<?xml version="1.0" encoding="utf-8"?>
	<rss version="2.0">
		<channel>
			<title>Green Building Forum - thickness of Insulation required</title>
			<lastBuildDate>Mon, 18 May 2026 04:32:04 +0100</lastBuildDate>
			<link>https://www.greenbuildingforum.co.uk/newforum/</link>
			<description></description>
			<generator>Lussumo Vanilla 1.0.3</generator>
			<item>
		<title>thickness of Insulation required</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=7715&amp;Focus=115369#Comment_115369</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=7715&amp;Focus=115369#Comment_115369</guid>
		<pubDate>Wed, 24 Aug 2011 00:00:52 +0100</pubDate>
		<author>sinnerboy</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: CWaters</cite>I'm not sure the Building Regs allow you to insulate an existing wall that badly :-)<br /><br />I think the worst it can be is around 0.3 but I haven't been back to check Part L.</blockquote><br /><br />Your right CW - <br /><br />http://www.planningportal.gov.uk/uploads/br/BR_PDF_ADL1B_2010.pdf<br /><br />Table 3 Page 18 looks for 0.3  W/m2K .  <br /><br />It does footnote to state (paraphrase) that the U Value may be reduced where floor areas are affected by +5% reduction . And Item 1.7 page 2 states "the adoption of any particular energy efficiency measure should not involve unacceptable technical risk of for instance excessive condensation" . Page 23 refers to BR 262 Thermal insulation: avoiding risks (2002 edition) for guidance on risk assessment . Anyone have a copy ? ( I don't) . No mention of EN 15026:2007 Hygrothermal Performance Of Building Components And Building Elements - Assessment Of Moisture Transfer By Numerical Simulation - the method (using WUFI software ) that Joseph Little used to prepare his report. <br /><br />Something JL stressed in his report is that " even the closest attention paid to micro issues, such as insulation type and membranes, are not enough if macro issues like driving rain, substrate type & U-value havenâ€™t been dealt with"<br /><br />So as in the case of the OP with a Victorian brick house - I  would  at the very least approach my local BCO with my concerns about the 0.3 W/m2K value. <br /><br />Or find someone expert in WUFI to run a simulation based on local climate data.  Last time I checked there aren't so many such folks around.]]>
		</description>
	</item>
	<item>
		<title>thickness of Insulation required</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=7715&amp;Focus=115371#Comment_115371</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=7715&amp;Focus=115371#Comment_115371</guid>
		<pubDate>Wed, 24 Aug 2011 00:11:17 +0100</pubDate>
		<author>Saint</author>
		<description>
			<![CDATA[Here is someone who has renovated their victorian terrace to passivhaus standards, including 130mm of internal insulation on the front facade: <a href="http://www.treehugger.com/files/2010/02/passivhaus-renovation-of-heritage-home.php" target="_self" rel="nofollow">http://www.treehugger.com/files/2010/02/passivhaus-renovation-of-heritage-home.php</a><br />acheiving U=0.1 <a href="http://ecohome.tumblr.com/page/5" target="_self" rel="nofollow">http://ecohome.tumblr.com/page/5</a><br /><br />Wookey they actually say they used an additional 50mm Kooltherm so 180mm in total. Even so there must be an airspace included as well unless Kingspan is claiming a TC of 0.019W/mK for Kooltherm.......nah they wouldn't]]>
		</description>
	</item>
	<item>
		<title>thickness of Insulation required</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=7715&amp;Focus=115372#Comment_115372</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=7715&amp;Focus=115372#Comment_115372</guid>
		<pubDate>Wed, 24 Aug 2011 00:34:56 +0100</pubDate>
		<author>sinnerboy</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: seanie</cite>Well I think that pretty much answers any concerns about IWI.</blockquote><br /><br />Couldn't agree less seanie ( no offence ) <br /><br /><blockquote ><cite >Posted By: seanie</cite>From the article;<br /><br />"But there is another problem with interior insulation of this magnitude: heat loss through the exterior walls will be virtually eliminated. A little bit of heat loss through old brick walls drives out moisture; if you get rid of it completely, there is the possibility of freeze-thaw cycles causing the brick to deteriorate. Fortunately London doesn't get too many of these." </blockquote><br /><br />1. The UK does not start and finish in London. <br />2. The most substantial risk with IWI is the accumulation of condensation immediately behind the insulation. This will happen even in the absence of freeze/thaw cycles which impact the outer face. And - London's housing stock is old - very old , and very attractive too visually. Taking such time spans into account how many freeze thaw cycles do we responsibly subject this brickwork to ?]]>
