Home  5  Books  5  GBEzine  5  News  5  HelpDesk  5  Register  5  GreenBuilding.co.uk
Not signed in (Sign In)

Categories



Green Building Bible, Fourth Edition
Green Building Bible, fourth edition (both books)
These two books are the perfect starting place to help you get to grips with one of the most vitally important aspects of our society - our homes and living environment.

PLEASE NOTE: A download link for Volume 1 will be sent to you by email and Volume 2 will be sent to you by post as a book.

Buy individually or both books together. Delivery is free!


powered by Surfing Waves




Vanilla 1.0.3 is a product of Lussumo. More Information: Documentation, Community Support.

Welcome to new Forum Visitors
Join the forum now and benefit from discussions with thousands of other green building fans and discounts on Green Building Press publications: Apply now.

The AECB accepts no responsibility or liability for any errors or omissions in the content of this site. Views given in posts are not necessarily the views of the AECB.



    • CommentAuthorPeter Clark
    • CommentTimeOct 16th 2009 edited
     
    Posted By: TunaSo, breathability does not prevent building failure through gross leaks.


    Posted By: Peter ClarkNo, but it is designed explicitly to help deal with such leaks.


    Still re reading all this!

    just wanted to amend my response:

    Breathability cannot prevent gross leaks of course.

    But breathability is intended exactly to prevent building failure through gross leaks, as well as through less gross leaks.

    Peter
    •  
      CommentAuthorfostertom
    • CommentTimeOct 16th 2009 edited
     
    MikeG, I'm coming to that asap!

    Cambridge paper yes, plus any others
  1.  
    Mike

    If you're using breathable sarking membrane then it makes more sense to ventilate the batten cavity. This way the sarking membrane protects the insulation from the wind. The belt and braces approach would be to use PUR below the rafters & something vapour open between them. My preferred sloping ceiling is, from the inside:

    12.5mm Fermacell;
    0.3mm polyethylene VCL, laps & edges taped (530MNs/g);
    9mm OSB3 lining board (2.2MNs/g);
    400mm Crown Rafter Roll 32 between 400mm Masonite rafters;
    22mm Pavatex Isolair woodfibre sarking board (0.55MNs/g);
    Tyvek Supro Plus sarking membrane, laps & edges taped (0.17MNs/g);
    38mm counter battens, 25mm vent to eaves, 5mm vent to ridge;
    25mm tile battens.

    David
  2.  
    Hi David, I take your point about the breather membrane [which is why I said many say it is unnecessary] The reason I have the ventilated cavity below the breather membrane is that I have seen condensation on the underside of such material. I'm not going to say which one but it is a reknowned product. I think a high level of ventilation is necessary in a PUR insulated roof. Note that in my scenario, approximately 150mm surface area of timber rafters is exposed to the ventilated air. This compared to 250mm encapsulated by PUR. Above a high humidity situation [ie bathrooms] I would tend to oversize the rafters [structurally] to allow the ratio of exposed/unexposed timber to be 50/50

    The job on which the condensation occurred was a simple cold roof scenario with horizontal insulation above conventional plasterboard ceiling. It occured before the tiles were laid. Perhaps some 'freak' weather conditions caused this to happen but seeing condensation on something which is supposed to be breathable rather knocks one's confidence in it.

    I don't see any problem with your construction at all other than it is extremely more expensive than mine. This not just due to the material cost, but to space/structural requirements resulting from the extra volume necessary to contain it.

    In short, if there is any benefit, it is not worth the extra cost [to me] For those who have the luxury of being able to afford more 'natural' products then good for them
  3.  
    Posted By: fostertomMikeG, I'm coming to that asap!

    Cambridge paper yes, plus any others


    So anything [peer reviewed or otherwise] which does not fit with your point of view on how vapour 'behaves' is wrong?
  4.  
    Mike

    So how about:

    12.5mm plasterboard;
    0.3mm polyethylene VCL, laps & edges taped;
    30mm PUR below rafters;
    150mm Crown Rafter Roll 32 between 150mm rafters;
    Tyvek Supro Plus sarking membrane, laps & edges taped;
    38mm counter battens, 25mm vent to eaves, 5mm vent to ridge;
    25mm tile battens.

