Home  5  Books  5  GBEzine  5  News  5  HelpDesk  5  Register  5  GreenBuilding.co.uk
Not signed in (Sign In)

Categories



Green Building Bible, Fourth Edition
Green Building Bible, fourth edition (both books)
These two books are the perfect starting place to help you get to grips with one of the most vitally important aspects of our society - our homes and living environment.

PLEASE NOTE: A download link for Volume 1 will be sent to you by email and Volume 2 will be sent to you by post as a book.

Buy individually or both books together. Delivery is free!


powered by Surfing Waves




Vanilla 1.0.3 is a product of Lussumo. More Information: Documentation, Community Support.

Welcome to new Forum Visitors
Join the forum now and benefit from discussions with thousands of other green building fans and discounts on Green Building Press publications: Apply now.

The AECB accepts no responsibility or liability for any errors or omissions in the content of this site. Views given in posts are not necessarily the views of the AECB.



    • CommentAuthorOj0001
    • CommentTime23 hours ago
     
    Hey,

    I’m currently in the progress of building a single story extension on the rear of my house, located in the midlands.

    For the extension I drew up and got approved plans for a timber frame structure. The wall build up from inside to outside is currently:

    15mm plasterboard
    145mm studs with 100 PIR. (Resulting service space to inside, all joints tapped for Vapor sealing)
    11mm OSB
    Vapour barrier
    70mm EPS with direct render.

    However, since then I have read more into interstitial condensation, and under winter conditions there is a risk at the outside face of the PIR could suffer, this is behind the OSB and could lead to issues. Also the OSB becomes sandwiched between two layers, although EPS should have some permeability.

    So far I’ve looked at :

    -Increasing the PIR to 140mm and adding an internal service void does not seem to resolve it.

    -Switch to 140mm Rockwool between studs. (Decreased performance notably, but increase breathability). Still need to add internal service void as internal vapour layer needed.

    -Switch to internal PIR layer, add external ventilated cavity and render board. Also considered external PIR to reduce thickness, then cavity and render board.

    Really just looking for a sanity check, is there a fundamental issue with the project as designed, is there a way to add improvements, or does anyone have experience with similar?

    There’s a lot of discussion on similar build ups on here, but nothing quite the same.
    Any and all help is appreciated!
      IMG_6435.jpeg
    •  
      CommentAuthordjh
    • CommentTime22 hours ago
     
    Welcome to the forum :)

    A vapour barrier near the outside is generally considered a complete no-no, and some don't even like them in their usual place on the inside of a wall. What led you to such a decision? What does condensation analysis show you?

    Personally I wouldn't use PIR anywhere, because of the pollutants it can produce in a fire, but each to their own.
    •  
      CommentAuthorfostertom
    • CommentTime20 hours ago
     
    This is what I discovered, playing with WUFI - but let no one take it as my advice, just a suggestion, a variant to be considered, to your own (and BldgInsp's) satisfaction:

    Similar to what you have: 15 p'b'd on 145 studs, 145 blown-in Warmcel between, or EPS or fibreglass roll if preferred. Like Dave, hate PIR usually. Don't need a service zone - the p'b;d' can be punctured at will, not being reqd to be either airtight or vapour resistant.
    11 OSB3 outboard, all joints glued and screwed. The OSB3 is the airtight layer, mustn't be punctured.
    No VCL! - it performs better without any VCL.
    100 EPS glued to the OSB3, direct rendered.
    The whole is vapour permeable right through.
    Being about half way through the insulation sandwich, the OSB won't see any condensation - that'll happen only in the outermost bit of the outboard EPS, where it'll do no harm.
    • CommentAuthorOj0001
    • CommentTime17 hours ago
     
    Thank you for the feedback :)

    I must admit, the PIR route stemmed purely from past experiences and the analytical view of U value performance. I think I came across a detail somewhere that illustrated this build up, did the basic maths and moved on. I assumed so long as the warm room air didn’t enter the wall there was no risk of condensation.

    Having played around with a WUFI calculator it is fascinating how different materials have such different behaviours , how moisture moves through the wall structure and how you need to think of the complete construction not just the U values. Also the change in behaviour with vapour barrier and where they’re located.

    In theory the current wall does hold up, but is very dependent on that interior vapour layer to allow no interior air through. I do much prefer the idea of a moisture permeable wall, that allows movement and has no risk due to lack of sealing or puncturing.

