Posted By: roseramblerIf a simply solution is what you are looking for, try reducing the load on the heating system. Your woodburner seems to have more KWs output than needed, have you thought about a back boiler on the woodburner (and / or another woodburner) and link in a few rads to it to one side of the house. That means you could focus the heat output to a smaller area, thus more efficent, less noise and more heat.
Only a thought.
I would say also, 10,000kw per annum for a 220 sq m house - is that just space heating, space heating and water heating or all energy.
Most normal houses usually need to throw 15,000 - 20,000kw for energy costs to a family home
RR
Posted By: daysleeperSo unless our AHSPs have a COP over 3 (and bluntly I suspect they struggle to hit 1 in cold weather) then we are being sorely let down.ASHP's are available which maintain their capacity down to -20oC, but you need to read the specifications carefully & you pay for what you get. However, I don't think this is the main issue. Even if the GE215's heat pump was maintaining its 1365W capacity, this would not be enough to keep your house warm. Whoever designed the heating system did not do their sums correctly & they've specified the wrong equipment.
Posted By: davidfreeboroughASHP's are available which maintain their capacity down to -20oC, but you need to read the specifications carefully & you pay for what you get. However, I don't think this is the main issue. Even if the GE215's heat pump was maintaining its 1365W capacity, this would not be enough to keep your house warm. Whoever designed the heating system did not do their sums correctly & they've specified the wrong equipment.
David
Posted By: stonesAs has been said before, exhaust air heat pumps are limited in they can only extract whatever heat is in the outgoing air, and that of course is limited by the flow you set. That said, it would seem logical that the CoP of an exhaust air heatpump / what heat energy the heat pump can produce will remain constant as its supply (air extracted from the house) temperature remains constant.If as in daysleeper's case the ASHP uses the MVHR exhaust then it's inlet temperature, capacity & COP will go up & down with outside air temperature. If there's no MVHR involved then most of the ASHP capacity is going to be used moving heat from the exhaust air to the supply air & very little will be left for DHW. So the problem is one of capacity rather than COP. In effect, almost all the DHW & space heating will be provided by the immersion heaters.
Posted By: stonesIs this better than a direct air source heat pump ? The CoP of air source heat pumps reduce as the ambient air temp reduces. Eventually you get the point where the CoP is 1, and at that point you are as well using immersion. That is the reason Iavoided a direct air source heat pump.But you're using the immersion all the time. In an Exhaust Heat Pump system the ASHP is being used to move heat from the house to the incoming air or from the house the DHW. In either case you have already paid to put that heat there, so you're paying once to put it into the house & then again to move it to somewhere else in the house. If you're using immersion heaters or other electrical resistive heaters then the overall "system COP" will be significantly less than 1.
Posted By: stones As has been said before, exhaust air heat pumps are limited in they can only extract whatever heat is in the outgoing air
Posted By: davidfreeboroughIn an Exhaust Heat Pump system the ASHP is being used to move heat from the house to the incoming air or from the house the DHW. In either case you have already paid to put that heat there, so you're paying once to put it into the house & then again to move it to somewhere else in the house.
Posted By: RobLDo I understand this system correctly - is the MVHR unit exhaust being used as the energy source for the ASHP heating for the house ?
Posted By: daysleepero that is 0.28 to 0.33 Air changes an hour across the house. (seems low to me?)No, that's perfect actually.
Posted By: RobLSurely this exhaust gas, which will be a few degrees above external ambient at a slow flow rate, will be chilled massively below external ambient by the ASHP? Won't this make the ASHP COP very low ?No! Not at all - the ASHP removes the heat from the internal ambient air, it is after that heat has been removed that the exhaust is cold. The COP will be quite high actually. The problem here isn't COP, it's capacity.
Posted By: CWattersBut a lot worse than an MVHR unit with an effective COP of 20 to 30.Posted By: davidfreeboroughIn an Exhaust Heat Pump system the ASHP is being used to move heat from the house to the incoming air or from the house the DHW. In either case you have already paid to put that heat there, so you're paying once to put it into the house & then again to move it to somewhere else in the house.