    This has a slightly better U value than the all PUR approach (0.16 versus 0.17) and is probably lower risk in terms of condensation. The ventilated batten cavity would be seen by some as belt and braces, but you could see it as insurance against moss filling the gaps around the tiles. Would this cost any more than you're currently paying?

    David
    • CommentAuthorMike George
    • CommentTimeOct 16th 2009 edited
     
    Thanks for your comments Peter. Sorry I haven’t had chance to respond earlier, I was hoping to do a combined one with whatever comments Tom intended to make:bigsmile:

    Posted By: Peter Clark

    The general problem is that IF some water gets in to that construction it may be hard to get out again. That might be all right too, depending on how much gets in and where.


    Significant water getting in from above would show itself [somewhere] quickly. Smaller leaks would not affect the construction as the surface area of rafters exposed is such that a high level of ventilation would be adequate to ensure such water would evaporate and be vented away.

    Any water vapour which migrates from the internal environment would also be vented in the same way.


    Posted By: Peter Clark

    If a tile slips and is not noticed for a while, water could run onto the breather and through into the rafter/insulation.


    No, if the breather membrane is undamaged and correctly lapped, no water will get in.

    Posted By: Peter Clark

    Might the damp have a detrimental effect on the rafters? If the insulation in between and below the rafters was hygroscopic, it would protect the rafters. If it had good capillarity, the water could run throughout the structure and not pool. If it was very vapour open in addition, it could dry out faster. This would happen especially if the 5:1 ratio of vapour openness was present.



    I don’t believe the moisture necessary to cause such damage can remain hidden within fabric which is ventilated in the way I proposed. Dry rot for example, requires a certain temperature range and moisture content, as well as a distinct lack of ventilation. Ensuring any one of these three things does not happen will make dry rot impossible- One will of course try to ensure all three but the presence of sufficient ventilation is enough to avoid problems resulting from non visible leaks. No need to go to the extent [and cost] of the 5:1 ratio, which no doubt works equally well [not withstanding the debated effect on internal ‘health and well being’

    Posted By: Peter Clark

    If a hole is created in the plaster/vapour barrier, eg by picture hooks, water vapour could be getting in there, at a very low rate, but maybe continuously, day and night, for months on end, each year, year after year.



    This may happen, depending on internal conditions but is unimportant due to my ventilation comments above.

    In general, the risk of humidity levels being high enough to cause significant risk of interstitial condensation are exaggerated in my opinion. Bedrooms for example do not continually ‘force’ water vapour into the fabric in a way suggested by some. It’s complete rubbish.

    Posted By: Peter Clark

    A sloping ceiling/roof is probably the safest bet, as I am sure you were aware when you chose it. What about the same kind of construction for a wall – with electrical sockets and service penetrations through to the outside?



    I don’t like timber framed walls personally, due to the risk of someone somewhere along the line getting it wrong. Obviously there is nothing wrong with it when it is designed correctly and installed as such. Unfortunately, the complexity of the 5:1 design style makes problems more likely in my opinion. Masonry on the other hand, is easier for everyone to design and build at least in terms of basic weathering and hence durability. Correct installation of insulation however is another argument, which is why I use partial fill PUR, and rigorously inspect things as they are done. I wonder how many realise that such inspection is now a requirement under Part L of the building regulations?

    To answer your question about how the polythene integrates with the walls, it is simply lapped down over the wall plate; trapped behind metal lathing; and rendered over.

    Posted By: Peter Clark

    It all depends on the plastic vapour retarder being installed perfectly, is this realistic? What about the joints between the plastic sheets? Will they be perfect? How long will the adhesive last?