    Funnily, the best performance for drying and moisture movement, comes from moving the OSB internally, using rockwool (or similar) between studs and then wooden batts directly to the outside of the studs and render. You do have to increase the thickness however to achieve the same results. I’d have to do a cost comparison also.

    Thank you for the suggestions Tom, I’ve seen you suggest similar elsewhere, and the calculations do stack up for condensation. I’ve a preference for fibreglass over warmcell as I can DIY, and less mess. Presumably you glue and mechanically fix the EPS?

    EPS does seem to be the way to go, I like the idea of wood batts, but they’d have to be thicker, and nervous of using it only 150mm from ground level.
    •  
      CommentAuthordjh
    • CommentTime17 hours ago
     
    Posted By: fostertomBeing about half way through the insulation sandwich, the OSB won't see any condensation - that'll happen only in the outermost bit of the outboard EPS
    I suppose if the current weather is the new climate, we might have to design for condensation on the inside as well?
    •  
      CommentAuthorfostertom
    • CommentTime15 hours ago
     
    Whoo, there's a thought
    • CommentAuthorOj0001
    • CommentTime4 hours ago
     
    Throwing Air Conditioning into the mix would make for some additional complications….

    Putting the current build up of 100mm EPS and either rockwool or wood fibre between studs,without a membrane is showing condensation at the OSB inside face for me…. It’s only really bad at -5C, once near zero it improves significantly.
      IMG_6446 Large.jpeg
  1.  
    Only a few points from me in response to others. I started a response yesterday but it fell off the cliff...

    Of all the mainstream insulants PIR gives close to the best 'headline' figure but it's only as good as the fit and the 'cloaking' of any thermal bridges. As FT highlights, anything with no thermal bridge mitigation is less than ideal, so anything that's 'all between studs' is, in my humble view, worth avoiding. For the OP's original construction, full (140mm) fill with Frametherm 32 (lambda 0.032W/mK) comes v close to the U value you'd achieve with PIR, and the fit will be better, because of the 'squidge'. *But you still want to cloak the bridge of the studs (see FT's suggestion).

    ''I like the idea of wood batts, but they’d have to be thicker, and nervous of using it only 150mm from ground level.''

    I used a lot of WF, but XPS (or, for my preference but not necessarily the comfort of system providers, EPS) below ground and above ground to at least the height of 'local splash-up' (the industry suggests rain splashes up 150mm. I have a 300-ish 'tide mark' on my shed...). In my view (and contrary to 'conventional wisdom') a set-back (plinth layer not as deep as main EWI layer) is not essential.

    Try that for size and I'll come back later if any 'supplementaries' req'd.
    •  
      CommentAuthorfostertom
    • CommentTime3 hours ago
     
    Oj, what software is that screenshot? Doesn't use the obsolete, flawed Glaser method, does it? You've previously used WUFI?

    In your cross section drawing at top, have you met any resistance to base wall 'only' 140 thick? If the stud above is 95 wide, I don't see why not 100 block base wall - significant economy of construction, smaller footprint. But I've had BldgInsps and Engineers insist it must be min 190 thick (meaning 215 or 2x100 cavity wall) but they can't say why. Anyone?
    •  
      CommentAuthordjh
    • CommentTime2 hours ago
     
    How high rain splashes depends on what the surrounding surface is like. We have a gravel topped French drain all round our house for that reason. The downpipes from the roof gutters discharge onto the gravel and we haven't seen any problems.
    •  
      CommentAuthorfostertom
    • CommentTime2 hours ago
     
    Personally I like to see a bit of splashback staining, and def no plinth course - because I prefer a building to look like it's grown out of the landscape instead of a pristine box temporarily plonked down like a Portakabin.
    • CommentAuthorMike1
    • CommentTime2 hours ago edited
     
    Posted By: fostertomwhat software is that screenshot? Doesn't use the obsolete, flawed Glaser method, does it?
    It does - it's Ubakus, so not very helpful.

    Posted By: Oj0001EPS does seem to be the way to go, I like the idea of wood batts, but they’d have to be thicker, and nervous of using it only 150mm from ground level.
    A big advantage of wood (or hemp) batts is that they significantly reduce the decrement delay - effectively the time taken for heat to reach the inside from the outside; once heat reaches the inside then the building starts to heat up, and you want to delay that in a heatwave. Wood beats hemp for decrement delay, hemp beats wood for its moisture handling properties, both beat non-biological insulations (EPS, mineral wool, etc). You could use both though - EPS on the outer face, wood / hemp between studs.