		</description>
	</item>
	<item>
		<title>thickness of Insulation required</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=7715&amp;Focus=115373#Comment_115373</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=7715&amp;Focus=115373#Comment_115373</guid>
		<pubDate>Wed, 24 Aug 2011 00:40:47 +0100</pubDate>
		<author>sinnerboy</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: Saint</cite>Here is someone who has renovated their victorian terrace to passivhaus standards, including 130mm of internal insulation on the front facade:<a href="<a href="http://www.treehugger.com/files/2010/02/passivhaus-renovation-of-heritage-home.php" target="_blank" rel="nofollow">http://www.treehugger.com/files/2010/02/passivhaus-renovation-of-heritage-home.php</a>" rel="nofollow" >http://www.treehugger.com/files/2010/02/passivhaus-renovation-of-heritage-home.php</a><br />acheiving U=0.1<a href="<a href="http://ecohome.tumblr.com/page/5" target="_blank" rel="nofollow">http://ecohome.tumblr.com/page/5</a>" rel="nofollow" >http://ecohome.tumblr.com/page/5</a><br /><br />Wookey they actually say they used an additional 50mm Kooltherm so 180mm in total. Even so there must be an airspace included as well unless Kingspan is claiming a TC of 0.019W/mK for Kooltherm.......nah they wouldn't</blockquote><br /><br />I hate to seem not wish this initiative well ... but Sir Humprie comes to mind. " Very courageous ! "]]>
		</description>
	</item>
	<item>
		<title>thickness of Insulation required</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=7715&amp;Focus=115377#Comment_115377</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=7715&amp;Focus=115377#Comment_115377</guid>
		<pubDate>Wed, 24 Aug 2011 07:09:31 +0100</pubDate>
		<author>Dominic Cooney</author>
		<description>
			<![CDATA[I thought U=0.35 for the walls was acceptable for refurb, or has it changed since I worked mine out?]]>
		</description>
	</item>
	<item>
		<title>thickness of Insulation required</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=7715&amp;Focus=115381#Comment_115381</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=7715&amp;Focus=115381#Comment_115381</guid>
		<pubDate>Wed, 24 Aug 2011 07:55:36 +0100</pubDate>
		<author>seanie</author>
		<description>
			<![CDATA[<blockquote >Couldn't agree less seanie ( no offence )</blockquote><br /><br />I was being sarcastic.]]>
		</description>
	</item>
	<item>
		<title>thickness of Insulation required</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=7715&amp;Focus=115391#Comment_115391</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=7715&amp;Focus=115391#Comment_115391</guid>
		<pubDate>Wed, 24 Aug 2011 09:13:50 +0100</pubDate>
		<author>sinnerboy</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: seanie</cite><blockquote >Couldn't agree less seanie ( no offence )</blockquote><br /><br />I was being sarcastic.</blockquote><br /><br /><img src="/newforum/extensions/Vanillacons/smilies/standard/shamed.gif" alt=":shamed:" title=":shamed:" />]]>
		</description>
	</item>
	<item>
		<title>thickness of Insulation required</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=7715&amp;Focus=115394#Comment_115394</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=7715&amp;Focus=115394#Comment_115394</guid>
		<pubDate>Wed, 24 Aug 2011 09:41:48 +0100</pubDate>
		<author>CWatters</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: sinnerboy</cite> 2. The most substantial risk with IWI is the accumulation of condensation immediately behind the insulation. This will happen even in the absence of freeze/thaw cycles which impact the outer face. And - London's housing stock is old - very old , and very attractive too visually. Taking such time spans into account how many freeze thaw cycles do we responsibly subject this brickwork to ?</blockquote><br /><br />I've no idea if this is a real issue but what stops the outer leaf of a modern insulated cavity wall suffering the same fate? They seem to survive ok.]]>
		</description>
	</item>