Better than throwing the heat away though.
Posted By: davidfreeboroughBut a lot worse than an MVHR unit with an effective COP of 20 to 30.No, an HRV system has a COP of less than 1 as the temperature of the air supply back into the house is lower than the ambient temperature. The most it could be is 1.0 - which would mean all the heat from the exhausted air is recovered plus all the waste heat from the motor to operate it.
Posted By: stonesI assume in saying an MVHR with a CoP of 20-30 refers to a passive crossflow type MVHR unit with a 90 to 95% efficency? It may be that this would be the most effective method (with an inline heater to boost temp when needed) of providing fresh warm air into the house, but at some point, the temperature differential between outside air and heat that can be recovered passively will become so much that additional heat is needed to make up the difference (-10 degrees outside, inside 18 degrees for example). Additional energy would be required to lift the temp back up presumably??I'm assuming a 90 to 95% efficient counterflow type heat exchanger. The type used in Passivhaus designs.
Posted By: stonesYou mentioned in an earlier post that a suitable size ASHP for daysleeper would be 5kw, run mainly on E7. On the coldest days(-16 degrees last year), my immersion (5.3kw) was on for 5 hours. I assume an ASHP would need to run for a similair period to heat a tank of DHW?Yes it would need to run for the same time as an equivalent immersion heater but it would consume a third of the electrical power, assuming a CoP of 3. In such extreme conditions the ASHP would need to run for longer than 7 hours &, if the CoP/capacity was to be maintained, it would need to use CO2 refrigerant.
Posted By: Paul in MontrealNo, an HRV system has a COP of less than 1 as the temperature of the air supply back into the house is lower than the ambient temperature.I'm defining CoP as the heat energy moved per second divided by the electrical energy consumed per second. For the design I've been looking at a 90% efficient heat exchanger will recover around 10,000kWh per annum, while the fans consume around 500kWh. I'm characterising this as a CoP of 20 because an exhaust air heat pump in the same position would need that CoP to be more efficient at that job.
Posted By: Paul in MontrealAn exhaust air heatpump, as far as I understand, still has the cross-flow heat exchanger to perform the pre-heat of the incoming air, plus the heatpump itself can extract whatever heat there is between the incoming air temperature and the exhaust air temperature - this is where the heat gain comes from, not from the ambient air of the house itself (except for any latent recovery that takes place).This is the case for daysleeper, but stones is using a pure exhaust heat pump which doesn't have an MVHR heat exchanger & uses a heat pump both to heat the air drawn into the house & heat DHW.
Posted By: RobLDo I understand this system correctly - is the MVHR unit exhaust being used as the energy source for the ASHP heating for the house ? Surely this exhaust gas, which will be a few degrees above external ambient at a slow flow rate, will be chilled massively below external ambient by the ASHP? Won't this make the ASHP COP very low ? Wouldn't an ASHP make better use of external air (admittedly marginally colder than the MVHR exhaust) at a higher flow rate ? To compound using the MVHR exhaust, it will probably be at 100% RH whenever the weather is chilly.This is the situation for daysleeper & I agree that an ASHP placed outside & unlimited by MVHR flow rates would be a better choice of heat source. The one thing you can do for an ASHP is give it an unlimited supply of air & by wrapping it around an MVHR unit or using it as an exhaust air heat pump we are severly limiting its capacity.
A useful check would be to measure the ASHP exhaust air - can that be related back to the ASHP COP ?
I think I'm just actually repeating what CWatters said, now I check his comments!
Posted By: davidfreeboroughFor the design I've been looking at a 90% efficient heat exchanger will recover around 10,000kWh per annum, while the fans consume around 500kWh.So that design will lose 1000kWh per year while consuming 500kWh. That's not a very good COP! The heat is already inside and has been payed for. Your HRV is still cooling your building at a rate of 500kWh a year. An exhaust air heatpump will always be more efficient than this, even without a pre heat of the incoming air as the exhaust temperature is always lower than the inlet temperature. In the HRV case, the exhaust temperature is always higher than the inlet.
Posted By: JSHarris
Those temps seem a bit high to me, for emitter temperatures.