the cladding on the exterior then consider insulating between and over the outside of the studs in the wall. With 75x50 studs we had 65mm PIR between the studs and 75mm PIR over the outside
    •  
      CommentAuthorfostertom
    • CommentTime1 day ago edited
     
    Neat - but is that really a fine enough mesh? I'd a thought nearly all insects cd wiggle thro. Perhaps they come in different versions. but ordinary EML isn't fine enough.
    • CommentAuthorphiledge
    • CommentTime1 day ago
     
    The ones we used are skim beads with a very fine mesh.....much smaller gaps than typical eaves vents. The angle beads for basecoat plaster or render have a much coarser mesh
    •  
      CommentAuthordjh
    • CommentTime1 day ago
     
    They sell extra-fine insect mesh to mount behind the PVC cladding vents I mentioned. It could probably be used in other applications too.
    •  
      CommentAuthorfostertom
    • CommentTime1 day ago
     
    Thanks philedge, will look into it. And Dave.
    • CommentAuthorphiledge
    • CommentTime1 day ago
     
    Similar to these....https://www.diy.com/departments/expamet-mini-mesh-steel-angle-bead-l-2-4m-w-25mm/35790_BQ.prd

    With 25mm mesh they fit over the ends of 25mm perfectly:)
  3.  
    What a great solution.