	<item>
		<title>thickness of Insulation required</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=7715&amp;Focus=115396#Comment_115396</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=7715&amp;Focus=115396#Comment_115396</guid>
		<pubDate>Wed, 24 Aug 2011 09:57:07 +0100</pubDate>
		<author>seanie</author>
		<description>
			<![CDATA[Looking at that project website it's very impressive.  And it shows how challenging the goal was.  Look at how they dealt with the issue of joist ends;<br /><br />"As well as the thermal bridge issue, there is an additional concern - that the joist ends will be exposed to dew point temperatures. Wet joist ends are worrying because the wood can rot and, ultimately, break.<br /><br />Addressing this issue is one of the major engineering challenges of our project, one that we have spent a great deal of time considering and one to which we are applying an extremely innovative solution. In brief, it involves cutting the floor joists away from the external wall, hanging a steel beam off the party walls, insulating outside the steel beam and then hanging the floor joists off the steel beam; i.e. now entirely within the thermal and airtight envelope. As with pretty much everything on this build, there is an enormous amount of fine detail that I havenâ€™t covered here "]]>
		</description>
	</item>
	<item>
		<title>thickness of Insulation required</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=7715&amp;Focus=115406#Comment_115406</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=7715&amp;Focus=115406#Comment_115406</guid>
		<pubDate>Wed, 24 Aug 2011 11:58:30 +0100</pubDate>
		<author>sinnerboy</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: CWatters</cite><blockquote ><cite >Posted By: sinnerboy</cite>2. The most substantial risk with IWI is the accumulation of condensation immediately behind the insulation. This will happen even in the absence of freeze/thaw cycles which impact the outer face. And - London's housing stock is old - very old , and very attractive too visually. Taking such time spans into account how many freeze thaw cycles do we responsibly subject this brickwork to ?</blockquote><br /><br />I've no idea if this is a real issue but what stops the outer leaf of a modern insulated cavity wall suffering the same fate? They seem to survive ok.</blockquote><br /><br />Well the cavity provides a safety release mechanism for water which drains down the inner faces of the outer leaf. From the inside vapour will condense here and so too ,  from the outside , penetrating rain water. The modern brick and mortar fabric can cope better with freeze / thaw action than our historic stock weathered for decades or even centuries . Such uninsulated  walls have coped by absorbing the internally generated heat unhindered by insulation together with ambient external heat outside the heating season - in which case the uninsulated vapour barrier free wall back diffuses i.e. vapour is driven into the building. I hope the old building refurbished to passive standard copes .]]>
		</description>
	</item>
	<item>
		<title>thickness of Insulation required</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=7715&amp;Focus=115407#Comment_115407</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=7715&amp;Focus=115407#Comment_115407</guid>
		<pubDate>Wed, 24 Aug 2011 12:00:36 +0100</pubDate>
		<author>sinnerboy</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: seanie</cite>Looking at that project website it's very impressive.  And it shows how challenging the goal was.  Look at how they dealt with the issue of joist ends;<br /><br />"As well as the thermal bridge issue, there is an additional concern - that the joist ends will be exposed to dew point temperatures. Wet joist ends are worrying because the wood can rot and, ultimately, break.<br /><br />Addressing this issue is one of the major engineering challenges of our project, one that we have spent a great deal of time considering and one to which we are applying an extremely innovative solution. In brief, it involves cutting the floor joists away from the external wall, hanging a steel beam off the party walls, insulating outside the steel beam and then hanging the floor joists off the steel beam; i.e. now entirely within the thermal and airtight envelope. As with pretty much everything on this build, there is an enormous amount of fine detail that I havenâ€™t covered here "</blockquote><br /><br />That is impressive alright. It's akin to constructing a timber framed house within the existing walls. I wonder if they  left ventilated cavity at the interface ?]]>