    No adhesive involved. Everything is physically lapped and trapped. Staple holes are insignificant, again because of above rafter ventilation
    • CommentAuthorMike George
    • CommentTimeOct 16th 2009 edited
     
    Posted By: davidfreeboroughMike

    So how about:

    12.5mm plasterboard;
    0.3mm polyethylene VCL, laps & edges taped;
    30mm PUR below rafters;
    150mm Crown Rafter Roll 32 between 150mm rafters;
    Tyvek Supro Plus sarking membrane, laps & edges taped;
    38mm counter battens, 25mm vent to eaves, 5mm vent to ridge;
    25mm tile battens.

    This has a slightly better U value than the all PUR approach (0.16 versus 0.17) and is probably lower risk in terms of condensation. The ventilated batten cavity would be seen by some as belt and braces, but you could see it as insurance against moss filling the gaps around the tiles. Would this cost any more than you're currently paying?

    David


    Cost wise probably no more. And I understand why some would choose such a construction. The theory is that your construction is sound, but like I said, the experience I had seeing condensation on a breather membrane leads me to prefer the above insulation vented method. That's the main reason.

    The condensation risk is a moot point I think and depends on factors other than just construction make up.
    •  
      CommentAuthorfostertom
    • CommentTimeOct 16th 2009 edited
     
    Posted By: Mike GeorgeSo anything [peer reviewed or otherwise] which does not fit with your point of view on how vapour 'behaves' is wrong?
    If I'm right, they're very wrong - as usual my 'listeners' must be the judge of that. Do you feel that you're in my firing line Mike? If so, I wasn't particularly aware of that.
  5.  
    Posted By: fostertomDo you feel that you're in my firing line Mike?


    No, not at all. Just surprised that you can be so dismissive of peer reviewed stuff.
    •  
      CommentAuthorfostertom
    • CommentTimeOct 16th 2009 edited
     
    What's all this faith in peers? Peers are by definition the ones who hold the conventional wisdom. Peers' fate is to be invoked when they agree with one, and to be ignored or rubbished when they don't. Majority (or even unanimous) agreement is not the same as the truth. There's no escape from the onerous duty to decide for oneself.
    • CommentAuthorMike George
    • CommentTimeOct 16th 2009 edited
     
    Faith is for believers in something unsubstantiated by science. Nothing to do with the peer review I was referring to

    Personally I trust what can be observed, measured or calculated by a combination of the two.

    But in any topic, one person cannot 'know' everything. There comes a point where one must put their trust in others who are experts in their particular field. For me it is about who I trust more- A manufacturer who has a Cambridge University report supporting their position, or a manufacturer who does not.
    • CommentAuthorTuna
    • CommentTimeOct 16th 2009
     
    Posted By: fostertomWhat's all this faith in peers? Peers are by definition the ones who hold the conventional wisdom. Peers' fate is to be invoked when they agree with one, and to be ignored or rubbished when they don't. Majority (or even unanimous) agreement is not the same as the truth. There's no escape from the onerous duty to decide for oneself.


    Nonsense. Peer review is about people with expertise in a subject looking for errors that laymen would be unlikely to spot, and checking that the article under review passes basic checks for quality of the analysis being undertaken. Peer review is not about following some consensus, it's about critical thinking - which some people seem all to happy to avoid if it doesn't fit their personal world view.
  6.  
    Peer reveiew is massivley overated for the simple fact that within the science community there is a HUGE amount of peer pressure to be seen to conform to the currently accepted scientific theory/dogma.

    One only has to look at scientific history to see that scientists spend the majority of their time being wrong whilst ridiculing anyone who steps too far outside the bounds of acceptable questioning.
    • CommentAuthorMike George
    • CommentTimeOct 16th 2009 edited
     
    Two extremes there tuna and bot . Maybe the reality is somewhere in between?

