Home  5  Books  5  GBEzine  5  News  5  HelpDesk  5  Register  5  GreenBuilding.co.uk
Not signed in (Sign In)

Categories



Green Building Bible, Fourth Edition
Green Building Bible, fourth edition (both books)
These two books are the perfect starting place to help you get to grips with one of the most vitally important aspects of our society - our homes and living environment.

PLEASE NOTE: A download link for Volume 1 will be sent to you by email and Volume 2 will be sent to you by post as a book.

Buy individually or both books together. Delivery is free!


powered by Surfing Waves




Vanilla 1.0.3 is a product of Lussumo. More Information: Documentation, Community Support.

Welcome to new Forum Visitors
Join the forum now and benefit from discussions with thousands of other green building fans and discounts on Green Building Press publications: Apply now.

The AECB accepts no responsibility or liability for any errors or omissions in the content of this site. Views given in posts are not necessarily the views of the AECB.



    • CommentAuthorEd Davies
    • CommentTimeJan 19th 2012
     
    By my rather crude approximation, a 10mm pipe with 40 mm of insulation at 60 K above ambient would lose 1 K about every 25 seconds. Obviously at more reasonable temperatures it takes a bit longer. Still, ten minutes of cloud....
    •  
      CommentAuthorJSHarris
    • CommentTimeJan 19th 2012
     
    Interesting; seems surprisingly high to me, even for the steep part at the start of the exponential curve. What value of decay constant did you use?
    • CommentAuthorEd Davies
    • CommentTimeJan 19th 2012 edited
     
    Here's my calculation, all done per metre of pipe:

    10 mm O/D, 8.8 mm I/D, 61e-6 m² cross-section.
    Density, 1000 kg/m² and SHC 4180 J/kg·K so linear heat capacity 255 J/m·K.

    40 mm of insulation with a conductivity of 0.04 W/m·K - wild guess, probably a bit too conductive but also a bit thick. U value 0.04/0.04 = 1 W/m²·K.

    Crude approximation by ignoring the fact that there's less area on the inside of the insulation than the outside: assume the area of the insulation is the area half way out, radius about 25 mm (half 40 mm plus radius of pipe) so 2·PI·r = 0.16 m²/m so heat loss is 0.16 W/m·K.

    At 60 K temperature difference heat loss is 9.6 W/m.

    (255 J/m·K) / (9.6 W/m) = 26.56 seconds/K
    •  
      CommentAuthorJSHarris
    • CommentTimeJan 19th 2012 edited
     
    The snag I can see there is that the cooling of the pipe when the pump is turned off will follow Newtons Law of Cooling, where the rate of heat loss at any instant is proportional to the temperature differential at that instant. This will give an exponential curve, where as the pipe cools the rate of heat loss drops, so slowing the rate of cooling. To solve the differential equation we need the decay constant, k, which short of going and measuring it experimentally it I'm not sure how to derive.
    • CommentAuthorEd Davies
    • CommentTimeJan 19th 2012
     
    But we're only looking for rough orders of magnitude.

    Anyway, supposing we did want a bit more precision then the maths is probably not too hard but using a computer is even easier:

    > function tempLossRate(temp) { return 0.16/255 * temp; }
    > var dT = 1.0;
    > var t = 0.0;
    > for (var temp = 60; temp > 0; temp -= dT) {
    ... console.log(temp, t);
    ... t += dT / tempLossRate(temp);
    ... }
    60 0
    59 26.562499999999996
    58 53.575211864406775
    57 81.05366014026885
    56 109.01418645605833
    55 137.47400788462977
    54 166.4512806119025
    53 195.96516950079138
    52 226.0359242177725
    51 256.68496267931096
    50 287.93496267931096
    49 319.80996267931096
    48 352.3354728833926
    47 385.5385978833926
    46 419.4481723514777
    45 454.0949114819125
    44 489.5115781485792
    43 525.7331690576701
    42 562.7971225460423
    41 600.7435511174708
    40 639.615502336983
    39 679.459252336983
    38 720.3246369523677
    37 762.2654264260518
    36 805.3397507503762
    35 849.6105840837096
    34 895.1462983694239
    33 942.0212983694239
    32 990.3167529148784
    31 1040.1214404148784
    30 1091.5327307374591
    29 1144.6577307374591
    28 1199.6146272891833
    27 1256.5342701463262
    26 1315.562047924104
    25 1376.860124847181
    24 1440.610124847181
    23 1507.016374847181
    22 1576.3098531080504
    21 1648.7530349262322
    20 1724.6458920690893
    19 1804.3333920690893
    18 1888.2149710164576
    17 1976.7566376831244
    16 2070.5066376831246
    15 2170.1160126831246
    14 2276.3660126831246
    13 2390.2052983974104
    12 2512.801452243564
    11 2645.613952243564
    10 2790.5003158799277
    9 2949.8753158799277
    8 3126.958649213261
    7 3326.177399213261
    6 3553.8559706418328
    5 3819.4809706418328
    4 4138.230970641833
    3 4536.668470641833
    2 5067.918470641833
    1 5864.793470641833
    7458.543470641833

    So it's down to 40 °C after 10 minutes, at 20 °C after half an hour and 6 °C after an hour.
    •  
      CommentAuthorJSHarris
    • CommentTimeJan 19th 2012
     
    Looks reasonable as an approximation, although I'd still like to measure the rate of cooling to get a feel for the value for the decay constant, k in the cooling equation, dT/dt = k.(T1 - T2)
    • CommentAuthorEd Davies
    • CommentTimeJan 19th 2012
     
    Doesn't k = 0.16/255 = 0.000627 K/(s·K) = 0.000627 s⁻¹ ?
    •  
      CommentAuthorJSHarris
    • CommentTimeJan 19th 2012
     
    <blockquote><cite>Posted By: Ed Davies</cite>Doesn't k = 0.16/255 = 0.000627 K/(s·K) = 0.000627 s⁻¹ ?</blockquote>

    Yes, possibly, but the reasons I'd like to do a measurement to confirm it are that the U value of the insulation will vary with temperature a bit (the range is outside that where we can presume it's reasonably constant, I think) and the copper pipe will add a small bit of thermal capacity. It's probably a moot point, anyway, as there are undoubtedly much big sources of performance variation in any given system.

    I remember calculating the rate of heat loss for a cup of tea years ago (trying to demonstrate that putting the milk in first kept the tea hotter for longer to resolve a small domestic disagreement) only to find that the actual rate of cooling when I did the experiment (two identical mugs filled with hot water one with milk, the other without, and a data logger hooked up to two temperature probes) was quite a lot different in practice to that predicted.
    • CommentAuthorTimSmall
    • CommentTimeJan 19th 2012 edited
     
    Posted By: JSHarrisbut the saving is so modest when compared to 15 mm pipe that I doubt it's worth worrying about unduly


    It is a small effect overall, but given that (assuming that you've decided to use copper anyway) - the 10mm is both much easier to install than the 15mm and also better performing, why bother with the 15mm?
    •  
      CommentAuthordjh
    • CommentTimeJan 19th 2012
     
    Posted By: Ed Davies13 2390.2052983974104

    Impressive precision!

    Crude approximation by ignoring the fact that there's less area on the inside of the insulation than the outside

    There's a specific formula for the Y-value of pipe insulation (I think they're called Y-values when they are linear rather than U-values for areas). I expect it's on the Navi site somewhere or else google will throw it up. I do remember there are magic values involved ('critical radius').

    And Tim, yes!
    • CommentAuthorEd Davies
    • CommentTimeJan 20th 2012 edited
     
    Posted By: djh
    Impressive precision!


    Well, yes, I did wonder if +/- 1 microsecond would be good enough. :bigsmile:


    There's a specific formula for the Y-value of pipe insulation (I think they're called Y-values when they are linear rather than U-values for areas). I expect it's on the Navi site somewhere or else google will throw it up. I do remember there are magic values involved ('critical radius').