		</description>
	</item>
	<item>
		<title>thickness of Insulation required</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=7715&amp;Focus=115409#Comment_115409</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=7715&amp;Focus=115409#Comment_115409</guid>
		<pubDate>Wed, 24 Aug 2011 12:24:28 +0100</pubDate>
		<author>brig001</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: sinnerboy</cite>Such uninsulated  walls have coped by absorbing the internally generated heat unhindered by insulation</blockquote><br /><br />Did anyone have heating 100 years ago, or even 50?  We didn't 30 years ago, just a gas fire downstairs.<br />Cue Four Yorkshireman sketch <img src="/newforum/extensions/Vanillacons/smilies/standard/bigsmile.gif" alt=":bigsmile:" title=":bigsmile:" />]]>
		</description>
	</item>
	<item>
		<title>thickness of Insulation required</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=7715&amp;Focus=115415#Comment_115415</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=7715&amp;Focus=115415#Comment_115415</guid>
		<pubDate>Wed, 24 Aug 2011 13:00:07 +0100</pubDate>
		<author>sinnerboy</author>
		<description>
			<![CDATA[Shoebox in't middle o't road <img src="/newforum/extensions/Vanillacons/smilies/standard/bigsmile.gif" alt=":bigsmile:" title=":bigsmile:" /> <br /><br />Luxury !]]>
		</description>
	</item>
	<item>
		<title>thickness of Insulation required</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=7715&amp;Focus=115418#Comment_115418</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=7715&amp;Focus=115418#Comment_115418</guid>
		<pubDate>Wed, 24 Aug 2011 13:32:20 +0100</pubDate>
		<author>SteamyTea</author>
		<description>
			<![CDATA[Had central heating or air conditioning all my life, so did most of the people I knew, even all the local farming folk, but then they were paid for doing nothing in those days I was lead to believe.]]>
		</description>
	</item>
	<item>
		<title>thickness of Insulation required</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=7715&amp;Focus=115422#Comment_115422</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=7715&amp;Focus=115422#Comment_115422</guid>
		<pubDate>Wed, 24 Aug 2011 14:21:37 +0100</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: Saint</cite>Wookey they actually say they used an additional 50mm Kooltherm so 180mm in total. Even so there must be an airspace included as well unless Kingspan is claiming a TC of 0.019W/mK for Kooltherm.......nah they wouldn't</blockquote><br />Where do they say that, Saint? I can't find it. <img src="/newforum/extensions/Vanillacons/smilies/standard/cry.gif" alt=":cry:" title=":cry:" />]]>
		</description>
	</item>
	<item>
		<title>thickness of Insulation required</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=7715&amp;Focus=115424#Comment_115424</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=7715&amp;Focus=115424#Comment_115424</guid>
		<pubDate>Wed, 24 Aug 2011 14:35:10 +0100</pubDate>
		<author>seanie</author>
		<description>
			<![CDATA[http://ecohome.tumblr.com/page/4<br /><br />"These Kooltherm 130 sheets (130mm thick) will go in the roof and the external walls of the top 2 floors. Eventually all the external walls will have it in, topped off with another 50mm, giving them a U-value of 0.1"]]>
		</description>
	</item>
	<item>
		<title>thickness of Insulation required</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=7715&amp;Focus=115445#Comment_115445</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=7715&amp;Focus=115445#Comment_115445</guid>
		<pubDate>Wed, 24 Aug 2011 22:01:11 +0100</pubDate>
		<author>wookey</author>
		<description>
			<![CDATA[The beam across the front taking the joist ends is sat on foamglass bearing blocks to stop it being a thermal bridge itself (and the whole end covered in tescon tape). Impressive attention to detail. I'm actually rather surprised that a couple of foamglass blocks will take that loading but I assume someone's done the sums.<br /><br />It is a thoroughly impressive project, and it will be most interesting to know whether it really does have a problem with facade deterioration or not over the next few decades.  I hope it does work, and I'm glad someone is trying it, but there are good reasons to worry.]]>