    Edit: Changed my mind, I think tuna has it about right.
    •  
      CommentAuthorfostertom
    • CommentTimeOct 16th 2009
     
    That's exactly watamentasay, bot - thanks.
    Actually, I admit the reality is prob not somewhere in between, but both extremes simultaneously.
    • CommentAuthorMike George
    • CommentTimeOct 17th 2009 edited
     
    Can I assume you cannot fault my insulated roof scenario then Tom?
    •  
      CommentAuthorfostertom
    • CommentTimeOct 17th 2009
     
    I want to take the time nec to do the question justice, but trying to be off-duty for the w/e! Soon.
    • CommentAuthorCWatters
    • CommentTimeOct 17th 2009
     
    Posted By: Mike George This is my standard sloping ceiling scenario. From Inside to outside

    Plaster, painted with matt emulsion
    12.5mm standard plasterboad fixed with 45mm galvanised clouts at 400mm centers. All board edges fixed into timber noggins
    Cheap polythene lapped accross at least 2 rafters and fixed with standard mild steel staples. Polythene lapped down walls to ensure continued air barrier at walls
    30mm PUR insulation fixed with 65mm clouts to underside of rafters. Joints filled with expanding PUR foam
    150mm x 50mm rafters at 400mm centers. Voids filled with 100mm PUR flush with rafter undersides and deliberately cut to leave 10mm short of rafters. The 10mm filled from above and below with expanding PUR foam.
    Clear 50mm cavity between rafters above insulation
    Breathable roofing membrane
    Slates/Tiles on treated roofing batten
    Eaves vented with continuous overfascia vents
    Ridge vented with dry ridge ventilation system.

    Some would argue that some parts of this construction make-up are unnecessary [such as a breather membrane]. But other than varying the insulation thickness to improve u-value, I believe it to be a belt and braces approach - Is it?


    Sounds perfect to me.

    The company that makes the breather membrane will say that ventilating the cavity under it is unnecessary but I doubt it makes much difference to the U-Value if the gaps are sealed as proposed.
    • CommentAuthorPeter Clark
    • CommentTimeOct 19th 2009 edited
     
    Posted By: Mike George
    No, if the breather membrane is undamaged and correctly lapped, no water will get in.


    Of course IF it is done correctly, that is one of the main points of breathability as I see it. IF it is NOT done correctly, now or later, what then?

    Posted By: Mike George
    Significant water getting in from above would show itself [somewhere] quickly. Smaller leaks would not affect the construction as the surface area of rafters exposed is such that a high level of ventilation would be adequate to ensure such water would evaporate and be vented away.

    Any water vapour which migrates from the internal environment would also be vented in the same way.


    This all applies to all types of construction, when done well, the point is, how easy is it to do one or the other well?



    Posted By: Mike George
    Peter Clark
    If a hole is created in the plaster/vapour barrier, eg by picture hooks, water vapour could be getting in there, at a very low rate, but maybe continuously, day and night, for months on end, each year, year after year.

    Mike George
    This may happen, depending on internal conditions but is unimportant due to my ventilation comments above.

    In general, the risk of humidity levels being high enough to cause significant risk of interstitial condensation are exaggerated in my opinion. Bedrooms for example do not continually ‘force’ water vapour into the fabric in a way suggested by some. It’s complete rubbish.


    This assumes that water vapour having got through the paint, plaster and VB, also gets through the insulation, what if it does not and accumulates around the joists, might some condensation happen there? If so, it would be difficult for that water to get out again.


    What is complete rubbish?

    That bedrooms will have a higher relative humidity during the night if occupied?
    Or that a higher humidity will constitute a ‘force’ encouraging water vapour into any holes in the walls?



    Posted By: Mike GeorgeI don’t like timber framed walls personally, due to the risk of someone somewhere along the line getting it wrong.

    So your answer to concerns about water damage in timber frame walls is, don’t build them?

    Posted By: Mike GeorgeObviously there is nothing wrong with it when it is designed correctly and installed as such.

    Obviously no one is arguing with that.

    Posted By: Mike GeorgeUnfortunately, the complexity of the 5:1 design style makes problems more likely in my opinion

    It is complex to discuss and understand perhaps, is it not easier to build?
    How is this:
    http://www.natural-building.co.uk/PDF/Pavatex/Pavaroof/Roof_PAVAROOF_PITCHED.pdf
    More complex than what you have described?


