Posted By: topherPaul, Thanks. Have you checked the filter in your primary circuit - if you have one?Nope, there's no filter as far as I'm aware. The installation using a "flush cart" was supposed to remove all the debris. So far in the 7 heating seasons (including the current one) the system has been in operation we've had one airlock that caused a dramatic loss of output and a "low refrigerant" alarm. The alarm was due to low pressure in the gas circuit due to restricted flow in the primary water circuit - basically no heat to evaporate the refrigerant and so the system thought it had escaped. The airlock was removed and everything returned to normal. I asked if there should be a pressure regulator but was told it was not necessary for the length of loop we have. Apparently it can take a few years for all the air to work itself out - especially as the pressures change between heating and cooling modes. There is an air bleed valve on the pumping module which I check every few weeks and there have been no problems since.
Posted By: topherThe average cost per Kw for the period was 0.06938 Euro...