    Yes, I have seen that somewhere but was just doing a quick and dirty calculation so didn't bother to search. It's a bit magic as I recall as it only needs the ratio of the inner and outer radii, not the absolute values, as the scale cancels with the circumferences if you see what I mean.

    Yep, Wikipedia says:

    http://en.wikipedia.org/wiki/Pipe_insulation#Heat_flow_calculations_and_R-value

    This has some significance here. 20 mm of insulation on a 10 mm pipe will be coming up to twice as effective (from the W/(m·K) point of view) as 20 mm of insulation on a 22 mm pipe.
    •  
      CommentAuthordjh
    • CommentTimeJan 20th 2012
     
    It's even more magic than that. Adding a bit of insulation to a pipe actually makes it lose MORE heat than before. The rate of heat loss increases up to the 'critical radius' and then starts decreasing. Some extra thickness later it gets back to just losing as much heat as the naked pipe and after that more insulation actually does something useful.

    http://www.raeng.org.uk/education/diploma/maths/pdf/exemplars_engineering/2_SteamPipe.pdf

    (or see p72 of http://web.mit.edu/lienhard/www/ahtt.html)

    and just to illustrate what a dodgy place the internet is, have a look at this one, which gets it totally wrong: http://www.reviewpe.com/penotes/heat_t/b5_3.htm and even wikipedia gets it partly wrong http://en.wikipedia.org/wiki/Heat_transfer#Critical_insulation_thickness
    • CommentAuthorwookey
    • CommentTimeJan 20th 2012
     
    That's quite remarkable, and most unintuitive. The maths in that paper had integrals in it which is where I always lose the plot. Why does a small amount of insulation make things worse?
    •  
      CommentAuthorJSHarris
    • CommentTimeJan 20th 2012 edited
     
    Thanks for posting those links. Don't you just love it when you find something like that out? I hadn't for a moment thought about the increase in surface area effect, but having read that I'm now sitting here scratching my head and wondering if dementia is setting in early.............
    • CommentAuthorEd Davies
    • CommentTimeJan 20th 2012
     
    Posted By: wookeyWhy does a small amount of insulation make things worse?


    DJH's last link (Wikipedia) explains it very succinctly.
    • CommentAuthorpmusgrove
    • CommentTimeJan 20th 2012
     
    Fascinating stuff but the good man from Rolls-Royce was interested in steam pipes of radii 60mm. The graph we need to see is that relating to water at about 65C in a pipe of radii 15mm. Has anyone worked those figures through the formula to find out the critical thickness of insulation?
    • CommentAuthorwookey
    • CommentTimeJan 22nd 2012
     
    DJH's last link (Wikipedia) explains it very succinctly.


    True, but he posted that with the caveat that it's 'partly wrong', so I wasn't sure how correct it was. So the explanation is that surface area increases faster than heat-transfer attenuation to start with. Fair enough. Now DJH needs to say what part is wrong.
    •  
      CommentAuthordjh
    • CommentTimeJan 23rd 2012
     
    Posted By: wookeyNow DJH needs to say what part is wrong.

    I already did, on the Talk page :bigsmile:

    The description on this page is wrong.This sentence has the logic reversed "The point where the added resistance of increasing insulation thickness becomes overshadowed by the effect of increased surface area is called the critical insulation thickness." It should read "The point where the added resistance of increasing insulation thickness overcomes the effect of increased surface area is called the critical insulation thickness."
    • CommentAuthorcrusoe
    • CommentTimeJan 23rd 2012
     
    Pedantic semantics aside, plastic pipe (mlcp) is used in places with as much sun as Mallorca, and has survied several seasons to my knowedge. I've had to add to such systems, and had to use the same material, to avoid ripping out and starting again. But in principle, copper or ss - depending on your ideology - neither has massive advantages - are the materials for the job.

    Many panels stop at a max 180C, (30C direct sun, not your usual UK conditions) many have drainback, with oversize storage so temps can't reach stagnation levels, so use of plastic in some parts (return) of a system may be countenanced in future legislation. But to be safe here, for all classes of reader, we're better sticking to metal.