My house in Cambridge had a low energy renovation around 15 years ago with triple glazing, increased thermal insulation, solar thermal system, thermal store and MVHR. The MVHR unit is a Vent-Axia Sentinel Kinentic BH.
For most of the time since it was installed it has worked very well and I rarely needed to open any of the windows. However, during the recent Amber Heat Alert the house overheated badly. Possibly the high humidity made it worse than in earlier years or my age and, maybe medication, made me less resilient.
My suspicion is that during an extended heatwave with tropical nights the MVHR is unable to maintain comfortable indoor temperatures. With or without a summer bypass, if the air temperature is over 35º C outside then the MVHR will import that air. Even if the air temperature drops lower overnight it can't catch up and the house continues to retain the heat, made worse by the high quality of thermal insulation.
Some form of air cooling may be required! My back garden is nowhere near big enough for a ground-coupled heat exchanger so active cooling may be an option.
I have seen an example where a reversible heat pump was connected to a water/air duct heat exchanger (eg. Zehnder ComfoPost). However, my house has a gas boiler.
Has anyone else experienced similar problems or can suggest possible solutions?
Posted By: john.connettWith or without a summer bypass, if the air temperature is over 35º C outside then the MVHR will import that air.That may depend on the sophistication of the MVHR unit. My Zehnder cools the incoming air down to a set temperature using the cooler outgoing air, if that's cooler than the incoming air. For the summer, I've adjusted the set temperature down to the minimum 12°C, rather than the default 22°C to take full advantage of any cooler outside air - check your MVHR manual as you may be able to do the same.
Posted By: john.connettI have seen an example where a reversible heat pump was connected to a water/air duct heat exchanger (eg. Zehnder ComfoPost).Unfortunately air has a low specific heat capacity, so you need to move lots of air to make a big difference - more than an MVHR unit typically handles.
Posted By: john.connettMy suspicion is that during an extended heatwave with tropical nights the MVHR is unable to maintain comfortable indoor temperatures.If the air is so hot that the building doesn't have chance to cool, as in an extended heatwave, that's a problem that can only be solved by active cooling - typically air conditioning or chilled underfloor central heating. I have the same problem as I have nowhere to install a heat pump.
Posted By: john.connettMy back garden is nowhere near big enough for a ground-coupled heat exchangerA garden isn't necessary; I've seen a vertical borehole drilled through the floor of a plant room in a London home. It would, however, cost several time the cost of an air source heat pump / aircon unit.
Posted By: Mike1I've installed a HomEvap adiabatic cooler before my MVHR but...Another 'but' is that you need to have insulated the air distribution ducts & accessories for this to stand a chance, or the cooled air may well have warmed again before it reaches the ceiling vents. I'm loosing 2 to 3°C on mine, but I haven't yet insulated the manifold nor the main duct from the MVHR unit.
Posted By: CerisyOur 16 year old Titon unit is fine for most of the year but the summer bypass function is useless in our set up. In these heat waves (we live in Normandy and recorded a temperature over 41 degrees!) I switch the MVHR unit off during the day with all the windows and upstairs shutters closed. When the outside temp in lower than in the house I’ll open windows to draw some cooler air through.Summer bypass can't work when it is hotter outside than inside. In those circumstances the best an MVHR can do is to bring the heat exchanger back into the circuit which makes the supply air a little bit cooler than the air outside. Air con is as you say the only real solution, although fans do help somewhat.