Home  5  Books  5  GBEzine  5  News  5  HelpDesk  5  Register  5  GreenBuilding.co.uk
Not signed in (Sign In)

Categories



Green Building Bible, Fourth Edition
Green Building Bible, fourth edition (both books)
These two books are the perfect starting place to help you get to grips with one of the most vitally important aspects of our society - our homes and living environment.

PLEASE NOTE: A download link for Volume 1 will be sent to you by email and Volume 2 will be sent to you by post as a book.

Buy individually or both books together. Delivery is free!


powered by Surfing Waves




Vanilla 1.0.3 is a product of Lussumo. More Information: Documentation, Community Support.

Welcome to new Forum Visitors
Join the forum now and benefit from discussions with thousands of other green building fans and discounts on Green Building Press publications: Apply now.

The AECB accepts no responsibility or liability for any errors or omissions in the content of this site. Views given in posts are not necessarily the views of the AECB.



    • CommentAuthorhowdytom
    • CommentTimeNov 7th 2008
     
    Somehow I lost this post for 6 months, could it be PASH ?(passive annular simple head). what great links and info folks.
    I'm about to start some bore holes this winter and find out what the subsoil depth is etc. we are on boulder clay with limestone base, I put some deep drains, 100m away and slightly (3meters) down hill from the proposed heat-store site, several years ago. we got 5 meters down and were still in clay, that was the limit of the digger and deeper than we needed for that job, while they were their it was worth the extra time as I was hoping to find the limestone !.
    So I'm proposing drilling holes 100mm dia and lining them with stainless steel pipes, I was aiming for a depth of 6 meters (6 months @ 1meter/month) and then having a coil in the bottom meter of the liner circulating an antifreeze solution from solar panels during warm weather. perhaps a solar powered pump would be sufficient in a closed circuit. The question is how many bore holes and at what spacing ?. the building is 10m x 5m approx with open land east,south and west.
    Tom
    • CommentAuthormike7
    • CommentTimeNov 8th 2008 edited
     
    Hi Howdy

    It would be great if a proposal such as yours could work, but I urge you to be cautious. My own calculations suggest that a 50m2 presumably well insulated building is just too small to be viable for interseasonal heat storage (unless you're rich) because too big a proportion of the heat saved in summer will leak away before it can be recovered in winter.

    What works for a project like Drakes Landing where there are 50 plus houses won't scale down well to a single house because the dimensional scaling also affects the timescale, by something like a factor in the region of 5 in my Drakes Landing/Howdytom comparison. So if you have 49 willing neighbours, or can move to somewhere with a 70 day year, you'd be better placed.::sad:

    I'd be delighted to be proved wrong.

    Edit: PS havn't heard from Zenbiscuit lately. I fear the worst for his project, which was even smaller.:sad::sad:
    •  
      CommentAuthorfostertom
    • CommentTimeNov 8th 2008
     
    mike7, we didn't complete our previous discussion about this. You showed me that the temp gradient gets steeper (square-law curve) as you move in from infinity to the core of the heat store. But to me that doesn't prove your point about losses only becoming acceptable the bigger the store volume is; i.e. that single-house schemes are doomed. Given sufficient time (years) the temp gradient will get steadily flatter and flatter, so loss steadily diminishes. That's true even if that very flat curve is steeper near the core - despite that fact, it can still get very flat even close-in.
    • CommentAuthormike7
    • CommentTimeNov 8th 2008 edited
     
    Hiya Tom
    My formula was for a steady state, ie what the system will tend to after an 'infinite' amount of time, when the thermal inertia of getting the surrounding earth charged up to its ultimate steady temperature has been overcome. The leakage in earlier years will be higher than djh's or my formula gives, as extra heat is required to charge up the regions beyond the working heat store.

    I wouldn't say that single house schemes are necessarily doomed - just that the smaller you go, the harder it is going to be, and the crossover from no-go to go will depend on many factors - local conditions, climate, soil type, house size, comfort level, definition of 'viable' or depth of pocket, etc.

    One situation which would help a single house scheme would be if all your neighbours just happened to do the same. A whole bunch of small schemes close togther would behave much like one large one. ( This is the opposite of GSHP schemes, where it can be to your disadvantage if your close neighbours do the same).
    • CommentAuthormike7
    • CommentTimeNov 9th 2008 edited
     
    Tom - sorry but the answer really does lie in the maths.... eg. if the store was one-dimensional, say a long perfectly insulated rod, then it would work as you suggest. In two dimensions apparently it would too, although I find this harder to visualise. Also, it would approach the steady no-leakage state much more slowly, if I'm getting it right.