    Posted By: Mike GeorgeMasonry on the other hand, is easier for everyone to design and build at least in terms of basic weathering and hence durability.Correct installation of insulation however is another argument

    Agreed, so masonry WITH insulation is not easier for everyone to design and build?

    Posted By: Mike Georgewhich is why I use partial fill PUR

    Why is this better than hygroscopic, breathable insulation?

    Posted By: Mike GeorgeNo adhesive involved. Everything is physically lapped and trapped. Staple holes are insignificant, again because of above rafter ventilation

    But to benefit from the above rafter ventilation, any moisture that gets through the holes in the VB has to also get through the insulation, both layers?

    Sorry, this has got very complicated as a post.
    You seem to me to be saying that the construction you described works well, as long as we exclude all the situations where it does not work well!
    I am sure if you design a single roof pitch with no services, windows etc. and you supervise the construction, and any further work, then everything will be fine.
    I am concerned, and this does appear to be the focus of the 'breathability' corner, about all the ifs:
    What if YOU do not design it or supervise it?
    what about timber frame walls?
    what about complex roof shapes with windows and dormers.
    What about when someone replaces a tile later and damages the roof membrane?
    etc.

    The construction is not 'robust' because it depends upon all those things being OK, but how likely is that in practise?
  7.  
    Wow Peter, that is a rather long list of queries. I'm not going to answer them sorry as I simply don't have the time. In any case I would only be repeating comments I have already made. I think we are going around in circles and it was obviously a mistake [on my part] to digress from the original focus of the thread by posting what I still believe to be my optimum [sloping]cold roof construction.

    What I will say is that there are many ways of swinging a cat . For me its about picking the best option for a given scenario. There is much more to consider than breathability and it should never be the number one consideration in my view. In my experience for most people the primary consideration is function [obviously linked to cost]

    So we will have to agree to disagree please. I have my view and you have yours.

    Just to declare my interest - I have never worked for a PUR manufacturer in any capacity. Neither have I ever sold or comercially promoted any product or particular building system. I have however spent quite a few years putting such constructions together on site. Never had a problem with my detailed roof construction yet. If you were correct in your criticisms I surely would have done by now.
  8.  
    Posted By: Mike GeorgeWow Peter, that is a rather long list of queries. I'm not going to answer them sorry as I simply don't have the time. In any case I would only be repeating comments I have already made. I think we are going around in circles and it was obviously a mistake [on my part] to digress from the original focus of the thread by posting what I still believe to be my optimum [sloping]cold roof construction.


    Sorry for the long post.

    I don't think it was a mistake, thanks for the opportunity to talk. I respect your experience.

    I am not sure myself that we have got to the bottom of this. I hope you are correct that there are no problems with your construction.

    Certainly there are more ways to swing a cat...

    Peter
  9.  
    Thanks also for the discussion Peter. Only a mistake in that I started a side debate that I am unable to finish. Can only spend so much time on here.
  10.  
    why all theory? haven't vcl / barriers been in use for 40 years, can't we see the results of all the screw holes, joins etc?
    • CommentAuthorTimber
    • CommentTimeOct 25th 2009 edited
     
    Going back to the start, I read an ammended/shortened version on the article in Site Lines the other day.

    It was saying that the gaps around the insulation (between it and timber studs etc) allows the passage of moisture vapour though the wall.

    Funny thing though.... the BBA certificate also states that gaps around boards in installation will allow the passage of moisture vapour, however it also states in that same BBA certificate that all gaps around boards must be filled with an expanding foam!

    I wouldn't trust anything that is spouted by the rigid insulation manufacturers regardless of what it is about. Othres are just as bad... did you know that another large insulation manufacturer don't have 3rd party certification for the use of their insulation in pitched roofs?!?! No-one has ever tested it! They stated that they/everyone had been using it for ages like that so they havn't bothered to test it.

    Damage to VCLs in timber frame walls will cause issues, simple as that. I may have said in the past that it is not a huge issue, but some recent digging on my part says that anything over about the size of a single socket outlet can result in condensation on the external wall sheathing (if fitted). That is not to say that condensation results in a major faulure but it could if it were really bad.

