Posted By: englishjohnThe windows would originally have sat on the blockwork, approximately 200mm inboard of the finished face of the EWI.Yes, that's what you should - sat on the blockwork is a big thermal bridge - embed the windows within the insulation thickness, not touching the blockwork. Your choice of 200 EWI makes that a lot easier than e.g. Nick's 160. Within 215 (incl bedding, render etc), a 95dp window (like Russell Timbertech 1.1U 3G) leaves 120 for reveal depth plus a bit of space away from the masonry; 150EPS or 160 woodfibre leaves the reveal depth very minimal, and worse if your frames are more than 95dp (like Russell Timbertech PH grade 3G).
I need to move them outwards
Posted By: Victorianecouse ... brackets?Steel has conductivity 500x worse than ply (stainless steel half that), so even a few small-section steel brackets make a worse thermal bridge, in the inboard>outboard direction, than a continuous 'box' of 18 (I'd say 12) ply. Lately I've settled on the attached instead of either of those - track the heat-flow paths and I think it works better than the ply 'box' and can use Compriband instead of any sticky tapes.
Posted By: fostertomeven a few small-section steel brackets make a worse thermal bridge, in the inboard>outboard direction, than a continuous 'box' of 18 (I'd say 12) plyand then comments
Posted By: fostertomLately I've settled on the attached instead of either of those - track the heat-flow paths and I think it works better than the ply 'box' and can use Compriband instead of any sticky tapes.so yes it's incidental to
Posted By: djhmoving windows outboard to be in EWI instead of masonry
Posted By: Victorianecothey would be covered by the EWI alsoBut barely - both close to both outside and inside air (as is the ply box idea) thus v little insulation in the heat flow path.
Posted By: Victorianecoonly small in area compared to a timber box600x smaller? No.
Posted By: VictorianecoI'm not sure? Surely a wooden box is more than 600x the width of a few fixings and a piece of angle bracket?Do the sums for yourself, and become a believer
Posted By: VictorianecoWhy not just use 50mm x 50mm CLS instead?Yes. The detail above, if adapted for EWI on a masonry inner, would have a 50x50 'picture frame' screwed/sealed airtight to the masonry face (or 50x75, projecting edgewise), with the 35x35 glued and screwed airtight inside it.
Posted By: Victorianeco- The plywood box displaces the equivalent space of say EPS so this needs to be accounted for
- Angle brackets are hidden 'behind' the EWI so calculations need to factor full build up not just 'box v brackets'
Posted By: VictorianecoSo assuming a masonry cavity wall. What is the box detail? 11mm frame screwed to inside of existing reveals? And then the windows screwed into/through that? Is that substantial enough?Yes, although screw the box to the window first (easier to seal). A box has a high 'tuning moment' so will support a fair bit of window weight hanging off it. Don't forget insulated cavity closers if no full fill.