    The third dimension of a real store gives a solution which has a continuous leakage at final steady state. Hence your problem.
  1.  
    I have been waiting for someone to simulate thermal storage with dynamic software?

    The key would be to be able to simulate for at least 3 years but 5 would be better.

    Fostertom, are your projects getting any further ahead?
    • CommentAuthorMike George
    • CommentTimeNov 10th 2008 edited
     
    Posted By: Jeff Norton (NZ)I have been waiting for someone to simulate thermal storage with dynamic software?


    Love to! and I have done some preliminary stuff. Unfortunately require funding to take it further. To my mind there is several YEARS of research [and software development] before we are at a stage where we can confidently predict results with DSM software.
    • CommentAuthorshelterre
    • CommentTimeNov 10th 2008
     
    Jeff, I have been following this long thread with interest. One of the best performing buildings in the UK which uses PHS is the Mile End Ecology Park Building, London. It uses the six metre umbrella insulation rule, is partially earth sheletered and uses earth tubes connected to an MVHR system for heating and cooling. I was involved in monitoting this building with the sustainability team at BDP a few years ago (the then director was part of the orginal design team for the Mile End Building). This previous project was modelled partly in TAS (2D) and Ambiens (CFD).

    The findings of the Mile End Project contributed to my own modelling methidology when I modelled the use of Trombe walls and thermal stoarge with a dynamic thermal simulation software application (TAS) nearly ten years ago, as part of my PhD (a study of the design and thermal perfomance of two-storey earth sheltered housing for the UK climate) and as a result set-up a module teaching dynamic thermal modelling for building services engineers and architectural technologists at the University of Glamaorgan in 2001.

    I joined UWIC in Cardiff earlier this to establish a research group in the architectural department and one of the applied research/enterprise services which is feeding directly into teaching our architectural technologists is dynamic thermal modelling. In fact I am currently leading UWIC's input into a four year UK government funded research project led by University of Salford to develop a software application for modelling urban regeneration and UWIC is contributing the building thermal performance modelling amongst some other modelling techniques for projects at the ealry stages of the masterplanning/design stages, see www.suregen.co.uk.

    We may be able to look at your query as part of a student project/research in the new year, particularly as I am currently developing a Professional Doctorate in Ecological Building Practices, which is being validated by UWIC in January 2009. My University contact email is jlittlewood@uwic.ac.uk.

    John
    • CommentAuthorEd Davies
    • CommentTimeNov 10th 2008
     
    I too started some thermal simulation software with a view designing a PAHS type house then dropped the matter a bit over a year ago when I had an attack of common sense and decided that the whole thing was too risky. In particular, I was worried about having to dig the whole thing up again if it was found that water was flowing through the bit that was supposed to be storing heat.
      1998-08-03.jpg
    • CommentAuthormike7
    • CommentTimeNov 10th 2008 edited
     
    Edit: Puerile harrumph. Deleted
    • CommentAuthorshelterre
    • CommentTimeNov 10th 2008
     
    mike7, I will pass your comments on to Wates and Arups, I am sure they will be delighted that you are calling them academics. You might have missed the point about SURegen, it is funded by the government (£2.5M) and by industry £500K and is designed to benefit industry. It is a project that has been created in partnership with leading practioners over the past few years.
    • CommentAuthormike7
    • CommentTimeNov 10th 2008 edited
     
    Ph.D as previous
    •  
      CommentAuthorfostertom
    • CommentTimeNov 10th 2008 edited
     
    Posted By: shelterreOne of the best performing buildings in the UK which uses PHS is the Mile End Ecology Park Building, London
    Gorgeous buildings/bridge, but things have moved on quite a bit since then, haven't they? What's the state of the art now?
    •  
      CommentAuthorfostertom
    • CommentTimeNov 10th 2008
     
    Posted By: Jeff Norton (NZ)Fostertom, are your projects getting any further ahead?
    Workin' on it, Jeff!
  2.  
    How many years before I (as oppossed to some expert - acedemic or not) can get an indication of how much money I might save by making my 2 top stories (SE and SW walls) Trombe walls (about 100m2 worth not including glass)? The aim of this stuff being, I hope, to make a difference to the people a fit further down the food chain - and I don't mean at the bottom just not people doing energy calcs as a reguler part of ones life.
    •  
      CommentAuthorfostertom
    • CommentTimeNov 10th 2008
     