    To be honest, most of what people say and assume about breathability is just opinion and conjecture, and that includes what i say and think as well. Things like condensation risk calcs are all well and good but they are far too simplistic to really give a good and robust understanding, and that is even more undermined when the information from the product manufacturer's is sometimes completely wrong!

    What really needs to be done is some indepth hygrothermal tests on different types of wall construction to show how moisture does really interact with the structure.

    Timber
    •  
      CommentAuthorali.gill
    • CommentTimeOct 25th 2009
     
    I agree about the hygrothermal testing Timber and it would be nice to see some data from the BRE demonstration site not just based on thermal performance. Although saying that they're unoccupied anyway and need serious tweaking as it is to meet designed performance levels being empty, it all goes out the window when the house is full of lively teens, cats, dogs and parents.

    The Canadian studies on timber frame homes that have been refurbished ten years later and black mould is found on the osb sheathing are great examples of identifying mistakes and designing new solutions.

    Regarding peer review i think if peers review independently then there is a value in the technical knowledge and experience so long as it is experience based not reciting what they were taught or regurgitating someone elses work. A great example is Climate Change or the real history of King Arthur (both of them!) or 9/11.

    When peer review is done in a group environment then you enter into the science of 'group speak' which is proven to alter an individuals original and independent perception and the brain even rewards with a dopamine hit when in agreement with the 'general consensus'.
  11.  
    Posted By: TimberTo be honest, most of what people say and assume about breathability is just opinion and conjecture, and that includes what i say and think as well. Things like condensation risk calcs are all well and good but they are far too simplistic to really give a good and robust understanding, and that is even more undermined when the information from the product manufacturer's is sometimes completely wrong!

    Timber


    :clap:Well said that man
  12.  
    City-sponsored project awarded funding to study "breathing wall" indoor biofiltration system

    Toronto and Region Conservation (TRCA), with support from Works and Emergency
    Services and Toronto Public Health, was recently awarded a $53,700 grant from
    the Green Municipal Funds (GMF). TRCA will use the funds to install and test an
    indoor air biofiltration system, also known as a breathing wall, at the TRCA
    head office.


    "We are very pleased to work in partnership with the City of Toronto, the
    Federation of Canadian Municipalities and the private sector to test this
    exciting new technology," said Dick O'Brien, TRCA Chair. "The Living City,
    TRCA's vision, is about making the Greater Toronto Area one of the most
    sustainable, livable regions in the world and this project is a step in that
    direction."


    "The breathing wall is an innovative alternative to improve air quality with
    the potential to reduce energy costs and cut greenhouse gas emissions -
    important goals of the Green Municipal Funds," said Mayor Yves Ducharme,
    President of the Federation of Canadian Municipalities. "We look forward to the
    results of this project and its potential to promote cleaner air."

    Updates on the breathing wall project will be posted on TRCA's Web site at
    www.trca.on.ca. For more information about the City of Toronto's environmental
    initiatives, visit www.toronto.ca, or FCM's Knowledge Network at www.kn.fcm.ca.
  13.  
    Ferns and moss clean indoor air in Canadian experiment.

    A cure for "sick building syndrome" may be in sight. Canadian researchers and business people are testing an environmentally friendly air-cleaning system nicknamed the "breathing wall."

    Although it looks more like a modern art installation than an air-filtering system, the breathing wall is actually an indoor ecosystem composed of rocks, plants, fish, and microorganisms. In effect, it inhales dirty air and exhales clean air.

    Modern buildings with closed-air ventilation systems have a nasty habit of circulating stale and polluted air throughout the office. Workers who breathe fumes, dust, fibers, and biological contaminants day after day could use some relief.
    •  
      CommentAuthorfostertom
    • CommentTimeOct 28th 2009
     
    That's confusing, bot - a completely different (tho more appropriate) use of the term 'breathing wall'.
   
The Ecobuilding Buzz