    For various reasons, look to achieve good levels of airtightness. OSB3 could form part of an airtightness layer if the joints are sealed, but not all OSB3 is airtight, so check the manufacturer's data for the brand concerned.

    Posted By: fostertomIf the stud above is 95 wide, I don't see why not 100 block base wall - significant economy of construction, smaller footprint. But I've had BldgInsps and Engineers insist it must be min 190 thick (meaning 215 or 2x100 cavity wall) but they can't say why.
    I'd guess that's due to Building Regs structural stability requirements (Part A, 2C6) Solid walls constructed of coursed brickwork or blockwork should be at least as thick as 1/16 of the storey height - although most of wall is not in brickwork or blockwork, the part that is would be subject to similar forces.
    •  
      CommentAuthorfostertom
    • CommentTime1 hour ago
     
    Posted By: Mike1Wood beats hemp for decrement delay, hemp beats wood for its moisture handling properties, both beat non-biological insulations (EPS, mineral wool, etc)
    Compare also to Warmcel blown in to quite high density? Warmcel also has unbeatable gap-filling properties, hence pretty good airtightness without added membranes, becomes excellent and robust-in-depth, puncture tolerant, when paired with glued-and-screwed OSB3, easily proof against slumping, and along with fringe stuff like sheep wool (and hemp), has valuable humidity-stabilising (hygroscopic) properties. It's an interesting material, which people shy away from - install cost is dominated by the fixed cost of the installer's visit, much less by the quantity used. And Youtube is full of DIY installation by converted vacuum cleaner. To me, it's supreme, tho oddly Icynene is a close rival.
    • CommentAuthorOj0001
    • CommentTime27 minutes ago edited
     
    Posted By: fostertomOj, what software is that screenshot? Doesn't use the obsolete, flawed Glaser method, does it? You've previously used WUFI?

    In your cross section drawing at top, have you met any resistance to base wall 'only' 140 thick? If the stud above is 95 wide, I don't see why not 100 block base wall - significant economy of construction, smaller footprint. But I've had BldgInsps and Engineers insist it must be min 190 thick (meaning 215 or 2x100 cavity wall) but they can't say why. Anyone?


    It is Ubakus, apologies that's my ignorance, I hadn't fully appreciate the differences between the two methods. Although I don't fully understand why this method is considered less accurate from thermal and vapour gradients standpoint? I presume your actual WUFI build up of the above suggestion didn't show condensation risk?
    • CommentAuthorOj0001
    • CommentTime26 minutes ago edited
     
    Posted By: fostertomOj, what software is that screenshot? Doesn't use the obsolete, flawed Glaser method, does it? You've previously used WUFI?

    In your cross section drawing at top, have you met any resistance to base wall 'only' 140 thick? If the stud above is 95 wide, I don't see why not 100 block base wall - significant economy of construction, smaller footprint. But I've had BldgInsps and Engineers insist it must be min 190 thick (meaning 215 or 2x100 cavity wall) but they can't say why. Anyone?


    The studs are also 140mm, hence the 140mm block. The plans as they appear were accepted as a full plans submission by BC with no queries other than a Radon report.
    • CommentAuthorOj0001
    • CommentTime9 minutes ago
     
    Posted By: Mike1
    For various reasons, look to achieve good levels of airtightness. OSB3 could form part of an airtightness layer if the joints are sealed, but not all OSB3 is airtight, so check the manufacturer's data for the brand concerned.


    Is there a specific difference between air tightness (I presume to reduce thermal losses due to air passage) and Vapour diffusion through the wall? Since vapour barriers are designed to prevent air movement, but still allow vapour transport, why is there such an objection to them?
    • CommentAuthorOj0001
    • CommentTime6 minutes ago
     
    Posted By: fostertomPersonally I like to see a bit of splashback staining, and def no plinth course - because I prefer a building to look like it's grown out of the landscape instead of a pristine box temporarily plonked down like a Portakabin.


    Funnily enough I was looking to add a decorative plinth course, while adding additional EPS below dpm to help with the thermal bridging.
      Screenshot 2026-08-26 134326.png