    What kind of kit are you meaning by Trombe wall? What will you do with the heat it collects? store it, if so for how long; or dump it into the building immediately? or 6 hours later?
  3.  
    I don't want to hijack this thread but this topic has the information:

    http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=2849&page=1#Item_11

    Which is making progress but its painful.
  4.  
    Thanks for all your reply's, it all sounds reassuring for ground thermal storage but it seams it will take a while. I will make contact with John and see if a project of mine can be used for student dissection (fingers crossed).
    • CommentAuthorshelterre
    • CommentTimeNov 14th 2008
     
    Jeff, please do get in touch: jlittlewood@uwic.ac.uk.
    • CommentAuthormike7
    • CommentTimeNov 24th 2008 edited
     
    Another bash at the algebra approach while you wait for somebody to sort some software:-

    The viability of smaller scale annual heat storage will depend on the proportion of heat collected that leaks away before it can be used. Here's my effort at estimating the proportion. I've tended toward generous assumptions in the process, so my results are likely to be nearer the best possible outcome.

    The results support what I have been saying, ie that the smaller the store is, the harder it is to make it viable, but I don't know enough about the costs to say where the cross-over might be - and for some people costs may be secondary.

    Enjoy!
    Or not - found I can't get the file uploaded.
    • CommentAuthormike7
    • CommentTimeNov 24th 2008 edited
     
    Try it longhand:-
    The store is a complete sphere radius r1 immersed in an infinite field of uniform properties:
    Conductivity K = 1.0 W/mC. Vol. Spec. heat V = 2.0 Ws/m3.C 10*6

    The temperature distribution in the region beyond the influence of the annual fluctuation is in a steady state, i.e. that which the system will tend to eventually.

    Far ground temp T0 = 10C, Store minimum T1= 30C, Max T3= 70C, store average T2= 50C.

    Store capacity Qs = 4/3pi.r1^3 V (T3 - T1) Ws which is 93.r1^3 kWh

    Heat loss rate = 4pi.K.r1(T2 -T0) = 503.r1 W
    Therefore annual loss QL = 365.24/1000 (503.r1) = 4400.r1 kWh

    r1 can be eliminated using the above to give QL in terms of Qs:-

    QL = 970.(Qs)^1/3 kWh (that's the cube root of Qs there)

    With this I can make a table of the total heat input required annually for various sizes of heat store:-

    Qs 10,000 kWh......QL 21,000........Qtotal 31,000 ie multiplier of 3.1
    ....20,000 ...............26,400.................46,400....................2.3
    ....50,000................35,800.................85,800....................1.7
    ...100,000...............45,200................145,200....................1.45
    ...500,000...............77,200................577,200....................1.15

    Note that a complete sphere will have lower losses than a real store even if insulated.

    If the outer limit were say 10 times the r1 radius instead of infinity, the losses would only be about 10% greater - it just makes the maths easier.

    Soil properties chosen are on the favourable side, but not the best. This is the formula if you want to try different values:

    QL = 1224K(Qs/V)^1/3 kWh

    Using a different value of T3 doesn't affect the results much. 30C seemed the lowest realistic value for T1 unless a heat pump is used.

    I've been assuming that all the central store capacity is available to meet the heating load, and none is required to buffer the heat loss, other than that provided by the zone between the core and the steady state region (marked A and B on a diagram I have yet to post). My assumption may be wrong.

    Hope this helps!
    • CommentAuthortony
    • CommentTimeNov 24th 2008
     
    Brilliant -- so to store 25000 kWh ( I only need 8600 out again) how deep a borehole should i go for?
    • CommentAuthormike7
    • CommentTimeNov 24th 2008
     
    Note please that my various caveats mean that you will need not less than 25000 kWh - how much more you'd actually need I don't know. I wouldn't fall off my chair if it turned out to be twice as much. Nor do I know how to calc the borehole design, but a bunch of shorter holes would be better than one long, perhaps in a wigwam-style pattern to reduce losses near the surface.

    How far down before you hit water where you are?
    I salute your indefatigability!
    •  
      CommentAuthorfostertom
    • CommentTimeNov 24th 2008
     
    mike7, one thing I don't get about this discussion - if we're talking about storing heat into the ground at an insertion point, which spreads out to create an in-ground store of heat which is boundary-less, then who's to say how 'big' the heat store is? The heat store, with its notionally single insertion point, doesn't 'know' whether it's being fed from a single-house scale of solar collector, or a 100-house estate. Other than your assumption that there's an active sphere of storage surrounded by primeval subsoil, and your further assumptions of various notional sizes for that sphere, how do we know what 'size' the system under mathematical scrutiny is? In fact there's no meaningful boundary between an active sphere of storage, and its surroundings - it's a continuum that with time evolves a smooth square-law temp gradient curve, from the insertion point, eventually out to infinity!
    • CommentAuthormike7
    • CommentTimeNov 24th 2008 edited
     
