Posted By: daysleeperBy the way the house is about 418 M^3 and apparently this Genvex machine should balance at 120-140 M^3 an hour
So that is 0.28 to 0.33 Air changes an hour across the house. (seems low to me?)
Posted By: JSHarrisModelling this whole system is the challenge, particularly the time-dependent factors through the day (heating demand being out of phase with solar gain, for example), but with an adequately sized thermal store and a careful bit of design and construction it should be perfectly possible to use an exhaust air heat pump very efficiently.I don't want to undermine any of the good work you're doing; it's all good research for your build. However, the Passivhaus people have put a lot of work into simulating low energy houses & they have years of experience of adjusting their simulations to match reality. They have mandated heat recovery ventilation because it is the most energy efficient way of ventilating an airtight building. I suggest using their approach as a starting point & building any DHW/heating system around this.
Posted By: daysleeperJust to put some more context on this... It was rainy here yesterday followed by clear ish skies overnight. MHRV running at 100%, heat pump had been on for a couple of hours but off overnight.Given the limited capacity, I would a leave the heat pump running 24x7 whenever the extracted air drops below a preset temperature.
Posted By: CWattersDaysleeper.. Do you have bedroom doors shut at night? Are they too well fitting? Is it possible the MRHV can't remove the water vapour because doors are shut preventing air circulating from the incoming to extract vents?
Posted By: davidfreeboroughThey have mandated heat recovery ventilation because it is the most energy efficient way of ventilating an airtight building. I suggest using their approach as a starting point & building any DHW/heating system around this.
So that is 0.28 to 0.33 Air changes an hour across the house.- those are plausible numbers but I seem to remember that building regs require a capacity of at least 0.44 ACH (possibly expressed in m3/m2?)
Posted By: roseramblerSo I am paying a blended rate of 10p per KW. If you don't have a thermal store set-up is here a busness case for E7 / E10? Especially if all my other power / etc is electric, and I have my heating when we are up - not in bed?You need storage to make Economy 7 work, a thermal store &/or a well insulated building with high thermal mass. A masonry/concrete build insulated to Passivhaus standards will only lose a couple of degrees a day, so heating timing ceases to be critical & you can pump heat in at the times which are most economical/convenient.
Claims Notification....
...provide to us professional reports at your
expense to verify the claim where it relates
to the performance of central heating,
sound insulation, squeaking floors.
Posted By: Chris P BaconHere the building regs no longer permit the use of air source heat pumps in new houses, as far as HPs go all that is now allowed is ground source or exhaust air.The NIBE website describes this as an exhaust air heat pump. There's no mention of an MVHR type heat exchanger, but a supply air module is available for heating the supply air.
In order to fulfil this demand NIBE has developed the F750 exhaust air heat pump which combines both a balanced MHRV and a 6kw air to water heat pump, the exhaust air temps from which go to about -20 deg C.