    The size of the usable core of the store depends on the details of the heat delivery/retrieval system.
    I'm assuming an array of pipes (not a single insertion point) within the core so that ideally all parts of the core will achieve the max temp when full, and the min temp when empty, during a typical yearly cycle. Surrounding this core is the A and B labelled zone or shell which will respond to the annual fluctuation of core temp, but to a lesser extent the further out one goes.(Using the 6 metre per year rule of thumb, one could suppose this shell might be around 3 metres thick). Outside this AB shell, the annual fluctuation would not be felt, as indicated in my graph of temp versus radius.

    The curve is perhaps more neatly described as a plain old reciprocal curve ... T = Constant/R. The heat required to build up this 'bund' of temperature has of course been built up over several - or many - annual cycles until the steady state is approached. At the steady state, the gradient the reciprocal curve MUST have to satisfy the maths of a spherical geometry is the gradient that gives rise to the continuous heat loss, oozing away in three dimensions rather like a puddle of spilt oil would in two (but the curve would be different!). The bund thus needs fresh dollops of heat annually to maintain its 'height'.

    I hope this clarifies it. Pip pip :wink:
    •  
      CommentAuthorfostertom
    • CommentTimeNov 24th 2008
     
    Thanks mike7.

    A 'useable core' defined by the extent of an array of pipes - I'd be more interested in the point of insertion of heat as just that - a single point - with temp effects spreading progressively/continuously out from that. Or if greater heat transfer area reqd, then OK an array of pipes, but no assumption that to be 'useable', all parts of a core must achieve 'max temp when full, and the min temp when empty'.

    The AB zone I'd say is too thin, even within a simplified approximation. Not sure of the 3m rule of thumb, any more than the 6m one. At any rate, the 'beyond', where 'the annual fluctuation would not be felt' should be much further out, I'd say.

    Seems that your estimates of loss versus size are v much determined by these assumptions, which I appreciate are most helpfully estimated so as to get a 'scale of' approximation. Fundamentally, is it fair to say that any notion of 'size' depends upon a non-continuous model, with discrete zones proportioned to approximate to continuous reality?
    • CommentAuthormike7
    • CommentTimeNov 24th 2008 edited
     
    Thanks fostertom!

    A single point source would have too high a temperature: T = Constant/R, so small R means high T.

    Doesn't have to be all at the max/min temp, but the sums are easier. And the store is more compact, the losses lower.

    Further out? Too thin? Maybe, maybe not. Show me your sums!

    "Is it fair to say...." Sorry, you've lost me there. But one thing a canny store designer/user might do would be to charge the centre of the core first, and draw on the outer regions of the store first. That might help a bit. We need it.
    • CommentAuthormike7
    • CommentTimeNov 30th 2008
     
    <blockquote><cite>Posted By: fostertom</cite>

    Seems that your estimates of loss versus size are v much determined by these assumptions, </blockquote>

    I don't agree. My estimates are determined by the basic characteristics of the system, but with a degree of inaccuracy which will be determined by the fairness of the assumptions. Not the same thing. On the other hand it seems your assertions are based on ... well ...what?:wink:
    • CommentAuthorhowdytom
    • CommentTimeDec 9th 2008
     
    My conclusion so far.
    Instead of bore holes/ducts (fairly expensive), if I dug a trench say 4m deep by 1m wide 4m long (house foot print app 10m x 7m) down the center of the foundations and installed a water storage tank a 1m tall by 800mm wide 3.8m long,

    then insulated the sides and top with 100 PUR and back filled.

    I could then charge it during summer with an indirect coil to allow stratification, eventually the whole tank would heat and thereby transfer some heat downwards into subsoil. from that point the 6m rule will/should kick in.. etc,etc.

    Having a liquid store makes good sense for DHW with a smaller tank/coil upstairs, maybe even UFH.

    Your excellent comments please... I'm trying to keep up with them, but need to read them several times before they sink in

    Tom
  5.  
    Your store is hopelessly small - it's just over 3000l which, if you charge it up by 20C, will give you about 70kWh of capacity, or 140kWh if you can charge it up by 40C or 210kWh if you can charge it up by 60C. How long do you think that would last you? A few days at most in winter I'd think. This is assuming you wouldn't want to cool it below about 20C (otherwise it wouldn't be heating the ground below it).